Search the Community

Showing results for tags 'serial rtu communication'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 190 results

  1. connection to omron CJ1M PLC

    I have an omron PLC (CJ1M type) at home which I would like to connect to, however, lately, I can't anymore.  I'm trying on two different PC's a newer and an older one, both running on windows 10. 1 is just mentioning a DLL error and I can't even start cx-programmer, the other one seems to work, however, when I try to go online it always fails I'm using a usb to serial device and after some searching on the net, I thought the issue was with the prolific driver.  I tried all kind of fixes, but nothing seemed to work.  I have now purchased another device, the XS8801 from usconverters and installed the latest driver.  I have checked if cx programmer is set to work with the correct port and this is the case. My knowledge is very limited but I would really want to connect to that PLC again, so hoping someone out here is able to help me. Thanks a lot    
  2. Hi all,  I want to ask some questions regarding Ethernet Communication with FX3U PLC series. I have 2 PLCs of FX3U series (FX3U-48M and FX3U-64M) and I want to monitor its data (input and output) using ethernet communication in real time. My questions are: 1. Does FX3U PLC have ethernet port so I can connect it directly to my Laptop/PC? 2. If no, do I need to use FX3U-ENET-ADP and can it be used for 2 PLC or only 1? 3. What software do I need to use to configure the communication between PLC and FX3U-ENET-ADP? 4. Does this configuration change the existing PLC program? 5. Can i transmit the data wireless-ly using some kind of ethernet to wifi adapter and what additional hardware do i need for that?  
  3. Check serial connection to Omron PLC

    Hello, I am building an application in CitectSCADA and I want to communicate with an Omron Sysmac CS1G. The connection between the plc and the Citect computer is through an ethernet to serial adapter (the computer doesn't have com ports on board). I'm having some difficulty establishing the communication and I want to make sure that I can actually reach the plc. Is there a way to check that the computer can reach the plc over the serial connection without using CX programmer? Maybe using Hyper Terminal, Putty or something similar. Thank you, Liron
  4. HI All,  I have an issue with my SCU32 communication.  Back ground Two SCU32s  (top and bottom side) connected via a 1100M datacable  using port1 ( 9600bps,  8-2-E, start code FF, end code FE, Tx save to d1000-d1200 , Rx save to d2000-d2200). PORT2 of bottom SCU32 is connected to a compass( 2 wire, 8-1-N, 19200 bps, serial gateway MODBUS ). Refer to photo Issue  Without compass, the receiving data at top is very stable and is didn't see any fluctuation. But if is compass is connected at bottom side port2, there is a fluctuation at the top side RX data(specifically d2000-d2005 ) .  I checked the data a bottom side TX (d1000-d1200) and it is stable. Only after sending the data and Receiving at Top side, then only the starting words fluctuate. I am not sure sure what is wrong, I am using logical ports for the DTXDU/DRXDU and compass.   Appreciate all your feedback and suggestions.  
  5. InTouch Comms

    Hi Everyone, I've just installed InTouch V10 and am trying to develop communication with Emulate5000, for educational purposes. I looked over the internet and found some videos on how to develop communications by setting up the topic name and node name in DA Server manager, but the issue I'm facing is that my SMC only shows logViewer and nothing else (snapshot attached). Am I missing some vital component or dirver? Or is there some problem with my installation? Help would be much appreciated.   P.S: Window Maker and Viewer are working fine. Thanks, Sabih
  6. hello expert i want ask some help So i tried to communicate my Omron PLC (cj2m cpu31) with SCADA from Schneider (power logic) on my omron side the comunnication on PLC already take to communication to NB so i add communication module CJ1W-SCU41-v1 I want asking how to open the communication if i want the scada become a master and my plc become slave i got this from omron website is that program compete for my case? i need configuration for scu41 module also to communicate or if you have suggestion i really open i just need to open port RS232c from scu41 so scada can read the data from my plc  tahnkyou for your help MRTU_CPU_Slave.zip
  7. Hi! I would like to ask how could I send data from PC to CJ1M PLC, by SCU-41 module and RS232 cable, in order to activate an actuator (LED)? In my environment, I have a sensor that sends data from PLC to PC (I'm checking data, "HelloWrld" with Putty), with this configuration: And I have another section where I want to read the data from the PC in ordr to activate a LED I would like when I send for example a letter 'a' trough Putty, the LED activates. How could I do that? Thank you very much!
  8. Siprotec Relay 7sj62

    I have 24 Siemens Siprotec relay(7sj62) which i want to communicate with Scadapack 330E (Schneider) on 103 Protocol. but every time I try to communicate it shows Slave device is failed to communicate. trying to communicating via serial (RS-485). What should i do..?? or do i need to communicate it with Siemens PLC..?? If so which PLC should use..??
  9. PC to PLC Kommunikation

    Hello, i want to connect my PC to the PLC(RSLogix5561)  over TCP/IP. In rslinx the Ethernet driver are configured. My PLC IP Adresse is 192.168.1.100 and my PC Adresse is 192.168.1.105. From my PC i can successfully ping the PLC IP Adresse, but from the PLC i can't see my PC. And it does'nt schow in RSlinx. Is there anything i am missing?
  10. Hello there, I am new to OMRON so need some help to communicate two PLC over FINS.   Here are the description of the system... (IO Table image is attached)   PLC1-  CJ2M-CPU33 IP- 10.113.218.34 SUBNET-255.254.0.0 UNIT NO - 00 (set the dial available on the CPU in HEX) NODE - 22 (set the 2 dials available on the CPU in HEX) PLC2-  CJ2M-CPU33 IP- 10.113.218.35 SUBNET-255.254.0.0 UNIT NO - 01 (set the dial available on the CPU in HEX) NODE - 23 (set the 2 dials available on the CPU in HEX)     Now, what i have to do is to transfer the D100 to D110 from PLC1 to PLC2's D200 to D210 and Transfer the D100 to D110 from PLC2 to PLC1's D200 to 210.   I have tried RECV and ECHRD blocks but didn't succeed yet.   Two CPU are connected over ethernet via a industrial switch.   Can you help me to achieve data transmission please...
  11. Hi All need to convert a Decimal Value into Ascii code to send out on serial 485. eg. Weight comes in as Int 12345 i need to send it out in Ascii as 23 32 20 31 32 33 34 35. I have created an array 0 of 8 (Word) DB. Is there an easy way split the int into Digits convet in into HEX and slot the value into the various array positions? Array 0 of 8 = 23 means # Array 1 of 8 = 32 means 2 (Station ID) Array 2 of 8 = 20 means Space Array 3 of 8 = 31 means 1 Array 4 of 8  = 32 means 2 Array 5 of 8 = 33 means 3 Array 6 of 8 = 34 means 4 Array 7 of 8 = 35 means 5 Array 8 of 8 = D means CR    this sends the value of 12345 to Display ID 2 . need help to convert the decimal number in ascii. the decimal number will be max of 5 digits and less than 32000   any help will be greatly appreciated.
  12. Hey everyone, I have a CJ1M PLC with a CJ1W-SCU21-V1 serial card. It is unit 6 and I am using port 1. I have bit 1659.06 ((1500 + 25 * Unit #) +9, bit 6) as "characters in buffer" but it never comes on (data is being received through the port successfully). It is on No-Protocol mode. Does anyone have any ideas as to how I can detect data in the buffer?
  13. HMI and PLC Communication problem

    hi there. .. i am new to plc programming.. Right now i am having problem related to communication between hmi and plc.. i have HMI WEintek 6070ip and plc mitsubishi FX2n.. i have written a program in gx developer . and communicate it with EASY Builder for HMI. so for now plc is communicating with my program written for hmi on pc. but when i downlaod to hmi and connect plc cable to hmi then hmi shows no plc communication. i am having a problem for communication between hmi and plc. any help will be a life saver. thanks in advance
  14. Serial comm with FX1N PLC

    I need to communicate with a Mitsubishi PLC using Matlab. To do that, I open a serial communication with the appropiate parameters (7,e,1,9600), and write an ASCII message based on the manual I have (attached). I have tried examples as the one in the attached image. The response starts with a 6, that is, the ASCII number for ACK, so something must be working. But the rest of the response is junk (149, 149, 149...), although its length depends on the input length (if I add terminator, the response is longer, and so on). I am completely stuck. Some information that might be helpful: I am using a Serial to USB converter that I have used successfully with other PLC (which used Modbus, so everything was easier) There's a VB application (of which I don't have the code) that is able to connect to the PLC (I need to connect directly without using this intermediate app). I have decompiled it trying to get some info, but was just able to confirm the 7,e,1,9600 parameters, since the rest of the code is too mangled to analyze The attached manual was sent to me by the guy who designed the PLC and its ladder code, so I guess it is the correct one I have tried the echo mode (TT) to no avail, response is always the same I have some doubts regarding the reading of a value (see attached image). Why is there a second message from the PC? Shouldn't I just need to read the response? GX Developer tells me that the address D8120 (which is supposed to define the comm format and protocol) contains a 0, which seems weird. Any help or hint would be greatly appreciated. Thanks jy992d69901e.pdf
  15. Hi everyone! I got this machine with a CP1H PLC and NS8-TV00B-V2 as PT. I was told that they were working fine, but suddenly, It appeared a communication issue: black screen and "connecting..." at right bottom. I dont know if It is a configuration problem or some hardware damage.  These are the configuration in the PT and the PLC. The communication is through RS232 Serial.  I tried to communicate another PT screen with the same communication settings and IT WORKED!. ' I've been thinking that, perhaps, the serial port A is damaged, I have tried to set port b, but I havent could. How can I configurate PORT B??   THANKS...  
  16. Hey all - I am working on a car wash system design that will utilize the Nayax payment system. Has anyone utilized them? How do I incorporate the device with PLC to automate the system. After payment is approved how can I send out that signal from them, all via ethernet on a managed switch w/ wifi for exterior comms for the Nayax.
  17. Hi All, Hope you all doing well in this pandemic life.  I would need your expertise with an issue I have been struggling with for past few days and thought to reach out here. I am working on a migration project with GE PLC and Citect SCADA 7.10. The GE PLC is migrated to ControlLogix L74 Rev24.10 while Citect SCADA is retained. For testing I only have L71 and L82 and could not managed to organise L74. When the code the loaded in L71 and connected to Citect, I cannot see tags in Graphic page but I see the subscription.txt in Debug folder shows all tags good . The same code when loaded in L82, the Citect works instantly.  Does anyone know this behaviour of PLC and SCADA? Regards, DeeEngr    
  18. Sorry for my bad english speaking. I want to change the baud rate to 19200,38400,.... for send it via Programmer-Serial-Port. The software GX-Developer can do it!. When the PLC is switched on, we generate a value in the data register D8116 and D8117. GX Developer reads the PLC type and data registers D8116 and D8117 at startup and generates a value. This value is written in D8118 and D8119. The big question is: how is D8118 and D8119 generated ??
  19. Mitsubishi Fx5uc

    hello everyone, Im new with mitsubishi and  ive got a project with a Fx5uc but im stucked in communication protocol to communicate with a weintek HMI ive already tested easybuilder simulation with a modbus tcp ip symulator and it works but im completlely lost about mitsubishi, is there a way to communicate via Modbus TCP/IP? or which protocol would u recommend as i have to connect 2 drives as well. thank you in advance
  20. Fatek PLC Communication Problem

    hy all. i am having an error while communicating with fatek plc. when i communicate it gives an error. " Com port open fail, plz check if this port is used by other programme when we online the PLC (Fatek/ WinProLadder). kindly Guide me   as it looks like port is already used by another program . and i dont know how to kill that program ..       
  21. Hello guys, I am very new at this. I am trying to make a Schneider PLC (TM251MESE) to send some serial commands (485)  to a integrated stepper motor from Automation Direct (STR-MTRD-17030RE, but I am lost. The driver has been program to receive the SCL commands. But not quite sure how to send those from the plc. Im using SoMachine V 4.2 Have any of you done anything similar? Any example will be greatly appreciated.  Thanks 
  22. INFO

    Dear sir, I am working in container terminal, we have Siemens plc  s7-300 , Bromma spreader with SCS-3( codesys software) spreader field device sensor (ifm) connected to slave ifm CR9011, now a days we are facing too much issues in scs-3 so we planned for isolate the SCS-3 but we want to know ifm module Cr9011 how to communicate to Siemens plc  7 how to write in hardware configuration. can you please suggest us.  
  23. Produced and Consumed Tags

    How can I determine if both my Produced and Consumed tags are communicating with each other, and if have the right set of tags since I forgot how I named them?  Is there a way to confirm that both my P & C are communicating.
  24. I have IPC and need to detect status of IPC and PLC communication . I need help with the same that how can in detect it ? Is it possible with message instruction ? if it is then how ?
  25. Can anyone help me with the issue in the picture? We have the correct version in place yet it gives me a version error stating it needs the version that is installed. Doc1.docx