Sign in to follow this  
Followers 0
Newbie System Designer

Hot Standby Question

6 posts in this topic

Hi, Just want to confirm if is it possible to add a modbus connection to a Hot Standby configuration (Quantum) with existing Remote I/O drops. The CPU Module is 140 CPU 67 160. I also used a Ethernet Module (NOE 771 01) for the network communication. The specs say that I should connect the CRAC Units via modbus cable to the CPU's. Is it possible since the CPU module has a modbus port? If yes, do I still need other modules (specifically for modbus connection) ? Hope that someone can help me. Edited by Newbie System Designer

Share this post


Link to post
Share on other sites
sure you can. You have an integrated modbus port. You could even configure the switchover of the addresses if the cpu swapped to the other.

Share this post


Link to post
Share on other sites
Correct me if I am wrong, will I use a splitter (for MODBUS) to be able to connect it on both primary and standby CPU?

Share this post


Link to post
Share on other sites
The modbus port master could have addresses from 1 to 119, automatically the modbus port standby will have address master+128. ie mb master = 1 mb standby = 129 So both ports could be connected to the same serial bus because their addresses are managed by the hot-standby system. You can use any modbus equipment but remember that the integrated CPU modbus port are RS232C so you need to configure previously in rs485. I don't know what you mean with "splitter", you have to create a multi-drop 485 bus. you could use i.e. the SCA62 and two cables VW3A8306 for connecting the quantum cpu's

Share this post


Link to post
Share on other sites
Modbus is an RS-232 serial comm link. You cannot "parallel" the connections. They must be isolated with a modem of some type. As mentioned the address' will (if selected to) be offset by 128.

Share this post


Link to post
Share on other sites
Just in case (see above) you have to convert your electrical signal from RS232 to RS485 link with for example the XGSZ24 RS232/485 converter (just to stay in Schneider house) or others

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!


Register a new account

Sign in

Already have an account? Sign in here.


Sign In Now
Sign in to follow this  
Followers 0