Search the Community

Showing results for tags 'data file'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 135 results

  1. NS15 - Data Log Graph Decimals

    Hello.I'm having variable Voltage expressed as UNSIGNED DOUBLE INT.For example: Val = 23423For displaying the right value I have to divide value by 100 ... Val/100 = 234.23V.For showing the value I can set the decimal place to 2 and Unit&Scale to 1002.The problem is:THE GRAPH IS SHOWING Val=23423. I WOULD LIKE TO SHOW Val=234.23.HOW CAN I USE THE DECIMAL PLACES IN GRAPH?WHERE CAN I SET THIS SETTING?Thanks.BR, Andrej.
  2. Read/Write data to PLC

    Goodmorning a question... I builded a simple monitor of plc. I need to read the data of the Mitsubishi FX3GE PLC. In example I should read: D14  FLOAT 32bit D16  FLOAT 32bit alarms from M100 to M119 and a bit of state M450 How can I do this? The PLC is connected via ethernet and the port il 5002.  I'm working with PHP and normally use modbus, opc-ua, etc. But here? Thanks in advance Carlo
  3. How I open file bin ihm fuji UG 530h ?

    I need help, I want modification ihm fuji UG 530h , the upload file bin, I am use software VSF edit V6.0, but not open.
  4. FX3U Stop Reading Channel Data

    Hello Everyone,  Need help with reading channel data of FX2N-4AD with FX3U Cpu. I have added all the logic and it works also. Problem is that, FROM function stop reading/fetching data from FX2N-4AD after some time i.e couple of hours and value just hang. Like 502 or something, untill you reset the whole PLC. What could be the problem. For the further info, -I have connected the FX2N-4AD on the right of fX3U-64M. -There are two extension blocks FX2N-16EX and FX2N-16EYR also added to the right of FX3U-64M -Order of mounting....FX3U-64M > FX2N-16EX > FX2N-16EYR > FX2N-4AD > FX2N-4AD   I have tried using the 2nd special module connected at the end, but It showed similar problem after few hours of running. THis shows that both Special blocks fx2n-4ad are okay. There is something wrong with PLC maybe? Please help
  5. Omron CSV FILE

    Hi Everyone.I want to read the csv file to plc. How can I do it. I will use to NB 5Q-TW001B for hmi.  PLC model : Omron CP1L-E
  6. simotion MMC img file

    Hello I have a SIMOTION MEMORY CARD 16MB for C230-2. Order No: 6AU1700-0AA01-0AA0 That formatted with windows. I need image file from Simotion MMC 16MB for write to This MMC with s7 img writer. Someone can help me. Thanks.  s7imgrd2.zip s7imgwr2.zip
  7. There have been many good discussions on the applicability of cloud-based solutions for manufacturing and process control systems. On one side, some people have concerns regarding security and control of the information, on the other side, there are identified benefits enabled by cloud systems. From VMS minicomputers to DOS and Windows, from ArcNet to Ethernet, it is inevitable the industrial automation systems shall adopt the technologies that are getting predominant in IT general use; the current environment that I am calling the “Cloud-iPad era” is no different; therefore the practical discussion is not if those new technologies will be applied in the industrial environment, but how. This paper is not intended to join the conceptual discussion about the cloud, but just to present a few simple practical examples, where cloud technologies are already enhancing industrial automation solutions and enabling new business opportunities. CloudPracticalApplications.pdf
  8. I'm attempting to make a backup of a program, complete with comments. I go connect to the PLC over Ethernet, and select Use Upload File to merge the comments from an original copy of the program. After that, I go file-saveas to backup the program. However the new saved file, complete with comments is only 134 KB, and the very original copy of the program is 230 KB, from 2003. Is there a reason for this, the program hasn't shrunk in size, only minor tweaking of some span calibration numbers.
  9. Hello people, I hope someone can help me with this. The system is connected with 8 PLC's. I want to transfer the data memory of a PLC to another like this: D850 from PLC2 to D900 PLC1 D850 from PLC3 to D901 PLC1 D850 from PLC4 to D902 PLC1 D850 from PLC5 to D903 PLC1 D850 from PLC6 to D904 PLC1 D850 from PLC7 to D905 PLC1 D850 from PLC8 to D906 PLC1 The data memory is an integer.
  10. Hello, Completely new to Mitsubishi PLCs and I need to use a date and time stamp for data collection purposes. We have a Siemens PLC as well and this has the data type "Date_And_Time" which is what I need to replicate. I have been attempting to write my own data type but am struggling with how to go about this as it is not straightforward and I cannot find anything about how the Siemens Date_And_Time is made up so I have nothing to go off. Does anyone have an example of a data type they have made that is the same? Or is there a data type which does this already in GX Works 2 that I just can't seem to find?  Please help!
  11. Hi Everyone, I would like to know  if two S7-300 CPU can exchange data via MPI protocol using X_Put and X_Get blocks. is it possible to test the data exchange via PLCSIM to verify. CPU1 = 313C-2DP CPU2 = 312 Please advise. Thank you.
  12. MBE Driver can't save config file

    Hello!I am using MBE Driver v7.46b on Windows Server 2012 R2. Problem is that I can't save config file. I can edit Channels, devices and data blocks, I can see incomming values, I save a file without any message. But config file is not saved. In Event viewer I get error as you can see on picture. It says: Error writing to system registry: Driver App 00000001 \Driver defaults. Other error says: Error writing to system registry: ServerMsg 00C54BB8 \Driver defaults.Is it server or driver problem? Please help. At the moment I can't edit anything in driver so I can't configure it to use it with my SCADA iFIX 5.8
  13. Hello! I am beginner in PLC world, also in SIEMENS PLCs. I managed communication over private network. Now I have a problem that I get same values on all inputs. Picture below shows my configuration of driver and data monitor. First picture shows values when input I0.0 is in state 0. Second picture shows values when input I0.0 is in state 1. Physically on PLC only input I0.0 is forced to 1, input I0.1 stays 0. But data monitor shows both inputs as state 1. Where is problem? Is problem in PLC program, TIA portal? I saw some guys using DataBlocks but I am not skilled enough to use it. Third picture shows simple PLC program on my PLC. Please help. Thanks in advance!
  14. Hello folks,   I am a rookie, self-training in PLC programming. I have written an SFC exercise (attached ACD file). I also try to call STL written subroutines and add-on instructions, from within the SFC main program. Calling the created subroutine works fine, but calling the add-on instruction fails from a reason which is above my level. I tried, tried and tried different solutions, with no avail. I am either wrong in writing the add-on (perhaps some missing but missing tag ?), or wrong is calling it. Can someone please give me a hint on what I do wrong ?   Thank you, Radu PS . I use Studio 5000 v24, combined with RSLogix 5000 Emulator.     SFC_trial.ACD
  15. Lets say I worked in a factory that made multiple models of parts. I need to run data tracing on the off shift due to certain models only running on 2nd and 3rd shift. I want one data trace to capture one group of bits at Model 1, Then reset the Data Points and run again for Model 2, Model 3 and so on. So the Bits that I am mapping with the trace need to change.  I can change the trigger easy enough with my program. I see in the manual the CPU has a "separate memory area" for trace settings. Can this area be accessed from the Program so I can set my bit addresses to monitor to a word or E_?   See attached pic for clarification of what I aim to change through the program.   
  16. Modbus Addressing in Weintek HMI

    Modbus addressing in Weintek HMI to poll data from Temperature sensor through RS485. In my system i have connected Temperature sensor to I/O Scanner has output in terms of RS-485 which directly connected to COM3 Port pin. No. 6 (as Negative) & 9 (as Positive) of HMI (Model No: MT8071iE) and HMI connected to PC via ETHERNET. I want to read temp on HMI screen via MODBUS protocol. So, can you please provide me instruction about addressing of MODBUS register in Easy-Builder Software so can read data of corresponding register. Because when i do compile i got an error like " Device no Response". I hope i will get reply from your side as Fast as possible to overcome this problem. Thank you.
  17. Cimplicity Auto Report Generation

    Dear All, I am having a problem with my cimplicity Auto Report Generation, When I Click on Generate Report, it shows "0 values collected" does anyone knows what's possibly could gone wrong here ??
  18. CID and ICD file creation. Hi, I have a system that is using a PowerLogic G3200 to convert Allen Bradley MicroLogix 1100 Modbus to IEC 61850, but I am lost when it comes to creating an ICD / CID file. Does anyone have any experience in doing this? I have no help from Schneider technical support, they say the G3200 is not supported. Thanks in advance. Steve
  19. Mitsubishi GX Developer

    Hello all ... i am a new plc user.. i am using D500 for taking value as it is a latched register.  i am taking value for a flow meter. i have two questions. 1. how totalizer is calculated from flow rate as my flow rate is in m3/h. 2. the value of register is gone upto 32000 approximately... i want that this value to go on.. i mean how 32 bit register is declared in plc .. a
  20. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.
  21. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.
  22. We have Q06UDEHCPU PLC.   We require to attain 1k of file registers in standard Ram. Please find our settings attached - PLC Parameter.png; When we try to down the register file – we attain the following error; “Failed to access standard Ram” error message (attached - Downloading Error.png); The program is very small – and thus we have plenty of space as well.
  23. Mitsubishi GX Works Bugs??

    Hello I have been using GX Works 3 for a while now and I have discovered a couple of things, maybe bugs. I have not had any training for the software or hardware so maybe I did something wrong. 1 Labels. If you sort a global label table into any order other than the unsorted order that appears by default you are unable to create, delete or edit any labels. Our Mitsubishi representative discovered that if you click on the column header between 'Data Type' and 'Class' the order does not change but now editing is available. This, it turns out is a really bad idea. It seems the position the label was in when it was created is preserved, I think this is the unsorted order you get by default. If you sort the list and then delete a label it is possible that the label that should be in that position is also deleted. I have attached a small project to demonstrate this. Open the Global Labels notice the order they were created. Now change the sort order, click on the column header I described earlier to make them editable and then delete the label in position 1. For a while I thought this was the only problem but recently there has been a number of instances where I have created a label, given it a carefully selected address only to discover that it is being overwritten by another variable. I have not been able to work out exactly what is going on but I believe it is connected to the sort order of the labels. Also if you sort the order and change an address, have you changed the address of another label? The only solution I have found is to keep label tables very short so they are managable without having to sort the order, that is probably good practice anyway 1 Axis software limits. I have been using a number of axes in pairs, in incremental mode as caterpillar feeders, using FX5U-40SSC simple motion modules. I had a problem that the axis synchronised to follow would suddenly stop moving, the customer was having to power down the machine and start again. This problem persisted for months with Mitsubishi scratching their heads unable to fathom it out and ultimately stating that the problem must be in my code somewhere. It was suggested by the customer that it may be getting to a software limit, I showed the customer that the software limit was disabled in the setup and it was confirmed by Mitsubishi that it was not the problem. guess what, it is a problem. Once the actual position reached the limit of the double word memory it would stop moving. The solution is the take the servos out of synchronisation in order to set the position (datum) to zero every cycle. Unfortunately the drives do not always re-synch on the first attempt so you have to keep trying till it does, this now causes slight variations in cycle times but it works. Andy EDIT: I have since been informed that to disable the software limits they must be set to zero. This implies that the Enable/Disable setting is invalid and the limits are defaulted to their respective max values. Surely a default to zero would be more appropriate.     Label Test.gx3
  24. CP1L connected with scanner symbol DS-4308 reading 2D data matrix,  with RS-232 on board CP1W-CIF01 Hi all, need some help because I can't read the information. Let me explain, I have a PLC, " CP1L-L14DR-D " with a RS-232 option borad " CP1W-CIF01 " , a scanner Symbol DS-4308, and I'm trying to read a data matrix 2d barcode (I don't know if that matters). so I build a cable with the next configuration, (one side male and the other female) PORT CONFIG PIN OUT SCANNER CABLE RJ-50 TO RS-232 PINOUT Maybe I'm missing a connection? a bridge? power supply ? ground?   in the program, I only have this to check the communication,       When my reception flag complete (A392.06), my instruction RXD is going to execcute, reading in D1500 the data. if is any error in communication (A392.04) or overflow (A392.07), my port is going to restart (A526.00) (ignore w0.03) with the followign config: (9600, 7,2,E, RS-232C, End code: Received Bytes 3       and I'm reading only, data on D1500 and D1501, and the data makes no sense.   with the configuration of End Code: CR, LF,          can't make it work, I read nothing. and if I change the END CODE: Received bytes to 4,      don't work. and my flag A392.04 go to ON.   PLC HAS 4 PIN SWITCH, ALL ARE OFF The configuration on the scanner is setting to default and then config to RS-232 Standard.   So, what I'm missing?  bad connections? plc don't support? scanner config? program?      
  25. Hello All, What are the methods to get the monitoring data from A series PLC? I know its not supported any more, interface modules are not available...,    So the basically,   If I want to write customer software (may be embedded) what is the protocol I need to follow? I am connected to CPU unit by the way, there is no other modules except few digital and analog interfaces on PLC. Thank you in advance for your direction, direction in any way would help!