Search the Community

Showing results for tags 'modbus rs485'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 209 results

  1. Hello, I'm trying to connect a CJ1M-ETN21 as slave Modbus TCP with a Modbus/Dali Gateway. I download from Omron website some FB with ones should be possible.   https://www.myomron.com/index.php?action=kb&article=1245 The FB only can be used with the direction unit 0, but we can change some directions inside the FB and can be adjusted to other units. In the download I found this FB: MTCP_ETN_Connect, MTCP_ETN_Fn01, MTCP_ETN_Fn02, MTCP_ETN_Fn03 .... Supposed with connect we can establish the connection with the master, but the FB never make nothing. Should I make some special configurations to use this FB? I appreciate any help. Thanks
  2. Indusoft Web Studio

    i am using indusoft web studio for the modbus logging. program runs successfully but after a half day or a day it shows error " error initializing the driver modbu 10.10: invalid serial port "any suggestion will be appreciated.RegardsZubair Ahmed
  3. I have a Siemens HMI 6AV2 124-0MC01-0AX0 in my machine. I want to clone the display on the HMI to PC/Laptop. My question is: 1. What software that I need for this task? 2. What kind of interface that I need between the HMI and PC/Laptop (for example ethernet cable, etc)? 3. Do I need to communicate with PLC connected with HMI or can I just connect with the HMI? Thanks in advance for the answer.
  4. Modbus with CJ1W SCU31-V1

    Hi every one, I want communication Inverter mitsubishi D700 with module CJ1W SCU31-V1,  any one give me a correct solution and send any sample program. Thanks
  5. I'm trying to communicate with INVT PLC and DGM8002(grain moisture analyzer) via mobus RTU.   Can anyone explain about these Modbus address ? Please kindly see in picture . example working mode address K0 (0-stop ,1-manual,  2-Auto) Actual Moisture Address K6 What is meaning of K0,K1,K3,K6.  https://drive.google.com/file/d/1-mGzpEvw4UlewWhR9k3wOd1mO-uhsklL/view?usp=drivesdk Is that K0= 0000 K2 = 2000. K3=3000 ? Any suggestion please. I'm really appreciated your comments.❤️  
  6. Hello I have a wago PLC and i try to communicate to a device through RS485 using the module 750-652. I tried using the WagoAppCom library and came up with this code But i always get errors regarding FB_init block. I though the instance would be automatically matched. I still can't see how to resolve this as Wago library documentation is very poor and contains 0 examples. Has anyone else solved serial comms problems?  
  7. Good day everyone!   I have some question relate with above subject. While i try make protocol for the CJ2M PLC.  i found out "Primary Expression (yN+x)" function but i cannt understand what`s this for. even i tried to find in the reference manual. i can not.  you can find it "Message Editor" -> "Message Variable" -> "Variable" sorry i tried to upload picture many times but it kept showing failed to upload.    hope so i could find the answer. thank you!
  8. - i'm from VietNam, Who can help me?? - I cannot communicate the RFID card reader with the FX3U PLC using the FX3U-485ADP-MB module; - register error D8438 = 3821; D8423 = 1025; D8422 = 212. - Here is the connection picture and my PLC code thanks !!!!
  9. Q03UDVCPU Modbus Setup

    Hi Guys, I need help to set up modbus tcp/ip parameter for Q03UDVCPU, i want to use the predifined protocol and built in ethernet port. do you guys have some usefull references how to setup modbus tcp/ip, or is there any example program from mitsubishi? Thanks
  10. Dear Engineerds,   My Master (non siemens) doesn't see the Holding Registers of the Slave (S7-1200) plc. However the Q coils are fine and all Diagnostics don't show errors. The Hardware: S7-1200 – CPU 1215C CM PtP – CB1241 RS485 (6ES7 241-1CH30-1XB0) - Half Duplex RS584   Firmware: Modbus_Comm_Load (V3.1) Modbus_Slave (V4.0)   I've tried with various DB, UDTs and manipulating HR_Start_offset parameter with no success. Could you advise what am I possibly missing? Modbus_Comm_Load_DB_Snapshot.xlsx Modbus_Slave_DB_Snapshot.xlsx
  11. Hmi temperature delta

    I have connected 2 temperature devices with him delta with plc delta by rs485. When I run plc I can see the temperature change on pc but the problem in hmi  it's give errors. Com 2 errors  I need someone help me to connect these devices please 
  12. From DM:   Hi; my name is Metin , I live in turkey. unfortunately I have a problem that I could not reach a conclusion here. I hope you can help. I need to communicate with CJ1W-ETN21 with a device via modbus tcp and read information. I downloaded ready-made protocols on omron site, connection is established but I cannot read. I tried the attached protocols. the device I am trying to communicate with :  https://www.gmweighing.com/products/weighing-indicator-m02  I will get the weight information from the weighing device. Thank you in advance for your help. MTCP_ETN_Client.zip
  13. Hi there, Im having issues controlling ATV 320 VSDs over Modbus RTU with a M221 plc, does anyone have any pointers for me to look at? I believe I Have set everything up correctly but when I run the program on the plc the atv's just stay in 'NST' state I have included screenshots if they are any use   My speed reference in this example is taken from the memory word %MW0 which I am inputting via a HMI   I have addressed all my ATVs accordingly in there setting with the correct Modbus parameters and selected Modbus under the FR1 configuration, am I missing anything?? Any help is appreciated as I am really struggling   Tom
  14. Hi everyone I'm new bie, I try to control VDF-M via fx1n-485-db. please help!! Thanks.
  15. Hi everyone I'm new bie, I try to control VDF-M via fx1n-485-db. please help!! Thanks.
  16. hello expert i want ask some help So i tried to communicate my Omron PLC (cj2m cpu31) with SCADA from Schneider (power logic) on my omron side the comunnication on PLC already take to communication to NB so i add communication module CJ1W-SCU41-v1 I want asking how to open the communication if i want the scada become a master and my plc become slave i got this from omron website is that program compete for my case? i need configuration for scu41 module also to communicate or if you have suggestion i really open i just need to open port RS232c from scu41 so scada can read the data from my plc  tahnkyou for your help MRTU_CPU_Slave.zip
  17. Hi All need to convert a Decimal Value into Ascii code to send out on serial 485. eg. Weight comes in as Int 12345 i need to send it out in Ascii as 23 32 20 31 32 33 34 35. I have created an array 0 of 8 (Word) DB. Is there an easy way split the int into Digits convet in into HEX and slot the value into the various array positions? Array 0 of 8 = 23 means # Array 1 of 8 = 32 means 2 (Station ID) Array 2 of 8 = 20 means Space Array 3 of 8 = 31 means 1 Array 4 of 8  = 32 means 2 Array 5 of 8 = 33 means 3 Array 6 of 8 = 34 means 4 Array 7 of 8 = 35 means 5 Array 8 of 8 = D means CR    this sends the value of 12345 to Display ID 2 . need help to convert the decimal number in ascii. the decimal number will be max of 5 digits and less than 32000   any help will be greatly appreciated.
  18. PLC to PLC communication

    Hello everyone Does anybody knows how to estblish a communication between 2 Mitsubishi CPUS with modbus? THey are RCPU and FXCPU  
  19. CP1H Modbus issues

    From @Janaka Angampitiya: Hello, I have Three CP1H PLC with Cj1w scu31-v1. I need to send a Modbus command SCU unit through Modbus RTU compatible power meter. I use instruction TXDU and CMND but it's not working. My PLC Arrangement CP1H PLC  - CP1H-X40DT1-D    ver. 1.3 Option Board 1 mounted Cp1w-CI41   to NB HMI its work Option Board 2 Mounted CP1W-CIF12-V1 to PLC 1, PLC 2 and PLC 3 between communication Serial gateway mode it is work. CJ1W SCU31-V1  (ver.1.3) and Modbus compatible Power meter it's not working. Please help to how to connected and what is the use of instructions for this case. 
  20. Hello! I have one Controlllogix project that communicates with a modbus slave through modbus TCP, using a Prosoft module model MVI56-MNETR. Does anyone know what happens to the data polled in case the network fails? Do all variables go to zero or do they freeze in their last value (or something else entirely)? I couldn't find anything in the Prosoft manual. Thanks for any help!
  21. Hello There I need to set up communication PLC to PLC ( R08CPU to Fx5CPU) but i dont have the modbus library for  the R08  Does anyone have the library? or where can i get it? thank you.
  22. Hi there, I have a controller NX1P2-1140DT. I want to control a VFD with modbus serial communication. Can someone help me start from scratch ?
  23. NX1P2 Modbus RTU Code and Write Up. View File This code is designed to implement Modbus RTU on an NX1P2 Controller using the NX1W-CIF11, NX1W-CIF12 or NX-CIF105 module (mounted to controller or EtherCAT coupler).  Created by an Omron Engineer. Submitter Michael Walsh Submitted 05/22/20 Category Tutorials and Quickstarts
  24. Version 2.12

    213 downloads

    This code is designed to implement Modbus RTU on an NX1P2 Controller using the NX1W-CIF11, NX1W-CIF12 or NX-CIF105 module (mounted to controller or EtherCAT coupler).  Created by an Omron Engineer.
  25. i am trying to communication my weintek HMI with Siemens Energy Meter PAC3200. I am using MODBUS TCP/IP Protocol but i am unable to read the data register of my energy meter. Somehow i got to read the 32bit data register but still unable to read the 64bit data register of my total KWHr Energy consumption. I have also attached the manual of my energy meter. Please guide how to read all the data registers of that energy meter. Please see the page 40 onwards for reference. The manual the about 7MB so i cannot attach the file. https://support.industry.siemens.com/cs/attachments/26504150/A5E01168664B-04_EN-US_122016_201612221316360495.pdf