Search the Community

Showing results for tags 'i have problem to connect 2 temperature device with him delta with plc delta by rs485..when i run plc i can see the temperature change on pc but the problem in him its'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 205 results

  1. Hi  I need to show 2 different history buffer setup ID's in a single Historical Trend graph. as much as I tried only 1 ID of buffer setup is shown on trend graphs, but for comparison purposes I need to show 2 or even more? ( i already have defined 2 rows of my history buffer setup with different D in row 1 and 2 = ID1 and ID2 ) can somebody help me please?  thanks
  2. I am trying to communicate Delta HMI Dopsoft -W software on PC and corresponding PLC program in Delta PLC ES2 .I don't have Delta HMI at the movement.I have prepare communication cable myself. This cable communicate properly when I simulate the plc Software with delta PLC software WLPsoft. But it dosn't communicate with online simulation with Delta HMI software DOPSoft-W .but whenever Ipressed any button on PC HMI I can see the PLC communication indication LED blinking every time. I have set all the parameters of communication many time but no use. I am using comm1,9600,even,1 and station 0 or some time station 1. but I get the communication error 7 and 10. evey time and no action. Every time I compile my program in dopsoft it compile with no errors, and if i go for off line simulation it works fine. I have put the correct read and write address of my used components, like X0, X1 and Y0 and data memory D400 same in DOPSoft and PLC. could any body help in this situation. I can also attached the image files of my PLC Ladder program and HMI program on PC later on.
  3. Device point error between Parameter and PLC

    Hello all, I am a beginner with PLCs programming. I have an issue on GX Developer programming software from Melsoft trying to program my Mitsubishi Q-series PLC. CPU is Q03UDCPU. When the program is written and I try to upload it to the PLC, with the write to PLC window, I check -Program -- MAIN and -Prameter -- PLC/Network/Remote, click EXECUTE and a message appears : "Device point that is set in parameter is not match the device point in PLC". I can't fix it. In Parameter - PLC Parameter - Q parameter setting (window) - I/O assignment tab : I have (see image). Whe I use CHECK button it says there is no error. The X41 input device is plugged on slot 1/00. I am making this folowing the instructions a PDF I found on the Mitsubishi electric's wesite : Q-series basic course (for GX Developer). Thanks for the help, A. S.
  4. Modbus Addressing in Weintek HMI

    Modbus addressing in Weintek HMI to poll data from Temperature sensor through RS485. In my system i have connected Temperature sensor to I/O Scanner has output in terms of RS-485 which directly connected to COM3 Port pin. No. 6 (as Negative) & 9 (as Positive) of HMI (Model No: MT8071iE) and HMI connected to PC via ETHERNET. I want to read temp on HMI screen via MODBUS protocol. So, can you please provide me instruction about addressing of MODBUS register in Easy-Builder Software so can read data of corresponding register. Because when i do compile i got an error like " Device no Response". I hope i will get reply from your side as Fast as possible to overcome this problem. Thank you.
  5. Delta eserver problem

    Hi Guys, Im using delta eserver to get data from access and there is an error. How do you solve this? Eserver is installed on windows server 8  
  6. Hey everyone! New member here, and this site has always been a big help!  I try to help other folks too, but a lot of guys are super quick on here.   I've got a problem using some obscure components. I inherited a sensor network at work that uses Panasonic S-Link and I need to read them from a Q-Series. Panasonic makes a module that slots into the Q Series called an SL-VMEL-Q that I have.   My question is:  Did I do everything correctly on my Mitsubishi side? I put it into the parameters as an intelligent module with 64 points and I put the correct address in for the start I/O. Is that all I have to do?  This is the first time I used a module that wasn't on the drop down list when you add one in GX Works 2.   I can read and write to the buffer memory, but I can't get the unit to send to or receive from the sensors. I think the problem is that there is no end unit on the S-Link line (I don't know if it's just a terminating resistor or what), but it previously worked without one, so I can't be certain.
  7. Hi everybody, I have a GT2310 communicating with the Mitsubishi F800 VFD. I am using the Freqrol 800 communication driver, connected to the RS-485 terminals of the GOT and on the F800. The comm settings are the same on both devices. I also tried to use the “auto negotiation” setup. I have communication between the two devices. I can read and write to F800 registers.   Anyways, The GT designer diagnostics is complaining about a communication error in the system alarms. The error can be reset but it will appear again.   This also happened when I created a new, empty project where just the communication was setup as described above.   Did anyone experienced the problem and how to troubleshoot / solve this?   Best regards
  8. Parity Error

    Any one  have any experience to due with Parity Error when RS485 input can't get? Below is the circuit trace i get. It shown me that Parity Error when input signal from my device. But some of the time I can get the input message completely. Sometime can't. Is there any way to solve it?  
  9. i am new in plc programming . i know the basics difference between the rs232, rs422, rs485. but i am little bit confused in it. so i have the following question regarding these terms. 1.  can these protocols communicate with each other i mean rs232 can communicate with rs422 or rs485 and same. 2. my plc has port rs422  but i can connect it with my laptop serial port which is rs232 ? 3. what are the main important points that kept in mind during communication or cross communications.   any help will be greatly appreciated.
  10. Greeatings .   I have modicon TSX premium plc (TSX P57103) I have problem i cant connect to my plc. I have tsx pcx 1031 cable and have com port on one PC and on the second i have connector to this cable with usb. when i try xway test i have problem , the request is always 0 . Can someone help me ???
  11. Dematic PTL

    For the Dematic PTL (Push To Light) systems, does anyone have any information on the protocol used.  I'm assuming it's RS-485 based since the buttons use MAX1487 drivers. What I'm looking for is if anyone has a starting place to look at the handshaking or messaging.
  12. GX Works 2

    Hello everyone! Can anyone suggest to take all the Input and Output (digital) status at a time in a single file for backup in gx works2 in FX2N PLC. I need to confirm that all required IO are in perfect condition before start operating the machine. Also I plan to design a troubleshooter to find problem.
  13. Hello Everyone I have a problem to connect FX5U with Inverter Mitsubishi D700. ( no  respond from inverter) . I did read and following the manual. Could any one can help me?
  14. iFIX restore problem

    Hi, I have .fbk backup file of iFix aplication (i mean).. When I try to restore it by "Backup&Restore Wizard" in part where I "Browse" the way to Backup file and click on "Next" is problem. Pop-up window show -> "Bad file format. The archive file may be an old version or a wrong version in header signature or is not a Proficy iFIX full backup file (.fbk)" ....  My question is = Is possible to find what of version is my backup file ??? when i suppose this error mean i have installed wrong version of iFIX sofware (my version is iFIX 5.5).. Or is no problem of my iFIX version ?  Thanks
  15. Hi, I have some trouble with a CJ2M-CPU33. My client did a backup to memory card earlier today, and after this we did some changes through remote link. Now the client wanted to restore the previous backup to the PLC and has done so, but the system would not function correctly. After going online on the PLC it seems like the PLC is stuck in "Stop/Programming Mode". When trying to change to "Monitor" or "Run" mode a dialog comes up containing the following message: "Failed to change the operating mode. The operating mode may be still changing in the PLC."  - All the dip switches are set to off after restoring backup - The PLC has been rebooted  - I have downloaded the application again through CX-programmer  - Verified that the PLC is set to start up in "Monitor mode" But nothing helps. The same message comes up when trying to change the operating mode.  Hoping anyone can help to resolve this issue as it is very critical for us and the client. In advance, thanks for any tips or help received. Best regards Stian
  16. PICTURES ON DELTA HMI

    hey, I can send pictures to display on HMI. I want to define some places on the picture as if they can do something if they are touched but i don't know how to do it? is it possible through macros?(dopsoft v2)(delta sb07s211)
  17. NX-105 Received Data

    Hello,  PLC: NX1P  Comm module: NX-CIF105   I am running a serial (RS485) network to control several motors. As a trigger for to read the serial port I am using the ( Ch1 Receive Data Exist) bit, which is an internal bit that's ideally should be energized when there's data in the Receive buffer. However, this bit isn't reliable at all. I am reaching out today to figure out if there's another way to trigger the receive command ( preferably without a delay)    thank you all  Cheers! 
  18. Delta PLC Analog Noise Reduction

    Hello All, I am Using Delta SE Series PLC and 06AD Module for Pressure Transmitter. But Analog input get fluctuate continuously. Is anybody have program for analog scaling.
  19. Hello, I have managed to send output to a terminal using a serial channel.  I have not been able to send data from the terminal to the Mitsubishi PLC. I am not using terminating resistors but I have a slow baud rate of 4800.  I am just using regular wires (1.5mm square) .  I think the hardware is okay as I can see the output from the PLC on the screen. Attached is the code.  I just send from the terminal the character 22 every second, I hope this is not too incomplete to get some help.   The plan I guess later is to interface with LabVIEW probably using Modbus but I need to try to get this working first.     UL9.gx3
  20. Hello i'm new in all things about plc, i do a project for school and i use a festo fc 34 plc. The plc is programmed via serial port RS232 my pc not support a serial interface and i use a RS232 to usb adapter. when a try to download the program to plc give me a error: "ERROR: Cannot access controller".  What i do wrong.  Thank you in advance and sorry for my English. Have a nice day.
  21. I am trying to connect a Delta ASDA-A2 Servo internal motor encoder to a Delta DVP28SV high speed counter input.  I was successful in connecting the servo to the plc on position mode with an external encoder connected to PLC high speed counter.  Currently having trouble in finding the correct wiring between the servo drive and the plc to count the pulses from the internal motor encoder.  Attached are some figures from the servo drive manual. OA --> X0 is obvious, tried s/s to GND, COM-, VCC and VDD... no result. Any suggestion would be highly appreciated.  
  22. fx3u ENET card, ip change

    hallo all again, is there some way to change external IP (target one) using ENET-502 card without reinit via sending 1 to BFM1600? I would really appreciate it (time savings) but from little what i know it seems impossible :(   thanks in advance
  23. GX Works 2

    Hello everyone! Can anyone suggest to take all the Input and Output (digital) status at a time in a single file for backup in gx works2 in FX2N PLC. I need to confirm that all required IO are in perfect condition before start operating the machine. Also I plan to design a troubleshooter to find problem. Thanks in Advance..
  24. S7 300 Profibus fault

    Dear All, We are in need of your expert opinion. One of the nodes of our Crane's Cabin gives a station failure problem, due to which whole Crane shuts down. we have done everything from replacing Dp connectors to changing Profi cables, swapping modules with other stations, changing Power supplies but the problem remains the same. Following are the system details, 1. CPU S7 319 F3 fail safe 2. IM 153 interface module 3. OLM module for signal conversion fibre to profibus from main CPU.   We have several nodes after OLM but fault was persistent with 3 nodes. After comprehensive working, it came down to just one but still not diagnosed. I will also upload the diagnostic buffer if needed.
  25. Morning Guys, For my latest project I need to read a gas sensor via 485 from a Momentum PLC. I've been through the help files, but they seem to only raise more questions than they answer, they only seem to reference PLC -> PLC comms. I've had a play with the 'MBP_MSTR' & 'OUT_IN_MBUS' function blocks, but i can't seem to get anywhere, Has anyone got any examples of reading in data via 485, or can anyone lead me in the right direction?