Search the Community

Showing results for tags 'redundancy module'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 40 results

  1. IC200ALG264 Analog Input module

    Hello all, Thanks for the forum which has provided me with a lot of help overtime. I'm posting my first thread since I can't seem to find an answer to my issue. I'll quickly explain the situation: I'll be installing a RTD sensor to a GE Fanuc IC200ALG264 analog input module using a 4-20mA converter. Everything is fine except I can't seem to understand the polarities of the Fanuc inputs. I'll explain better: the module has an IC200CHS022 for the terminals, 15 terminals total, and the manual is reporting a "number" and a "connection" for each terminal. Now, the "number" seems to correspond to the visible pin of the terminal. But the positive and negative symbols are represented on the "connection", which I can't seem to wrap my head around what it means. Attached are abstracts from the manual and a photo of the terminals. Please tell me where to connect positive and negative outputs of the 4-20mA converter. Thank you. Terminals Table Terminals drawing Terminals photo (front)
  2. Hi all! We have a problem with a Mitsubishi system. After switch off the machine in home position and back on, it resets the servo encoder value to 0.  I checked the servo parameters, and the Absolute encoder is enabled, the ext. battery is ok and no zero reseting in the program ( I think...). Is there a parameter I should check or some setting in the intelligent module? The system consists Q01CPU, QD77MS2 im., J4 200B amp with 6v battery, and HG-SR152 motor.
  3. Cpu dulpex notwork

    Hi dears, I have cs1d plc with 2 no. Cpu65h and one dpl02d. When i download my program to cpu cx- programmar alarm that program download to simplex mode. And one cpu not work. How can i set cpu redundancy? Thanks
  4. PID Loop Review

    Hi all, I am trying to set up a PID loop for a project I'm working on, and I was hoping someone could take a look at it for me. Most of what is written comes from the Q, L programming manual, but I've changed a few things so that the program can write changes to the SV as needed. The processor is a Q03UDE and the Analog Module is a Q64AD2DA, using only channels 1 and 5. Thanks for looking! PID Project.gxw
  5. HMI Redundancy

    Hi Dears, I Have CS1D-65H Duplex control system with two CS1D-ETN21D. I want to use ETN21 for connection between CS1D and NS15 touch panel. I have question about HMI redundancy. (when one CPU is faulty second CPU connect to HMI) Note: I have one NS15 Touch panel. how can do i it? which setting is necessary in CX-Designer? and second question: i have one CP1H with CIF41(FINS)  that must be connected to this NS15. means CS1D with 2 CPU and CP1H is connected to one HMI. is it possible to connect CP1H and CS1D simultaneously to one Touch panel? can i have manual for do this settings? is it possible use of FINS and ethernet (ETN21)  simultaneously?   best regards.
  6. Hello Everyone, I am new at this forum, seeking help from you guys and gals. Scenario: I have a Controllogix 1756-L71 5570 controller installed with 1756-TIME module. The function of time module is to take time from GPS clock module in NTP format and send it to controller in PTP format. All the status LED's on Time module are OK. Also sync LED is Green. Still the time of controller is not synchronized with GPS clock there is a difference of 45 mins. Fellows please help. I'll be helpful.
  7. We recently added a new analog card to a remote rack that is communicates to a processor rack that has a redundant partner... We made the change when the processor was online, do we need to do anything on the redundant side? 
  8. Does anyone know how to reset the "Maximum Total Observed" CIP Connection statistics on a EN2T or a L83 Processor?
  9. I am investigating a failure that occurred...  We have a L62 Processor with RIO and Redundancy, it was reported that a system "failed to stop" this system is started and stopped via outputs channels on an OW16I card on one of the RIO racks. Has anyone had experience an issue with IO not responding as it should if the redundant partner is disqualified? Also, there was a know network issue and the main Ethernet card (Slot 1) did have a communication issue (not the same Ethernet card for the RIO (Slot 3).
  10. Omron Hardware

    Please let me know if it is allowed to sell PLC hardware on your forum. I accumulated lots of Omron hardware  that I want to get rid off. Here is the list, I have several of each type, asking $12 each plus shipping. All in working condition.  Base Unit C200HW-BI051 Base Unit C200HW-BC101 16 Point DC Input Module C200H-ID212 16 Point Digital Output Module 24VDC C200H-OD212 Power Supply Module C200-PA204    
  11. Counter module FM450-1

    Dear all, the following error happened with me as following  1-power cut happened  2-rack with DO wasn't working "meaning no DO on plc module or from PLC but from function was active & some DO was blinking very fast" action I took  1-after more try change address for DO module from H/W configuration with spare DO "using Rewiring Option" worked well  but I face the following error "i don't if problem was new or related to last action' error on counter module FM450-1  I/O access error and error on FC40 "System function for counter module" no change in H/W wiring in field was done  any one need more data can ask  DO & FM not on the same rack  CPU416
  12. HI I'm using PlC5/20 when I click on setup screen on the BTR block (to view the analog input configuration) i find the following message: No modules exist in the IOconfiguration for this R/G/M however the analog input signals is running properly....i just want enter the setup screen for configuration. I'm assuming that I need to enter I/O module in the I/O configuration? Can I do this without taking PLC to Program mode?  
  13. A1S68DAV parameter

    please can anyone tell me how to set A1S68DAV analog output module parameters , such as voltage output and resolution? or is the parameter can't be set at aLL (ie, fixed at -10V to 10V)?
  14. Hi, I have been helping a client overseas to upgrade and install some CPE330 PLCs configured as CRU320s to replace their faulty CRU320s. They had been previous controlling primarily from the Secondary (PLC B) for the last 6 years or so until PLC B finally failed due to a power surge. Having configured and downloading the previously working project to the PLCs in their respective hardware configuration, the system refuses to allow PLC A to control via the Citect SCADA, despite showing as Active and Ready on both Citect and the RMX Modules, although no outputs are read through Citect when PLC B is switched off at all. I found this forum from searching a previous post about drivers and if 90-30 and Rx3i required any changes (their previous setup before being Rx3i was 90-30), but as you confirmed in that thread, that the driver should be fine, unless you know of any issues with it working alongside newer PLCs configured as older ones? I should note we have discovered that the firmware revisions on each PLC is different and will be getting them to upgrade the later one to coincide. Each PLC has been tested in either HWC and both operate when configured as PLC B and neither operate fully as PLC A. We've had a GE technician check over the project and extracted text files from the PLCs and has confirmed the code and config looks correct. We're running out of ideas and out next step is to try and borrow 2 PLC racks and try to run them all first hand to see if PLC A runs on the SCADA in our office to try and rule out the software altogether! Any help you can provide would be much appreciated, Gene
  15. hello everyone,,,, I want to running the motor in 100 rpm but how to setting electronic gear to control speed in servo motor HG-SR502,, does anyone know how?
  16. hallo everyone ...i use mitsubishi Q00UJCPU and QD77MS2.. i try to make a speed control program and the speed wants to be changed during servo operating, i use dedicated instructions ZP. PSTRT1 (axis 1) and have tryed but it was only successful to change speed with "change speed control" function once ... is it like it? cannot change "change speed control" many times when servo operations?
  17. Is it possible to add another AB Rockwell PLC to the network tree as a Generic Ethernet Module and use it as IO? Any idea where I would find information regarding assembly instance and size of I/O/C for AB Rockwell products? If possible, what are the pros and cons when compared to produce/consume and MSG instructions? Don't need to use it real world, just curious. Many thanks in advance.
  18. Delta PLC Analog Noise Reduction

    Hello All, I am Using Delta SE Series PLC and 06AD Module for Pressure Transmitter. But Analog input get fluctuate continuously. Is anybody have program for analog scaling.
  19. Hi guys! Can anybody help me? I have an existing controlnet network. How can I connected a new module? Like an 1794 IB16. What should I need to do after I connected the new module? One more question: What's the difference if I do not connected the new module right after the last module, but I connected between already existing module. Then what should I need to configure. If anybody want to help, please write like step by step. I'm a beginner, but I want to imporve myself. Thank you for your help. I almost forget, I need to work with Allen-Bradley PLC, and I have RSLogix 5000 software.
  20. I'm using Controllogix L61 redundancy system as a slave with DCS using ethernet tcp/ip socket programming. The communication between master and slave will fail after a switchover. Kindly give solution for this. Thanks and regards, Rasu
  21. Hi Everyone! I try to read Analog Data in PLC Master through Salve Module (ECT-21) but i dont see any data, with an Digital Module i can read and write, but with analogic module i can't do anything. The analog module works perfect, i have 4-20ma Simulator and work fine. Modules: PLC: NJ501-1300 Slave: ECT-21 Analog: ADO81-V1 Can u help me? Regads..
  22. Looking for some servo application help. Software: I have GX works 2, GT Designer, and GX Developer.  Hardware: PLC L06CPU-P, GOT2000 HMI, MR-J4-350B servo amps, HG-JR35JK motors, LD77MS2 Pulser I have (2) AC servos that will simply move an aluminum frame backwards and forwards using a FESTO belt mover and I have a servo gear reducer 20:1. I have a "simple motion module"and all of this hardware and software, plenty of time, and would really like to finish this project off. But this is my first servo and my first hmi project. I have some experience with Omron, Mitsubishi, and Allen-Bradley plc's, and consider myself novice at best. Any sample programs or help getting me started would be greatly appreciated!  
  23. Hi, I have encountered an unexpected "PRI" LED indication of 1756-RM Series B module. When the affected redundancy module is set to primary, the status of the "PRI" LED indicator is blinking red. On the other hand, it is set to a solid red when the RM is set as secondary. I have read the manual and there are only two expected behavior for the "PRI" LED indicator, green if it is set as the primary and off if it is secondary. Does someone encountered this scenario already?   P.S. The RM does not have any minor/major faults when accessed. The status indicator indicates "PRIM" when the affected module is set as primary and "SYNC" when set as secondary. Manual switchover between controllers are done and was successful. Thanks in advance! Regards, RIValencia
  24. Version 1.0.0

    52 downloads

    Using this module to replace of FX3U-ENET to reduce the cost(if not using the e-mail function)
  25. FX3U-ENET-ADP User's Manual View File Using this module to replace of FX3U-ENET to reduce the cost(if not using the e-mail function) Submitter pigflying Submitted 01/19/17 Category Manuals, Tutorials