Search the Community

Showing results for tags 'siemens logo memory card'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 247 results

  1. A1S68AD CARD

    Hello. I have a system in which an A1S68AD card is used, that card has been damaged . I replace that damaged card with the new A1S68AD card with same wiring and same setting of dip switch. But at channel number 3 there is a RTD connected which gives 4-20 mA signal. But in Plc at channel number 3 the data register is showing -2400 fixed value all the time and in actual the temperature is varying. But PLC SHOWS FIXED VALUE OF -2400. PLEASE HELP ME OUT.
  2. Hello guys, I have an application with a Delta PLC (slave), Load cell module and Delta HMI.  The problem is that the Delta PLC has to report to the already existing platform of Siemens S7 PLC (Master) with Profibus. The Master (Siemens) writes and reads data from the Delta PLC. The question is, how can I set up the Profibus communication? Are there any documentations about the Memory Mapping, configuration etc. There are some modules for Profibus Slave from Delta but I cannot find any references or anything. Thanks in advance.
  3. I have an analog output card 1734-OE2V and there is in the fault/actions page parameters for program mode. What is program mode and when it is activated? Fault mode is clear but... Program should be written the value, but when this happens?
  4. CJ1G-CPU42H BACKUP

    Hi,  I have CJ1G-CPU42H plc, when I try to backup the program it just fails at step 6 as indicated in the attachment, 6- plc memory  ##error aborted ##
  5. I am setting up a vision inspection station which will require me to have 3 independent jobs within the camera. I am using 2 Cognex 9912, a Cognex 2000, and a S71200 PLC. Cognex has sent me a copy of the job call FB, but it is giving me fits. There are several tags referencing a data base called Insight1_Inputs, when I try to create a data base with this name it will not allow me. Any help would be greatly appreciated. I can upload pictures if needed. thanks in advance 
  6. communication

    i want to communicate ml1400/compact logix L24ER to simatic s7200 via ethernet.Please help me with it i am new to it and dont know how to do it.
  7. HOW CAN I USE NETWORK I/O ON LADDER SOFTCOMFORT?

    Hi! I was doing an project using function block, but at one point it became too complex to use FBD so I would like to use ladder.  I'm using an ihm and that's why some inputs are of the network type, in FBD, it's easy to use the network i/o, but in ladder, the network inputs, where I receive data from the ihm, don't have outputs for me carry out the logic. How can i do this? USING FBD USING LADDER As you can see, theres no output on network analog input, on the digital to!
  8.  Hello!   I was trying to communicate my siemens logo with an kinco hmi but this error are appearing on the hmi, what am I doing wrong? Im using an ethernet hub! ETHERNET SETTING ON THE HMI THE PUSH BUTTON THAT ACTIVATES M1 THE LAMP THAT'S REPRESENT "Q4" AND THAT I DON'T KNOW HOW ITS WORKS BUT I JUST PUT ON THE SCREEN TO THE PROGRAM ON LOGO SOFTCOMFORT I JUST SET THE LOGO AS SLAVE WITH THE HMI IP THE LOGO IP AND THE ERROR MESSAGE
  9. LOGO!SoftComfort - Help with Analog Instructions

     Hello! I was trying to configure an Temperature Sensor using the Analog Threshold Trigger to parameters and output activation but, when I put this function on the program, there's just input point, on the output there's no way to link to an DO, when I select the other one's analog function's to see, they all have the same problem. How can I fix this?
  10. Logo mem card

    Hello,      i have one questions. Is possible upload program from  SIEMENS LOGO MEMORY BATTERY CARD ? If is possible ... how?    Thank you for your help.       Regards Beny
  11. Siemens S5-95U PLC and Battery Concern

    Hi All, We have a hydraulic press that is being controlled by Siemens S5-95U PLC . Lately the S5-95U has been randomly stopping during operation thus causing the hydraulic press to stop running. However the S5-95U instantly returns to RUN status after stopping. This is the first time it has happened after a decade of service. Prior to the random stops issue, around January 2021 the S5-95U completely stopped and the program in the RAM was erased so we had to replace the PLC battery and restore the program with our backup. Strangely, the PLC battery we replaced still had 3.4VDC upon checking. What's even more baffling is that even after we replaced the PLC battery with a new one,  Battery LED is still yellow although the program is still retained in the RAM. In summary, we have two concerns: 1. S5-95U randomly stops and resumes during operation ever since we were forced to replace the PLC battery and restore the program. 2. PLC battery has been replaced but the Battery LED is still yellow but the program is still retained in the RAM.   I have a suspicion that the two concerns I mentioned above are somehow connected but I lack the technical expertise to diagnose. I'm hoping someone can help me figure out our issue. Worst case, I think our S5-95U needs to be replaced.   Thanks,  
  12. MPI Connection problem

    Hi there. Recently I've experienced problems when connecting to a S7-300 PLC via MPI/PROFIBUS. I use a PG with CP5711 processor. The thing is that I'm able to connect when I plug the 6ES7901-0BF00-0AA0 cable (male to male) directly to the PLC connector, but when I try to do connect to a PLC that has any device connected to the DP port (let´s say an inverter or HMI) I get 33:17075 error. PG/PC Interface it's correct, in fact another PG with the same configuration is able to connect through the already connected DP device's cable. Station number and transmission rate is all correct.  So I tried the Simatic NET Diagnostics Test and I got error 0x0313 and since the mentioned parameters are correct I refered to this link:  How do Diagnostics and Remedy work in STEP 7 when an online connection with the CP... - ID: 11492532 - Industry Support Siemens Where they say the following:    I've searched for this readme file but can't find it, and there are no useful results when looking for it on internet.  Why am I able to connect directly to the PLC but not when another device is connected and I have to use the female connector of the DP connector itself? Should I try to reinstall CP5711 drivers? According to Windows, I got the last drivers for the CP.    Thanks in advance and I hope you can help me!
  13. Hello all, I need to read device memory mostly I need to read R registers from PLC L26. I read device data, but inside of table, I can't find R or ZR registers. Can you help me?  What I did wrong?   BR KS  
  14. Hi All, We have a hydraulic press that is being controlled by Siemens S5-95U PLC . Lately the S5-95U has been randomly stopping during operation thus causing the hydraulic press to stop running. However the S5-95U instantly returns to RUN status after stopping. This is the first time it has happened after a decade of service. Prior to the random stops issue, around January 2021 the S5-95U completely stopped and the program in the RAM was erased so we had to replace the PLC battery and restore the program with our backup. Strangely, the PLC battery we replaced still had 3.4VDC upon checking. What's even more baffling is that even after we replaced the PLC battery with a new one,  Battery LED is still yellow although the program is still retained in the RAM. In summary, we have two concerns: 1. S5-95U randomly stops and resumes during operation ever since we were forced to replace the PLC battery and restore the program. 2. PLC battery has been replaced but the Battery LED is still yellow but the program is still retained in the RAM.   I have a suspicion that the two concerns I mentioned above are somehow connected but I lack the technical expertise to diagnose. I'm hoping someone can help me figure out our issue. Worst case, I think our S5-95U needs to be replaced.   Thanks,  
  15. Help Logo!8 to HMI Alarms

    I have an existing LOGO!8 and im adding a HMI (SImatic HMI KTP400). i want to bring up an alarm based on the status of a Flag in the PLC. i can see that i cannot address an alarm to a Bool Tag. so my question is how to i get it to work. Example. i have LOGO flag 1 (M0.0) and Flag 2 (M0.1) what to i need to do to make them into a WORD for the alarms.   Cheers
  16. Hello Savvy! Can you pls advise on how to use FBD so this rod cylinder is working? There are two solenoids,   Tx a million   Ms Newbie    
  17. Hi guys, Has anyone ever implemented a Siemens S7 RFID tag reader into a Mitsubishi PLC system? Is this something that is fairly supported to be able to achieve? Or a right pain to set up?
  18. Hi, I am new using SIEMENS. I am programming a KTP 400 Comfort. linked to a S7-1200. I would like to ask you how to do a solution I normally used in OMRON. There, I use an "indirect label" to index the line of a TXT file I want to show in a label of a button or indicator. This is similar to the "list of text" in TIA Portal. However, in OMRON I found the way to updated automatically the TXT file in the HMI using a computer but not using the software of OMRON. So, I would like to know how to do something similar using this SIEMENS HMI. I would like to show a label whose text changes according to the value of an index. However I would like to be able to change the file where the index points (TXT, CSV, etc) but not using TIA Portal. I would program a software to send the updated file automatically under FTP, or under the protocol you suggest me. Thank you very much.
  19. Siemens WinCC 7.0 SP3 SCADA Value Freezing

    Dear All, We are using Siemens WinCC 7.0 SP3 SCADA software. We are using two Redundant SCADA Computers that are communicating with PLC (CP-343 module) via Ethernet. One Ethernet cable from each PC is connected to Cisco Ethernet Switch and one Ethernet cable from the Cisco Switch is connected with CP-343 Siemens Ethernet Module.  The problem is after every 75 hours one PC value become still (Freeze).Only One system values freeze at a time. If i restart the system the problem is resolved. Please help to resolve this problem. Thanks  
  20. Dear Mr. PLC forum members, I am brand new to the world of PLC’s and I am looking for advice on PLC platform selection for a device prototype. The proposed PLC is for a “smart” hydroponic system. Please see system I/O and other parameters below. Parameter 1: Price - I am self-funding this so price of PLC and software is important. Happy to spend ~$2000 for PLC; I/O cards and related hardware. Total prototype cost is around $15,000 including PLC. Parameter 2: Availability & Support in Australia. Parameter 3:Newbie Friendly: I intend to code the PLC myself and have never coded a thing in my life before.  Parameter 4:Discrete Outputs: 11; Discrete Inputs: 0; Analog Outputs: 2-3; Analog Inputs: 9  Parameter 5: Capability to extend to IOT for remote access control and monitoring (via cellular or wifi router)   As you can see, this is a relatively simple automation project. All my research seems to point to Automation Direct’s BRX PLC but I just wanted to get some suggestions and feedback before purchasing. Anything else that might suit my needs? Any insight would be greatly appreciated. Bruce   
  21. I have Chinese machine which has 226CN cpu I'm trying to communicate with it to upload the current program and maybe modify it. But I can't communicate with it  I'm using Chinese cable rs 232 to usb and windows xp. When I use it I get "you must use rs232/usb PPI multi master" massage  Is there a problem with the cable or the software? I tried to change language of the software to Chinese ( as a solution I found on the internet)but it doesn't help What should I do?        
  22. GOT 2000 Buil-in Memory exceeding

    Hello Everyone I have an issue with a  Got 2000, im updating and adding some screens in  a old  HMI application with size was about 47 MB,  as im still updating i wanted to test the application  which now sizes about 52 MBbut is not possible due to the shortage of  ROM and RAM, what can I do in this case as the application must be in the built-in Flash memory which is very limited?   Thank you in advance
  23. Simatic pc to simple pc with profibus card

    Hi every one, One of my machine i have to fix , has simatic pc unit installed that causing too much trouble  and client want to replace it with simple pc with additional profibus card installed in PCI slot, is there any way to configure image of simatic pc in new simple pc
  24. I have a Siemens HMI 6AV2 124-0MC01-0AX0 in my machine. I want to clone the display on the HMI to PC/Laptop. My question is: 1. What software that I need for this task? 2. What kind of interface that I need between the HMI and PC/Laptop (for example ethernet cable, etc)? 3. Do I need to communicate with PLC connected with HMI or can I just connect with the HMI? Thanks in advance for the answer.
  25. Lacthed Memory Turned Off?

    Hi guys. I'm experiencing a latched memory turned off even all of the contact is still on and trigger the coil. Anyone familiar with this? Thanks!