Search the Community

Showing results for tags 'got2000 device bit'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 47 results

  1. Hi, I would like to automatically close the VNC viewer connection, which is used to view the GOT2000 HMI remotely. Very interested to know if any options are available. Thanks in advance !!!
  2. GOT2000 DIRECT TO D700 PU PORT

    Hello Every body Peeps, I downloaded the GOT2000 comms manual where it describes how to connect to the D700 DIRECT on the PU port. I then placed the D700 template of the HMI from GT Designer 3 onto a GS2107WTBD. Parametized the drive, etc.   In the template  I changed the devices to match the station of my drive which is 1. i.e. on the template I had Device 0-0 SP122, for start forward, i then put my station no. 0-1 SP122, and that works.   However, other than that, and the stop nothing else works, despite changing the station no. on devices, but I read in manual that if Pr 37 not 0 and SP127 = 1, then HMi cannot monitor SP109-111 which are devices used in my amps and speed setting, which they are not displaying on HMI. I can change Pr 37 to anything other than 0, but i have no idea how to change SP127, which description is Link parameter extended setting.   Any ideas?   Thanks.
  3. Hi there!   I'm trying to communicate a Weintek cMT2128X with a CP2EN via Ethernet. The thing is I'm getting 'No device response' messages every 2-3 seconds. They'are connected at some point because some values are updated, but the connection error keeps showing up. So far I've checked: - Comm. settings are okay in both sides - Wiring is good - Happens the same with a CJ2 CPU. - There are two arrays of 50 UINT each, I don't know if that's slowing things but that would surprise me...   I've worked with Weintek HMIs before (communicating with different CPUs: LOGO!, CP1, CJ2...) and never had this problem. I just set the IP addresses and everything was working fine, so I guess I'm missing something. Hope you can throw some light at this! Thanks in advance
  4. Hello, I want to ask "is there any formula that shows how to calculate the HMI data logging retention time?" For example, I want to set Trend and Alarm data retention time to 1 month. So how to calculate and setup in GX work3 HMI Designer? If you have any related documents, please share. Thank you. Have a good day!
  5. Hi all, I would like to know how to communicate scale indicator device mettler Toledo ind 320 using  module QJ71C24N-R4 by predefined protocal   I also tired to communicate in CH1 with the G.INPUT instruction to communicate when the device in MT continue mode it does communicate but I dont know how to convert value Now by trying modbus communication predefined protocal works fine but i cannot read data the is no SD/RD transmission happening  Can anyone help me with this  Thank you serial monitor.gxw serial monitor.gxw
  6. Recipe in gt designer 3

    I have a gt2310_vtbd and i want creat recipe but i cant find Recipe from object .
  7. Hi All, As a system integrator coming from an Allen-Bradley based environment to a Mitsubishi based environment (GX Works 2, Q series PLCs), I am used to doing this with Allen-Bradley PLCs: when you hit save while online, you are prompted to upload the values in the tags and can save these values and view them offline - which is useful when doing modifications and analysis offline, as well as backing up settings in case your PLC dies and has to be replaced with a brand new one. I was wondering if anyone knows if there is a way to store the current values of the devices in a Mitsubishi PLC to my PC along with the .gxw  file that is saved when doing a "Read PLC"? I am aware you can set up a File Register but it seems to only save ZR devices as well as specifically designated "Extended Data/Link" D and W devices, but most data is not stored in these devices. Thanks
  8. 2 PLC with 1 HMI

    Hello, I am going to be adding plc on press welding machine. the machine has PLC FX3U-16M and attached with 15 16points I/O module. is there any best way to connect 1 HMI with both 2 PLC ? 
  9. I've set up 20 or so of my alarms under the 'User Alarm Observation' section. I then added an 'Alarm Display (User)' object. Will this object display my alarms when they come in? I'm noticing an Alarm ID section in the 'Alarm Display (User)' object section. What is this Alarm ID for? Can the 'Alarm Display (User)' object only display one alarm? That doesn't seem to make any sense? How would I got about configuring this object so that it will show all my alarms as they come in? Thanks!
  10. GOT2000 <-> Omron CJ PLC

    I have an application where I'm using GOT2000 to read data from the weighing unit using RS232 and I send this value to Omron CJ2M through Ethernet/IP. Some variables from that PLC are connected to the elements of the HMI. The problem is when writing the weight value to the PLC through script or Data Transfer is disabled, the RS232 reading works fine, it's fast, etc. However, when I enable the script which writes data to the PLC, the RS232 slows down by a lot, like it refreshes every 2-3 seconds. If i set the script to execute like every 1-2 seconds, it is working better (still slower compared to when the script is disabled) but I cannot leave it like this, because the weight is used to control some valves, pumps, etc. Enabling script doesn't slow down normal communication with PLC, because I tried to test it by displaying the value of seconds from PLC on the HMI and it refreshes every second. Does anyone have idea why such tiny script causes so many problems with RS232?
  11. Hello, Good Day All. I am facing this issue while I am going to copy old plc to new plc. but old plc having 4965 steps, once going execute this program to new plc its showing more than 8000 steps. please suggest on this. PFA.
  12. Hi! We have a GOT2000 HMI with a Q06UDVCPU system. During an investigation, I found that the address on the HMI (for example D10120) and the address in the PLC (D10020) are different. The value is the same, it appeared instantly during monitoring, but when I searched for it, didn't find it (I couldn't find the D10120 in GxWorks2, and couldn't find D10020 in GtDesigner3). The HMI's address is 100 higher. I never saw anything like that. Where is this difference can be set? Knowing this, I can navigate in the program..it's just annoying.
  13. I would like to send ascii data  to other devices using RS232 interface. and the example format is "0009" (it is product counter machine marking). how can I do this? I am using q03ude, I usually convert 1001 to ascii using BINDA and use the last data (01). but, when it double word data e.g. : 100009 the last data is 9 and null, not 09 
  14. GOT Mobile 2000

    Hi. I have a problem with the communication GotMobile in GOT2000 This is the error (Photo). PLEASE HELP!!!
  15. GOT2000 as MODBUS TCP slave

    I have this setup: FX3G CPU connected to GT2103 through RS422 (CH1). GT2103's ethernet port connected to LAN and set up as modbus TCP slave (CH2). I want to read/write PLC word devices using a modbus TCP client, from a PC. The HMI is acting as a gateway between PLC and PC. I used the Device Data Transfer function to send PLC's D register values to GT's internal GD registers. D0....D9 ==>  GD0....GD9 After some tries, I get valid response from the modbus slave. Reading the holding registers 0....9 (40001....40009), I get only zero values. Those registers can be written back with different values, correctly. I'm sure I didn't understand correctly the modbus address mapping to GT's internal memory. Can anybody help me? Thank you.
  16. Hello fellas. I am having trouble with understanding the communication between my AB PLC and my Balluff BNI0085, which is connected through an IFM AL1120 IO-link deivce. I am currently running a setup with an AB PLC (L18ER) that is connected to a local network through a network switch. I have connected my IFM AL1120 to this switch, and the IP configuration for both devices have been completed. The communications are made by using two add-on instructions, supplied by Rockwell: The BMC_AOI_PROC_BNI0085 instruction (For the Balluff smartlight), and the Generic_4PORT_IOL (For the IFM IO-link). I have additionally been supplied an ACD-file by my ex-coworker, containing a program that administrates the communication between the two add-on instructions. I have attached the routine from this as a PDF. What works: I can go online with my PLC, and by using the parameter "BNI0085_Mapped_Data.O" I can control the smartlight. I can change the settings for light-mode (Segment, Level, Runlight, Flexible), and the different parameters for each mode. What's the problem: When I change the Mapped_data.O to run in level-mode, I can adjust the light to show the level desired. When I try to adjust the level above halfway, the light switches off, and can't seem to be steady lit (Light turns on/off, random dimming). I speculate this might be due to the small power supply for the IO-link device, and the setting for brightness is not included in the AOI for the smartlight.  I therefore tried to adjust the brightness by connecting through the LR-device software from IFM(The same used to configure the IO-link). I added the IODD (IO-link device description, "Balluff-BNI_IOL-802-102-Z037-20190215-IODD1.1.xml") for the smartlight, and connected the device, which is discovered in the device list once the IO-link IP has been entered. I can read the values from both the IO-link and the BNI0085 devices, and I can write parameter settings to the IO-link device. Whenever I try to edit any parameter for the smartlight, I get the error attached. I am currently trying to follow the SmartLight userguide for the Balluff, as it describes the brightness setting as being in the ISDU index 51hex, but I don't know how this pertains to the AOI.   I am in over my head with this issue, and I don't know what information is needed or what is unnecessary. I've tried to include all that I think is relevant, I'll gladly provide what might be missing.  Any help is greatly appreciated, cheers :)   Balluff_smartlight_com_MainRoutine.pdf
  17. GOT2000 Recipes

    Hi I'm new to GOT2000 Hmi and I have a problem about creating recipes on (GT2107). Do I need sd card or usb memory stick to save recipe or I can save it in inside memory of hmi?  Can someone told me how to do it step by step cause I only have errors when I want to save or load recipe.  Thanks in advie 
  18. Hi all:   Hope somebody will help me with the below error encounter on the NA. I mapped a external device (NJ PLC) variable (which is a structure) to a NA Global variable and the structure is automatically created in the NA data type as expected. I then create a new NA global variable and defined its data type as the auto created structure. However i observe the created new NA global variable is highlighted with an error "a data type cannot be used by both mapped and unmapped variable ....." ( pls refer to the attached screen).  I have found and view on the Youtube this video :"Introduction To The NA DataTypes" (link: https://www.youtube.com/watch?v=VZxWnVn1CSY). that clearly show the "imported" structure can be used for unmapped NA global variable even there is some variable already mapped to external device variable (starting from the 3:50minutes mark of the video). In my NA program i would need to create such unmapped variable for my logic use. Also i observe that i was unable to delete the auto created structure from the NA Data Types even after i deleted all variables that are defined with that specific structure. How can i delete such auto created structure in case i want to clear off some of those unused data types. I am using Sysmac Studio version 1.30.0.17. The HMI Device created is the NA5-9W00 (version 1.11)          
  19. Hello Guys, I have a problem with my Screenbuttons, if i push them, my drive moves only an Impulse. I see on the Simple-Motion Module that the Signal is during pushing the screenbutton is active, but the Axis moves only an Impulse. In example M400 is for drive the 2nd Axis to the right side and M405 for the left side. My Hardware is: FX5U, GOT2000 (GT2505HS-VTBD)
  20. GT2710 screen not refreshing

    Hi All, and apologies for what is probably a proper newbie question. I have a Mitsubishi GOT2000 (GT2710) connected via DH485 to an Allen Bradley SLC500. Most of it works fine except for one base screen, which when opened doesn't get updated with any values. Opening any overlaying window screen will then causes the underlying base screen to then get populated. It's almost as though the first screen doesn't know where to get it's data from until the second screen is opened. As before I'm a beginner with this, so hopefully there is a simple setting that I haven't spotted. Thanks in advance for any advice.  
  21. Hi, I am using IQ-R Series "R16ENCPU" With Inbuild CC-LINK IE FIELD "RJ71EN71" and attached CC-LINK "RJ61BT11". Problem is, Even though my remote IO cards are in Online connected with masters, I cannot able to On/OFF Remote Device station IOs in CC-Link IE FIELD network. But CC-Link Normal is working fine. Refresh settings and Network Config Settings are done, Below attached the pics for reference. I cannot able to find the problem, Can anyone help me in this.  
  22. Hello everyone, I would like your help on an issue. I have a screen designed with GT Designer3 ver1.156N. I found the Ver1.156N software, I installed it, but I can't open the project. I would appreciate it if you could help me with what to do.
  23. GT2107-WTSD not showing in GT Designer3

    Hi guys, im just looking for some help if possible, I am trying to setup a HMI (2107-wtsd) but GT Designer3 does not have this model nor does it have any 2107 models in the GOT type dropdown. How can i get my model to show? I have tried setting the GOT type as a G2105 and the GT softGOT2000 and these did not work, the HMI is on a white screen with install package data but i cannot do this if it is not in the GOT dropdown correct? I have attached some pictures to show. the HMI is connected to the PLC via ethernet and the laptop is connected to the HMI via usb I am very new to this so we are using test benches so if anything looks wrong i am very sorry
  24. GT designer

    Hello everyone Im updating a HMI with GT designer, the problem occurs sometimes when i try to save the new changes it display the pop up notification that i have attached, therefore i cannot save my changes and i must start over, what is pretty frustating because once i do it again and save it there is no problem.  Does anybody know if im doing something wrong? the application was created with melsoft Navigator, what it seems to me being the problem not a fan of mitsubishi... Thank you in advance
  25. Hi all. This is hopefully an easy fix. I have words and bit values in a recipe that I am trying to show in a logging file. I can get numerical values to show but I can't get the word devices from the recipe to show up on the logging file. Eg my devices from recipe set as a string starting with device gd60120 and in the logging file I want gd60120 to show the word, they are both set as unicode.