Search the Community

Showing results for tags 'high speed pulse output'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 75 results

  1. Delta Plc Solenoid Pulse

    Hi there, I'm working on a project on a cupcake machine. I have to throw empty wrappers so I'm using a photoelectric sensor to sense the empty cupcake and after 2.5-sec air solenoid activated with delta PLC to throw that empty wrapper. The thing which I want to discuss here is that I want to operate my solenoid with pulse means when the empty wrapper comes to the solenoid through the conveyor then the solenoid gives a pulse of air so the upcoming filled wrapped will not disturb with this air. how Should I program my delta plc it is a transistor base. Can I use PWM? Best Regards, Asad Raza
  2. Evening, I struggle with simple task... I need to activate PLC Output at the specific time of a day. I`m using GSV to obtain PLC time, data is being moved to DIN[7] registers. Then I have three EQU (Hour / Minute / Second) and at the end of rung there is OTL for output. Rung below I have two EQU (Hour / Minute) to disable output at different time - OTU. However every time OTL is energised , OTU on rung below is fired too. What am I doing wrong here ?
  3. Hello, I need to control a stepper motor(have stepper driver) using NX-PG0232-5 with NJ301 PLC. The function is simple, i need to run the stepper motor continuously at a specified velocity. So, in NX-PG module I've made the settings (Ch1 output mode as "Velocity continuous pulse output") and given the tags to IO (as shown below, sorry i'm not able to attach image). I've also added the initialization program to switch on the vfd. Now to move continuously i should should just give speed in pps in "PG_Ch1_Command_Velocity" right?      Ch1 Controlword    Control word 1    W    WORD                 Ch1 Switch On    Switch ON for pulse output 1    W    BOOL    PG_Ch1_SwitchOn        Global Variables     Ch1 Enable Voltage    Start turning on the power for pulse output 1.    W    BOOL    PG_Ch1_Enable_Voltage        Global Variables     Ch1 Quick Stop    Immediate stop for pulse output 1    W    BOOL    PG_Ch1_QuickStop        Global Variables     Ch1 Enable Operation    Start operation for pulse output 1    W    BOOL    PG_Ch1_EnableOperation        Global Variables     Ch1 Fault Reset    Reset errors for pulse output 1    W    BOOL                 Ch1 External Output    Aggregated data of external outputs for pulse output 1    W    BYTE                 Ch1 Command Position    Command position of pulse output 1    W    DINT    PG_Ch1_Command_Position        Global Variables     Ch1 Command Velocity    Command velocity of pulse output 1    W    DINT    PG_Ch1_Command_Velocity        Global Variables  
  4. Hello everyone, I have a Kinetix 6000 CIP drive (unwind) and I need to control its speed by a PID controller. I have everything working except the MCD instruction doesn't pick up on the PID output value change. It changes the JOG speed, which I use to control the unwind, if I set the speed manually, which is slow. The PID changes the speed almost continuously. Any suggestions are welcome. This is how I'm attempting to control the speed: A1_r_JogSpeed = PID output value   Thank you    
  5. Hi guys, I just starting to use Sysmac Studio. Its a bit confusing as I am currently used to CJ series PLC. Usually, we can use P_1sec, P_0_2s and so on to create a simple clock pulse timer function. However, I couldn't find the command or FB to do that in Sysmac Studio. Anybody could explain on how to do that in Sysmac? Thanks 
  6. HSPsO

    I am using fatek FBs 32MN PLC. i need to run the nema stepper motor synchronized with induction motor's speed with some ratio. in my case the speed of stepper motor will change as the speed of induction motor changes its speed, may be many times in a second. Problem is that the speed of stepper will be constant as before until i have to disable and then enable again HSPSO function. is there any solution that i can dynamically change the speed of stepper without disable and enable HSPSO function ?
  7. I have a Base tag of BOOL logic that will not activate the MOV output.  The Base tag is paralleled with an Alias tag for a NO pushbutton.  When the pushbutton is actuated it produces the desired output.  Has anyone encountered this issue from a togglebit base tag before?  Why would a base tag produce a different outcome from that of an alias tag that function properly?
  8. Hello Everyone, I am struggling with interfacing Incremental encoder with FX5U PLC, Does anyone have parameter setting and sample program for same. i am unable to fetch counts...   Encoder: 500ppr, 24V line drive, A-B phase,  PFA datasheet
  9. Hello all I am have FX3G PLC, where i am trying to use SPD function for speed monitoring and controling. currently i am working on software only. I am using x4 as input (s1) , sk1000 (s2), and d4 (D) in monitoring mode when i am forcing X4 to ON/OFF ,  there is no any value change occure on d4 i have tried to change the s2 value from k1000 to k10000, but not fruitful i need your valuable support to confirm that my primary setup is correct or not and what things are required/missing attached program screeshot  
  10. rc01cpu and r60da4 help needed

    Hi every body, could you please help me; i have a mitsubishi plc serie iq-rwith the followings modules:powersupply r61p, r01cpu , rx40c7 inputs , ry10r2 outputs , r60adv8 analoginputs and r60da4 analog outputs. i am newbe with mitsubishi plc ;i would like to learn using the analog output of the R60DA4.for exemple i would send a digital value to the ch1 and convert it a voltage that i can mesure on the output of channel1.i have tried but i didn't succeed.i am using gxwork3.i have configured channel1 as +10v -10v output, normal mode , normal output;then i made a simple program in sfc to try this conversion but i get nothing in the output of channel1. i found that the digital value should be sent to the adress D11 wich is the adress of channel1.here you will find the file i made with gxworks3.could you please help me. ANALOGOUTPUTSCF.gx3
  11. Hello there, I am using a Kinetix 5700 drives to control bunch of axis. HW used : 5069-L320ERMS2 GurdsLogix, 2198-S086-ERS4 Servo Drive with MPM-B2152M-M motor and the 843ES-SIP12BA6 safety encoder. All is working fine except I can't figure out how to dynamically change an axis velocity  controlled by a MAG instruction. I have a virtual master axis controlling the velocity and each physical axis is controlled by a MAG instruction with a gear ratio. In my safety program I have SFX and SLS function block used to determine the safe speed limit. The  SLSLimit output of the SLS function block is linked to a SS1 Request of my servo drive. This causes the axis to stop when safe speed limit acceded.  What I'd like to be able to do is to dynamically change velocity (limit it to safe speed if SLS instruction is active) of each axis without having to change the gearing ratios and thus avoid the SS1 safe stop action.  I know how to do that using JOG or MOVE but is it even possible to do that using the MAG instruction? Regards Martin
  12. FX5U high speed counter

    Hi All Does anyone know if it's possible to simulate the HSC function using just the software? I'm using the Hioen command but I want to try and simulate it if possible. Thanks in advance Scott
  13. Hi all,  I am in the process of doing a project for some school work and need to do a SWOT analysis of the latest modular PLCs from Mitsubishi (R series), Siemens (S7-1500) and Allen Bradley (ControlLogix).  So I thought what better way than to ask the people on what they think are the pros and cons of each! Thanks for your responses in advance!
  14. Pulse FLow Meter

    i have a paddle Wheel Floweter of TOkyo Keiso W2000. its frequency is 88 Hz .  Flow Rate  30L/min. i want to connect it with mitsubishi fx3u plc digital input as it is pulse flow meter.    kindly tell me how can i determine its pulses for liters.
  15. Best Practice Rack 0

    Is there any reason not to have input and output modules on the same rack as the processor and Ethernet cards? We have RIO’s and sometimes have networking outages, I want to move critical IO to Rack0 the same rack as the processor, is this bad practice?  I've seen architecture for BMS that only have Ethernet cards and processors in Rack 0... 
  16. Hello guys, I am running an application for packaging measurement using a sick DFS60B incremental encoder (programmable from 1 to 10000 PPR). In more detail, it passes packaging on a conveyor belt and we have created an inspection station and an expulsion station (defective packaging), so we use the encoder to check at specific points of the packaging for defects (we use special sensors to check defects). ) (there are four in total). However, the problem we are having is the following: When reading the encoder in the PLC, the same means that performs "jumps" and does not enter the windows (GRT and LES) created on the ladder, ie, as if it were not continuous. . I understand that because the VHSC24 card works at 1 MHz in counter mode, this type of problem should not occur according to our application is not even 100 KHz. For example, our case: Using 1000 PPR and the motor speed (coupling output) is 3600 RPM (in practice it is around 1750 RPM) the frequency is calculated as follows: F = (PPR X RPM) / 60. : F = (1000x3600) / 60 = 60 KHz, ie 60 KHz is much less than 1 MHz, I think this kind of problem does not occur. Application Info: . Studio 5000 V31 . PLC Model: Rockwell 1769 - L19ER-BB1B CompactLogix 5370 . Encoder Card: 1734-VHSC24 / C . Incremental Encoder: Sick, DFS60 up to 10,000 PPR and HTL Electrical Interface. Using a 200 mm circumference / perimeter wheel. . Motor Nameplate Data: 1670 RPM, 0.37 kW / 0.5 HP, 60 Hz . Inverter: Weg CFW500, Output Frequency 62 Hz. Card Settings we use RPI: 2 ms Type: Counter, but we already use it as Encoder X1 Store Count Mode: Disabled Filter: No Filter, but we use 50 KHz and 5 Khz filters in our tests. Counter Attenuator: 1 Wiring Diagram VHSC24 We turn on encoder A at input 0 and encoder Aret at input 1 In logic (Structured Text) Using the PMUL instruction to convert encoder (Pulse) data to mm scale. (Ladder) The window comparisons part (GRT and Les) and other part of the process. We emphasize that we performed the tests also only with the reading and comparison part of the data, excluding the other parts, precisely to verify the issue of Scan, but the problem persisted. If anyone here in the forum has some information that can help us, I would appreciate it.
  17. Control Panel

    Is it possible to view the values / states of all inputs, outputs and workbits (e.g. 64.00 through 64.15 on Omron CQM1 PLC) on a single screen or control panel within CX-Programmer software?  I'm trying to troubleshoot some ladder logic that I wrote and need to know the values of 5 or 6 inputs/outputs/workbits simultaneously.  Having to scroll up and down through my ladder logic repeatedly does not work well with code that changes state every 5-10 seconds or so. Any help is welcome.
  18. Using a AD041 and DA041

    Hi, I'm using a CJ2M CPU 33, and also a CJ1m Ad-041-V1 Analog Input and DA-041 Analog Output card.  I am using the Analog input to measure my current in my one heating application and  Ihave that reading and scaled correctly, but now  I want to use my Analog output to replace the Rheostat  we have in the system. I'm having some issues setting the range and getting voltage to vary. I also am a little new to Analog Outputs and don't know what I'm doing wrong. I have attached my program here. Any help would be greatly appreciated. Analog Heat.cxp
  19. Hi, I can’t find an answer to the following and I was advised to ask it here.I’m programming an Omron CJ2M with an MD212 high speed I/O card. I usually do all my programming in Structured text, simply because I like it a lot over ladder or sft.Now, if I want to read the hight speed counter (incremental encoder), I have to make a ladder section and use the PRV instruction to store the present value in a chosen location.The manual says the current PV is stored in A271, but I can’t get a readout there. Apparently the only way to read it is through this instruction.Does anyone know if there is an equivalent to the PRV instruction for Structured text? or another way perhaps? Again, when I check the actual memory adress, there’s no value there withouth the use of the PRV instr.
  20. I am controlling the powerflex 527 drive with MSO instruction, first setting the drive on and then running the motor with MAJ instruction. After MSO instruction, motor is rotating about 2 sec and then stops to wait the  MAJ. I have not find any solution for this. My configuration is frequency control, no feedback, sensorless. One hint i found from the rockwell pages but it did not help me. Rated slip speed is set to zero.  
  21. Omron Hardware

    Please let me know if it is allowed to sell PLC hardware on your forum. I accumulated lots of Omron hardware  that I want to get rid off. Here is the list, I have several of each type, asking $12 each plus shipping. All in working condition.  Base Unit C200HW-BI051 Base Unit C200HW-BC101 16 Point DC Input Module C200H-ID212 16 Point Digital Output Module 24VDC C200H-OD212 Power Supply Module C200-PA204    
  22. OD212 Card Outputs not powered

    Hello! I'm running into a problem with a malfunctioning OD212 output card on my PLC.  I figure the problem has something to do with my wiring, because I've put 2 different cards in with the same results. The card is unable to switch any of the relays I have as outputs although the indicator lights on it are functioning as expected. The setup it is in is: A PA202 power supply, followed by a CJ1M CPU13 CPU, 2 ID211 input cards, and 3 OD212 output cards. The bad card is the second OD212. All of the other cards work fine, it's just this one that's been having problems.  8 of the terminals on the bad card are hooked up to relays that each draw 0.02A and two more are attached to relays that draw 0.05A. So in total that's 0.26A if all the outputs are on at the same time (which they never will be.) I saw someone was having a similar problem to me on the forum, which was solved by switching out the PA202 supply, but that didn't work in my case. I don't think the problem lies with the PLC or the card's placement in the rack because I switched the card's position with the one next to it (output card 2 switched with output card 3) and tested that card (output card 3 in output card 2's place) without hooking it up to the original wiring and it worked just fine. However, I was still getting the same issue with the bad card even though it was in a different position, leading me to believe that I fried it somehow. Some other quirks of the bad card are that its outputs do not turn on and off with the indicator lights like how the other OD212s do. Below is a link to a video that shows this. The bad card has already been switched with the one next to it in the video - so it's on the end, but it's original position was second to last. https://youtu.be/wTvvGCHFpsc ( you may want to watch it at half speed ) So what I'm wondering is: how am I frying these cards / Is the problem easy to fix or will I have to send them to Omron? Thanks in advance!  
  23. Hello      I have a cj2m processor and md211 module and I want to read position from rotary encoders who are put on the stepper motors. I use high speed counters to count the number of(I made settings like in documentation) but every time I read velocity.   In first two picture I have 3 blocks for PRV function , I set port specifier [#0, #1 and #3] because on this ports I command 3 axis. Please help me!              
  24. Hi there, is somebody experience whereby the output of the 1769-OF4Ci is not responding on the value entered?.  Setting: 4-20mA Res: 0- 32767 - PID set whatever value I key in the output current remained.  please help. Ganie
  25. hallo everyone ...i use mitsubishi Q00UJCPU and QD77MS2.. i try to make a speed control program and the speed wants to be changed during servo operating, i use dedicated instructions ZP. PSTRT1 (axis 1) and have tryed but it was only successful to change speed with "change speed control" function once ... is it like it? cannot change "change speed control" many times when servo operations?