Search the Community

Showing results for tags 'relay'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 16 results

  1. Hello, I am trying to flash an indicator light (Banner  K70LBGYRPQ ) every .5 seconds.  The PLC manual says 2.5A per channel.  The light uses roughly 113mA max current @ 24vdc.  I am using output 0 to do this (O:0/0).  I think I may have ruined the output by flashing the indicator light.  Has anyone ever experienced this before?  Is there a minimum pulse time for this PLC?  What do people normally do when wanting to flash an indicator light such as this?  This is not the first time I have seen this happen.   Thanks in advance!
  2. Hello,  I am using Omron’s safety G7SA to relay 24 volt line. But the strange thing happening is that, one relay’s output is only 5 voltage, even the relay is on. I exchanged relays, it remains the same. Maybe the base socket is problematic?  Or is this just G7SA failure? 5v (exactly 4.96v) is strange. Please give me some advice.   Many thanks in advance.   Ting    
  3. I have a question regarding hazardous zone design. My control cabinet will be in safe area but I need to have e-stop and safety limit switch located in hazardous area, Div 1 Zone 1. I am assuming that I can use zener barriers or isolators between the field devices and safety relay. I just wonder if the safety relay will function properly with barriers in between? Also do I have to use 24VDC safety relay for this application? I don't know what voltage/current is present on the terminals connecting to safety devices.
  4. Siemens IEC 60870-5-103

    Hello!, im having some troubles communicating Siemens Relay 7SJ622, with the IEC 60870-5-103 protocol, with some SEL controller, i don't have any signal of the slave relay 
  5. Siprotec Relay 7sj62

    I have 24 Siemens Siprotec relay(7sj62) which i want to communicate with Scadapack 330E (Schneider) on 103 Protocol. but every time I try to communicate it shows Slave device is failed to communicate. trying to communicating via serial (RS-485). What should i do..?? or do i need to communicate it with Siemens PLC..?? If so which PLC should use..??
  6. Good Afternoon  im a complete newbie when it comes to PLCs but have done plenty of PIC programming in the past. I've been gifted a couple of FX0s 20mr units to try to repair something I made with PICs years ago. It got damaged during a move and I can’t see well enough now to make PCBs anymore so thought that this might be a solution. The basic operation is  1. switched on 2. motor A moves till hits limit switch (X000) 3. Wait 2 seconds 4. motor reverses till hits second limit switch (X001) then once this has been completed then the following  5. Motor B turns clockwise for 30 seconds then stops  And while Motor B is turning I need Motor C to turn until hitting limit switch (X002) I then need to get it to repeat on the press of a button but I need to reverse operation of Motors B and C I am using double position relays to drive the motors so motor A is on Y000 and Y001 if I power either relay the the motor turns in that direction. Same with Motor B and C Y002 to Y005 is this something that’s possible with one of these controllers or am i going to be programming a PIC to control the PLC ?   All the various COM and powers are connected up, I can individually make every motor do what I want, but the program doesn't flow from one item to the next. but this is probably just me      
  7. MC protocol

    Hello once again, before I'll dive into mitsu manuals, does anyone of you know if there is some special relay signaling that PLC (FX3GE) have lost communication via MC protocol? Thank you in advance
  8. Relay Digital signals

    I have a CJ1M-CPU13. It will be used for a prototype and later if successful, a better PLC fit will be employed. This system does not have the ability to drive pulses for servo control. However, will this system relay a digital signal at ~1kHz? I also need the PLC to count the pulses, reset at 1000 and start again continuously and never miss an input pulse. I see that the published transactions give  <15 microsecond decision times. I would think it would be no issue. Thank you.
  9. Hi, I would like to provide the PLC control for a scenario where the temperature in a machine, heated by the two electric heaters, is controlled with use of 1 TCK and 2 s/s relays. Please see draft “plc4” sent attach. The TCK is fixed to the machine and is not in a physical contact with the heaters. Nominal temperature of machine is 200degC. The machine temperature tolerance is +/-2degC. This means that the heaters should be turned on when machine T drops to 198degC and turned off when T reaches 202degC.  For this moment I have created the start PLC diagram outlined on draft “PLC4”.  I am still learning PLC. Therefore, I would be very grateful for your opinion whether the PLC diagram shown on picture “PLC4”, in terms of the tools used (direct contact, direct coil, etc.) and their layout, is of proper design. I know that there is much more work needed to complete this task (e.g. set up of the variables, etc.). I am using Unilogic software. Please help. Regards
  10. Hi All, We have an old machine using a Mitsubishi Fxo-30MR/ES and I will be replacing the PLC with a FX3S-30MR/ES.  This old machine would power some led's on a panel mounted PCB using the PLC outputs.  The 24V from the PLC output would go to the PCB board where a resistor would drop the voltage for the LED.   This PCB is damaged I would like to avoid getting a new PCB made and instead power some panel mounted LED rated for 24V directly form the PLC output.  I guess these panel mounted LED have a built-in resistor.  Power consumption for the LEDs are 20mA at 24V volts.  The 24V power supply has plenty of capacity for this. Are there any issues with doing this? I have attached the spec sheet for the panel mounted LED (I will be using the 24V versions).   Panel Mounted LED.pdf
  11. Elecrical Control Panel

    Which type of electrical panel is most reliable, give some idea about that ..?
  12. Hello, I have a remote io cabinet with a rack of Siemens ET200isp. This was chosen because the almost all of the equipment connected to it comes from the hazardous area and is Ex ia. This presents me with a problem because I have two pumps that I need to turn on and off with this rack, and I cannot drive a contactor with intrinsically safe io for 2 reasons: 1. The power output is too low to pull in a contactor 2. There would be no barrier to separate the intrinsically safe wiring from the 'safe area' wiring containing the 3 phase for the motors. Output card is a 4 F-DO Ex 17.4V/40mA (6ES7138-7FD00-0AB0) My original plan was to use a Pepper and Fuchs KFD2-SR2_Ex2.W on the output of the Siemens DO card to provide a safe area dry contact that I can use to power my contactor. This did not work however as the KFD2-SR2 is not designed to be connected to an active current source, so both the IO card and the barrier were trying to power eachother and switching was not possible. I can get it to work if i power a standard 24v relay from the DO card, however this does not solve the problem of properly isolating the hazardous area wiring from the safe area wiring as a relay is not an intrinsically safe barrier. I can put a zener barrier in line with the coil of the relay however this cuts the power down too much and the relay contacts do not reliably pull in. I'm asking if anyone has any ideas, we are beyond the point where installing a new IO rack that is non-ia is an option, it would require a whole new cable run for the profibus. Is there such a thing as a relay that can be powered by the intrinsically safe output? I hope that is enough detail, please feel free to ask if more info is required. Thanks in advance for any suggestions.
  13. RSlogix500 Tutorials `

    I was hoping to get feed back on my website.  The site is for beginner PLC programers. The tutorials start right from the beginning with describing what a PLC is and then teaches basic instructions. Please take a look and tell me what you think, I would love the feedback.   thank you   ladiesandtech.com   1. What is a PLC Part1  https://ladiesandtech.com/2015/12/03/watch-whatisaplc1st-on-youtube/  2. What is a PLC Part2  https://ladiesandtech.com/2015/12/09/watch-what-is-a-plc-part-2-on-youtube/ 3. What is a PLC Part3 https://ladiesandtech.com/2015/12/15/watch-plc-programming-tutorial-for-beginners-part-3-on-youtube/ 4. What is the Binary Numbering System https://ladiesandtech.com/2016/04/01/watch-what-is-binary-numbering-system-and-how-to-convert-to-decimal-on-youtube/ 5. Relay Logic Intro https://ladiesandtech.com/2015/12/04/start-stop-motor-circuit/ 6. Relay Logic Intro Start/Stop with a seal  https://ladiesandtech.com/2015/12/04/watch-stop-start-relay-control-circuit-on-youtube/ 7. Relay Logic to Ladder Logic https://ladiesandtech.com/2015/12/04/watch-relaystopstarttoladderlogic-on-youtube/ 8. RSlogix Communication Driver and Configuration Tutorial  https://ladiesandtech.com/2016/01/14/watch-allan-bradley-comms-set-up-on-youtube/ 9. Micrologix500 Communication Set Up Tutorial https://ladiesandtech.com/2016/01/14/watch-allan-bradley-comms-set-up-on-youtube/ 10. Timing Relay Lecture https://ladiesandtech.com/2016/02/11/watch-timing-relay-on-youtube/ 11. RSlogix500 Timer On TON Instruction Tutorial https://ladiesandtech.com/2016/02/14/watch-plc-rslogix500-timer-on-delay-ton-instruction-tutorial-on-youtube/ 12. RSlogix500 Timer  Off TOF Instruction Tutorial https://ladiesandtech.com/2016/02/16/watch-rslogix500-ladder-logic-timer-off-delay-tof-instruction-tutorial-on-youtube/ 13. RSLogix500 Retentive Timer RTO Tutorial https://ladiesandtech.com/2016/02/19/watch-rslogix-ladder-logic-retentive-timer-on-rto-tutorial-on-youtube/ 14. How to do Online Edits in RSlogix500 https://ladiesandtech.com/2016/02/29/watch-how-to-find-and-download-autocad-files-for-allen-bradley-ab-plcs-and-products-on-youtube/ 15. RSlogix500 Counter Tutorial https://ladiesandtech.com/2016/02/25/watch-rslogix500-counters-on-youtube/ 16. RSlogix500 Counter Up CTU Tutorial https://ladiesandtech.com/2016/02/26/watch-rslogix500-count-up-ctu-instruction-tutorial-on-youtube/ 17. RSLogix500 Move MOV instruction Tutorial Part 1 https://ladiesandtech.com/2016/03/14/watch-rslogix-tutorial-on-move-instructions-part-1-on-youtube/ 18. RSLogix500 Move MOV instruction Tutorial Part 2 https://ladiesandtech.com/2016/03/14/watch-rslogix-tutorial-on-move-instructions-part-2-on-youtube/ 19. Rslogix500 Compair Instructions , LES, LIM, EQU etc Tutorial https://ladiesandtech.com/2016/03/17/watch-rslogix-tutorial-on-compair-instructions-grt-lim-equ-les-etc-on-youtube/ 20.How to Create a flashing bit in RSlogix500 using timers https://ladiesandtech.com/2016/03/24/watch-how-to-create-a-flashing-light-program-in-rslogix500-on-youtube/ 21. How to Create a program with a flashing light https://ladiesandtech.com/2016/03/24/watch-how-to-create-a-flashing-light-program-in-rslogix500-on-youtube/  
  14. Horner XL4

    Greetings, I'm having trouble with a Horner XL4 power cycling itself when 120 V is switched with its relay outputs. I have tried both polarities and slowing down the switching quite a bit. The unit appears to power cycle even when the relay is not switching, and only when 120 V is applied to the relay outputs. I am driving a control 24 - 230 V AC/DC light off an on once a second or so, with the identified/neutral attached to the 120 V AC / 12 V DC PSU. Would anyone be able to guide me into what could be causing this? Thank you.
  15. I have been using a micrologix 1400 L32bxba. I have had a reoccurring problem of the contacts sticking on the processor. I have added diodes on the coils of the contactors. Using 700CB220EJ relays. I also have the problem of the leakage current being so high it pulls in the relays with the output off. Any help would be appreciated.
  16. I am working on Remote IO panel and plan to use the following components: 1734-AENT 1734-OW4 - qty 2 1734-IE4C I wonder if I need to separate the bus between the relay output module and analog input module? Or anywhere else in this setup? Thanks.