Search the Community

Showing results for tags 'power meter'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 36 results

  1. Power SCADA Expert 8.0 Need help

    Power SCADA Expert 8.0 Need help. May I know how to start for this power scada and how to use Template Editor, Profile Editor, and the equipment editor?
  2. Hi everyone, Currently i am having a PGP server fail to connect to the node as per the ICI status screenshot as per link below. https://www.dropbox.com/s/0qg435zkqzou9p3/Node%20Disconnected.bmp?dl=0 Appreciate anyone can assist me on this matter. I'm a new control engineer who just started working in a power plant and has limited exposure to the troubleshooting of this and i really hope that any of you can assist me. Thank you very much.
  3. 1738-EP24DC

    I have an EP24DC module that will not supply power to the bus. Swapped the module out and still have the same issue. Any Idea's !
  4. I need to make a setup like the readings in the energy meter should be a GSM then from this GSM the data should be sent to another GSM using Twido PLC.,please help me how to establish this connection. (Energy meter ----+ Twido PLC----+GSM) data from this should go to another similar set up (GSM----+Twido PLC---+Energy Meter) I dont know is this possible or not please help me,,
  5. ML1400 and C400 Resetting Values

    At work we have been having a slightly increasing number of instances where the Micrologix 1400 that is paired with a Panelview C400 resets values when we cycle the power. Originally we thought the solution was a bad battery in the ML1400. This was the case the first few times that it happened. However, we recently had one doing the same thing and when the program was loaded onto another PLC and HMI combo it had the same issue. So either the battery for both just happen to be bad, or there is something in the program that is forcing the values to automatically reset when the power is cycled. I cannot post the program on here but I can tell you that the tags that are being reset are only used in the PLC program once. There are six total that are being reset and they are the high and low range in an SCP function that is used to scale inputs. I will be testing the program myself in house on a bench setup, but I wanted to get this question out there as soon as possible in case it is not an obvious problem. Has anyone seen this before? Any suggestions? If I come up with an answer I will post it. Thanks.
  6. SIMATIC OP7 RAM failure

    In our SIMATIC OP7 console ram failure message is appering while power on, do anybody know about the problem and its remedy ?
  7. Hi Good Day, I need a suggestion, I have an omron encoder, encoder counter meter (K3NC-NB1A) and communication card RS-232C 25pins (K31-FLK1). My question is, what is the best omron software to read and manipulate the data from the encoder (I have CX-one software but I only use CX-programmer). I want to capture the encoder pulse and convert to velocity, acceleration, deceleration and also energy absorbtion. I have to use mathematical formula such as two times differentiation. I also need to show grapf and display final result that is energy absorbtion reading. Or is it much simple if I use VB / labview / java software? Thank you in advance
  8. 1734-AENT 115VAC

    I wonder if there is version of Ethernet Remote IO that can be used with 115VAC supply rather then 24VDC? This would save me a power supply which is really needed for this module only.
  9. Micrologix 1400 HSC:0 Looking for a configuration example. Using a gas meter with a contact output representing x pulses per cubic foot of gas. Want to calculate flow rate and totalize.
  10. Dear All, I have a little problem in reading data from Power Meter to Vijeo Citect v6.0 I'm using Schneider PM810MG for Energy reading from Power Meter and for the SCADA I'm using Vijeo Citect v6.0. I can do some simple data reading like current, voltage and the others using variable tags from Vijeo Citect with Data type INT. But i dont know how to read the data for "Real Energy In" since the data range from 0 to 9,999,999,999,999,999. Waiting for all your help soon. Thx. Best Regards, Budiman Chandra