Search the Community

Showing results for tags 'unit setup not accepting ip address'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 49 results

  1. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.
  2. CX-Supervisor 3.4.1

    Hi After updating CXS to ver. 3.4.1 I can't see point address I can see them when I editing but in the list form only the array len. is shown. When I enter a new point I can see the address. Anybody now hove to solve that ? Banker
  3. Double address - Alarm

    Hello, I would like to see your logical opinion about this situation and in which part of system where I need to find solution - software or in the physical field. Subject: Twelve old system based on Mitsubishi PLC AnS series, Profibus Here is pneumatic transport, with 5 lines, each line have a shredder and discharge valve. A few months ago, when line 1 works , display shows line 2 and vice versa, it was first problem, but the system was still working. From the last week system doesn't work. On the display appear line 3 in works, but system can not started. Alarm shows Double address (perhaps two valves have some address), Alarm still appear after reset and even all lines are turned off. What is your opinion where to find proble (PLC, I/O moduls, cables,...)  
  4. Hello.   I'm trying to communicate between two PLC's  using FINS function block _CPU011:ReceiveData.   PLC1: IP 192.168.1.50 (MASTER)   PLC2:IP 192.168.1.51 (SLAVE)   If I don't use »IP Address Table« everything works using NODE number &51.       The problem is that on the real project these two PLC's will be on different subnet.   For example:   PLC1: IP 192.168.1.50   PLC2: IP 192.168.2.50   So I will have to use »IP Address Table« to achieve communication between these two PLC's.   I tried to sett IP Address Table on MASTER: Node 1=192.168.2.50   But If I try to communicate I see that packet is sended to network but I've got error #1005.   Do I have to sett the SLAVE IP Address Table?   Hoe to do this?   What are the right settings for MASTER and SLAVE IP Address Table?     I'm attaching pictures of CARD settings.  I don't want to use CX-Integrator because I would like to make project to UPLOAD and forget.       Thanks.  
  5. Dear all, I'm first time using M580 (hotstandby). Now finish the configuration, but the problem is how to write the address for Digital Input, Digital Output, Analog Input, and RTD module in elementary variable ? I try to put name DDI_1 and the address is same with M340 topology like %I2.1.0.1.1  and for digital input but got message after build : {Elementary Variables}    :     The instance is located on an address that isn't configured. :     DDI_1 Thank you for your advice regards  
  6. Dear all Please identify me i am having one Issue in my PLC.When I changed the IP of my plc then suddenly its showing error ERH its mean IP address wrong but  My CPU setting is same like previous means unit no=0, x16^0=0 ,Node=x16^0=1  and IP is 192.168.0.15 Mask add.255.255.255.0. but when I, transfer to PLC (in Program Mode) its not transferred(Failed to Transfer) please rectify me where I am doing wrong.
  7. I READ IN THE MANUAL FOR THE CJ2M-CPU34 THAT IT IS POSSIBLE TO CHANGE THE IP ADDRESS BY WRITING TO D30098 AND D30099 (MY DEVICE IS UNIT 0).  I TRIED TO DO THIS ON A TEST PLC BUT AM NOT HAVING ANY LUCK... I WROTE MY IP ADDRESS #C0A8 TO D30098 AND #0E30 TO D30099 (IP ADDRESS 192.168.14.48) WITH THE CPU IN PROGRAM MODE, I SET THE RESET BIT (A501.00) TO TURN ON ON THE TRAILING EDGE OF THE FIRST SCAN BIT, I CAN TELL THE CARD RESETS BECAUSE I AM CONNECTED VIA ETHERNET AND I GET DISCONNECTED, BUT THE IP ADDRESS DOES NOT CHANGE.  IS THERE ANY WAY TO CHANGE THE IP ADDRESS WITHOUT CX-PROGRAMMER?  I NEED TO GET A SOLUTION TO MY CUSTOMER TONIGHT AND MY SUPERVISORS DO NOT WANT TO RELEASE OUR DEVELOPMENT CODE TO THE END USER.   THANK YOU!!!
  8. FR-DU04 (FR-A500) vs FR-DU04-1 (FR-V500). Programming unit differences. (A VSD question) What is the difference between these units? Why are they not interchangeable. (Other than the fact that the FR-DU04-1 is used for vector VSD applications, and the FR-DU04 is intended for standard induction motor applications. Is this a matter of firmware differences?
  9. I have entered the messages many times into the Alarm Setup but every time i re-open the alarm setup, every message that has the Trigger Value=1 will be deleted.  Anyone have a similar issue?
  10. hi.  i want to make some program that work with indirect adress. example, i make program with many much type. I make with Got-1000 mitsubishi.   can you bring me some example? i am sorry, my english is Bad
  11. HI Everyone,  Recently i have bought a plc fx3ge and gt2000 hmi .the problem is that whenever i use a device address d280.b1 in hmi .i am not able to use the same address in gx works for plc (LD D280.1).can anyone help me with this problem.   
  12. Ring main unit switching devices have three position designs - closing- opening and earthing.. anyone know more about earthing ?
  13. PLC setup error location

    Dear sir, how to solve this problems non fatal error 9b, Omron cpu44 c200hx
  14. CPU 948R

    We have Redundant S5- CPU948R we have the requirement of knowing input address for FUM signals(Open & close signals).. Also how can we identify which cpu is acting as main CPU and which one is Standby. We look forward to a solution. Kindly advice us.
  15. Hello, we have 6 encoders and 2 of them lose their mac address every time power goes out. The other encoders find their Mac address by themselves. Can anyone help me with this issue? Thanks for reading. Have a great day.
  16. How do I assign an IP address to an S71200 CPU for the first time? Is it possible to do it over ethernet? Thanks in advance!
  17. RENU FP3035-5 and FL005-0808p

    Hi, Can anyone tell me how to get the FP3035-5 and FL005-0808p to talk to each other via the com1? may be a sample program would be nice. thank Arie
  18. CPU 314IFM adress

    Hi, I have a CPU 314IFM order number 6ES7 314-5AE10-0AB0 when i select it in hardware config it show I/Q adress 124 -155 while it should be to 129 only (the manual mention that and it covers all inputs and outputs and the special funaction also) I try (offline) to change the order number only (another 314IFM) found it give different address range for each CPU while it all have 20 DI/16DO 4AI and 1AO
  19. Hello, At the plant I work at there are devices with IP addresses starting with 192.168.0, 192,168.1, and 193.168.2 The SLC in question is on 192.168.2 We would like to access it from our laptops which are on 192.168.0 The laptops have their subnet mask set to 255.255.252.0 and we are able to pull see other controllers on the 192.168.2 network. However, for some reason we can't with this one, not even when I'm plugged directly into the Ethernet port on the controller unless we change our IP address to one on 192.168.2 I believe the subnet mask on the controller isn't set right. Can anyone tell what I'm missing here? Here's an overview of the current settings: Laptop: 192.168.0.20, 255.255.252.0 Controller: 192.168.2.17, 255.255.252.0 Any help would be greatly appreciated. Ben
  20. Good morning, I'm having an odd issue with CX Programmer and have hit a wall. I'm trying to upload a previous version of a program to an existing PLC (CS1G-H CPU42) and I keep getting the following error when I compile while online: "The read protection properties which are not supported by the connecting target PLC are set. Check the unit version of the PLC." This prevents the program from being uploaded. I have a first revision CS1, manufacture in 2005 from what I can tell. This exact program has been uploaded previously, but a modified version replaced it recently and I need to go back to the older version. Things I have tried so far. without success: - Removed UM Protection - Made sure Task protection is off for all tasks - Check DIP Switch #1, which is write protection, and made sure it is off - Used "Remove Password" and "Release access" functions from the PLC/Protection menu - Used the auto-verification to confirm the configured PLC is correct - Reuploaded a full backup of H & D memory, from the older program I am able to compile the program when offline, but it chokes when online. I am connecting to the PLC via a serial cable. I haven't found any help from the CX Programmer help, or the CS1 programming and operation manual. This error message is nowhere to be found. Anyone has a clue ? I'm at a loss right now. Thank you !
  21. Hi. I have a ST-Lite Ethernet base (STL-ETH1) with 1 16 bit digital in card, 3 digital out cards, 2 analog in and 2 analog out cards. I have a Q03UDE CPU (Q PLC) with 1 16bit digital in and 1 digital out card. Now I like to setup the remote I/O (STL-ETH1) mapped to the Q PLC via the ethernet port on the CPU. Is it possible not to use Modbus at all. I don't want to go and buy a Modbus Ethernet card now. Have someone done this before?
  22. I need to set up D/A module. I have few questions. What is the difference between offset and gain setting mode? I would like to use range 0 to 10V which would have to be set as user range setting, can I do it using GX Works 2? Or do I have to use the GX Configurator-DA package?
  23. How to know what is my Megelis IP address?