BIGEYE
SLC 5/04 Major Error
12 posts in this topic
I have an SLC 5/04 going in to fault and cannot find the cause. The error description reads: A minor eror bit is set at the end of the scan. refer to S:5 minor error bits. When I reset the fault and switch back to RUN, the plc goes in to fault immediately. The only way I can get the PLC operational is to download a backup of the PLC code to the PLC. However, after a couple of days, the same fault comes back again. The column of boxes at the left shows a 1 in only the Major Error Halt S:1/13 if this is of any significance. Appreciate any help on this one. TIA
Hi Bigeye, Normally on SLC's system bits S:20 and S:21 can point you to the problem. S:20 is the rung and S:21 is the Routine. These values are at the bottom of the status screen where you see the S:1/13
Thanks for that, I have the PLC up and running just now and will check if/when it fails next time and get back.
Also check S:6 to see what fault you're dealing with. Then goto the help and search Faults. Might just be a mathoverflow fault... Should point you in the right direction.. Once you find out what fault you're dealing with, write us back and we'll help. Regards,
We've had this scenario happening for three months in a row a couple of years ago...Whatta pain!.... Someone did some "test programming" and forgot to either suspend the new logic or properly complete it. It was a CTU without a RES instruction!!!! It had a PRESET of 32767 and it counted every minute interval. So, of course, every twenty something days it was taking down the SLC in which's functional logic was residing! Downloading a back-up file will evidently place a lesser value within the counter's ACC bin and everything will be fine untill the ACC will become larger than PRE! Search the C:6 (and any other C: type )Data File and make sure every used counter has a RES instruction implemented (and functional) within the ladder logic. Edited by dmargineau
HMMM? A counter should not cause a fault when it's ACC exceeds its PRE. Also it should not cause a overflow when it reaches 32767, it will turn negative and continue counting towards zero. Someone correct me if I'm wrong. Edited by Mickey
Nope the CTU ACC exceeding the PRE should not fault the controller.
Mea culpa... It's been a while since the incident... The ACC value of the CTU was being used as the PRE of a TON. Of course, when the CTU ACC rolled over to negative values, the above mentioned TON wasn't defined anymore, causing an immediate hard fault within the processor. Most of the processor's "un-resetable" hard faults I have encountered, presuming functional hardware, were caused by Math Overflows and by timers with negative PRE values.... Edited by dmargineau
I have gotten into the habit of using LIMs, GRTs or GEQs in front of every DIV with a non-constant divisor, and in front of every Timer.PRE calculation...sometimes it's simpler to do the math and then limit check/clamp it. An ounce of prevention... Edited by OkiePC
Correct me if I am wrong, but but isn't S:5 the bit address for the Mathoverflow Trap. If this is the case you should take your process and safety considerations into account, but if you cannot find what is causing this issue, which it is likely it is not a program issue at all but a field device, you can get around this problem until you find the cause by adding an OTL S:5 at the end of your program. Hope this helps, and forgive me if I am wrong.
follow up I meant OTL S:5/0
I think you meant OTU at the end of file 2 and I would think the math overflow is a programing issue and not a field device but I have been wrong before.
