riandanualdy
modbusrtu How to connect omron CP1E with modbus RTU
25 posts in this topic
Hallo, i want to connect PLC Omron CP1E to indicator weighing scale with modbusRTU connection and i have a CP1W-CIF11 module to connect indicator with CP1E. ,but I have no experience in RTU modbus communication in the PLC.
How do i start?
*i just need output:
1. Coil (Reference No = 0. Output bits) for input switch with address 3 (Tare).
2.Input Status (Reference No = 1) for output lamp with address 17 (stable)
3.Input register (Reference No = 3) to read data with address 5 (gross weight)
4. holding register (Reference No = 4) to write comparison data with address 17(over)
page 85 - 94 in attachment
ad4402_manual.pdf
How do i start?
ad4402_manual.pdf
Please check this manual below about Modbus RTU Easy Master at section 14-4 page 245 - 253
https://assets.omron.eu/downloads/manual/en/e480_cp1e_users_manual_en.pdf
1 hour ago, riandanualdy said:
how about wiring CP1W-CIF11 if my indicator is use 3 wire (A,B,ground)?
You don't need to connect SG please follow this connection below
CP1W-CIF11     <------------>       AD-4402
RDA-  <------------>   SDA
RDB+  <------------>  SDB
If it cannot connect swap cable
RDA-  <------------>   SDB
RDB+  <------------>  SDA
i done use
RDA- <--> SDA & RDB+ <--> SDB
or
RDA- <--> SDB & RDB+ <--> SDA
and i use this cx programmer, but the a641.00 value is not 1 but the a641.02 value is 1 and if i check memory a641.02 is 90.
what should i do now?
modbus coba coba euy (2).cxp
59 minutes ago, riandanualdy said:
i done use
or
There are Error Code Response Timeout please check communication parameter (Baud Rate, Data Bit, Stop Bit, Parity Bit) that match setting with CP1E and AD-4402
You should use A641.00 to A641.02 that belong to Optional Serial Port If you use A640.00 to A640.02 It is belong to Built-in RS-232 Port.
Maybe you should check program as below and clear PLC Memory (There are some random data on D1300 - D1400) and download project again.
modbus coba coba euy V 3.cxp
i try your ladder diagram and i change wiring SDA- to A and SDB+ to B or SDA- to B and SDB+ to A is connected and indicator of com in CP1w-cif11 is on. yesterday i think the wiring is wrong and now is correct. but now if i check in memory d1305-d1349 it's cannot change (Screenshot_27.png), what should i do?
if i want to display data address 3,5,7, is it already correct my cx programmer?
Thank you
Please check that you config Modbus parameter on AD-4402 match with CIF11 parameters and set D1300 to #0001 that means Modbus slave address 1.
modbus coba coba euy V 4.cxp
i think cx programmer is work, and the output is in memory d1355 or more. but i have a question, why the output is just <1 second and after that back to "0", how to repair that?
thank you
example: 5 second still "0" after that output is "1234" after < 1 second back to "0".
i just want the output "1234" stay >1 second
Edited by riandanualdy
Please change D1303 to #0005 and D1304 to #0006 then check D1350 should be 1 and D1352 should be 0 and D1354 to D1359 should be data that read from AD-4402.
Please capture data monitor screen to check result.
sir, the problem is change value the memory just <1 second so i can't print screen the memory, how to show the value for >1 second ?
15 minutes ago, riandanualdy said:
this is the result of your cx programmer and i change D1303 to #0005 and D1304 to #0006  . the 4402 show the value of scale is 20,68kg
D1355 is #0008 D1356 is #1400 When you combine it will be #0814 that equal 2068 at decimal (use calculator in program mode).
For decimal point number read address #0001.
can you explain me about function of memory d1302,d1303,d1304,d1305 ?
i know this cx programmer for input register, because i still confused for coil, input status, and holding register how to use it in cx programmer?
coil work like switch, holding register is to write and read data, input status is like output lamp (indicator lamp)
Thankyou
Thankyou
For Function of D1300 to D1304 describe as follow
D1300 --> Slave Address
D1301 --> Function Codes (01, 02, 03, 04, 05, 06, 16)
D1302 --> Number of Communication bytes (count byte data from D1303 to Finish byte for example use D1303 and D1304 are 4 bytes [1 word = 2 bytes])
D1303 --> For Function Code 04 (Read Input Registers) are Start Address that you need to read
D1304 --> For Function Code 04 (Read Input Registers) are number of address that you need to read
For other modbus functions please check this manual first to understand about modbus data frame for each function
http://modbus.org/docs/Modbus_Application_Protocol_V1_1b3.pdf
Finally i can use the modbus all of them, Thank you and have a nice day
Hi Wasan & Riandanualdy,
I have been reading your topic and it helps me a lot to establish my connection, I have "CP1E-N60DT-D" and a modbus RTU RFID device.
I followed your " modbus coba coba euy V 4.cxp", I have a comm and see it flickering. The only problem is A641.00 gets stuck on ON status, and just flickers. I'm not getting any response at all from DM location D1350 onwards, I got zero values. Unfortunately, I cant attached the forum isnt allowing me.
I only got the response when I stop the CPU, and A641.01 turns ON. I got 2 questions;
1. From your program the bit "W0.01" on when A641.00 turns ON. Shouldn't this bit place on the "W0.15"  as the manual said so?
"Turn ON A641.00 (Execution Bit) to send command data stored starting at D1300." I am confused.
2. How will I fix the issue whereby I only got response when I stop the CPU?
Thank you very much, still learning here.
Cheers :)
Hi @M302015 You need to understand data on OMRON Modbus first. Start by config communication data on D1300 - D1304
D1300 --> Slave Address of your RFID Device
D1301 --> Assign Function code that you need (I guess maybe 03 or 04 please check RFID manual)
D1302 --> Number of communication bytes assign 4 byte from D1303 - D1304
D1303 --> Start Register : Assign first RFID register to read
D1304 --> Number of address : assign how many data to read
Hi Wasan/Fellows,
My communication is doing good now using CP1L-EM to an RFID via Modbus RTU.
I am using the second serial port with 19200, 81E, Serial Gateway. Sometimes it works for an hour, and suddenly just stops as I can see A640.02 turns ON, and the COMM indicator no longer flickers.  I got an error code of "0x80 - Response timeout". I am thinking about lowering the baud rate. Do I need a terminating resistor? Please advice.
Thank you very much.
Cheers :)
RFID CP1L-EM_Mod4_2.cxp
@M302015 It is up to how cable quality or cable length or are there noise in system. First you may try to increase timeout for wait longer response. If not may be you can reduce baudrate. You will need terminate resistor when your cable have very long length or to balance impedance on your cable.
Hi Wasan,
You're so helpful, I need to check on that.
I may need your help. I need to manually clear the RFID tag, to an 8 register. Can you please share the exact code for it?
I'm using the serial port 2 for CP1L-EM, I would be glad for your help.
Thank you so much.
Regards :)
Hi,
I would appreciate for your suggestion. The main issue is, I need to clear the RFID UID after I read it.
Im trying to read an RFID, and the read section works fine.
But the clear or write function turns on A640.02 when W0.05 manually set ON.
Kindly advice.
RFID CP1L-EM_ReadW.cxp
