Search the Community

Showing results for tags 'serial to ethernet conversion'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 308 results

  1. Serial question

    I have a cell phone modem connected to my Omron CP1L on serial 2   Here is the issue  I need to pull the phone number out of the msg received (receiving text messages)  I receive a text msg and a lot of other crap like time and date ect. RDX says store in D100 the problem is that after I receive the SMS I see the phone number and copy the number to D200 to D2xx The next text comes in and it is added to the length of the previous text and the new phone number is not in the same D area as the first.  It seems the only time the serial port works is if you declare 20 characters and you get 20 characters Works every time. But sometimes I may get 12 characters and other times I can get more than 100. I have used the restart and clear port command with no luck.  If I set RDX to a large number and receive complete will not come on and the next receive will be added to the first.  I need a clear buffer for each receive.  How do I get around this?  If you set the RDX to 10 but 12 characters were received the 2 extra characters will be in the buffer and added to the next receive.  I can’t use end receive if x because there is nothing that is always available in the msg. And even if I do any characters received after end code is left in the buffer and screws up the next receive. I have never seen anything like this. Any ideas? Thanks Rob  
  2. Hi. what i've gathered, i need an EDS-file for the siemens s7-1200-system to be able to specify an ethernet connection in sysmac from the omron plc side to connect to the siemens ethernet/ip server. Anyone know where or how to get an EDS file for the siemens plc so i can import it into EIPprofiles in sysmac?
  3. GOT2000 <-> Omron CJ PLC

    I have an application where I'm using GOT2000 to read data from the weighing unit using RS232 and I send this value to Omron CJ2M through Ethernet/IP. Some variables from that PLC are connected to the elements of the HMI. The problem is when writing the weight value to the PLC through script or Data Transfer is disabled, the RS232 reading works fine, it's fast, etc. However, when I enable the script which writes data to the PLC, the RS232 slows down by a lot, like it refreshes every 2-3 seconds. If i set the script to execute like every 1-2 seconds, it is working better (still slower compared to when the script is disabled) but I cannot leave it like this, because the weight is used to control some valves, pumps, etc. Enabling script doesn't slow down normal communication with PLC, because I tried to test it by displaying the value of seconds from PLC on the HMI and it refreshes every second. Does anyone have idea why such tiny script causes so many problems with RS232?
  4. I'm trying to exchange some data between two controllers. I've used a manual which describes Tag Datalink communication. Everything works fine on the Bradley side, which means I can read values from Omron without problems. However, on the CJ it isn't working. In the Network Configurator I get error every 10 sec (Tag data ling error, code 03D5) and cannot read any data from AB. When I open Connection Structure Tree I see that the input tagset from AB has 'Broken path (0000000000000)' and Unknown Device right next to IP address. I've tried using EDS from the Rockwell as well as uploading it from AB PLC directly - I don't know if it might be EDS issue. The only thing I noticed that inside CJ2M-EIP21 EDS it says that Ethernet/IP is Class 1 connection, however in the 1769-L35E EDS Ethernet/IP is Class 2 connection. Have anyone ever had such a problem?
  5. Has anyone have any experience getting a Wieland Safety plc (SP-COP1-ENI) communicate with an Omron Plc (NX102) via Ethernet/IP? EDS file installed, connection is set as per the documentation yet  I cannot get it connected.  
  6. Error **03 Special Parameter Error

    Hello I have a problem whit PLC mitsubishi FX3U thernet communication, we have a module  FX3u-ENET-ADP. and we have the error "**03 Special Parameter Error".  
  7. Serial Port issue

    Sorry its long !! I am recieving text from a GSM modem for text msg Send and receive (SMS) works ok but would be better if I could make use of the start code and end code. This way I could cut down on all the crap that is received when a text arrives. I get this  CMTI: "SM",0 I have it stored into D80 and I have that trigger a TXD that sends AT+CMGRD=0 and that tells the GSM to send the msg (The 0 is the current msg in memory) ------ The problem is that there is Carriage  Return and Line Feeds in the received msg ----      AS below ((AT+CMGRD=0 +CMGRD: "REC UNREAD","+19028991212","","22/10/20,16:57:54-16"  Hello this is the msg  OK)) When the PLC sees the carriage return it stops receiving data. And I have no start code or end code setup. (I am using characters received) The way around this is to set a high  character count in the RXD (More than the actual msg (More than the msg length)   The main issue with that is I get garbage in as the msg gets bigger. Its unreliable. I clear the port after each receive and that helps but still get the odd garbage. (Never get garbage when connected to a terminal prg). Any Ideas???? ps Even the Start Code is unreliable as it will start receiving a few characters late. Rob  
  8. Serial Ports not working

    I have a CP1L-EM and the serial ports - both of them have an issue with the port ready flag will not turn on. Power cycle still no port ready flag In settings both ports are set up as 15200 8N1 CR/LF Verified and power cycled and still no port ready flag. Is there someplace in the PLC where the ports can be disabled? Rob  
  9. NB to CP1L-EM

    Has anyone connected a NB HMI to a CP1L-EM via ETHERNET NB = Node 2 IP 192.168.1.152 PLC = Node 1 IP 192.168.151 Using my Network Switch/HUB NB works fine when setup to com 1 on the PLC (Wrote the PRG using serial) NB says no response from PLC Is there a secret setting in the PLC i need ? ? Rob  
  10. Hello All, I would like to control Powerflex 525 drive with Omron NJ301-1200 PLC via Ethernet/IP (Set speed, start, stop). I've gotten until the part where I downloaded the necessary .eds files of the drive and imported into my Sysmac studio. However, I'm stuck after this point while assigning target variables and Originator variables and eventually setting speed and controlling the vfd. I've attached images for your reference.
  11. Until recently, I haven't had to connect to a piece of hardware using a serial connection in quite sometime. Well, that all changed yesterday when I needed to connect to a Watlow F4T Controller. I dug around in the bottle drawer of my desk and pulled at not one, but two USB-Serial Converters that I saved for just such an occasion! My old ones worked on everything from Allen Bradley SLCs, to Schneider Drives. Unfortunately, neither appear to work in a Windows 10 environment. Searching the internet, I was not able to find any drivers for these old converters, but did find some posts in another forum stating that Microsoft changed how it manages its USB ports from Win 7 to Win 10. Thanks Microsoft! Sorry, I will cut this rant short and just ask my question. Can anyone recommend a USB-Serial Converter that works in a Windows 10/11 environment?  Respectfully, Shane 
  12. I'm trying to understand the basics of using a serial to ethernet converter such as this Comtrol DM-EIP-2101, with Studio5000 code. Basically I have a weighing machine that only outputs data via RS-232 and I need to send that data to a PC that will process it through a Studio5000 program and have the data displayed on an HMI using FTview SE. Is it as simple as just connecting the serial and ethernet to the converter and it does all the work? Obviously checking ip addresses and firmware will need to be verified. The main thing I am unsure of is the process of passing the individual data packets from the machine to the Logix code on the PC,  things like what the weight of the item was, was it over weight or under, etc....  Would there be an AOI or tags built into the software for a machine like this Checkweigher? I've worked with much smaller items like Cognex Dataman cameras and I know you can just use their AOI that allows you to simply call a tag if you want to display information like if a scanned barcode was correct or whatever. If anyone has done something similar I'd appreciate any guidance. It can be difficult getting the information from the manufactures so I'm looking for answers anywhere I can. EDIT: I guess I should also clarify that only using one or the other (serial or E/IP) is not an option. It will be a serial connection from the Weighing machine to the converter and then Ethernet to the PC.
  13. Dear forum, I am facing a trouble at the moment and hoping somebody can assist. I have one HMI software, GT Designer 3, HMI: GS2107 and/or GT2107, the software works so far so fine. The software is used on several products, I dont want to maintain two or even more software versions. Two serial devices are connect: 1x MODBUS RS-485 1x MODBUS RS-232. The data transfer is done via DDT, no direct calls. The DDT transfer the MODBUS address to the internal GD-Registers. The GD-Registers are used within the HMI. My trouble is that in some cases, there is no RS-232 device connected. This creates time outs, slows down the HMI and its just not nice looking (I have a warning implemented "WARNING NO CONNECTION TO SERIAL DEVICE RS-232". Is there a way, that I can select (retained) that the RS-232 is connected / or not? Once the software is configured "NO RS-232 CONNECTED" I can handle the rest of the software.   Anybody an idea how to do this? Many thanks.
  14. 2 Words to Real

    Hi:       There are 2 Word, Let say  Word_0 = 5c29, and Word_1=3e8f, I combined that 2 word into  DWord=3e8f5c29; The result converted online (https://www.scadacore.com/tools/programming-calculators/online-hex-converter/) to Float will be 0.280 (expected result).   But with DWORD_To_Real , i get this result :    1.0354898e+09    REAL          May I know how to convert the 2 words into Real (Float ?) Omron PLC: NX1    
  15. I'm trying to set up an Ethernet/IP communication with a CIP block between a Micro850 and a SMC EX600-sen3 pneumatic Module. I can read the inputs of the module with the configuration below, but I CANT write to SET or RESET the digital outputs. There are NO errors showing communications issues in the CIP Generic Block I am using... I read that for some reason, it seems that there are problems with writing thru Ethernet/IP protocol between Micro family and other devices not from Rockwell... Does anyone know if there is a way to make it work? Configuration that is working to READ: CIP Service Code:     14 CIP Class ID:         4 CIP Instance ID:     100 CIP Attribute:         3 CIP Member ID:         0 Configuration that is NOT working to WRITE: CIP Service Code:     16 CIP Class ID:         4 CIP Instance ID:     150 CIP Attribute:         3 CIP Member ID:         0
  16. Hmi modbus TCP/IP device communication

    Hi all; I have Delta DOP110 IS hmi and i have a modbus tcp device. I want to communicate hmi and device with modbus tcp/ip but i didnt understand device's register address. For example, input bytes 0,1 analogue control word, What is the register address? 40.000 or 40.001 can you help me ?  
  17. G9SP Configurator

    I am at a client site that has a line with multiple Omron G9SP-N20S safety controllers installed and I need to make a modification to the system.  I tried to install the Omron Configurator and it asks for a serial number, and will not install without one.  Omron said that it is on the CD that ships with the unit, but the equipment manufacturer did not supply any of the CDs.  The only Omron solution is to order a replacement CD, that will take 5 days, which is 5 days too long as there is a hard stop in 2 days.  I have tried entering numbers found on the controller, with no success.  Does anyone have a better way, special contacts at Omron, to et it faster?
  18. I have a bit of an issue with communication between GOT1000 HMI (I think the exact model is GOT1675V) and Q03UDE PLC over Ethernet. The GOT is set to 192.168.1.4 and PLC is set to 192.168.1.2 but I get the error "Communication Error. Refer to System Alarm in Utility Menu". Now how do I access the utility menu? I have tried to tap and hold on the upper corners of the HMI but nothing happens. I also can not switch between screens when I press buttons even though they are directly linked via screen #. Almost like the HMI froze up. Wonder if anyone had similar issue and what the solution might be. Thanks for your help.
  19. Here is a post that we recently completed on the Automation Direct USB to RS485 Adapter.  The USB-485M is a 2-wire USB to RS-485 serial communication adapter for RS485 use. It does not require an external power supply or complicated configuration. It has a Type A (plug) USB connector for the computer side and a universal female RJ45/RJ12 modular connector. This will accept RJ12 and RJ45 plugs.  The USB-485M supports multiple baud rates and is USB V2.0 Compliant. Read the rest of the post... YouTube Video on the installation and communication to a Solo Process Temperature Controller via Modbus RTU. https://www.youtube.com/watch?v=aWE05ZNZNXw Let me know what you think, Garry www.accautomation.ca  
  20. I am trying to get a G9SP taking over serial to a NX1P2 using a NX1W-CIF01.  I have the details in Manual P545-E1 and it uses a example file which i am unable to locate OMRON_G9SP_SERI232_LD_EV100.SMC I have got the coms working with a CP1L using the example in Manual Z922-E1.  I was wondering if anyone has the example file or a working example they can share for Sysmac Studio. The serial comms will take a little bit to get going but it is the code for the checksum for the sending data that i would rather not have to translate from CX Programer fort he CP1L to Sysmac Studio...... P545-E1-01.pdf.lnk Z922-E1-07.pdf.lnk
  21. Sorry for my bad english speaking. I want to change the baud rate to 19200,38400,.... for send it via Programmer-Serial-Port. The software GX-Developer can do it!.  
  22. Hi! I would like to ask your help. I want to know more about the communcation systems what allen bradley use. Most important for me, is Ethernet IP communication, Controlnet communication, Sercos (servo) communication, maybe devicenet communication.  I know I can find some manulas on the web, but I thought I ask it here too, maybe you guys have some more documents which is contain more information. Every information is highly appreciated. Thank you very much guys.  
  23. Hi I am looking for a way to read and write data from PLC omron words, bits via FINS or EtherNet/IP protocol using python programming lang. Does anyone have any results in this? I really want to see your work, because all my attempts have failed. Thanks.
  24. I am new to automation systems and devices and I just want to know how to connect two HMI's (each one would control different things) to one PLC using Sysmac Studio and NB-Designer via Ethernet. The model of the PLC is NX1029020 and the HMI's are one NB10W-TW01B and an NB7W-TW01B. I searched for info about this topic online but I couldn't find anything that worked for me, I saw an article from OMRON where they connect two NB's to the CP series, but in my case, NB designer doesn't allow me to insert more than one HMI in the same project, I also found something similar on a youtube video that gave me an idea about how to connect multiple HMIs exporting the pks file and importing it to another HMI project but I still can´t figure out how to add both to my PLC. I would thank you a lot if you could help me with this because I know it's not a rare implementation, just I haven´t found the right way to do it. I also leave the links to the Omron article and the youtube video I found. https://www.myomron.com/index.php?action=kb&article=1554 https://www.youtube.com/watch?v=rXx5lut7G9I
  25. Hello, I've been using Mitsubishi and Omron systems separately (in their own environment), and I am fairly new when it comes to connecting these two brands together(plc and hmi). I've been scouring the net for wiring diagrams for the cable connections and also the parameters to be set for a successful communication between those two components. can anyone point me at the right direction as everything I've tried so far has been a failed attempt of making these two communicate. here are the parts and my current settings if this helps: FX3U-64M FX3U-232-BD NB5Q-TW00B or better yet, is there a proper cable that I need to buy for this to work?