Search the Community

Showing results for tags 'universal serial to ethernet'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 309 results

  1. I want to establish Ethernet IP communication between the following PLC CPUs. Schneider Electric - BMEP582040 Honeywell - ControlEdge UOC CPU900-CP1. Where the Schneider must be master and Honeywell must ne adapter. Let me know if anyone have done this or can help me to do so.
  2. QCPU to 2x kyence iv2

    Hello all, we are using Q03UDECPU and via built-in ethernet port its connected to two IV2-G30. (through unmanaged switch) to establish connection we are using FB LQnUDEEthActive (hereinafter referred to as  FBLQ) two instances of FBLQ in two instaces of our FB which is responsible for creating messages that are then send via FBLQ Both keyence devices have different IPs, ports and connection number. Problem is that it is working flawlessly, except the time its not working :/ from time to time it simply doesnt trigger Keyence device. It looks so far like its independt of turning machine OFF/ON, also both keyence devices are used in different times (about 10-20seconds of difference) Im currently working on sime kind of internal diagnosis to see whats happening when its not working, but im just curious if there is something obvious we are missing? any help will be apreciated Thanks  
  3. Fatek Ethernet PLC Module online

    Dear All,  Anybody can help me in communication between Fatek 20MAR2 & CBEH2A. The jumpers setting are JP1 is on left two pins (No password protected) & JP3 is on right two pins (forced boot operation mode). The Ethernet cable i used is type b T568. Fatek Ethernet module config software detecting module successfully (shown in attached pic) but on online PLC via ethernet cable its showing connection failed.   please help   thanks in advance
  4. hello Every one,    I am using a CP1-L PLC and want to communicate to domino ax350i printer over TCP/IP socket programming. For socket programming, I used Omron Function Block CPU012_SendCommand.  I defined network ID and node address. However, I am getting 0502 error which means routing table is not set yes. So, how can I set routing table for both devices?. my PLC on 192.168.250.1 and Printer is on 192.168.250.123 node 7000.    Can any one suggest me best way to do.  Thank you   attached file is for what I did in setting and program for the communication.      
  5. Monitouch HMI slow screen

    Hi there! I'm having some issues with a FUJI MONITOUCH V9100iSD HMI that communicates with a CJ2 PLC via Ethernet. This HMI is a migration from a previous V810iSD model. The thing is that the previous model worked correctly, but when using the new one, the HMI seems to be pretty slow when switching screens, for example. All parameters are the same, and after reading Fuji's FAQ, I've run out of ideas. Have you faced the same problem? Thanks in advance!
  6. FX3U to FX3U via wifi

    Good day fellow PLC ninjas! I have a question/ concern which I would love your opinions on. We have 3 FX3U PLC’s+ENET cards. Two of the 3 PLC’s move around in an EMS trolley. The other is a ‘base station’ with a GOT2000 connected via Ethernet. Base PLC IP = 192.168.1.11 HMI IP = 192.168.1.31 Carrier 1 IP = 192.168.1.61 Carrier 2 IP = 192.168.1.62 I have programmed the base PLC to use Active communication; we are using fixed buffer communication to send and receive data to/ from the Carriers. The carriers are set up as Fullpassive ‘slaves’. This part works well and the update time changes (using a counter in the base station) from 1s to 100ms (because it enters a different work station).  My issue is the following: using a network sniffer (WireShark), I pick up plenty of re-transmits and sequence number errors coming from the base PLC’s ENET card. This is troublesome and causes delays when the update time is required to be fast (100ms). I am sending and receiving 10 words of data. The wifi seems stable, and there is minimal noise in the area. The power has been turned down and the antennas used are suited well for the application. The antennas are at a similar height to minimize possible loss of signal. I have LOS (line-of-sight) to the carriers at all times; to at least one of the antennas (I am using 802.11n). Has anyone picked up issues or found settings which can be used for comms over wifi? I can easily do this using a S7-1200 Siemens PLC and have done so using 12x S7-1200 clients and 2 AP’s with 1 base PLC. I have also successfully done this using 8xFX3U client with a System Q base PLC. My suspicion is that the delay in reading and writing to/ from the BFM in the ENET card is causing this. I am not sure that if I change to a FX5U will help. The communication cards on the Mitsubishi PLC’s seem very limited. Does anyone have any technical details on the access times between the CPU and communications cards’ BFM? Help is as always, appreciated.
  7. CP1L Unknown IP

    Hello. I have CP1L EM30 with unknown IP. I have tried to use "Direct Ethernet Connection" with "Network Browser" but with no success. I have manually set the ethernet IP4 address to 192.168.20.20 / 255.255.255.0 I've got error: "The OMRON Ethernet Direct Connection Manager service is starting in Safe Mode because Windows APIPA is enabled. (0x82020003)Omron.Cxmw.Modules.SystemLibrary.SysLibException" The PLC does NOT have default ip 192.168.250.1. What Can I do? Please help. Thanks. BR, Andrej.  
  8. Hi all, First i apologise for my english, but it's not my main language. I am very new at this world so sorry if my question is too newbie but i have been for several hours trying to get some data from an Omrom NPX1P2 DT-100 using Ethernet/IP and now i am a bit desperate. I am trying to connect this PLC using a C# Library provided by steffan rossman and it seems to be very easy,  i can manage to connect it but every try i do to request data it fails. As i can see there are several ways to get the data, for example: In this example the function GetAttributeSinglec(ClassID, instanceID, attributeID) i need the ClassID, wich i don't know what is, the instanceID, i think in my case is 100, and the attributeID wich i don't know what is or where to define. If someone could help me about how to request data it will be very appreciated. Thx in advance    
  9. My HP laptop will lose communication with Mitsubishi PLC occasionally after removing ethernet cable to download from WiFi. Our company limits the ability to use the wi-fi when I have an ethernet cord connected to my laptop, it has to do with security. If I am connected to the Mitsubishi PLC, then want to download another file from our autosave, which we connect through the wifi, I have to remove the ethernet cord from my HP laptop to enable the ability to go wireless, however sometimes when I attempt to go online with the PLC after I re-connect my ethernet cable, GX developer will not allow it. I can ping the plc and even go online with other PLCs on the network, but for some reason, the one I was connected to will not connect. I restart my computer and even re-download the file again from autosave but no joy. Its not until an unknown amount of time that it will allow me to re- connect, its as if I lose the socket connection on the plc and it needs time to reopen. I talked to our IT department and they have no ideas. Thank you in advance for any help on this matter.
  10. Digital sealing

    Hi, I'm trying to figure out a way to make an automatic digital sealing for a NX-controller. Functionality: Each time I do a remote connect and/or change to the program on the PLC via VPN/Tosibox I want a counter to automatically increment. This counter is the digital sealing (checked by the authorities from time to time), and is displayed on a HMI. When the sealing breaks, the new value of the counter has to be reported. I've been thinking about incrementing the counter each time the Ethernet port on the PLC registers a rising edge on online establishment. But this will not work if there is a power failure (then the counter will increment unitented), or someone by mistake unplugs and replug the Ethernet cable. Antoher idea was to ping a specified IP-address, but there seems to be no PING-functionality. I've also been thinking about using some program data (i.e. last modified), but it seems there's no system variables on the PLC that contains this kind of information. Any ideas how to solve this in the PLC? Basically I want to know if the PLC program has been changed or if there a specified IP-address has been connected to the PLC-network.
  11. How to scan Ethernet/IP network?

    Scenario: You show up on site and the only knowns are Omron PLC and EtherNet/IP network. You have a laptop loaded with CX-One, an ethernet cable, and the ethernet port that is connected to a known EtherNet/IP Omron network (you can not see the PLC). I have previously worked with Siemens systems and used Primary Setup Tool and Proneta with wonderful results. Do similar tools exist for an Omron environment?  Question: How to (relatively quickly) scan an EtherNet/IP network for connected devices without knowing their ip addresses?  
  12. Have been able to exchange data types of BOOL, INT,  DINT & REAL between Omron NJ/NX CPU with Allen Bradley Logix CPU's with Ethernet/IP using the CIPUCMMRead & CIPUCMMWrite instructions. I now have a need to exchange "STRING" variable types. Have tried varions string lengths in the NJ without sucsess. AB default string length is 82 & Omron 256 but I think the difference is the length headder that AB has with within their String Tag type. I know I could convert my strings to an array of bytes & sent them this way, but was looking for a solution to sent them as native strings. Hope someone out there has done this & can share their leg work? 
  13. Hi all,   Is it possible to simulate LMC058 PLC with ethernet in soMachine software. I want to test the logic written in PLC which uses tcpudp library.
  14. I have a 2 CompactLogix PLCs running right now, communicating CIP Safety and Standard data over Ethernet I/P.  For reasons I can't explain right now, the IP address of the second one HAS TO change semi-randomly (the 1st PLC is static).  Setting the 2nd PLC's IP to static or assigning it a static DHCP address is the obvious solution, but for the purpose of this question, that cannot be done. Is there a way to programmatically change its IP address on the 1st PLC's program?  (There is an HMI attached to the 1st PLC and adding a screen to enter in the new address would be trivial.)  The only bit I'm still missing is how do I change the IP address on the module in the 1st PLC so that it's pointed at the right IP address of the 2nd one when it changes.    I found instructions on how to use msg instructions, but that hasn't worked yet.  Any help would be appreciated. Thanks!
  15. I have an Ethernet/IP bus and system including Ethernet/IP devices with CPU 1756-L81ES ControlLogix. PLC is connected to the switch. Bus is built from the switch as a line. Can I connect the last device on the bus back to switch again? In thes case bus will be ring. Do I get problems with connection it this way. Switch is Stratix 2500, which is lightly managed switch. I believe it will increase the traffic in the bus.
  16. HOW CAN I USE NETWORK I/O ON LADDER SOFTCOMFORT?

    Hi! I was doing an project using function block, but at one point it became too complex to use FBD so I would like to use ladder.  I'm using an ihm and that's why some inputs are of the network type, in FBD, it's easy to use the network i/o, but in ladder, the network inputs, where I receive data from the ihm, don't have outputs for me carry out the logic. How can i do this? USING FBD USING LADDER As you can see, theres no output on network analog input, on the digital to!
  17. Is there any way to monitor ethernet/ip bus, states or faults and to make an alarm to the panel alarmlist. I am using IO-stations (1734-AENTR) and I would like to monitor somehow the system. I feel that reading the slot status of the 1734-AENTR device is not enough, because it is not possible to monitor all the cards in a slot. How to get alarm on a screen if I lose any station on the ethernet/ip bus?
  18. Hi there, I am fairly new to programming serial communications, especially with Mitsubishi PLCs. Can someone walk me through in ladder logic how to bring in ASCII to the PLC, store the data in the data registers. Then send the data out to another PC once an 'X' input is satisfied? ASCII code would go like the following: C2,0,1,123,2,ABC,3,456,CR
  19. Hi, I have the following configuration where 4 PLC panels, with each having a Q12PH CPU and QJ71E71-100 module. All these QJ71E71-100 are connected to a HUB using straight cable. From the HUB one connection is going to an I-Fix SCADA which is already communicating with all 4 PLCs using MC protocol. I want to send data from 3 of this PLCs to the 4th PLC in the same network using fixed buffer communication. Can anyone provide a sample program for the same. Send and Receive side. I am using GX Works 2 for programming. Your help is very much appreciated.
  20. Hello guys. I have problem create communication between Omron FQ2 camera and Allen Bradley PLC. Can anyone advise me ?  I set it up according to this manual: ftp://85.129.89.106/Vision/FQ/Communication/EthernetIP/FQ2%20to%20AB.pdf.      
  21. I need to know what kind of connector/cables i can use for my network: Topology, ( all on one switch): * Ethernet: FX5U, GOT, Safety PLC (WS0-GETH00200) * CC-Link: 2X  Inverters FR-A840-00023 Does this systeem needs the RJ45 4wired  or  8wired cables/connector?
  22. HI All,  I have an issue with my SCU32 communication.  Back ground Two SCU32s  (top and bottom side) connected via a 1100M datacable  using port1 ( 9600bps,  8-2-E, start code FF, end code FE, Tx save to d1000-d1200 , Rx save to d2000-d2200). PORT2 of bottom SCU32 is connected to a compass( 2 wire, 8-1-N, 19200 bps, serial gateway MODBUS ). Refer to photo Issue  Without compass, the receiving data at top is very stable and is didn't see any fluctuation. But if is compass is connected at bottom side port2, there is a fluctuation at the top side RX data(specifically d2000-d2005 ) .  I checked the data a bottom side TX (d1000-d1200) and it is stable. Only after sending the data and Receiving at Top side, then only the starting words fluctuate. I am not sure sure what is wrong, I am using logical ports for the DTXDU/DRXDU and compass.   Appreciate all your feedback and suggestions.  
  23. I am trying to connect an Advantys RIO island with a STBNIC2212 ethernet/IP to a Omron CJ2 PLC. I need an EDS-file for the Omron Network Configurator but the Advantys Configuration Software will only export to .xsy for NIC2212 (Ethernet/IP), only way to get an EDS is to substitute the NIC with a NDN2212 (DeviceNet), but I doubt that will work in the Omron Network Configurator. There is an EDS file on the SE-website, but it seems to be a different setup than my island. I thought ethernet/IP should be easy :( Any suggestions? Geir
  24. Hello all, I am working on a project where I am communicating with a Mensor CPT6100 pressure transducer using a Micro-850 PLC. For this, I have used an AWA instruction to write some ASCII characters to the sensor. The sensor then responds to the write instruction by sending ASCII characters to the RX buffer and I used ACB and ARD instructions to read the ASCII characters. Now, I have set the ACB trigger type to 0 (msg triggered only once) and it successfully reads from the sensor. However, when I set the ACB trigger type to 1 (msg triggered multiple times), I do not get any reading in the ARD block. As a matter of fact, the ACB Q bit switches off every time the program is executed when the trigger type is set to 1. I am trying to get continuous readings from the sensor, but when the trigger type is set to 0, the program latches on to the first and only reading and it won't change. My question is, how can I change my program so that it can continuously and autonomously read from the sensor without me having to manually trigger the AWA and ACB instructions every time. I am attaching the program to this thread for your reference.  ASCII_Test_Copy.ccwarc