Search the Community

Showing results for tags 'melsec communication protocol locally'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 200 results

  1. Delta plc Communication Issue

    Dear allI have DVP14SS211R series Delta PLC Which is having 24V DC supply voltage. I am using PLC as master and My end device as slave. My slave device set device_iD=1I am using Modbus RTU protocol for Function code1baud rate =9600parity =noneStop bit=1data length=8I would like to know how to send request with Function code 1(Read coil Register). i have attached code reference. Communication block it wont give error it shows 0 .means No error
  2. Hey Everyone,   My company decided to purchase a piece of equipment from China, and I have the pleasure of updating its terrible existing controls. We were given the PLC program by the manufacturer, so I was able to make my changes pretty easily - or at least that would be the case if I could actually connect to the dang thing. The source program is indeed openable and editable via GX developer (the original configuration shows it as an FX3). I figured connecting should be straightforward, but I was wrong.    I initially used a serial/usb converter that I've used on some older Allen Bradley equipment (which worked fine for that). However, after no luck using it on the "Mitsubishi", I purchased a different cable that I found recommended on this forum (Tripp Lite USA-19HS - https://www.alliedelec.com/product/tripp-lite/usa-19hs/70101537/?gclid=Cj0KCQiAj9iBBhCJARIsAE9qRtB_n8TVAnJdFyYokoEu42W6H6LaT4kVsgJQI1qvPUsUF3rFviKpbt0aApLHEALw_wcB&gclsrc=aw.ds). Still, no luck. I've tried 7E1 and every baud rate possible, as well as some other bit/parity configurations (and yes, I've verified that I'm using the right com port, as well as tried moving the converter to different ports and trying those). Nothing seems to go through.  I have almost no experience with Mitsubishi beyond a couple of FX5s (which have worked fine, but I connect to those via ethernet). Any help would be greatly appreciated; if I can't make these changes, I'm going to end up rebuilding the whole cabinet with a PLC I can rely on.   Thanks in advance.
  3. Hi there! I've been working with NB HMIs with good result. But today I loaded a project to a NB7-TW01B and it feels slow, both offline and online. Switching screens and reading/writing take around 1sec or more. It first had some bmp images created with .bmp and .png files, so I tried using vector graphics instead, but didn't get any better. I don't have another NB to try it right now so I'd like to ask you if you've been in this same situation before or what could be causing this. PLC is CP1L and communication it's via Ethernet. Both devices are actually pretty close (cable is less than 3m) and the previous HMI (Pro-face GP) felt a lot faster. Thanks in advance!
  4. Hi, I am doing a project to extract analog data from Kashiyama pump through RS422 port. I am using QJ71C24N to establish the connection. But it encounter error code 7D00. Can someone help to take a look what go wrong?
  5. Modbus with CJ1W SCU31-V1

    Hi every one, I want communication Inverter mitsubishi D700 with module CJ1W SCU31-V1,  any one give me a correct solution and send any sample program. Thanks
  6. Error Indicator on FX3U-ENET-ADP

    Hi all, I have finished installing ethernet adapter module FX3U-ENET-ADP on the FX3U-48M PLC. From the ethernet module, i connected it to a wireless router and then i am planning of connecting to the ethernet module using GXWorks 2 on my laptop through wireless router. On the ethernet module, the error indicator LED is on (red). From the FX3U-ENET-ADP, it means that there might be setting or hardware errors.  I am asking if i have missed some steps on the installation process and if any of you have experience with similar problems. Thanks in advance for the answers.
  7. Good day everyone!   I have some question relate with above subject. While i try make protocol for the CJ2M PLC.  i found out "Primary Expression (yN+x)" function but i cannt understand what`s this for. even i tried to find in the reference manual. i can not.  you can find it "Message Editor" -> "Message Variable" -> "Variable" sorry i tried to upload picture many times but it kept showing failed to upload.    hope so i could find the answer. thank you!
  8. Hi all,  I want to ask some questions regarding Ethernet Communication with FX3U PLC series. I have 2 PLCs of FX3U series (FX3U-48M and FX3U-64M) and I want to monitor its data (input and output) using ethernet communication in real time. My questions are: 1. Does FX3U PLC have ethernet port so I can connect it directly to my Laptop/PC? 2. If no, do I need to use FX3U-ENET-ADP and can it be used for 2 PLC or only 1? 3. What software do I need to use to configure the communication between PLC and FX3U-ENET-ADP? 4. Does this configuration change the existing PLC program? 5. Can i transmit the data wireless-ly using some kind of ethernet to wifi adapter and what additional hardware do i need for that?  
  9. Check serial connection to Omron PLC

    Hello, I am building an application in CitectSCADA and I want to communicate with an Omron Sysmac CS1G. The connection between the plc and the Citect computer is through an ethernet to serial adapter (the computer doesn't have com ports on board). I'm having some difficulty establishing the communication and I want to make sure that I can actually reach the plc. Is there a way to check that the computer can reach the plc over the serial connection without using CX programmer? Maybe using Hyper Terminal, Putty or something similar. Thank you, Liron
  10. Hello Mrplc's members I have a Korean version " goldsec Moj2" of Mitsubishi plc A0j2 I need to know the right software for it And how to get it I tried GX Developer but it didn't work because it have only A0J2h type And I tried melsec medoc (version 1.64) but it didn't have A series CPUs
  11. Greetings everyone. I'm new here. Hoping to get help to operate the Omron V400-R2 barcode to the Mitsubishi QJ71C24N so that they can communicate the two devices with the correct method. PLC: Mitsubishi: Q03UDVCPU; barcode: Omron V400-R2; serial communication module: QJ71C24N. I use RS 232 communication cable, I have tried using predefined protocol and non protocol procedures but still can't communicate the two devices. I really appreciate your help.
  12. melsec medoc error

    Hi Mr.PLC Members, I have Mitsubishi FX16MT unit, I'm trying to transfer programs to it using melsec medoc version 1.64b but I can't  I'm receiving error "no reply from PLC system",I'm using 25 pin to 9 pin cable and I tried also to connect it with usb to serial cable but the same error appeared  my setup: PLC system        FX Bit rate                 300 word length          7 parity                    Even stopbits                 2 "windows XP" Attached are photo of my unit with my cables and the error of the program  
  13. Unable to read comments

    Hello, I seem to be having trouble reading comments from PLC in GX Developer.  The PLC is an ACPU, Everytime I try to read comments using GX Developer I get the following error. "The comment was not read correctly". I found an old project from this PLC that has comments, But im unable to read any current ones. Anyone experienced this before?
  14. InTouch Comms

    Hi Everyone, I've just installed InTouch V10 and am trying to develop communication with Emulate5000, for educational purposes. I looked over the internet and found some videos on how to develop communications by setting up the topic name and node name in DA Server manager, but the issue I'm facing is that my SMC only shows logViewer and nothing else (snapshot attached). Am I missing some vital component or dirver? Or is there some problem with my installation? Help would be much appreciated.   P.S: Window Maker and Viewer are working fine. Thanks, Sabih
  15. hello expert i want ask some help So i tried to communicate my Omron PLC (cj2m cpu31) with SCADA from Schneider (power logic) on my omron side the comunnication on PLC already take to communication to NB so i add communication module CJ1W-SCU41-v1 I want asking how to open the communication if i want the scada become a master and my plc become slave i got this from omron website is that program compete for my case? i need configuration for scu41 module also to communicate or if you have suggestion i really open i just need to open port RS232c from scu41 so scada can read the data from my plc  tahnkyou for your help MRTU_CPU_Slave.zip
  16. Siprotec Relay 7sj62

    I have 24 Siemens Siprotec relay(7sj62) which i want to communicate with Scadapack 330E (Schneider) on 103 Protocol. but every time I try to communicate it shows Slave device is failed to communicate. trying to communicating via serial (RS-485). What should i do..?? or do i need to communicate it with Siemens PLC..?? If so which PLC should use..??
  17. PC to PLC Kommunikation

    Hello, i want to connect my PC to the PLC(RSLogix5561)  over TCP/IP. In rslinx the Ethernet driver are configured. My PLC IP Adresse is 192.168.1.100 and my PC Adresse is 192.168.1.105. From my PC i can successfully ping the PLC IP Adresse, but from the PLC i can't see my PC. And it does'nt schow in RSlinx. Is there anything i am missing?
  18. Hello there, I am new to OMRON so need some help to communicate two PLC over FINS.   Here are the description of the system... (IO Table image is attached)   PLC1-  CJ2M-CPU33 IP- 10.113.218.34 SUBNET-255.254.0.0 UNIT NO - 00 (set the dial available on the CPU in HEX) NODE - 22 (set the 2 dials available on the CPU in HEX) PLC2-  CJ2M-CPU33 IP- 10.113.218.35 SUBNET-255.254.0.0 UNIT NO - 01 (set the dial available on the CPU in HEX) NODE - 23 (set the 2 dials available on the CPU in HEX)     Now, what i have to do is to transfer the D100 to D110 from PLC1 to PLC2's D200 to D210 and Transfer the D100 to D110 from PLC2 to PLC1's D200 to 210.   I have tried RECV and ECHRD blocks but didn't succeed yet.   Two CPU are connected over ethernet via a industrial switch.   Can you help me to achieve data transmission please...
  19. GXWorks 2 Comment Translation

    Hello, I was wondering if any of you have experience translating comments. To be more specific, I have been tasked with translating all of the comments in my plant from japanese to english. We have many different series of PLCs, but they are all mitsubishi, and I will be using GXWorks 2 for 99% of them. I had the idea of writing the comments to a CSV file, Translate them there, and then just read them from CSV back into the project. I have tried numerous methods, but it seems the CSV loses format and isnt able to be read back into GXWorks. Some of these comment files have almost 10,000 comments. Do any of you have any suggestions on the best way to translate these comments over, in a more automated way than manually one-by-one.  Thanks in advance for any support you can provide!
  20. Hi everybody; could you please help me;i would like to learn how to convert a sinwave signal with analog input of my R60ADV8 module.How many samples should i convert ? what is the maximum frequency of the input signal? and how to  recover the sinwave signal in the analog output of the R60DA4 module? i can convert dc signals from sensors  and recover them in the analog output;but i have no idea how to do with sinwave signals. Sincerlly yours
  21. HMI and PLC Communication problem

    hi there. .. i am new to plc programming.. Right now i am having problem related to communication between hmi and plc.. i have HMI WEintek 6070ip and plc mitsubishi FX2n.. i have written a program in gx developer . and communicate it with EASY Builder for HMI. so for now plc is communicating with my program written for hmi on pc. but when i downlaod to hmi and connect plc cable to hmi then hmi shows no plc communication. i am having a problem for communication between hmi and plc. any help will be a life saver. thanks in advance
  22. Serial comm with FX1N PLC

    I need to communicate with a Mitsubishi PLC using Matlab. To do that, I open a serial communication with the appropiate parameters (7,e,1,9600), and write an ASCII message based on the manual I have (attached). I have tried examples as the one in the attached image. The response starts with a 6, that is, the ASCII number for ACK, so something must be working. But the rest of the response is junk (149, 149, 149...), although its length depends on the input length (if I add terminator, the response is longer, and so on). I am completely stuck. Some information that might be helpful: I am using a Serial to USB converter that I have used successfully with other PLC (which used Modbus, so everything was easier) There's a VB application (of which I don't have the code) that is able to connect to the PLC (I need to connect directly without using this intermediate app). I have decompiled it trying to get some info, but was just able to confirm the 7,e,1,9600 parameters, since the rest of the code is too mangled to analyze The attached manual was sent to me by the guy who designed the PLC and its ladder code, so I guess it is the correct one I have tried the echo mode (TT) to no avail, response is always the same I have some doubts regarding the reading of a value (see attached image). Why is there a second message from the PC? Shouldn't I just need to read the response? GX Developer tells me that the address D8120 (which is supposed to define the comm format and protocol) contains a 0, which seems weird. Any help or hint would be greatly appreciated. Thanks jy992d69901e.pdf
  23. Hi everyone! I got this machine with a CP1H PLC and NS8-TV00B-V2 as PT. I was told that they were working fine, but suddenly, It appeared a communication issue: black screen and "connecting..." at right bottom. I dont know if It is a configuration problem or some hardware damage.  These are the configuration in the PT and the PLC. The communication is through RS232 Serial.  I tried to communicate another PT screen with the same communication settings and IT WORKED!. ' I've been thinking that, perhaps, the serial port A is damaged, I have tried to set port b, but I havent could. How can I configurate PORT B??   THANKS...  
  24. Hey all - I am working on a car wash system design that will utilize the Nayax payment system. Has anyone utilized them? How do I incorporate the device with PLC to automate the system. After payment is approved how can I send out that signal from them, all via ethernet on a managed switch w/ wifi for exterior comms for the Nayax.
  25. Hi All, Hope you all doing well in this pandemic life.  I would need your expertise with an issue I have been struggling with for past few days and thought to reach out here. I am working on a migration project with GE PLC and Citect SCADA 7.10. The GE PLC is migrated to ControlLogix L74 Rev24.10 while Citect SCADA is retained. For testing I only have L71 and L82 and could not managed to organise L74. When the code the loaded in L71 and connected to Citect, I cannot see tags in Graphic page but I see the subscription.txt in Debug folder shows all tags good . The same code when loaded in L82, the Citect works instantly.  Does anyone know this behaviour of PLC and SCADA? Regards, DeeEngr