Search the Community

Showing results for tags 'moore 352 digotal loop controller'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 63 results

  1. I am trying to create an Alarm handler for an NA5 HMI that can tell the end-user the 1SAN Drive AL Status code and an Annunciation according to the manual: I621. I already am using a similar method to use MFaultLvl.Codes in a Case statement that creates a message found in motion controller manuals. Ie. 16#6449: Fault_Axis0 := '1S Axis Immediate Stop Input'; I want to use the AL Status to create messages based on the Hex Code generated by the Alarm ie 16#20: DriveAlarm_Axis1 := '1S Overload Error'; 20hex being the AL Status from the Drive. However I  cannot find how to access AL Status from the Troubleshooter.   Thanks
  2. Facility where I recently started working has several "ancient" Moore APACS DCS systems.  The resident guru/expert has announced that after 40+ years with the company he'll retire next year.  The existing engineering team I joined was slowly converting from APACS to ControlLogix and this effort will get more attention now obviously.  Recently our Schneider Service Rep mentioned that they have an upgrade path for APACS to current tech with no re-wiring required.  The presentation was impressive as you would expect.  But I am wondering, anyone out there who has actually worked Moore APACS and Upgraded to Schneider Ecostruxure and care to share your joys and heartaches of that trip?
  3. Hey guys,  I'm trying to build a therapy tank for burn victims that requires a few automated processes of which I need help! Essentially this device will function a lot like a temperature controlled "hottub" with an circulation pump but on a much smaller scale (like 10 gallons). I would also like to be able to observe and control the device remotely outside of the users direct control for programming therapy temperatures. The goal with most patients is to start them at a temperature just under body temp (around 94) degrees and the get them down to treatments in mid 60's over time. The machine will used a liquefied burn gel that has a consistency like thin vegetable oil.  Here's what I need in a controller: ON_OFF functionality for a liquid chiller.  Contact relay for reed switch to disconnect power to device when lid is open. (this is a safety feature - when the treatment tank lid is opened I would like for a relay to disconnect the chiller's power through LV to ensure there is no chance of electrical shock.  "Delay On" relay (The chiller is and on_off refrigerant based device that will require a "delay on" relay to allow head pressure to dissipate before restarting) (See below) ON_OFF relay with programmable timer functionality for a liquid circulation pump. (to be set at intervals throughout the day) Temperature controller for K-type thermocouple - this will be used to monitor, maintain, and cool liquid. PID or Arduino? (Will need the ability to establish limits on backend) The ability to display temperature in either F or C Functionality: Ideally each unit would have a controller similar to an on_off temp controller or PID so that the home user could manipulate controls within a limit on the device locally. The device would then automatically maintain temperature based on set point and would have timed on_off sequences throughout the day for the liquid pump which were programmed into the device logic. This functionality in addition to the safety cut off features for use are all I need this device to do. Safety feature - being that this device could be in the middle of a chilling cycle when a patient would want to use it, I would like for the device to have the ability to instantaneously cut power to the HV 110V 16A Pump and Chiller without damaging those devices upon restarting... For instance if someone were to open the lid to feel the water and close the lid again quickly, the on_delay timer set to around 5min would prevent the compressor from restarting until the 5 minutes passed, thus keeping the short cycling from damaging the refrigerant system.   Remote monitoring and commands I would like to have the ability to push settings to these devices all across the city/state in peoples homes. The controller would need the ability to connect to wifi and transmit information as well as receive commands. This feature would be for those who would be put on a therapy program where we would control and push temp settings to their device remotely. Mobiel User Interface The BIG goal would be to tie all of this together and be able to control a device via iPhone or android. User downloads the app - The app has the ability to: turn on off off the device  adjust temperature (again within limits) turn on a timer 15 minute filter cycle with the press of a button Select/program a filter schedule with up to 8 time slots Circulation filter replacement reminders (messaging function) Therapy reminder.  Opt in for therapy pre programming pushes - me pushing temp settings to their device. Thats the novel for now!! Looking for someone interested in building this, or anyone willing to guide me through the process. This is just an idea and my 9-5 is a physical therapist, but I would love to bring this vision to life!   Sorry if this is fragmented or ignorant, but I just need help getting started or pointed in the right direction! 
  4. IC200EBI001 firmware upgrade problem

    As I follow the instructions as shown on the instuction leaflet 82A1043-PM01-A1 The whole proces stuck at step 15. leds are blinking "waiting to receive new firmware"  but  ftp command  "put"...  fails   reason: "no connection with host"  Does someone has experience with this firmware updates? regards John
  5. Please let us know if anyone needs to have their Siemens Moore Mycro controller repaired. We can repair these for you depending on the model. 352EA21NNF, 352EA21N1F, 352BA etc. We can also repair the power supplies that go with them and can upgrade the unit from B level to C level software. If you would like a free quote please contact us at customerservice@OttoAutomation.com  or visit us at www.OttoAutomation.com. All repairs come with a full 1-Year warranty and also include a complete refurbishment and testing to extend your units life cycle. Any member of this site will also get a twenty percent discount on these units. Thank you, Otto Automation
  6. Siemens Moore Mycro 352

    Hi, I was wondering if anyone knows where I can get the configuration software or the manual for Siemens Moore 352 and 353 digital loop controllers? I would be willing to purchase the software if anyone has a copy. Thank you. 
  7. controller is not coming online with rslogix 5000, but i can ping the ip from the pc. getting the error message says "controller failed to come online - error 701-8004250B" appreciate ur help.
  8. Hello friends I have worked with other series of omron plc but this is the first time I am working with cqm1h cpu51 series. In a factory, 4 of these PLCs exchange data with each other with a clk21 card. After a problem with one of the CPUs and replacement, I was never able to download the datalink settings. I did all the steps in the manuals step by step but I did not succeed. In cx-net software, after selecting online, I selected the data link menu, but as you can see in the attached image, the setup button is never activated. Thanks for guiding me
  9. Hi All, I am a new user to this Forum and definitely a newbie PLC user, so I'm not sure if this is a simple mistake. I am currently trying to correct the logic (of a sensor) on a PLC program to get a manufacturing machine back up and running. This is an issue that I have fixed via PLC several times previously, but for some reason I am having issues fixing it this time. The issue that I am having is that when I try to dig into the Logic of the PLC program (Programming > POUs > Programs > Logic > ...), nothing shows up where there is typically a PLC command ladder. I get the error "No instruction in rung" next to all of the PLC program modules. I am connecting to a Omron NX1P2 CPU via laptop & Ethernet cord. To give you background on my troubleshooting process, I have verified that the I am connected to the PLC controller, by using the Windows Run program to ping the IP address of the controller. After verifying connection, I attempted to connect to the controller using SYSMAC studio. At this step, a troubleshooting window appeared with the issue "Minor fault" "Tag Data Link Connection Timeout". When I look at the Controller Status at the bottom right corner of SYSMAC, it says that I am online and connected to the correct IP address (green circle). Under that, ERR/ALM has a red circle next to RUN Mode. Ignoring the troubleshooting window, I can click Synchronization and "Transfer from Controller". A dialog box pops up and reads "...Controller does not have the POU program source...". Pressing yes to ignore this, the transfer completes. This is where I encounter the issue of having nothing show up within the path of Programming > POUs > Programs > Logic > ... . I have a feeling that this is a connectivity or settings issue, but I am not sure. I have checked my ethernet splitter (D-Link DES-105) and everything seems to be connected and working. If anyone has some insight into this issue I would greatly appreciate any help. Thank you in advance! Best cszikszai    
  10. Remote Omron and Yaskawa control

    Information : On the websites - https://abrysshost.web.app (and https://abrysshost .firebaseapp.com ) detailed information about the construction of remote diagnostics and control (Iot) systems for control systems of objects based on OMRON and Yaskawa controllers. The information is presented in Russian and English.
  11. Hey Guys,  So i am working with Omron software to integrate it with the HMI screen.  Whenever I receive a user alarm, I have an acknowledge button on the screen, but when I click on it,  the alarm does not go away from the screen,  it is acknowledged though.    Can anyone please guide me to what changes I have to make in the system to make the alarm notification go away, or is this any sort of a bug in the Omron software ??   Please help guys !!!
  12. have a good day! and thanks for reading! this is video when i start program (after 10second the Axis4 move couple of times : https://drive.google.com/file/d/1HNB07ZzH0-lBHFFwaRIhcSGUxp1m0XHz/view?usp=sharing   if you see the images that i attached you can see, IF test - afterConverData1 > 0.1 MC_MoveAbsolute4(Axis4~~ ElSE IF test - afterConverData1 < -0.1 MC_MoveAbsolute4(Axis4~~   if the plc run cycle ever 1ms, why that code don't executed every 1ms? example, test - afterConverData1 this condition value go over like 10 or -10 but the condition > 0.1 or < - 0.1 dosen't figure it out to run the code "MC_MoveAbsolute4(Axis4~~)" they just run code couple of times  What am i do for this...?  
  13. Hello from korea :) i got some problem writing loop code in sysmac studio what i wanna do is simple, running process together with loop if u see the picture that i attached there is IF condition, i want my machine run loop in "if" condition but if i use while loop maybe other process dead right lol? in words... running process, i want my machine check the "if" condition....   What can i do in this case?   Do i have to run whole process in loop?    is there any way to run loop with Other process keep going....   Thanks for reading!  
  14. Structured text syntax error

    I'm writing a Function Block in Structured text language. I'm only testing, so the function doesn't do what it has to do. However, my first step is make a for loop inside a while loop, this is for increment the value of a index register while a condition is true.   My code so far:   WHILE X100 DO;          FOR ID_INDEX := 0 TO 99 BY 1 ID_INDEX;         ID_INDEX := ID_INDEX + 1;     END_FOR;                     END_WHILE;     X100 is my boolean for general start. ID_INDEX is the index for a array that I want to manipulate.   The errors that GXWORKS2 tells me are the following:   -  Cannot find 'END_WHILE' in a statement. Please check the error display statement or the preceding one.    C8006 -  Parser error.    C1200   This is the first time that I write code on Mitsubishi structured text, so I based on the examples that I saw on the structured text manual.   
  15. Hello,  Sorry I'm newbie with omron plc programming. I'm wondering how can i simulate plc program on sysmac studio with Hmi on Nb designer without hardware. because I want testing my program and my plc and hmi connection before buying hardware. Thanks in advance !
  16. Hello My emulator go to fault state as soon as it goes online and runs (Within a second) and the following error  Code 01, (May have been caused by an infinite loop, a complex program, or a higher priority task.) The same logic runs perfectly fine on a colleague's laptop  I'm using  RS Logix 5000 V30.00  Emulator V30.00.01 Running on Virtual Machine, Windows 7 Host system specs are:  8 GB RAM  Core i5 CPU @ 1.80GHz Socket 1 Cores 2 Logical Processor 4 Windows 10 Virtual Machine's specs:  4 GB RAM  Number of Processors: 2 Number of Cores per Processor: 2 Kindly suggest a suitable solution, what is the possible cause of this fault.    Thank You  
  17. Loop through optimized DB.

    Hi guys. Im trying to figure out how to loop through a number og object i an db. I received some controls modules for a project. I have to chaeck if any of them have an unacknowledge alarm. I could do it the manualle way but theres alot! there's 5 alarms on every analog. So I started to do a loop as i would have done it before theese optimzed block was an option... As I tryif to show in the picture theres a mix og optimized and non optimized block. the Bit "SCADA_ALARM_ACK", How can i loop through all 5 of them and then go to next opbjoect lidsted in the static? Please let there be a solution other than manualy check every single one......  
  18. Hello, CJ2M CPU-32 to IAI motion controller through ethernet/ip I'm working on programming electric actuators to pick up parts from a tray. I will have x (row) and y (column) coordinates that I need to update to move the actuators. So to go through the whole tray I would have to use nested loops. (below what i'm trying to achieve if i was doing it in C++)                                           6 Rows and 6 Columns, palettizing                                           data rows&columns DWORD (Row1,row2,row3...row6; col1,col2...col6)                                           c++ code                                           for i=0,i++,i<6;                                               rowData = row                                               for i=0,i++,i<6;                                                   colData = col                                                   execute movement                                                   wait for confirmation                                               end                                           end I have a way of doing it but it will require a lot of repetitive lines and typing every step, and I was wondering if there is a way on every iteration to increment the data location instead of the contents. In the picture below you can see the example where the goal is to copy data from D8100 to D8000, then in next step from D8102 to D8000, then from D8104 to D8000 and so on. So far in the documentation I was only able to find how to increment contents. Is it even possible to do what I want to?
  19. Hello Engineers, I  am Will from Levetop semiconductor. Our main product is LCD/TFT graphic controller. Support 8/16-bits MCU parallel interfaces, and SPI, I2C serial interfaces Built-in Ggeometric Drawing Engine: provide Point Drawing, Line Drawing, Curve Drawing, Ellipse, Triangle, Rectangle, Rounded Rectangle Drawing Built-in 2D Graphics Processing Unit: provide Magic Rotation, Reflect, PIP (Picture in Picture), Hybrid Graphics and Transparent Display Built-in 128Mbit Display Memory Support 16/18bits RGB type TFT Panel from 320*240  QVGA to 1280*1024 SXGA Built-in Standard ISO/IEC 8859 Fonts Built-in Two 16-bits PWM Timer Support SPI and I2C Master Interface Three Power Saving Modes: Standby,Suspend and Sleep mode Package: 128pin LQFP We have STM32/ST51C demo code open for developers, function libarary and Arduino Library available, too. Our product P/N as follow: LT7681   640*480   8/16bits/SPI/I2C LT7683+  1024*600    8/16bits/SPI/I2C LT7686   1280*1024  8/16bits/SPI/I2C LT7680A  640*480   SPI/I2C LT7680B  800*600   SPI/I2C LT7680+  1280*1024  SPI/I2C any questions, feel free to contact us   www.levetop.tw/en
  20. Hi everybody,For a while I’ve been wondering, in every plc forum where the use of loops come to discussion I find most people answering that it’s best to stay away from them and that there are better, easier and mostly less scan time demanding solutions out there. Why is that?In my experience they’re the next best thing.Why would referencing data from an array of 40 Dwords using a FOR X:= 0 TO 40 DO loop be any more scan time demanding then the PLC scanning through 40 rungs of statments?Just curious if I’m missing something here. Cheers
  21. Please could you assist with the software required to download data tables from 4 off DIRIS A10 Multifunction Meters into TM221CE40R Logic Controller via TMC2SL1 Comms Cartridge using Modbus Protocol over RS485. I have downloaded the Modbus tables from Socomec but not sure how to get these into the PLC. I would really appreciate your help in achieving this. I am using EcoStruxure Machine Expert - Basic to program the PLC & DAQ Factory Developer Release for my Touchscreen. Link to Socomec Modbus tables: https://www.socomec.com/files/live/sites/systemsite/files/SCP/6_gestion_energie/diris/diris_a10/DIRIS-A-10_COMMUNICATION-TABLE_2018-01_DCG01013_MULTI.html#General
  22. Hello,  I have 30 recipes(g_Blend_Recipes) and want to search for an item number in the recipes and compare it with what the operator enters on the HMI. The recipes itself is an array and there are 5 item numbers in each recipe. I read about the FSC instruction but did not figure a way out yet. I am attaching a picture of the recipe. Any help would be appreciated.     
  23. Omron_control

    Version 1.0.0

    170 downloads

    New app developed - Omron_control for connection Android smartphone and OMRON controllers.
  24. View File Omron_control New app developed - Omron_control for connection Android smartphone and OMRON controllers. Submitter sasha Submitted 08/17/19 Category Utilities
  25. Please help find a controller. We require a controller for 8 nema 23 stepper motors. Must have pulse direction and at least 8 axis or more (16 would be nice). Must have kinematics for linear and circular motion. Must be able to use gcode such as G01 X10 Y10 Z10 A10 B10 C10 U10 V10. Must have axis parameters for all 8 axis eg velocity, rotations, etc. We also need the drivers. Must be reasonably priced under $1000 or so. We found Dynomotion KFLOP which can do 6 axis and we kind of made it work for 8 axis. It is super cheap at around $250 plus KStep drivers so under $1000 total with free software, unfortunately, it can not do kinematics for 8 axis.