9pol
FX3U-ENET-ADP Connection Problem
I try to use FX3U-ENET-ADAP (Ver 1.22) with FX3U-16M (Ver 3.15) for Ethernet Data Monitoring.
I use GX Works2 (Ver 1.98c) to Configure the parameter. The parameter as follow.
57298b925f9f1_Setting1.PNG.b738120624e40
57298b95dcdb9_Setting2.PNG.6d0629eb1ea97
After write the parameter to PLC and Turn off and on the PLC. I cannot connect to PLC via Ethernet port.
And the LED status ERR. on as follow.
IMG_20160504_115858.thumb.jpg.858ea38933
I try to use Ethernet diagnostics tool to check the problem but no error show as follow.
57298b990464d_Diag1.PNG.9a13a87429ae2ae2
57298b9b6958a_Diag2.PNG.4bb7e3af842732ec
57298b9de3f38_Diag3.PNG.e9a878ff76cd7476
The Connection Status shown "Connecting" and "Disconnected" when I remove a cable.
57298ba0e7542_Diag4.PNG.37bb526329f4aa4a
Anyone has experience with these device? Please advise me how to configure the system.
Thank You.
Edited by 9pol
Is the Error led flashing or on continuous?
If it is flashing than you have a parameter setting error.
Maybe it is the port parameters. The 5000 and up are usually used for Mitsubishi Software. So that might be the same as the Melsoft connection (I suggest you try 4000)
Edited by Gambit
may be RJ45 connecter terminal is not right ?  "T568A " or T568B"?
Change the E-net ADP port to 5556. This should fix the routing.
F.Y.I. If you had a SFM E-net module that module's port is typically 5551.
