Search the Community

Showing results for tags 'device address'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 34 results

  1. Hmi temperature delta

    I have connected 2 temperature devices with him delta with plc delta by rs485. When I run plc I can see the temperature change on pc but the problem in hmi  it's give errors. Com 2 errors  I need someone help me to connect these devices please 
  2. Hi all:   Hope somebody will help me with the below error encounter on the NA. I mapped a external device (NJ PLC) variable (which is a structure) to a NA Global variable and the structure is automatically created in the NA data type as expected. I then create a new NA global variable and defined its data type as the auto created structure. However i observe the created new NA global variable is highlighted with an error "a data type cannot be used by both mapped and unmapped variable ....." ( pls refer to the attached screen).  I have found and view on the Youtube this video :"Introduction To The NA DataTypes" (link: https://www.youtube.com/watch?v=VZxWnVn1CSY). that clearly show the "imported" structure can be used for unmapped NA global variable even there is some variable already mapped to external device variable (starting from the 3:50minutes mark of the video). In my NA program i would need to create such unmapped variable for my logic use. Also i observe that i was unable to delete the auto created structure from the NA Data Types even after i deleted all variables that are defined with that specific structure. How can i delete such auto created structure in case i want to clear off some of those unused data types. I am using Sysmac Studio version 1.30.0.17. The HMI Device created is the NA5-9W00 (version 1.11)          
  3. Unrecognized Device

    Hey all - I am stumped and looking for some assistance. I have a project in studio 5000, v.32 where I have some ABB drives that are not recognized. I've installed the EDS files, exact same one my co-worker besides me did, and mine will not go recognized and it is driving me crazy! I've done it while online with the PLC and offline, still to no avail. I've also installed the EDS files by going through Tools>EDS Hardware Installation and by right-clicking on the ABB drive in the controller organization tree and registering EDS file. Thanks for any assistance, -k
  4. I am trying to get produced and consumed tags set up between 2 1756 racks with different ip's. The 1st rack has an ip address 172.28.6.3. The 2nd rack has an ip address of 10.81.105.8. Would this be as simple as adding an EN2T card to one of the racks and setting the ip of one onto the same network? Or is there a better way to do this?
  5. CCLink

    Hi guys, I've just completed pre-commissioning on a Mitsubishi project which uses CCLink. My remit was to get the CCLink network up and running which I eventually did but not without issues. Basically, my problem was to do with the number of bits and registers consumed by a station. I read in a manual that each station consumes 32 bits and 4 registers for read and 32 bits and 4 registers for write. On my network I had 3 ST1H-BT modules occupying 2 stations each and 3 non Mitsubishi devices occupying 4 stations apiece. My RWr address starts at W300 and RWw at W500. Like I said everything matched up and I/O checks completed successfully. My question is, and I've trawled through the manuals looking for an answer, how is the number of points calculate? For example my non-Mitsubishi devices they occupy 4 stations, Expanded Cyclic Setting is Octuple and the number of points is 896. How is the 896 calculated? Thanks in advance
  6. Hi everyone My system consists of 2 main stations with 2 CPU Q06UDEH and connected together by QJ71GP21S-SX module but I don't know how to link the address between these 2 CPU together? so can anyone help me? Thanks so much   
  7. We have an iQ-r R08cpu that will not display some labels or addresses.  The PLC and the machine it controls run as expected.  However, when we read from the PLC, some of the labels and addresses are not shown.  Although it runs as expected, we are hesitant to make any changes or write to the PLC. There is a screenshot attached.  Any advice or solutions for this?
  8. CompactLogix L35E

    Hi folks, I'm trying to communicate with an old CompactLogix L35E via Ethernet. I have already establish communication via DF1 Serial port and was able to go online but I Do not know the IP address to communicate via Ethernet. Can someone please tell me how I could determine the IP Address or create a new one ? This Controller was remove from a working machine. Any help will be highly appreciated. Thanks, Anthony.  
  9. hallo all, I want to ask if I click "read PLC Data" the "points" will appear, I use the QY18A output module that uses 8 points but there is no choice, the smallest is only 16 points.  so I can't put 148 in the "start XY" column ... will it affect the I / O address in the program?
  10. Device point error between Parameter and PLC

    Hello all, I am a beginner with PLCs programming. I have an issue on GX Developer programming software from Melsoft trying to program my Mitsubishi Q-series PLC. CPU is Q03UDCPU. When the program is written and I try to upload it to the PLC, with the write to PLC window, I check -Program -- MAIN and -Prameter -- PLC/Network/Remote, click EXECUTE and a message appears : "Device point that is set in parameter is not match the device point in PLC". I can't fix it. In Parameter - PLC Parameter - Q parameter setting (window) - I/O assignment tab : I have (see image). Whe I use CHECK button it says there is no error. The X41 input device is plugged on slot 1/00. I am making this folowing the instructions a PDF I found on the Mitsubishi electric's wesite : Q-series basic course (for GX Developer). Thanks for the help, A. S.
  11. Hey everyone! New member here, and this site has always been a big help!  I try to help other folks too, but a lot of guys are super quick on here.   I've got a problem using some obscure components. I inherited a sensor network at work that uses Panasonic S-Link and I need to read them from a Q-Series. Panasonic makes a module that slots into the Q Series called an SL-VMEL-Q that I have.   My question is:  Did I do everything correctly on my Mitsubishi side? I put it into the parameters as an intelligent module with 64 points and I put the correct address in for the start I/O. Is that all I have to do?  This is the first time I used a module that wasn't on the drop down list when you add one in GX Works 2.   I can read and write to the buffer memory, but I can't get the unit to send to or receive from the sensors. I think the problem is that there is no end unit on the S-Link line (I don't know if it's just a terminating resistor or what), but it previously worked without one, so I can't be certain.
  12. GX Works 2

    Hello everyone! Can anyone suggest to take all the Input and Output (digital) status at a time in a single file for backup in gx works2 in FX2N PLC. I need to confirm that all required IO are in perfect condition before start operating the machine. Also I plan to design a troubleshooter to find problem.
  13. Lets say i have a PLC, with a name PLC1 with IP/Subnet of 10.125.34.243/255.255.255.0 I have to communicate this PLC1 with 2 other PLC's, PLC2 and PLC3 PLC2 with IP/Subnet of 10.125.34.10/255.255.0.0 PLC3 with IP/Subnet of 10.125.46.10/255.255.0.0 I imagine that, all these three are in different subnets, and so there should be no communication at all, but when i tested it, PLC1 to talking to/from PLC2 and not PLC3.  anyone know the answer to this ? How does it talk to PLC2 with different subnet, but not PLC3 which is in different subnet as well. 
  14. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.
  15. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.
  16. CX-Supervisor 3.4.1

    Hi After updating CXS to ver. 3.4.1 I can't see point address I can see them when I editing but in the list form only the array len. is shown. When I enter a new point I can see the address. Anybody now hove to solve that ? Banker
  17. Double address - Alarm

    Hello, I would like to see your logical opinion about this situation and in which part of system where I need to find solution - software or in the physical field. Subject: Twelve old system based on Mitsubishi PLC AnS series, Profibus Here is pneumatic transport, with 5 lines, each line have a shredder and discharge valve. A few months ago, when line 1 works , display shows line 2 and vice versa, it was first problem, but the system was still working. From the last week system doesn't work. On the display appear line 3 in works, but system can not started. Alarm shows Double address (perhaps two valves have some address), Alarm still appear after reset and even all lines are turned off. What is your opinion where to find proble (PLC, I/O moduls, cables,...)  
  18. GX Works 2

    Hello everyone! Can anyone suggest to take all the Input and Output (digital) status at a time in a single file for backup in gx works2 in FX2N PLC. I need to confirm that all required IO are in perfect condition before start operating the machine. Also I plan to design a troubleshooter to find problem. Thanks in Advance..
  19. Hello.   I'm trying to communicate between two PLC's  using FINS function block _CPU011:ReceiveData.   PLC1: IP 192.168.1.50 (MASTER)   PLC2:IP 192.168.1.51 (SLAVE)   If I don't use »IP Address Table« everything works using NODE number &51.       The problem is that on the real project these two PLC's will be on different subnet.   For example:   PLC1: IP 192.168.1.50   PLC2: IP 192.168.2.50   So I will have to use »IP Address Table« to achieve communication between these two PLC's.   I tried to sett IP Address Table on MASTER: Node 1=192.168.2.50   But If I try to communicate I see that packet is sended to network but I've got error #1005.   Do I have to sett the SLAVE IP Address Table?   Hoe to do this?   What are the right settings for MASTER and SLAVE IP Address Table?     I'm attaching pictures of CARD settings.  I don't want to use CX-Integrator because I would like to make project to UPLOAD and forget.       Thanks.  
  20. Dear all, I'm first time using M580 (hotstandby). Now finish the configuration, but the problem is how to write the address for Digital Input, Digital Output, Analog Input, and RTD module in elementary variable ? I try to put name DDI_1 and the address is same with M340 topology like %I2.1.0.1.1  and for digital input but got message after build : {Elementary Variables}    :     The instance is located on an address that isn't configured. :     DDI_1 Thank you for your advice regards  
  21. Dear all Please identify me i am having one Issue in my PLC.When I changed the IP of my plc then suddenly its showing error ERH its mean IP address wrong but  My CPU setting is same like previous means unit no=0, x16^0=0 ,Node=x16^0=1  and IP is 192.168.0.15 Mask add.255.255.255.0. but when I, transfer to PLC (in Program Mode) its not transferred(Failed to Transfer) please rectify me where I am doing wrong.
  22. I READ IN THE MANUAL FOR THE CJ2M-CPU34 THAT IT IS POSSIBLE TO CHANGE THE IP ADDRESS BY WRITING TO D30098 AND D30099 (MY DEVICE IS UNIT 0).  I TRIED TO DO THIS ON A TEST PLC BUT AM NOT HAVING ANY LUCK... I WROTE MY IP ADDRESS #C0A8 TO D30098 AND #0E30 TO D30099 (IP ADDRESS 192.168.14.48) WITH THE CPU IN PROGRAM MODE, I SET THE RESET BIT (A501.00) TO TURN ON ON THE TRAILING EDGE OF THE FIRST SCAN BIT, I CAN TELL THE CARD RESETS BECAUSE I AM CONNECTED VIA ETHERNET AND I GET DISCONNECTED, BUT THE IP ADDRESS DOES NOT CHANGE.  IS THERE ANY WAY TO CHANGE THE IP ADDRESS WITHOUT CX-PROGRAMMER?  I NEED TO GET A SOLUTION TO MY CUSTOMER TONIGHT AND MY SUPERVISORS DO NOT WANT TO RELEASE OUR DEVELOPMENT CODE TO THE END USER.   THANK YOU!!!
  23. hi.  i want to make some program that work with indirect adress. example, i make program with many much type. I make with Got-1000 mitsubishi.   can you bring me some example? i am sorry, my english is Bad
  24. HI Everyone,  Recently i have bought a plc fx3ge and gt2000 hmi .the problem is that whenever i use a device address d280.b1 in hmi .i am not able to use the same address in gx works for plc (LD D280.1).can anyone help me with this problem.   
  25. GOT1000&CompactLogix Tags

    Hello Im new using HMI got1000, Im trying to connect using Ethernet this HMI to a compactlogix, i already imported the tags, but i can't use any of them, because the gtworks3 says "you have to map the tags for set a device", i dont know what means map the tags, some one can help me please?