Search the Community

Showing results for tags 'fx5u control inverter d700 through rs485'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 182 results

  1. Powerflex 525 single phase

    Hi ! I have a powerflex 525 inverter. I have three phase motor. It is possible to make running the motor like this? If yes how ? Should I change some parameter in the inverter ? Thanks in advance. 
  2. Hello Everyone, I am struggling with interfacing Incremental encoder with FX5U PLC, Does anyone have parameter setting and sample program for same. i am unable to fetch counts...   Encoder: 500ppr, 24V line drive, A-B phase,  PFA datasheet
  3. Hmi temperature delta

    I have connected 2 temperature devices with him delta with plc delta by rs485. When I run plc I can see the temperature change on pc but the problem in hmi  it's give errors. Com 2 errors  I need someone help me to connect these devices please 
  4. inv002_refresh scanlist

    Hi all Can someone please clear the scanlist value up for me which is part of the INV002 function block the documentation says that whatever nodes you have assigned are what bits you need enabled in the scan list they give the example of node 1 and node 14 being used from this they get a scan list of #4002, where does this number come from? https://docplayer.net/59460263-_inv002_refresh_v31-bool-dword.html for my next job i will be using 3 inverters and am not sure what my scanlist should be
  5. Hi All First ever post so forgive me if I do anything wrong. My customer has given me an FX5Uc PLC and a Delta DOP-B03S211 HMI. Comms need to be via serial. Ethernet not an option. I have configured the HMI as the Delta DOP datasheet(see attached) I have configured the PLC as: - MC-Protocol - 19200,8,1,Odd I however get an HMI error: - ########################################## COM 1 STATION 0: COMMUNICATION ERROR 3. READ ERROR No Response from Controller ######################################### I have created a simple page on the HMI  consisting of a push button (M reg) and a numeric display (D reg). When pressing the push button I can see the change in the PLC. (Transmission good) Any change of the D reg in the PLC is not reflected on the HMI. Confirms the message. I have tried all combinations of settings on both side but no joy. The PLC seems to be happy as it receives and transmits ok with no errors. Can any one see what I am doing wrong? DELTA_IA-HMI_Mitsubishi FX5U_CM_ENG_20170728.pdf
  6. Constant Web Tension Control

    So I'm having trouble writing a FBD within my current program for a slitting line. I need to keep a constant tension on my web as it is being recoiled onto our recoiler. I wrote a simple program using a sensor to read the growing rate of the coil to get a radius and I have feedback on my torque on the recoiler motor. The simplest math for this application without getting into anything too fancy should be Tension(lbs)= Torque(ftlbs)/coil radius. only problem is when its less than a foot then my calculation is thrown off and it actually shows tension goes up until it reaches the one foot mark then it seems to scale correctly. Do I need to scale something else? Any help on this would be appreciated.
  7. Hi guys I am trying to connect a Mitsubishi FX5U PLC to a Siemens WinCC RT Advanced. I did find a document on the Siemens side on how to configure the HMI, but I can't seem to find any instructions on how to configure it on the Mitsubishi side. Any help, sample will be appreciated.   Kind Regards Morne
  8. Hello.  I'm a newbie.  First project. So I need to connect the inverter to PLC and I have used inverters RS485 port and PLCs inverter input. I have made sure the wiring is correct and used a 100 ohm resistor as was shown in the manual. At least I hope its correct.  I have set most of the parameters as follows: P117 0 P118 192 P119 1 P120 2 P121 1 P122 9999 P124 0 P340 10 P502 0 P549 0 But still when I'm loading work on PLC then Module diagnostics is hitting me the error code H7602 that the communication has timed out and I don't know what to do.  Is it my parameters? I have checked the parameters in the gx works 3 also so they matched and now I'm stumped.    Please help  
  9. Hi, I have a problem because a TON Timer instance in an ST program does not start running. Is this a known limitation on FX5U CPU's or ST Language in General ? On the internet are some discussions, and there is a person which says it works for FX CPU's: https://stackoverflow.com/questions/58463316/delay-timer-in-structured-text?noredirect=1&lq=1 But not for me.... And some discussions here in the forum: http://forums.mrplc.com/index.php?/topic/20864-plc-failing/ http://forums.mrplc.com/index.php?/topic/37923-calling-a-timer-in-st-code/ The last one is interesting, but it did not helped in this simple case.   For clarification, I created a very small program in GX Works3 (v1.057K) The FB instance in Picture 1 works very well if one sets M10 to True. The ST instance in Picture 2 does not start when setting M20 to True. Has anybody a clue? Any help welcome DWIM  
  10. Hello everybody I have strange effects when connection MODBUS TCP IO-Boxses from my FX5U-80xx. So I thought about looking for network issues fixed in the firmware. So, the website below has firmware 1.201 and I have 1.110 currently. Does anybody know where to look for the revision history of these Firmware fixes? https://www.mitsubishielectric.com/fa/download/software/cnt/plc/index.html#js_swdata_cat_9 The Japanese have some more info here: https://www.mitsubishielectric.co.jp/fa/download/software/detailsearch.do?mode=software&kisyu=/plcf&shiryoid=0000000051&lang=1&select=0&softid=1&infostatus=8_1_1&viewradio=1&viewstatus=&viewpos= Translate:  "New functions added in firmware version 1.201 (2019/11) For details on the additional functions, refer to "Addition and modification of functions" in the related manual "MELSEC iQ-F FX5 User's Manual (Application)". The CPU unit serial number can be used from "17X ****" or later." I was not able to download these manuals (Japanese login screen). So I googled it and found it. But I was not able to find it in this document.  If someone knows more. Would be nice.  Thank you DWIM  
  11. Can someone please suggest a Control Panel Builder that is located in Germany?   I work for a company in Australia and due to Covid 19, we are struggling to meet an onsite date for a project in Germany.   This project uses Siemens PLC gear, Danfoss drives, and mostly Schneider electrical gear. The enclosures are custom and stainless steal.    I have electrical schematics and enclosure drawings for quoting.
  12. modbus_fb_11.pdfHello to everybody. I'm new I download from Omron France the FB to read form one or more instrument some register by Mod Bus RTU Every things is working well, but some register from the Instrument are on REAL. How i can get a REAL word with the FB on the attachment? Thank you   Modbus_03_Read_Holding_Regs.cxf
  13. I have a Mitsubishi FX5U-32M with 3 MR-JE-40C servos. Our system will be used in a robot cell, and needs to convey some information to the customers system, which is this EtherCAT side of things. They want to know RPM, torque values, position ,etc, of things on our system.. Our Mitsubishi supplier recommended an AnyBus X-Gateway (AB7961). They have a few YouTube videos on configurations, but unfortunately none on the Mitsubishi side i found. I've only been using Mitsubishi for a little over a year, but know my way around GX Works 3 pretty well.  I come from the Rockwell world with EDS Files and tag based setups, and for the life of me cant figure out where to start with this AnyBus. I've gone to the support page, got all the downloads and software, and gotten online with the Anybus. As far as beginning to setup the Anybus in GX Works side, to setup what registers i want to send, im lost... Anyone out there have experience with this sort of thing?
  14. Mitsubishi FX5-4LC

    Hello Guys,                      can anyone help me programming of FX5-4LC temperature control module with FX-5U80MT PLC. I want to Read present temperature value of each channel and want to set Temperature Set value from PLC.
  15. Hi guys I need to be able to access a FX5U PLC through a FX5-ENET module. I am new to coding with Mitsubishi and would like some assistance. Is it possible, and how would I go about connecting if it is?   Kind Regards Morne
  16. Hi Every one, I have two 2198-P070 bus power supplies for that I’m using for four Kinetix drives, 2 drives per power supply, all controlled by one processor (5069-L350ERMS2). I have an enable contactor setup for each power supply for each set of drives. I have them configured as DC bus groups 1 and 2 respectively. I had the first set of drives working, setup inside the motion group, with no issues. When I added the second power supply and drives. I found that when I added them to the motion group I couldn’t get the enable contactor to close for the first set of drives. I f I took them out of the motion group and made them ungrouped then the first contactor would close but then I couldn’t get the contactor on the second set to close. Do you have any thoughts as to what I might be missing to get these to work? See the screen shots for more detail. Let me know what you think.  Also, I have heard that only one motion group is allowed per PLC, but my question is : Can I use  sevral axes and Power units in the same motion group? 
  17. Omron rs485 communication

    I am using OMRON CJ2M-CPU15 with SCU41-V1 communication module I want to establish communication (rs485 modbus) between omron and Schneider device for reading out electrical parameters. How I can do this? I could not find any manuals and this is becoming very hard for me. I want simply to read few registers from Schneider. Where do I set unit number, starting register, ending register, number of data? I was recently using Siemens and Unitronix and started working with Omron recenlty. Do you have any examples or manuals for this? Thanks in advance
  18. Dear all, Do you have some ready examples for Mitsubishi fx5u where you use PID ? I use two analog input from 0-10V and two PLC output and I want to head 2 heaters. So how can I use PID autotuning? As I see in examples in manual, there also have other parameters, which I must set, except PID function. Thanks in advance . :)
  19. Hello Everyone, I am looking for sample program which are compatible with Mitsubishi Gx Works 3. Program should contain some timers, counters, arithmetic, data conversation so i can see the instructions of each and every basic blocks... I am using iQ-F FX5U Plc with GXWorks3 Environment.
  20. Hello!  I'm learning how to use mitsubishi MELSEC fx5u-32mr-es and an hmi panel mitsubishi electric got2000 model GT2104-PMBD. I have no trouble programming the PLC and also I managed to display a layout on the hmi but I ran into trouble with: How to connect the PLC and hmi directly via ethernet. I tried to connect them but the hmi says there is a comm error.  How to run a simulation using gt simulator. I made a program in gx works 3 and a design in gt designer 3, started to simulate but it says that the PLC type of the project is different from setting gt simulator 3. I checked the gt designer there I selected the PLC model FX, which as the only logical choice and in gx works I use the correct PLC/CPU (fx5u) so I'm kinda in a blind spot.  I hope someone out there can help me troubleshoot this problem since i need it in order to compete on a national level.  Best Regards. 
  21. HI all,   I was trying to connect my compass with PLC via SCU32 RS485 (2 wire ) in protocol macros.[ Unit 1 port2]  My send command is   " 01 03 00 01 00 03 54 0B'  &  Expected reply is '01 03 06 XX XX YY YY ZZ ZZ ZZ ZZ" I created a new protocol using CX protocol and created  a send message & a receive message command  and added to sequence 000. (refer pics) Also added PMCR instrcution in cx programmer (refer pic). I can transmit the data , but i cant see any recieve data in D2000. I am not sure what had done wrong, or am i missing something?   Any help is much appreciated!! compass_macro2.psw Compass_TEST.cxp
  22. Please could you assist with the software required to download data tables from 4 off DIRIS A10 Multifunction Meters into TM221CE40R Logic Controller via TMC2SL1 Comms Cartridge using Modbus Protocol over RS485. I have downloaded the Modbus tables from Socomec but not sure how to get these into the PLC. I would really appreciate your help in achieving this. I am using EcoStruxure Machine Expert - Basic to program the PLC & DAQ Factory Developer Release for my Touchscreen. Link to Socomec Modbus tables: https://www.socomec.com/files/live/sites/systemsite/files/SCP/6_gestion_energie/diris/diris_a10/DIRIS-A-10_COMMUNICATION-TABLE_2018-01_DCG01013_MULTI.html#General
  23. hi all,  I am using SCU32 ( unit1, port2, 2wire and termination OFF)  to get the RS485 data strings from the compass with setting 19200bps, 8 databit, 1 stop bit &  No parity. I can send the TX string ( 01 03 00 01 00 03 54 0B)  from D100 memory and  write the Rx data to D2000 (01 03 06 xx xx yy yy zz zz CC CC). But the whenever the there is no RX data, The TXdata bounce back to RX. (refer to video, d100 is TX, D2000 is RX). I also tried wth SCU32 termination resistance ON. Same thing. I am not sure what is missing. Should i use different logical Port for TX and RX ?    EDITED: Just tried another scenarios  1) removed the connector and tried , D2000 - was written the TX values  2) Disable the RX  changing  LD from P_On to P_Off. D2000 - was written to #0000 0000 0000 0000  I am not sure what is  happening., Open connection also TX data bounce back to RX   Appreciate all help Thanks a lot  video1.mp4
  24. Hello, I have been so many days trying to comunicate the multiway software trought a serial usb converter with the SCU31 device, using a omron function block to read a holding register, but I can't achieved it. Now Im receiving some frames on multiway, but there is always some errors. I was wondering if somebody in here that have worked previously with modbus and omron can be able to help me in how to configure everything corectly to be able to read the value from multiway, on the plc, and where is this value saved.  I'll upload some captures to show what I have done till now.    
  25. Getting this error while adding MC_TorqueControl. I want to control torque from HMI value. Using R88D-1SN08H-ECT drive and R88M-1M75030T-S2 Ac servo motor with NX1P2 PLC. Newbie Here. Please support. Error    1    The Axis parameter of the MC_TorqueControl instruction does not support single-axis position control axes.    Program1 Section0    Row 6