Search the Community

Showing results for tags 'now a software solution is available for your modbus (mb) needs in rockwell/allen-bradley control logix or compact logix (clgx) family processors instead of a traditional 3rd party hardware like prosoft mvi-56'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 550 results

  1. - i'm from VietNam, Who can help me?? - I cannot communicate the RFID card reader with the FX3U PLC using the FX3U-485ADP-MB module; - register error D8438 = 3821; D8423 = 1025; D8422 = 212. - Here is the connection picture and my PLC code thanks !!!!
  2. NSF Converter PST

    eSoftTools NSF to PST Converter is another effective solution which helps to recover NSF files to PST without losing or tempering any content. It helps users to convert NSF files to PST, EML, EMLX, MSG, HTML, MBOX, VCF, CSV, ICS, Zimbra, Gmail, Yahoo and Office 365 format. A preview is displayed at each step of conversion for a better experience. Even a free edition is also presented to the user to check the performance. Read More - NSF Converter PST  
  3. Hi all,  I want to ask some questions regarding Ethernet Communication with FX3U PLC series. I have 2 PLCs of FX3U series (FX3U-48M and FX3U-64M) and I want to monitor its data (input and output) using ethernet communication in real time. My questions are: 1. Does FX3U PLC have ethernet port so I can connect it directly to my Laptop/PC? 2. If no, do I need to use FX3U-ENET-ADP and can it be used for 2 PLC or only 1? 3. What software do I need to use to configure the communication between PLC and FX3U-ENET-ADP? 4. Does this configuration change the existing PLC program? 5. Can i transmit the data wireless-ly using some kind of ethernet to wifi adapter and what additional hardware do i need for that?  
  4. I want to take data from an AllenBradley SLC 505, and send it to an Omron NX102-9000. Specifically F8: 46 from my SLC 505, which is a temperature sensor. Both PLCs are on the same Ethernet network, each with its own IP address. Have you tried it?
  5. Create TCP/UDP Socket

    I'm trying to send an int over TCP using a MSG Socket,  Compactlogix ==> Arduino Ethernet Shield I have set up TCP communication between two Arduino Uno's using Ethernet shield. I've set up the one as a server, the other as a client. server IP: 192.168.1.21 port 23. If the client is connected it reads incoming data as a byte or an array of bytes. The data between the two has been verified to work. I'm now trying to transition the communications between a compact logix-L32E. I'm looking to send a byte (or int being as there's no byte data type) from the Compactlogix to the Arduino using TCP. To my understanding I need to use a socket create, open, read/write, close. The manual to do this is vague as a step by step procedure. Does anyone have an example code for socket programming? I can open rs500, rs5000, and studio 5000 programs. If I can open a file to use as a reference I can translate it on my own. Any help/advice would be greatly appreciated. 
  6. Pneumatic Air

    Short backstory: We have a machine programmed with AB that has several banks of air solenoids.  This is an older machine so the solenoid banks are of the older variety.  On each bank there is a pressure switch that is outputted into a Allen Bradley 1734 Safety RIO module.  We are adding new modules to this machine after about 10 years and the Mec Eng. chose Festo CPX banks, but they did not put pressure switches on them. Question: Is it a requirement (OSHA, OMAC, ISO...etc. any of them really) to have a pressure switch for air module?  Or are they used to just make the machine smarter?  The big concern that I have is that the customer will notice that these new CPX's don't have pressure switches to monitor the status of the air like every other bank on the machine, then questions will be asked...yatta yatta...
  7. Hi, I have an old TSX 47 30 that has an I / O fault (red led on) green led on run and plc stopped. I'm writing to see if you can help me to establish communication and achieve the download of the program. I do not have the communication cable or the PL7-3 software under OS 2. So far I have done searches on the schneider page, forums and all the links are lost or deactivated. I have read your answers in plc of the same series and I observe that a converter rs 232 to current loop is needed. In this case here in Venezuela it is difficult to get this converter, however I have observed the black box model 232 CL-E, CL050A and I think it can be useful. I also have an old toshiba laptop with windows xp with a native rs 232 port to avoid another converter and I could make the connection cable DB25-DB9 to the PLC. Now I would miss the procedure to make an OS / 2 bios and get the software or make a virtual machine in which case I require the appropriate software .. thanks for your help
  8. Q03UDVCPU Modbus Setup

    Hi Guys, I need help to set up modbus tcp/ip parameter for Q03UDVCPU, i want to use the predifined protocol and built in ethernet port. do you guys have some usefull references how to setup modbus tcp/ip, or is there any example program from mitsubishi? Thanks
  9. Dear Engineerds,   My Master (non siemens) doesn't see the Holding Registers of the Slave (S7-1200) plc. However the Q coils are fine and all Diagnostics don't show errors. The Hardware: S7-1200 – CPU 1215C CM PtP – CB1241 RS485 (6ES7 241-1CH30-1XB0) - Half Duplex RS584   Firmware: Modbus_Comm_Load (V3.1) Modbus_Slave (V4.0)   I've tried with various DB, UDTs and manipulating HR_Start_offset parameter with no success. Could you advise what am I possibly missing? Modbus_Comm_Load_DB_Snapshot.xlsx Modbus_Slave_DB_Snapshot.xlsx
  10. I'm having trouble with some Powerflex 525 drives. Right now what I need to do is run them manually from the keypad to test conveyor belts.  Is there a way to do this and if so how?   Thanks in advance.
  11. MDS instruction would not complete

    Hany any you of guys dealt with MDS instruction not completing and being stuck on .EN bit but the motor itself just stopped running out of nowhere? I did read the tech note on this on Rockwell's website. Am mostly wondering if any of you have dealt with this and what you did to fix this.
  12. Square Wave Problem With Micrologix

    Hello all, this is my first post. I am using an AB Micrologix 1400 (1766-L32BXB Ser C FW 21). I was trying to generate a pulse train using the PTO instruction. I have modified PTOX funct. file. The ladder is just a simple XIO followed by PTO, (The Quick Start ladder from 1766-RM001). When I looked at the output waveform on my oscilloscope, I noticed that it wasn't a square wave. I decided to run it at several different frequencies to see how the wave form would change. At 10Hz i got a square wave. As I increased the frequency the falling edge became sloped and almost horizontal. Is this how the output should behave? The data sheet indicates a max frequency of 100kHz, but at frequencies over 150 Hz. The wave form looks like the output of SMPS. 
  13. I have a purchased Machine that came with a Siemens LOGO 8.FSR PLC (Smart Relay). Generally we use Allen Bradley or Mitsubishi. Anyway, we need to communicate data between the LOGO and an Allen Bradley Compact Logix.  I do not desire to add an additional network to the AB but as best i can tell the LOGO is exclusively Modbus TCP/IP. Has anyone come across a similar situation?  I look online and did find an  Anybus module that claims to be able to link them together.  Looking for anyone who has faced this challenge and succeeded, or failed.   Thanks
  14. Hello Everyone. We have Schneider TM241 PLC Along with Citect SCADA System at 100MWp Solar Power Plant to monitor and control various equipments like Inverters, Switch-Yard, MFMs, Weather Monitoring Systems etc... Government Authority here asked every solar plant to control the generation as per the instructions by Load Dispatch Center, for that we need to implement logic to control Generation as per requirement. For that we are controlling generation from inverters by giving them generation setpoints calculated by PLC using PID function.   But we are facing one problem while using PID. (FB_PID of Toolbox Library)   Suppose we need to generate only 60MW out of 100MW. So we set PID setpoint to 60MW and according to that we get PID output and according to that PID output value we provide generation setpoint to every inverters.   This system works very fine until the clouds comes into the picture.   Now suppose Setpoint of PID is 60MW and PV is also near about 60MW, and suddenly large cloud comes over plant and block solar radiation.   In this case generation comes down to 10MWp(or any value below 60MW), So output of PID will Increase and keep increasing and settle at the Maximum value. but without solar radiation generation value stays very down then Setpoint.   Now suddenly Cloud moves and again solar radiation increase, but the PID output is maximum at that time so, Suddenly Generation goes from 10MW to near about maximum capacity (100MW) instead of 60MW, and then it will slowly comes down to 60MW.   We need to rectify this generation shoot up when cloud moves. Anyone have idea how can we solve this problem or anyone have programmed PID in this kind of situation.   Is there any function block available to do this correctly like function block of PID with two Reference or something like that...   We are using TM241 which is CoDeSys based PLC.
  15. From DM:   Hi; my name is Metin , I live in turkey. unfortunately I have a problem that I could not reach a conclusion here. I hope you can help. I need to communicate with CJ1W-ETN21 with a device via modbus tcp and read information. I downloaded ready-made protocols on omron site, connection is established but I cannot read. I tried the attached protocols. the device I am trying to communicate with :  https://www.gmweighing.com/products/weighing-indicator-m02  I will get the weight information from the weighing device. Thank you in advance for your help. MTCP_ETN_Client.zip
  16. Hi there, Im having issues controlling ATV 320 VSDs over Modbus RTU with a M221 plc, does anyone have any pointers for me to look at? I believe I Have set everything up correctly but when I run the program on the plc the atv's just stay in 'NST' state I have included screenshots if they are any use   My speed reference in this example is taken from the memory word %MW0 which I am inputting via a HMI   I have addressed all my ATVs accordingly in there setting with the correct Modbus parameters and selected Modbus under the FR1 configuration, am I missing anything?? Any help is appreciated as I am really struggling   Tom
  17. Hello everyone, I have a Kinetix 6000 CIP drive (unwind) and I need to control its speed by a PID controller. I have everything working except the MCD instruction doesn't pick up on the PID output value change. It changes the JOG speed, which I use to control the unwind, if I set the speed manually, which is slow. The PID changes the speed almost continuously. Any suggestions are welcome. This is how I'm attempting to control the speed: A1_r_JogSpeed = PID output value   Thank you    
  18. Hi everyone I'm new bie, I try to control VDF-M via fx1n-485-db. please help!! Thanks.
  19. Hi everyone I'm new bie, I try to control VDF-M via fx1n-485-db. please help!! Thanks.
  20. Powerflex 525 single phase

    Hi ! I have a powerflex 525 inverter. I have three phase motor. It is possible to make running the motor like this? If yes how ? Should I change some parameter in the inverter ? Thanks in advance. 
  21. hello expert i want ask some help So i tried to communicate my Omron PLC (cj2m cpu31) with SCADA from Schneider (power logic) on my omron side the comunnication on PLC already take to communication to NB so i add communication module CJ1W-SCU41-v1 I want asking how to open the communication if i want the scada become a master and my plc become slave i got this from omron website is that program compete for my case? i need configuration for scu41 module also to communicate or if you have suggestion i really open i just need to open port RS232c from scu41 so scada can read the data from my plc  tahnkyou for your help MRTU_CPU_Slave.zip
  22. Good day all. I have an application which is running an Allen-Bradley SMC-Flex and the client would like to get the monitor the current of the soft-starter via an HMI connected to a Delta DVP-12SE. Is the SMC able to output a current and with what communications medium would I use?   Thanks.
  23. Indusoft Web Studio

    i am using indusoft web studio for the modbus logging. program runs successfully but after a half day or a day it shows error " error initializing the driver modbu 10.10: invalid serial port "any suggestion will be appreciated.RegardsZubair Ahmed
  24. Hi All need to convert a Decimal Value into Ascii code to send out on serial 485. eg. Weight comes in as Int 12345 i need to send it out in Ascii as 23 32 20 31 32 33 34 35. I have created an array 0 of 8 (Word) DB. Is there an easy way split the int into Digits convet in into HEX and slot the value into the various array positions? Array 0 of 8 = 23 means # Array 1 of 8 = 32 means 2 (Station ID) Array 2 of 8 = 20 means Space Array 3 of 8 = 31 means 1 Array 4 of 8  = 32 means 2 Array 5 of 8 = 33 means 3 Array 6 of 8 = 34 means 4 Array 7 of 8 = 35 means 5 Array 8 of 8 = D means CR    this sends the value of 12345 to Display ID 2 . need help to convert the decimal number in ascii. the decimal number will be max of 5 digits and less than 32000   any help will be greatly appreciated.
  25. PLC to PLC communication

    Hello everyone Does anybody knows how to estblish a communication between 2 Mitsubishi CPUS with modbus? THey are RCPU and FXCPU