Search the Community

Showing results for tags 'cpm1a-ad041 configuration'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 37 results

  1. Hi all, I am working on a safety PLC conversion project, for which I need to identify the input word address configured on a PSS AI IP card. The manual from the official website shows the address configuration via a DOS tool. I do have PSS SW PG WIN 4.9, but the project file has been created with PSS WinPro 2.3. Within this software there is only the option to configure how the input channel behaves, not which input word is used (see attached screen grab). Anyone with a distant memory if the addresses can be set with PSS WinPro?  
  2. Hi, About SmartSlice: „Smart Analog I/O performs data pre-processing to help you reduce PLC programming. Scaling and alarms, and even totalising or rate-of-change calculations are handled inside the unit.” How to get to this honey in case of GRT1-ECT bus coupler and NJ101 EtherCAT communication? What means “Configuration Tool” in W18E-EN-02 “GRT1-series EtherCAT Communication Unit Operation Manual”?
  3. Hi everyone, I have a question for you all, Is possible to configure CJ2M-CPU11 with tags trough network configurator to connect Control Logix PLC using EthernetIP? I did a configuration with CJ2M-CPU31 and Control Logix PLC with no problem, but now I need to communicate CJ2M-CPU11 with Control Logix PLC using EthernetIP. Some of you did this configuration between this two PLC before? Regards!
  4. RJ71EIP91 Configuration mismatch

    I have several machines that use the RJ71EIP91 module. I have not had any issues until now. I do not have the original apa file. I upload the configuration and try to restore it from the configuration.apa file, it does not show everything that is connected to the card or programmed in the PLC. when I verify this it says that the configuration is a mismatch. I have several of these scattered throughout the factory and I don't have this problem anywhere else. Is there a solution to this problem?
  5. need help with programing a cp1w

    hi i am tryning to make a program that takes 4-20ma signals from a  pressure sensor and converting it to show ML on a hmi screan. im using a CP1L with a CP1W-Ad041. but i cant figurout how to set up the setings in cx programer correctly. any tips?
  6. Hi All, I just start to setup a rotary servo (rotary transmission load type) and the designer pass me the spec of gear ratio 1:100. In my motion scaling page, I set Transmission I:O as 1:100  and then scaling unit is just position unit with 1:1. However, when i jog my rotary servo, it does not reflect the actual position in degree, so I went to read through the manual but still cant quite get how should i configure my scaling so that I can see that when the motor is rotating, i can see it rotate how many degrees? I try to set scaling 360 degree to 1.0 load rev, and the position feedback seems like much more finer....
  7. CP1W AD041

    Hi.. I have a problem with my analog CP1W AD041, it's reading value always "0". Can someone help me to configure software setting? I use PLC CP1E-N60SDT-D Thank you        
  8. Is there a way to run a compact logix program, while ignoring the the I/O configuration?   I used to do this with other PLC's to help develop the HMI screens while connected to development PLC that does not have the full complement of cards that the end user PLC will have.  Just lets me test logic that supports the HMI while working at home.   I used to do this on other PLC's with just a CPU on my desk.   Possible?
  9. I have been attempting to connect to connect to a couple of PLC's that are in some of our slide gate conveyors (CTI). I do not have a lot of experience with PLCs. Took a class on it a few years back, but haven't had much hands on experience since. So last year we had a technician come in and add a rung to the program of the CPM2A that allowed the PCB to hold at the out sensor and for the incoming machine to not accept the board until the conveyor is fully extended. What I was tasked with was checking the program in the CPM2A and applying that additional rung to the CPM1A on the other line. Unfortunately I cannot connect to the 1A and when I attempt to connect to the 2A it tells me that I am trying to connect to a CQM1 instead, but that's not what the PLC physically shows it being.  I have the CS1W-CIF31 cable and the CPM1-CIF01 as well. I am using the correct port (COMM4). Port settings are 9600, 8, even, 2. In CX-Programmer, I am clicking New > Device type (CPM2A) > Network (toolbus).... When i connect to the 2A it tells me its a CQM1... SO when I change the settings to that one and compile the program it shows me a very weird program. Doesn't seem to have any real instructions. Maybe I don't understand the program?  When I try to connect to the CPM1A-30CDR-A-V1 I just get a failed to connect every time. I Open CX-Programmer, New, Device type (CPM1A), Change CPU settings to CPU30, toolbus, etc.... Failed to connect. I have been trying to figure this out for a few days now and haven't gotten very far. I have tried to connect with Omron and haven't gotten far from there. Any Help will be appreciated, I'm very noobish sorry lol
  10. Simatic pc to simple pc with profibus card

    Hi every one, One of my machine i have to fix , has simatic pc unit installed that causing too much trouble  and client want to replace it with simple pc with additional profibus card installed in PCI slot, is there any way to configure image of simatic pc in new simple pc
  11. Hi, I've got a very old version of Wonderware, version 9.5, which isn't going to be upgraded anytime soon. I would like to configure a button to perform 2 tasks under "Touch Pushbuttons", ideally "Action" and "Show Window". I am unable to enable both at the same time, so I've been trying to write a script that would perform both functions, but so far unsuccessfully. Is this something that can be done, or is there another way to get around this problem? I would like the button to toggle a bit and to open another window with more controls.   thanks
  12. CPM1A with Kepware

    Hi Anyone here tried connecting Omron CPM1A PLC with Kepware ? I browse through the Kepware brochure and didn't see CPM PLC in the supported devices list.   I saw this post in this forum stating to try using Host Link driver wit C200 PLC and it should work. Can someone help verify that ? Thanks ! 
  13. Pls any one help me to simulate my omron HMI program with CPM 2A PLC  Means help me to communicate cx designer with CPM 2A plc Or with NT- series  support tool
  14. ad041 analog expansion resolution

    hi everyone, ive recently started working at a company who uses omron PLC's im a bit more familiar with siemens i used in university.   one of my first tasks at work was to go through the current plc programs we have installed, ive noticed going through them that the previous engineer doesnt use the whole resolution of the analog input, i was wandering if this was some sort of practice im not familiar with or if they just have done it their own way. for example the ad041 expansion unit has a resolution of 1/6000, which would be  scale of 0-1770 in hex, however in the programs im looking through this top end hex value is always listed as 1700.   im assuming there some safety precaution or something that i don't know about, thanks for any answers in advance * the image is of the data points being put into the SCL function  
  15. Hello,  I want to compare pulsed coming from flow meter with a constant value. And make a bit to high level when my set pulses are equal to present value in counter. I am using 1734 Vhsc24 module for this. If any body have sample program kindly attach it. 
  16. Hello All,  Am a bit new to practical PLC applications. I was trying to configure a Phoenix Contact I/O module (1452916) on a MicroLogix 1100 PLC but it kept faulting out with the fault light RED. It would say "Major Error Halt S:1/13". The error description says I/O mismatch. The error code is 187h (see attachment). The Phoenix module has a cable with 19 pin positions for the 8 input. I connected the pin 17 and 18 to 24 volts and  0 volts respectively. Then because I was using input 5 I connected the pink wire to PLC input (I/1) 24volts and the White/Yellow wire to the PLC common.  On the I/O configuration on RSLogix 500, I used "Other" ( See attachment) but did not know the vendor details. Could anyone help me with the steps on how to communicate with the module? I have also attached the PLC program I was running. Thanks        
  17. Hello, I have been so many days trying to comunicate the multiway software trought a serial usb converter with the SCU31 device, using a omron function block to read a holding register, but I can't achieved it. Now Im receiving some frames on multiway, but there is always some errors. I was wondering if somebody in here that have worked previously with modbus and omron can be able to help me in how to configure everything corectly to be able to read the value from multiway, on the plc, and where is this value saved.  I'll upload some captures to show what I have done till now.    
  18. Q06UDEHCPU MELSECQ Upload

    Hello ,  I dont have experience with Mitsubishi PLC.  I want to do a modification on the ethernet configuration but i dont have the source code .  According the information that i read we can use GX IEC developer or GX developer but my question are :  Can i upload and download the program with GX developer?  Even if was previous developed with GX IEC Developer i will not do any change on the code only on ethernet configurations , add a MC communication. I have another concern about the profibus module. For the profibus is necessary another program right ? But if i don't want do any modification on the profibus is dont need it, right?  My experience on Siemens when is necessary do a modification on the hardware configuration. I should have all the hadware configuration " right"  it means if i have profibus i should have the right GSD to allow do modification on the configuration .  But on Mitsubish i can´t understand that well . Regards  Roberto Fonte  
  19. BECKHOFF CX-9020

    Hello PLC experts, I am master student currently writing thesis. For this, I have a initial task of making some changes to PLC program (Just started getting to know about PLCs- complete beginner). I have a BECKHOFF cx 9020 PLC connected to my notebook using ethernet. I am using TWINCAT 3.1 (VS) as IDE. Firstly, I cannot find my PLC IP address connected to my notebook . I added the route in the Twincat and it shows the PLC is connected. When, I am trying to run a program (activate boot project), I am unable to login to the PLC. It gives an error "login failed for application port 851". What I undertood from BECKHOFF scripts,  there is something wrong with the ADS ams net ID which I am trying to figure it out. I appreciate all the help. Thank you.
  20. CJ1W-AD041-V1 - Damaging Channels

    Good Afternoon, I Need you help to fix something that is driving me crazy, here is the story: I am using a CJ1W-AD041-V1 to sense a motor current thru a current transducer ( Ohio Semitronics Mod. CT8-006D )  the nominal current we are sensing is 800 mA ( 8V ) Module is set at 0 - 10  VDC  [ 100 mA = 1 V ]  Lately,  module's channels are being damaged, and I cannot find the root cause  I added a zener diode + resistor to limit the input voltage to 10 VDC ( at the module's terminals ) but did not help at all - it starts by reading half of the actual reading but, it deteriorates after more testing, until it is completely damaged ( not reading at all, either #0000 or #FFFF )     Thanks in advance for your replies  
  21. Hello all. I have been working with an SLC 5/04 system, which houses various Digital and Analog INs and OUTs, up to Slot 29. I am currently mainly working with Slot 25, an Analog Input: 1746-NI16I. This is a system which has already been set up and has been running for the best part of 8-10 years. This particular card has had some spare inputs, one of which I am trying to connect to. In the Advanced Configuration, only a few Channels are actually "Enabled", and each channel is pretty much slightly different from another in terms of Input Type, Filter Frequency and Data Format. I am trying to set up Input 14, which is Channel 15, to "Enable" it, 4-20mA Input Type, Filter Frequency of 6 Hz and Data Format of either Raw/Proportional or Engineering Units. Now, after I have made my choices, I click apply, and then OK. I am then confronted by a pop-up which states: "Configuration Rung and Data Integer Data File Number: 25 Integer Data Element: 100 Rung to be inserted: XIC S2:1/15 COP #N25:100 #O0:25.0 24 At Program File Number: 4 82" I have the options of OK or Cancel. If I click OK, I now have LAD 4, Rung 82 Highlighted. This First Scan Bit and COP function were already here, but does that mean I have now altered what is being written to "#O:25.0"? I now Download the Changes. However, after all this, I am not getting any Analog input reading coming in from the Live PLC. What is this COP function? What does it do? How do I properly set up this Analog Card?   Thanks for your time, -Jame
  22. Looking for a little help.  Replaced a 1746-NO8V analog card that hadn't been working for years and the new card is giving a Configuration Error (Module LED flashes twice, all 8 outputs are flashing 12 times).  I have 2 other of the same cards in the same rack that have been working for a very long time and still working that seem to be configured the same way.  Is there any way to know what is wrong with my configuration.  or maybe my new card is just bad???  I have not yet swapped one of my working cards with the new card, have considered but really think I'm missing something.
  23. I need solution for master & slave configuration between 2 PLC Twido TWDLCAE40DRF. My final project is about a system for filling drink on a cup and do the packaging. the component of the project is the filling system (dropping cup, filling water, pressing the seal) and the packing (packing into a box and sealing the box). This project is using 2 PLC Twido TWDLCAE40DRF. My problem is how to configure one of them as the master and the other as the slave. I've read the manual book but it's hard to understand the instruction. if anyone can give a simplify explaination to me please reply this post or you can reach me at mail: tatangprayoga11@gmail.com  
  24. Mitsubishi CC link

    Hello every one. can any one explane me maximum how many CC link card we can configure in one  QJ61BT11N module. and whwt is difference between CC link and Input/Output card
  25. Ge Fanuc LM 90 30 PCM Commnications

    Hi ALL, Am trying to configure a PCM 301 (LM 90 30 Communication Co Processor Module) What software do I use,is it TERMF or PCOP? And where can I buy this software Thanks