Search the Community

Showing results for tags 'memory data'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 133 results

  1. I have an old Panelview 800 in a system that consists of the PV, a Micro 850 and 10 Powerflex VFd's running conveyor motors. My problems started when one of the motors would not run. It seemed that the PLC was not sending the Run command or the Speed. The problem got worse as I was working on it when two others did the same thing. The current situation is that 8 of the VFD's are getting a Run command and 2 are getting a flickering command. All 10 are getting a 0.0Hz speed command. I connected to the equipment with my laptop and looked at the PLC program and the PV program. I found that in the PV program that all of the user input data, which consists of Motor Speed (Hz), Accel and Decel times and some other timer values for the timing of some conveyor starts and stops, where all gone, set at '0'. this equipment is several years old and predates my presence here. The PLC program seems to be running and passing the commands that it receives to the VFD's. The data is passed to the PLC via Global Variables. I've never encountered this particular problem before. Any ideas?
  2. Hi, I have a problem with Omron PLC and Beckhoff IO. The IO just disconnects in a few minutes and comes back! I received different errors: Link off error, Illegal slave disconnection, process data reception timeout. When I also check "Display Diagnosis/Statistics information" I see errors on all ports A and B of all nodes.  I have called and talked to both Beckhoff and Omron.  I have two NX1 and one NJ101 to test. And I have three EP2318-0001. I have the same problem with all the PLCs and EP boxes. It does not matter if I have one, two, or three nodes. I have tried different revisions of the EP2xxx from the XML file, different settings for the slave, different task periods, and the error still is persisting.
  3. Currently have NX PLC setup as an OPC UA server and an OPC client setup and communicating.  The issue is only tags that do not have a Data Type are showing up in the OPC client.  I have 2 separate OPC softwares connected to this plc through OPC UA and both are having same issue.  If I setup the OPC as a polling service, then all the tags show up as expected.  Does anyone know if this is a known issue with Omron and their OPC UA server, or is there something that I am doing incorrectly (possibly a setting within Omron that I am not aware of)?
  4. NE1A-SCUP02-EIP

    Does anyone have experience with the NE1A-SCUP02-EIP safety PLC? We had a machine shutdown yesterday with a L9n4 error on the NE1A unit. The manual says this is a tag data link error. Does this cause the safety PLC itself to shutdown? I always thought the EIP portion of the safety PLC was only used for status reporting to the PLC. The safety portion is strictly on DeviceNet and is independent of the EIP network.  The CJ2 PLC's error log tells me it had problems communicating with the safety PLC, the VFD, and NX I/O's which were all in the same panel going through an Ethernet switch. 
  5. Searching the forum did not provide me with any useful results. If there is another post with an answer, my apologies. I had ran into an issue with a 1769-L32E processor running out of memory a couple of times. Is there any software or easy ways to analyze an entire RSLogix 5000 project and show how much memory programs, routines, UDTs, AOIs, etc. are using?  Ideally I would like to be able to find what components of the project is taking up so much memory quickly since our company standard is to use UDTs and there is a lot to look through. Thank you!
  6. Hi, I have quite a noobie question. I want to create a function block to do some simple operations on 2 variables. Both variables are In/Outs (see picture attached). How can I make this function accept variables regardless of the data type? Given these is just simple math I am able to use the same instructions in REAL, INT, UINT, etc. But, the function block only lets me assign one Data Type to the In/Out variables.
  7. Hi, Currently Im working on R08CPU using GX Works3 1.066U and I installed a 16GB SD memory card. Where can I find the tool to format the SD card in GX Works3 ?   
  8. Data Historian

    Hello, What would be the best data logger for Backhoff automation based automation? Idea is to record some analog and digital tags at certain time intervals. Present them in tabular as well as graphical form and print some reports based on selected time window. I have looked up TwinCAT Analytics and that seems to be one option. But want to check others before making decision.
  9. Memory registers on KINCO PLC

    Hello to everyone. I hope you are doing well. I have a KINCO PLC HP043-20DT. I'm communicating through free-protocol instructions XMT and RCV. The manual states that memory registers SMB86, SMB186 and SMB286 contain information about the state of the reception instruction. I would like to ask if any of you know of the existence of an analog register but with respect to the transmission instruction, instead of the reception. The manual does not indicate it and I could not find any information online. I've sended an email to the manufacturer but, until now, I have not receive any answer. Otherwise, how could I search for this information? I tried through the manual providede by the manufacturer, but maybe there is other way. I would appreciate any information. Thank you so much. Kind regards.
  10. Hi gents, I need to build up a communication between nx1p2 to another omron plc (any type with sql support). This is due to the fact that I have finaly to prepare the plc communication with the sql database, and nx1p2 doesnt support this.  Sorry, i know it's probably a noob question, but I'm a beginner. What type of technology i shoud use to make this connection between NX1P2 and another Omron PLC? Or might be some share some project?  
  11. Hey guys,   I know this is a topic that has been discussed before, but I am having trouble finding exactly what I am looking for.. I want to know the most efficient way to record data from my PLC to an Excel file on my PC. I want this to be done without the use of the PLC's webserver.  Specifically I am trying to record vfd speed every 10seconds with a time and date stamp. How can I do this?   Thanks, James  
  12. Hello all, I have a L82 having ethernet connection with 3 HAAS CNCs and other ethernet device. The ethernet card EN2T is at 19% capacity. But my Controller MESSAGE CORE is at 100%. How do it get it down so that we can have faster and better communication ?    I have attached the picture of the Tasks:   
  13. Hello! Is there any possibility to connect a Mitsubishi PLC to a program like Siemens Plant Simulation? With Siemens PLC I can do it through OPC UA protocol, or Shared Memory with SIMIT, or stuff like that. But I would need to do it also with Mitsubishi PLC. Can I use for example OPC Server? I couldn't find out, if Mitsubishi PLC-s have that function built-in. (I have a L02 and a FX3S COU, either of them would be great.) Thank you!
  14. Hi, I have inserted new RTD module into in my SLC500 as replacement to defected RTD module however the module LED is enabled but the channel LED's are blinking. I have checked the following: In the advanced I/O configuration the module configuration is shown as expected In the data file word format it is not corresponding to the channel preferences What should I do and how to fix the word bits?        
  15. Open data log in HMI

    Hi there! I have S7-1200 controller connected to a Comfort Panel. The machine has some pressure and temp sensors, as long as many valves and other stuff. I generate a daily datalog with some of those variables but, the thing is, I've been trying to figure out how to show these data in the HMI without using a trend viewer. I don't know if it's possible, but I want to be able to see what valves were open (for example) the day DD/MM/YYYY at HH:MM:SS, using the generated data log, kind of knowing the state of single bits at different past moments. I've been searching the web but I didn't find something exactly like this, don't know if I'm doing it properly so I'd like to know if you have done this or you can throw some light on the topic. Thanks in advance and hope you can help me!
  16. Have been able to exchange data types of BOOL, INT,  DINT & REAL between Omron NJ/NX CPU with Allen Bradley Logix CPU's with Ethernet/IP using the CIPUCMMRead & CIPUCMMWrite instructions. I now have a need to exchange "STRING" variable types. Have tried varions string lengths in the NJ without sucsess. AB default string length is 82 & Omron 256 but I think the difference is the length headder that AB has with within their String Tag type. I know I could convert my strings to an array of bytes & sent them this way, but was looking for a solution to sent them as native strings. Hope someone out there has done this & can share their leg work? 
  17. CJ1G-CPU42H BACKUP

    Hi,  I have CJ1G-CPU42H plc, when I try to backup the program it just fails at step 6 as indicated in the attachment, 6- plc memory  ##error aborted ##
  18. Hi I'm trying to set up Modbus RTU communication between FX3U PLC and a weigh module. I would use the ADPRW command using 0X03 to read the 16 bit Holding Register but in the weigh module the Data Address/Holding Register of the value I want to get is 400047 - 400048. How to translate the value in 16 bit?   Thanks, Fabio
  19. Logo mem card

    Hello,      i have one questions. Is possible upload program from  SIEMENS LOGO MEMORY BATTERY CARD ? If is possible ... how?    Thank you for your help.       Regards Beny
  20. Hello all, I need to read device memory mostly I need to read R registers from PLC L26. I read device data, but inside of table, I can't find R or ZR registers. Can you help me?  What I did wrong?   BR KS  
  21. NB Data log

    Hi there!  I need to implement a data logging that saves the log in a USB storage for a machine and just started searching for some info about data logging in NB HMIs. Up to now I'm clear about using the Data History function and the sampling method I'll be using but I still have some unclarified doubts about this. 1.- The data log should sample the value of, let's say, a couple of words, each second for an entire day (6:00 am to 6:00 am). NB's manual doesn't say a lot about Storage Type and Buffer Storage in "Save Data History" tab. Does "daily file" mean It deletes the .CSV file daily and it generates a new one? If is it, at what time does this occur? Does "single file" mean it generates a file and won't get deleted? Does this mean the sampling stops when completing the first one? Is "storage period" used to keep the file after the next log begins? 2.- Is it necessary to display the element in order to make the log work? Or can it be placed in a random screen you only enter once a day? 3.- In the "Channel Properties" tab. If I need to get the binary value of a word, do I need to set the max. limit to 65535? 4.- I asume that "Sample points" value doesn't matter when selecting Continue sample mode. Am I right? Thanks in advance, any help is appreciated.  
  22. Data Logging with GT Designer3

    Hello, I am trying to log data using GT Designer 3 and I'm having no luck. I found some sort of online documentation and even going through the myriad of steps still find my self unable to log anything. I am using the melsoft project navigator and GX Works 2 to simulate the logging of just one 16 bit signed word with a constant value. As logging data is clearly not as simple as just specifying D100 or D200 as the devices you want to log, I am hoping someone else on here has some experience on this matter and can help me out.  Thanks for any help in advance.
  23. GOT 2000 Buil-in Memory exceeding

    Hello Everyone I have an issue with a  Got 2000, im updating and adding some screens in  a old  HMI application with size was about 47 MB,  as im still updating i wanted to test the application  which now sizes about 52 MBbut is not possible due to the shortage of  ROM and RAM, what can I do in this case as the application must be in the built-in Flash memory which is very limited?   Thank you in advance
  24. Dear Friends, I have made this video to show you how to take data samples from Delta DVP PLC and save this log file in the Weintek HMI internal memory. The Weintek HMI internal memory is easily accessible using ftp. All the necessary steps are mentioned in the video. The link of the video is given below,    
  25. Lacthed Memory Turned Off?

    Hi guys. I'm experiencing a latched memory turned off even all of the contact is still on and trigger the coil. Anyone familiar with this? Thanks!