Search the Community

Showing results for tags 'iot plc m221 and hmi weintek - ip'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 28 results

  1. Hi there!   I'm trying to communicate a Weintek cMT2128X with a CP2EN via Ethernet. The thing is I'm getting 'No device response' messages every 2-3 seconds. They'are connected at some point because some values are updated, but the connection error keeps showing up. So far I've checked: - Comm. settings are okay in both sides - Wiring is good - Happens the same with a CJ2 CPU. - There are two arrays of 50 UINT each, I don't know if that's slowing things but that would surprise me...   I've worked with Weintek HMIs before (communicating with different CPUs: LOGO!, CP1, CJ2...) and never had this problem. I just set the IP addresses and everything was working fine, so I guess I'm missing something. Hope you can throw some light at this! Thanks in advance
  2. Hello,  after I updated my CMT-FHDX with codesys license, programming and uploading codesys i'ts ok , but I can't upload my CMT-FHDX project anymore. I see CMT  in easyweb, but easybuilder won't find the IP (won't recognize CMT HMI even if I manually add the CMT IP address)...so I can't upload project When trying to upload in easyweb, it's fails. I't say that is not the correct project (CMT-FHDX-220). I reset to factory de CMT and still the same problem. Before I updated with CODESYS license, I was able to upload succesfully projects to CMT-FHDX. Now I can't Please any advice Thankyyou
  3. I have problem when try to connecting M221 PLC to Citect SCADA 2018, I have try using twido and OPC KepwareKEPServer in device communication, but still can't connect when I using Ethernet to the device     Thank You
  4. Hey all,  So I am looking for some assistance because I am not understanding how the tags on an HMI and within a PLC are linked. There are no 'physical' buttons, just what is on the HMI. It is controlling a chiller. Communicates over Modbus TCP/IP. The PLC is an IDEC. I have some-what worked out how other tags are working when they are words being passed back and forth, but this one has me stumped. I've attached a few screenshots for referral. It looks like the run and unload buttons for the chiller are a single bit/BOOL toggle (but the chiller running latches itself in the PLC when the chiller starts to run). The stop buttons appears to be a parent for the single bit/BOOLs and when it is pressed it resets them all both on the HMI side and within the PLC side.  
  5. Hey Guys, Modicon M221 PLC, programming with Machine Expert. I have a project that I must create shifts for heating elements, requiring that some heating elements, those who were on for the longest period, do not turn on in the next shift. I'm looking for a sorting mechanism to determine what %MW (6 words of 8 total) have the largest value. I would like an array of 8 words, sort them, and retrieve the highest 6 or highest 4 or highest 2.   Thanks.  
  6. Hello, I need to replace an obsolete twido PLC to Modicon TM2221ME32TK and in the process would like to get the variables back into Citect SACDA V7.2 I have been reading up on REad_var and write_var but am seeking clarification on how to get the existing %MW, digital inputs %I0.0 etc and outputs  %Q0.0 mapped into modbus registers so SCADA can read them.  I intend to use modbus TCP/IP communcations with the ethernet/ip adaptor.  Do i need to use read and write_var to map into the addresses? Please find attached existing PLC code.   PLC.twd
  7. Hey! Whats up guys ;) I'm a student and I have been saving up money for PLC for quite a while now, I was recommended to use Schneider M221 TM221CE24R PLC. after buying it I looked online for some HMI and due to high price tag I ended up buying cheaper Kinco GL070E HMi for learning :D I'm trying to connect them both together using Ethernet cable but I'm having difficulties making them connected. The lights shows up ( blinking green ) and ( solid yellow ), I have tried Modbus TCP Slave, Schneider Ethernet (TCP Slave), M series, M200 Ethernet ( TCP Slave ), but nothing seems to be working :D  The best I got in 3 weeks of trail and error and countless non-english videos on youtube :D is error message on the HMI -> [2] PLC NO RESPONSE 0-01-03   I'm trying to learn and seems like I have hit a wall. Can anyone help me to see if it is even possible to connect them or do I need to save up for new HMI :( Any help would be greatly appreciated, sincerely Engelis :) 
  8. Dear All, Omron NQ HMI was installed with CJ1M CPU. Now I am trying to replace the HMI with weintek MT8071iP but HMI showing communication problem. I have omron HMI NQ program and set protocol settings as was set in NQ please see the attachment. Please suggest what may be the reason? waiting for reply Thanks Shoaib omron_settings.zip
  9. An IoT system that have a Web server from node Red and Grafana for Power Monitoring, the Pump is controlled by the Schneider PLC M221 with a HMI from Weintek MT8071i with Modbus communications on TCP with RTU Gateway from Volison ADM 5850g  
  10. In my system, MT8150XE and Allen bradley compactlogix communicate with PLC ethernet. When I compile the project I made with Easybuilder pro v5.01.04 and upload it to the screen with v6.05.01.565, it does not communicate at all and I get a no response error. only difference between the two projects Previously Driver V.1.50, ALLEN_BRADLEY_EIP_COMPACTLOGIX.e30 In the new one, the Driver says "Device ID: 156, v.1.80, as. ALLEN_BRADLEY_EIP_COMPACTLOGIX.e30" Copying the ALLEN_BRADLEY_EIP_COMPACTLOGIX DLL file from the old version driver folder to the new version folder, it rarely gets online. Is there a solution? Thank you from now
  11. Dear Friends, I have made this video to show you how to take data samples from Delta DVP PLC and save this log file in the Weintek HMI internal memory. The Weintek HMI internal memory is easily accessible using ftp. All the necessary steps are mentioned in the video. The link of the video is given below,    
  12. Hello, I have an M2I Top RW (model: 1000WD) connected to a Schneider Modicon M221 PLC. The HMI is connected and I is working perfectly reading data from the PLC via ethernet. I can't seem to find a way to write to the PLC from the HMI. I would like to control the PLC from the HMI, I know this is possible with Fatek PLCs with the same HMI model. please help - how would I create a bit command from the HMI to the PLC? what registers? what inputs in the PLC? thanks
  13. Hi guys, I'm in another project with another brand on PLC and this time I thick I hit a pretty solid wall. Long story short, I need to change a -10 +10v signal send to a DC motor drive based on a "recipe" selected with a 10 positions camswitch. I've never programmed schneider PLC, except the zélio one who are pretty simple to understand. Apparently Modicon are much more complex to program with the knowledge I have. Is there documentation available somewhere I can use to understand how to code analog output.
  14. hi guys i am using my Schneider m221 plc  but facing this below problem. how can write modbus address  i am trying below register data address but not accept this register data  address example i write %MW0:=16#10001 %MW1:=16#10002 %MW2:=16#10003 %MW3:=16#10004 so guys how can write this register address can me  share one example so i understand. also share read var setting . ObjType: FristObj: Quantity: IndexData: Thanks
  15. Hi there, Im having issues controlling ATV 320 VSDs over Modbus RTU with a M221 plc, does anyone have any pointers for me to look at? I believe I Have set everything up correctly but when I run the program on the plc the atv's just stay in 'NST' state I have included screenshots if they are any use   My speed reference in this example is taken from the memory word %MW0 which I am inputting via a HMI   I have addressed all my ATVs accordingly in there setting with the correct Modbus parameters and selected Modbus under the FR1 configuration, am I missing anything?? Any help is appreciated as I am really struggling   Tom
  16. Hello! I am new at PLC programming. I am using TM221CE16R PLC with TM3AI8 analog input module and SoMachine Basic v1.6. I am trying to scale analog input value. I am using 4-20 mA pressure sensor. I managed my wiring so that I get raw values in SoMachine Basic. But I don't know how to scale these values to usable values. My sensor works in range 0 - 16 bar. What is best way to get values? Is it PID function block or multioperand function block using equations to get range 0 - 16? I will appreciate your help.   Thanks in advance!
  17. i am trying to communication my weintek HMI with Siemens Energy Meter PAC3200. I am using MODBUS TCP/IP Protocol but i am unable to read the data register of my energy meter. Somehow i got to read the 32bit data register but still unable to read the 64bit data register of my total KWHr Energy consumption. I have also attached the manual of my energy meter. Please guide how to read all the data registers of that energy meter. Please see the page 40 onwards for reference. The manual the about 7MB so i cannot attach the file. https://support.industry.siemens.com/cs/attachments/26504150/A5E01168664B-04_EN-US_122016_201612221316360495.pdf  
  18. PLC and HMI freezing issue

    Hi I am using Delta DVP-20-SX2 PLC and Weintek MT8071IP HMI. I am experiencing a very strange issue. Whenever, i connect PLC and HMI to the same power source the PLC seems to freeze and does not perform required operations. However, when i connect PLC and HMI to separate power sources, the PLC keeps on performing its normal operation and updates data on HMI regularly. I have searched various forums and could not come up with an answer to why connection with same power source freezes PLC. Any help will be highly appreciated as it is not feasible to connect separate power sources for PLC and HMI.
  19. WEINTEK MT8100iE problem

    Hi,   I have a problem with MT8100iE when VNC is activated.It works for few days and then freezes.We have to restart it by turning off power supply every few days.Did anyone have the same problem? Cheers
  20. Hi guys, I have an M221 and trying to read process data from a HACH controller via Modbus 485. In the Read_Var function block I need to configure ObjType, FirstObj, Quantity and IndexData. Slave ID is 3 and I am using SL2. So, say if I wanted to read to following registers, Register #40001, Data Type Integer, Length 1, Description- Sensor Measure Register #40005, Data Type Float, Length 2, Description - Sensor Temp Register #40007, Data Type String, Length 6, Description - Sensor Name what do I put into the Read_Var function ? I am completely new to this and it's just not clear to me. Thanks John   
  21. Modbus Addressing In Hmi Weintek

    HI all.  Am in some kind of trouble.. i have a sensor which has modbus RTU 485 . i want to connect it directly on weintek HMI ..    kindly help me out.. 
  22. Modbus Addressing in Weintek HMI

    Modbus addressing in Weintek HMI to poll data from Temperature sensor through RS485. In my system i have connected Temperature sensor to I/O Scanner has output in terms of RS-485 which directly connected to COM3 Port pin. No. 6 (as Negative) & 9 (as Positive) of HMI (Model No: MT8071iE) and HMI connected to PC via ETHERNET. I want to read temp on HMI screen via MODBUS protocol. So, can you please provide me instruction about addressing of MODBUS register in Easy-Builder Software so can read data of corresponding register. Because when i do compile i got an error like " Device no Response". I hope i will get reply from your side as Fast as possible to overcome this problem. Thank you.
  23. How to connect Micrologix 1000 With Weintek MT6070ip HMI? i Can't connect my Allen Bradley Micrologix 1000 With Weintek HMI...
  24. WeinTek to AB PLC Issues

    I am connecting a WeinTek eMT3105P to a CompactLogix L2 series PLC via the WeinTek Rockwell PLC (CompactLogix) - Free Tags driver and I cannot for the life of me get the thing to connect. I have all my tags imported and have played around with all the settings in the manuals I can find. Any help/advice would be greatly appreciated. I know my IP addresses are correct and if I connect my cable directly from the HMI to the PLC I still get the "PLC no response" message 
  25. Hello I would like to connect 2 HMIGXU 5512 to my Modicon M221 is it possible please?