Search the Community

Showing results for tags 'profibus problem'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 82 results

  1. CX-Configurator - Profibus DP-V0

    Once again. I'm still facing problem with Pofibus communication between PLC and Comnet-DP module. I'm trying to connect Bosch valve station equiped with Comnet-DP communication module with Omron CJ2M and RPM21 (profibus master) I've made proper configuration in master settings (most important was baud rate but Bosch module adjust baud according to master) Then I've set slave configuration as you can see below: According to:   Other settings were unable to modify or just were left unchhanged. Omron is detecting connected slave but returns diagnostics that says that something is wrong in parameter settings. Same message I can read from Bosch module LEDs. Any experiance in profibus diagnosis, advices what to do? I've checked all settings configurations I have no idea what to do.        
  2. Hello I would like to first let everyone know I am new to the world of troubleshooting or programming plc's . What we have is a SLC500 system that is connected to a Panelview 1000 HMI via the DH+ network. The issue we have is the panelview displays a gate that is suppose to be closed at as gate fault. When i connect to the plc the ladder rung shows that the gate is closed. To show various positions of the gate the programmer used N13:70 as gate opened and N13:71 as gate faulted and N13:72 as gate closed. When i checked the logic it showed the bit N13:72 as engaged or true if you will. This logic is in the ladder rung that is labeled PV Status which i take is the status the HMI reads so my question is why does it show GF when it should be reading GC. Ive searched all through the logic and it doesnt appear to be wrong here is the logic the best I can simulate it  ladder 6 rung  53  instruction is  XIC O:13.0/11 and OTE N13:76/0 (Gate Open ) and the branch is XIC I:5.0/11and OTE N13:76/1 (Gate Fault) next branch is XIC N13:3/11 and OTE N13:76/2 (Gate Closed which this section is green or highlighted or true which ever you like) when i looked at the input XIC N13:3/11 this is what I found is that this XIC is on ladder four rung10 and has the following XIC T4:154/DN and branchoff that is XIC I:5.0/11(gate opened)XIC I:6.0/11(gate closed) which these two inputs are false or not lighted the output is OTL N13:3/11 and it is true which makes the previous rung true showing the gate closed. So why is the panelview showing the wrong position. I even went as far as resetting the HMI and the PLC so if anyone has a helpful hint I would greatly appreciate it.
  3. profibus connetion

    Hello, I want to ask you. Can I connect profibus master device as I drew? If not, when could to explain why?  The 9-pole D-Sub connector:    
  4. Hi everybody, I have a GT2310 communicating with the Mitsubishi F800 VFD. I am using the Freqrol 800 communication driver, connected to the RS-485 terminals of the GOT and on the F800. The comm settings are the same on both devices. I also tried to use the “auto negotiation” setup. I have communication between the two devices. I can read and write to F800 registers.   Anyways, The GT designer diagnostics is complaining about a communication error in the system alarms. The error can be reset but it will appear again.   This also happened when I created a new, empty project where just the communication was setup as described above.   Did anyone experienced the problem and how to troubleshoot / solve this?   Best regards
  5. Greeatings .   I have modicon TSX premium plc (TSX P57103) I have problem i cant connect to my plc. I have tsx pcx 1031 cable and have com port on one PC and on the second i have connector to this cable with usb. when i try xway test i have problem , the request is always 0 . Can someone help me ???
  6. iFIX restore problem

    Hi, I have .fbk backup file of iFix aplication (i mean).. When I try to restore it by "Backup&Restore Wizard" in part where I "Browse" the way to Backup file and click on "Next" is problem. Pop-up window show -> "Bad file format. The archive file may be an old version or a wrong version in header signature or is not a Proficy iFIX full backup file (.fbk)" ....  My question is = Is possible to find what of version is my backup file ??? when i suppose this error mean i have installed wrong version of iFIX sofware (my version is iFIX 5.5).. Or is no problem of my iFIX version ?  Thanks
  7. I'm sorry, guys, but I wouldn't be asking if I hadn't dedicated about 12 hours to this already. Long story short: ACS800 with RPBA-01 Profibus Adapter and RTAC-01 Pulse Encoder Interface. All we send to the drive (aside from CW permissives) is a position reference, and I believe the DriveAP functions execute how the drive will achieve that position. My final aim is to separate the encoder from going back to the drive, to instead going to a FM350-1 Counter module. I'm following someone elses work that is long gone, has been changed multiple times, and comments are almost non-existent. Where I'm stuck is understanding the data coming from the drive and being sent to it. PPO Type 5; DPV 0. In Step7, I have a DB for 20 bytes of data to drive and another DB for 20 bytes received from drive. I understand (with respect to data from drive) that it should be: SW; ACT; PZD3...PZD10 (10 x 2 byte Words). But, when I looked through all the settings in the group 51 parameters, the values in the form of (xxyy; index then subgroup; ex: 106 is parameter 1.06) don't seem to exist in the ACS800 Firmware manual. PZD 3 OUT: 7 --- PZD3 IN: 6 PZD 4 OUT: 8 --- PZD4 IN: 10 PZD 5 OUT: 0 --- PZD5 IN: 106 PZD 6 OUT: 0 --- PZD6 IN: 0 PZD 7 OUT: 0 --- PZD7 IN: 611 PZD 8 OUT: 0 --- PZD8 IN: 612 PZD 9 OUT: 0 --- PZD9 IN: 701 PZD 10 OUT: 0 --- PZD 10 IN: 706 The manual says parameter values 1-99 refer to a "Data Set" and each number specifies a certain word in a Data Set. For example, PZD3 IN: 6 refers to Data Set 2 Word 3, which is defined by paramater 92.03. But, that turns up something about short circuit protection, when what my DB value is displaying a distance (from a linear string pot encoder) that matches what the mill is actually at. The ACS800 manual says Data Set Actual Signal words are defined in Group 92. So I looked there: 92: DS Transmit (From Drive) --- 90: DS Receive (From PLC) 92.01: Status Word (Fixed) --- 90.01: 4501 92.02: 103 --- 90.02: 4309 92.03: 402 --- 90.03: 4505 92.04: 412 --- 90.04: 1 92.05:106 --- 90.05: 3 92.06: 0 Any help would be appreciated. Thank you.
  8. Profibus connection program.

    Guys I'm having some troubles (as usual) I have datasheet for my profibus slave device (attached).  I've probably done proper configuration in cx-configurator, I've got CIO 3200 (output) and 3300 (input) addresses for that communication. There's the question. How can I assign plc bit to specific valve position (its address)? I've made simple program where I can change 3200.00, 3200.01 etc. states but BF led on prm21 still flashing, and nothing happens.    
  9. Hi again. I'm trying to make profibus connection between CJ2M and "Bosch Rexroth HF03 Manifold 12 Station DeviceNet Bus Box". After configuration I/O table in cx-Programmer and up[loading it to plc I've tried to configure settings in CX-Configurator. I've set up correct connection parameters of cj1w-prm profibus master. When I use "Test" option or just go online I get errors: "Communication Failure with unit" and "CX-server cound not be initialized". Am I missing CX-Server? I don't have this software installed on pc... When i try to use scan option i get another error: "Scanning failed, DTM returned an error for the request. Following DTM reported the error: Tag: CJ1W-PRM21 PROFIBUS Master Name:CJ1W-PRM21 PROFIBUS Master (Version V1.xx) Vendor OMRON Corporation.: Any advices? I can't find any good manual for CX-Configurator but i get CX-Profibus manual - is it interchangeable? Because i can see  some same options in both. Regards!  
  10. Hello i'm new in all things about plc, i do a project for school and i use a festo fc 34 plc. The plc is programmed via serial port RS232 my pc not support a serial interface and i use a RS232 to usb adapter. when a try to download the program to plc give me a error: "ERROR: Cannot access controller".  What i do wrong.  Thank you in advance and sorry for my English. Have a nice day.
  11. S7 300 Profibus fault

    Dear All, We are in need of your expert opinion. One of the nodes of our Crane's Cabin gives a station failure problem, due to which whole Crane shuts down. we have done everything from replacing Dp connectors to changing Profi cables, swapping modules with other stations, changing Power supplies but the problem remains the same. Following are the system details, 1. CPU S7 319 F3 fail safe 2. IM 153 interface module 3. OLM module for signal conversion fibre to profibus from main CPU.   We have several nodes after OLM but fault was persistent with 3 nodes. After comprehensive working, it came down to just one but still not diagnosed. I will also upload the diagnostic buffer if needed.
  12. Mitsubishi FX3U Suddenly Stop Code

    Hi ,Im a Electronic Technic  in a Molding Factory and i have a problem with one of the machines because is suddenly stoping of execute the code without reason,i tough that was the hmi was is working well.  
  13. Hi everyone, I want to compare 2 programs with RS logix 5000 compare but logix opens the 2 ACD in L5K, with only tags.... thx for your help
  14. Grupa ProfAs Sp. z o. o. jest firmą doradczą, świadczącą usługi w szeroko rozumianej dziedzinie Human Resources. Specjalizujemy się w rekrutacjach na stanowiska specjalistyczne, średniego i wyższego szczebla. Wierzymy, że nasz Zespół złożony z profesjonalistów jest w stanie zapewnić perspektywiczne spojrzenie i najwyższą jakość wykonywanych usług. Aktualnie dla naszego Klienta - firmy z branży automatyki przemysłowej - poszukujemy osoby na stanowisko: Programista sterowników PLC Kraków / Piła / Poznań ZAKRES OBOWIĄZKÓW: Programowanie sterowników PLC Siemens Wykonywanie aplikacji dla systemów SCADA i HMI Dobór konfiguracji sprzętowych PLC Testowanie i uruchamianie maszyn u Klientów końcowych (delegacje krajowe i zagraniczne) Wykonywanie programistycznych prac serwisowych u obecnych Klientów Sporządzanie instrukcji obsługi maszyn   WYMAGANIA: Bardzo dobra znajomość sterowników PLC Siemens Umiejętność parametryzacji serwonapędów, falowników, etc. Znajomość paneli HMI oraz systemów SCADA Znajomość sprzętowa oraz programowa komunikacyjnych sieci przemysłowych ProfiBus, Profinet, Ethernet, DeviceNet, Modbus, etc. Znajomość zagadnień i komponentów automatyki (przetwornice, serwonapędy, obwody bezpieczeństwa, aparatura modułowa, itp) Mile widziana znajomość programowania innych sterowników: Allen-Bradley, Omron Prawo jazdy kat. B Komunikatywna znajomość języka angielskiego lub niemieckiego OFERUJEMY: Współpracę w oparciu o umowę o pracę Udział w profesjonalnych szkoleniach Korzystne warunki wynagrodzenia Rozwój w firmie z doświadczeniem na rynku międzynarodowym nr w rejestrze 14990 Osoby zainteresowane prosimy o przesyłanie CV na adres k.dominik@profas.com.pl lub kontakt telefoniczny pod nr tel. 881 700 778.
  15. CX SUPERVISOR

    HELLO ALL I HAVE PROBLEM CX SUPERVISOR RUN TIME WORKING WHEN I OPEN RUN TIME AFTER 2 OR 3 HOUR IT WILL STOP AND COMMUNICATION CUT FROM PLC I USE OMRON PLC AND MT NETWORK  SETTING IN PLC  ETHERNET (FINS/TCP)  I GIVE ONE IP ADDRESS  172.17.0.85          AFTER CUT COMMUNICATION THIS MESSAGE WILL COMING MY PC    - COULD NOT WRITE TO PROJECT FILE. THE DISK IS FULL,WRITE-PROTECTED OR HAS BEEN REMOVED FROM THE DRIVER  ple told me some one  how to salve this problem    
  16. Profibus Function Blocks for Q2ASCPU for Melsec ST Lite RIO inter-connection. Please assist in advising the attainment of such blocks - if any existing. Thanks
  17. Hi,   I have a client that uses a 1560-PDP1 PROFIBUS to SCANport Comm Adapter, they discontinued this item in 2015 and prosoft does not sell a replacement.  Does anyone know of an adapter that would work in the place of the 1560-PDP1 PROFIBUS to SCANport Comm Adapter.  Thanks
  18. Hi,   I have a client that uses a 1560-PDP1 PROFIBUS to SCANport Comm Adapter, they discontinued this item in 2015 and prosoft does not sell a replacement.  Does anyone know of an adapter that would work in the place of the 1560-PDP1 PROFIBUS to SCANport Comm Adapter.  Thanks
  19. I am using rslinx in my configuration with 2 devices: windows xp computer and an SLC 5/05 CPU.  The XP PC is running a program that relies on a file that is automatically dropped in a shared folder from a separate networked PC.  The file is deleted immediately from the shared folder.  The program on the XP PC uses rslinx to control the SLC 5/05 CPU to complete the operation.  The original XP PC hard drive failed and a new PC was installed with all the necessary software and services.  Ounce I completed the  setup, the process worked for 48 hours, then stuck in one operation (one file).  Now, I can restart rslinx and the software and the process will function normally, but stall, then get stuck on one file.  There are no files in the shared folder, rslinks has not lost connection.  The original router was replaced at the same time as the PC.  I am leaning towards rslinx storing the files somewhere and stalling/stopping the operation.  I can not find files anywhere.  Does the SLC 5/05 CPU store the files?  I'm lost.  Do you have any troubleshooting suggestions?  
  20. Hi all, I have a S7-1200 CPU 1214 DC DC DC and Cm 1241 6ES7241-1AH32-0XB0 communication module.I'm using TIA Portal 14 and i connected cpu but i couldn't connect cm 1241 communication module.When i looked diagnostic i saw" Diagnostics data are not available because the current online configuration data differ from the offline configuration data.".Then i looked for what was the difference.But i didn't see.Are there anyone can help me? Thank you
  21. Problem with CX-one instalation

    Hi I have problem with the instalation of CX-One over the instalation it stops and give the message: "Error-3: CX-Server Device Driver(Generic FINS Ethernet)failed to install. Try to install it manually from CDROM (Generic FINS Ethernet Device Driver\setup.exe) at the end of instalation." Then if I go to the CDROM and try this instal manually I got the message about the "Unable to locate CX-server" but CX-server I correctly instal from CDROM with sucesfull finish message. And If I try to start CX-Programer I got the message about missing cdmapi32.dll. So what I can do about this :(
  22. Hi everyone, Recently, I started working with the Micro820 Controller Embedded I/O. My project is simple : when the output _IO_EM_DO_00 is set to true, an LED light turns on. But, even though it's super simple, I can't make it work. Here's my setup. If you need more information, feel free to ask anything !
  23. Hi everyone ! I have a little project wich involves communication between two Micro820 controllers via TCP/IP. To do that, I started to work with TCP/IP socket. Within CCW (Connected Components Workbench), I tried to create a new socket instance using the instruction SOCKET_CREATE and set the socket address to 127.0.0.1:21. Basically, my computer through the FTP port. The problem was that it couldn't create a new socket instance (error variable is set to TRUE and status is set to 4, wich I don't know the meaning) because I didn't have a server-side application that listens to TCP/IP socket requests. That said, I found an open source application called SocketTest that listens for TCP/IP socket requests on a specified IP address and port. So, I started a listener on the following address : 127.0.0.1:21, but the error variable is still set to TRUE and status is still set to 4. So, my questions are : Is my IP address OK ? Is my port number OK ? What means the status code 4 ? Is SocketTest doing what I think it does ? Do I need to do something else before using the SOCKET_CREATE instruction ? Thank you in advance for your help !
  24. NB Designer V1.4

    I found NB Designer really struggled running on Windoze 10 Pro x 64 bit - bloody painful to be honest - on both the massively fast desktop and very fast laptop - no time to wait around - likes my horse power. Selected it to run in Windows 7 compatibility mode - way better - quite nippy actually. Highly recommended - it appears the NB Designer team may have not quite caught up with the latest Windoze OS.
  25. profibus packet problem

    I am new  in Siemens. I want to connect the oscilloscope to the TX and RX of the profibus  between PC and PLC . That is,I can observe its  wave and  packet. But , I  don't know how to understand this protocol . Is there information or paper about the Profibus protocol? thanks.