Search the Community

Showing results for tags 'control logix compact logix'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 153 results

  1. Hi All. i got a problem when accessing local reporting service website using microsoft web browser control at HMI. it showing only half of page. when i open the website from internet explorer at same server where i develope HMI, i got no issue. please your advice. thank you.
  2. FC1 Two hand anti tie down

    Version 1.0.0

    131 downloads

    Logic takes two inputs (I0.0, I0.1), debounces each (T0, T1), looks for actuation during a timed period (T2), and provides validation (M20.0). This logic is not designed, nor intended, to replace the use of any OSHA required two-hand safety control relay. It is provided for the sole purpose of it's educational value.
  3. FC1 Two hand anti tie down View File Logic takes two inputs (I0.0, I0.1), debounces each (T0, T1), looks for actuation during a timed period (T2), and provides validation (M20.0). This logic is not designed, nor intended, to replace the use of any OSHA required two-hand safety control relay. It is provided for the sole purpose of it's educational value. Submitter pop29684 Submitted 03/22/16 Category PLC Sample Code
  4. I need to learn about position control for 2 axis with a QD75MH2 module. I know how the basics about programming with the Q Series PLC but I've never done any positioning control. I'm having a really hard time understanding the program I have to modify and I don't know where to start. Is there any course you might recommend? Even if I have to pay for it. Thanks.
  5. PAROCK1 for HMI/SCADA View File Now a software solution is available for your Modbus (MB) needs in Rockwell/Allen-Bradley Control Logix or Compact Logix (Clgx) family processors, instead of a traditional 3rd party hardware like Prosoft MVI-56, Molex SST-SR4-CLX-RLL etc.  It is an Add-on instruction (AOI) for PLC/PAC firmware v16 or later, (other solutions are available for pre v16 systems).  For hardware interface, use PLC’s channel 0 (serial) or TCP/IP Interface module(s) to have as many MB TCP/IP devices or serial devices.  (Some limits apply based on system configurations, Comm. settings depending on HW used.) Connect any MB Client/Master or Server/Slave device(s) to your CLgx PLC, including flow computers, analyzers, VFDs, Power Monitors, Level gauges, Smart I/O, etc.  All the MB public/native function codes are supported.  32-Bit integers/floats as single entity are supported with byte and word level swapping. A separate utility automates the data mapping to your PLC logic.  Features -Serial Master (BASIC required Option); TCP; Slave; Redundancy; More than 5000 accumulative registers; MB CFC (Custom/Private Function Code) Support; Data mapping too – Between PAROCK1 & your PLC logic; Packaged with Rockwell; TCP/IP Interface Module; Volume Discounts; Annual Support Requirements -Rockwell/AB-CLgx processor with v16 or later.  Contact PCI for earlier versions. -If using CPU’s Chan0, you cannot use Chan0 for any other user mode activity. You can use it for non-user mode activities -TCP/IP Interface Modules from Rockwell/AB supported, are: -1756-EN2xx ControlLogix® Ethernet/IP communication modules, firmware revision 5.007 or later -1756-EWEB ControlLogix Ethernet/IP web server module, firmware revision 4.006 or later -1768-EWEB CompactLogix Ethernet/IP web server module, firmware revision 1.002 or later -1769-L30ER, 1769-L30ERM, 1769-L30ER-NSE, 1769-L33ER, 1769-L33ERM, and 1769-L36ERM CompactLogix controllers, firmware revision 20.011 or later -1769-L24ER-QB1B, 1769-L24ER-QBFC1B, 1769-L27ERM-QBFC1B CompactLogix controllers, firmware revision 20.011 or later -1769-L16ER, 1769-L18ER, 1769-L18ERM CompactLogix controllers, firmware revision 20.011 or later Other Related Services/Items -Custom PLC Add-on instructions building -PLC upgrades, troubleshooting, applications -PC Windows, iOS5, Linux, Mobile devices Comm. Drivers -Custom development, Technology Transfer Services  -Other Non-AB communication drivers for serial or TCP  -Full control system integration, training, architecture design This driver can be conviniently used with Visual Studio in development of complete large scale complex HMI/SCADA Systems. It can be used to perform advanced reporting MES, analytics, IoT, Big data type apps. One example is available to download here For More Info Overview of Parijat Drivers: Click here  Additional supporting Info about Parijat Drivers:Click here Complete Related Driver options: Click here     Submitter Scadadoctor Submitted 03/10/16 Category Other PLC Demo Software
  6. C200HW-MC402.pdf View File C200HW-MC402-E Motion Control Unit Operation Manual Produced June 2001 Submitter IO_Rack Submitted 03/09/16 Category Manuals
  7. C200HW-MC402.pdf

    Version 1.0.0

    23 downloads

    C200HW-MC402-E Motion Control Unit Operation Manual Produced June 2001
  8. Hey guys, first post!  Friends at Practical Machinist sent me over here b/c we were stumped.   I have a Mitsubishi 500M control CNC machine.  There is a section of the ladders that i don't understand, and Mitsubishi couldn't help, and the OEM is defunct.  I do not have a hardcopy of the ladder circuits. I have an output , [Y13], that i can't get to turn on because of an internal relay | M453 |       see pic 1 When i searched for relay M453, it seems as if it's in some sort of array function.  see pic 2 None of the relays from M448 thru M512 ever turn on.  I understand that all these are controlled thru this circuit, but i have no clue what is going on with the R registers, and how the heck these internal relays can be turned on. Can you guys help explain?   Thanks!
  9. Sequencer Input

    I have a program using the SQO instruction. However, I am looking to control my program with a sequencer input. I have never used the sequencer input before and I have 16 sensors to move cylinders using the sqo.
  10. Hello All, I have a guardlogix processor that I just safety locked with a known password. When I tried to unlock, that password didn't work. Upon reading a bit I realized that the lock and unlock passwords are separate. I never set the unlock password but blank doesn't work. Could it be a leftover due to program copy paste or is there a way to find/reset this unlock password.    
  11. Can anyone advise if there are data structure #s associated with each of the data types in Logix?  Example if it is a Bool, I believe Logix advises it is a 32 bit number.  But is there an "under the hood" data type reference number for each Logix data type?  I.E.  if it is a Bool, that is a RA data type #1, if it is a DINT, it is a RA data type #2, etc.  
  12. Dear colleagues and siemens experts, I''m new in siemens. As all I make my program for PLC, but I need help with PID autotunig (pretuning) I use : 1.CPU 1214C DC/DC/DC (6ES7214-1AG40-0XB0) 2. 6ES7214-1AG40-0XB02. 16IN/16 OUT DC/DC/DC (6ES7-223-1BL32-0XB0) 3. 2x 6ES7231-5PD32-0XB0 ( 4 channel RTD analog module - PT100) We use 7(seven) Pt100 points with 7(seven) heaters ... so I need 7 additional outputs..... [you can see example of wiring in attached pic 6es7231-5pd32-0xb0-modules.jpg] Maximum heating point is around 220 degrees. I make my configuration for PID_Compact : 1. Basic settings 1.1 Controller type : Temperature : °C Set mode to : Pretuning ( sometimes I make it Automatic mode) 1.2 Input_Per(analog) -----> Output_PWM 2.Process value setting: 2.1 Process value limits: Process value high limit : 220.0 °C 2.2 Process value limits: Default 3. Advance setting 3.1Process value monitor : Default 3.2 PWM limits Minimum ON time : 0.5 sec Minimum OFF time : 0.5 sec 3.3 Output value : Default 3.4 PID parameters : Default I start Commissioning with these steps : 1. Measurement : Sampling time 0.5 Start 2. Start PID_Compact 3.Tuning mode : Start When I try first time my setpoint was 90 degrees , second time I try with 120 degrees. After 4-5 hours it stop more in Progress bar it stop when I reach a little more then 50%, and I stop PID. For heaters it is not normal to process to be 4-5 hours, there have some wrong. Example with 120 degrees : During process I make : When Input_PER reach 120[1200] degrees I stop physical access to heaters. When Input_PER reach 100[1000] degrees I start physical access to heaters So 4-5 hours is soo long time for this type process. Time to reach 120 degrees from 100 degrees is around 2-3 min. Time to fall from 120 degrees to 100 degrees is around 4-5 min. Total time for one whole cycle around : 8min. Sometimes when I set setpoint to 140, 150 degrees it writes me that output set value is to high after I give Start Pretuning ? Even sometimes when try for 120 degrees .... As all I want to start PID pretuning (autotuning) with setpoint 140 - 150 degrees. Which are minimum requirement to start PID autotuning with PID_Compact ? Could you send me some very simple example and steps that I must make or only steps ? I attached files in dropbox with images and program example, because I can't attached nothing here. This form don't give me access to attached something. So link is here : Even program is there. Thanks in advance Best regards : Altan
  13. I forgot how to do this. If I put in let's say 1234569632<cr><lf> how do I store the carriage return line feed along with the number in my ST file??? 1234569632(chr$13)(chr$10) something like this, but can't remember. Thanks
  14. Hello! I'm working on a project. I cannot get online with the PLC. The compagnie who made the program does not exist anymore so they cannot help me. Does anyone knows how to unlock a locked controller ? Do you know a compagnie who can solve this kind of problem ? Otherwise my only option is to wipe the all thing and reprogram it .... which would be bad. Thanks !
  15. Hello, my question today deals with a particular way of coding in RS Logix 5000. I have two routines ( titled "Gauge" and "Alarm"). where rung 10 in Gauge is the exact same as rung 2 in Alarm. How can I make a change to rung 10 in Gauge and allow the program to automatically make that same change in rung 2 of Alarm? The only reason these two routines have the same rung at 10 and 2 respectively is to make trouble shooting easier whenever an issue arises. So instead of searching through the "Gauge' routine to find out where the fault is, I can easily look at the "Alarm" routine and find out what the problem is. I just want to be able to make changes to the Gauge routine and find someway to allow the program to automatically update the exact same rung in the Alarm Routine. Thanks.
  16. Good day, I´m helping with small project and currently i am stuck because of this problem. And I hope you can help me out. I´m using PowerFlex 525 connected with AB CompactLogix 1769-33ER PLC via EtherNet/IP. Connection is working, I can read and write values from/to 525. To configure both devices i´m using RSLogix 5000. 1) First problem occurs after I loaded configuration to 525 and it´s, that 525 keeps overwriting values of Accel and Decel Time 1. It happens when i directly change parameters in Module Properties (online) or after I upload configuration to device. It happens even if i set parameters directly to 525 with its HMI panel. - I kinda get around this problem when i use Accel/Decel Time 2 for Step logic, but if i send direct reference value motor still jump to it and that is not good, especially when changing direction of rotation. 2) Second problem is that I cant get Speed Sources and Start References right. Usually Is working only option 1 and others are not, or they are doing something else that they should. For better imagination this is what i want to do: I have 3-state switch (left = 1 ON(DigIn TrmBlk 02), 2 OFF; center = 1 OFF, 2 OFF; right = 1 OFF, 2 ON(DigIn TrmBlk 03)), In center position I want to control 525 with EtherNet (already working when: Start 1 AND Speed 1 = EtherNet/IP). In left position I want to control motor directly with Drive Pot and In left position a want to start Step Logic (which i have already set) - Funny thing, If I set Start 1 = Ethernet, Speed 1 = Step, Start 2,3 = DigIn, Speed 2,3 = Drive Pot then in all three position motor goes in Step logic.. Or when i get left and right position working then Ethernet is blocked.. and this kind of things.. I Attach print-screen of my current settings, if you need something more just, tell me. Thank you for your time, and I hope someone will be able to help me.
  17. Automation professionals, I would like to read the display values of a red lion DP700 in a control logix PLC. I was able to successfully integrate both devices through EtherNet / IP and I am geting the corresponding values in a DINT register in the PLC. But the problem is that the value in the PLC register is not in the same format as in the DP700 display. The display reads the length of a product in inches like 288.484 etc. Where as the value in the register is a 10 digit number like 1133526516. For sure, there is a definite correlation between these two values but I am not able to figure out the exact relationship as a function of a formula. I have given below 25 data pairs for your analysis. I tried to find out the scaling factor (slope and offset). The scaling that I found fit the first 10 records but did not fit the remaining 15 records Can you help me to find out the relationship between the ? # DP700 PLC register 1 288484 1133526516 2 288627 1133531202 3 288631 1133531333 4 288739 1133534872 5 288741 1133534937 6 288742 1133534970 7 288746 1133535101 8 288757 1133535461 9 288776 1133536084 10 288796 1133536739 11 241060 1131482972 12 241043 1131481858 13 241027 1131480809 14 241032 1131481137 15 241055 1131482644 16 241038 1131481530 17 241078 1131484152 18 241025 1131480678 19 241030 1131481006 20 241037 1131481465 21 241040 1131481661 22 241023 1131480547 23 241053 1131482513 24 241041 1131481727 25 241077 1131484086
  18. Sinamics G-120 Drive on Profinet

    Dear Friends, In my present project, I have a S7-1500 PLC & 3 Nos, Sinamics VFDs(PM-240s) with Profinet ports.(CU-240E -2PN) The drives and PLCs are on the same Profinet network. I wish to know the essentials of controlling the command and speed reference of these drives directly from the PLC on profinet. Reading the help in TIA portal got me nowhere its all about Telegrams and things that I haven't figured out yet Thanks for looking in; I shall greatly value all help and advice.
  19. B&R plc, motion control, CNC

    Hi all. I have a B&R PP420 panel, some I/O on the X2X and 4 Acopos servodrives /servomotors. Successfully created and tested 4 axes, they work OK, control via NCtest or X2X IN, or PP420 display. But creating CNC system is the problem... On NCtest, I have errors, and no move. Error 7742: ACP10_MC FB error or aborted Info: Axis Index [0] Info: ACP10_MC FB error number [29226] Info: Command aborted [0] Info: ACP10_MC FB number [1] = MC_BR_MoveCyclicPosition (cyc. pos.) On SDM, axis error: 32274 Network coupling: The broadcast channel was not configured Can someone help? Thanks.svinaga@yahoo.com Foto errors.pdf
  20. CJ1W-TC001 PID question

    What is Omron naming convention for PID settings? I need to adjust the upper MV limits for PID running on CJ1W-TC001 installed on CJ1M-CPU13. Looking at the CJ1W-TC001 Operation Manual I am not really sure which values would these be. I guess Omron naming nomenclature is a bit different than what I am used to. It seems that the Manipulated Value Monitor is just feedback, which value would I need to set or modify to adjust the upper MV limit?
  21. Dear Messrs., I need information to reverse engineer a GML diagram from the uploaded script. 1)Documentation for GML script language (iCODE ) Thanks,
  22. Currently we have a remote I/O module to connect with our PLC, yet it's not showing up whenever we try to connect it via inside RS logix 5000.
  23. Hello All, I want to read data from a Control Logix PLC, into a PLC5/60, using Ethernet and a MSG instruction in the PLC5. When verifying the MSG instruction in the PLC5, I get an error message. "Target Address in invalid". Once I figure out how to do this I need to replicate it in another PLC5. Scope is to read the status of 4 paint pumps controlled by the CLX. If any of the 4 stop, the PLC5 needs to know, because it is controlling the paint application equipment. Source data resides in a Control Logix 1756-L63. The tag is INT type, 4 elements long, and the name is PUMP_STS_B2. The IP address of the CLX is 4.2.6.230. There are 2 ENBT cards, one in slot 1, and the other in slot 3. 4.2.6.230 is slot 3. PLC2,5 / SLC Mapping has been created in the CLX. File=421 Name PUMP_STS_B1 and File=422 Name Pump_STS_B2. The file mappings represent a binary file created in each of the PLC5's B421:0~4 in Booth 1, and B422:0~4 in Booth 2. The PLC5/60 is Enhanced series E model using the Ethernet side card. The IP address of the PLC5 is 3.26.5.61. I also created MG file types in each of the PLC5/60. MG420:0~19 in each processor. This was necessary to use the MSG instruction in the PLC5. I have searched the forums for examples of how to do this with no solid results. I am trying to follow the best practices of reading the data into my PLC so anyone who follows can tell where it is coming from. While the IP addresses are not closely related they should be able to communicate. I say this because all of our PC's are on the 4.2.6.XXX network on a 255.255.252.0 sub net and we have no issue communicating with the 3.26.5.61 IP address. Any help and advice would be greatly appreciated. Regards, Mike Carter
  24. I'm having a bit of difficulty with the MSG function on a logix5000. I'm simply trying to get a REAL value ("BH5_Flow") out of another logix5000 and assign it to a tag in the PLC. I've created a MSG function and created a new tag "BH_5_Flow_MSG" for the message, and created "BH5_Flow_M" for the value that will come from the MSG function. When I click the "..." button to bring up the config, I put the following in: Message Type: CIP Data Table ReadSource Element: BH5_FLOWNumber Of Elements: 1Destination Element: BH5_FLOW_MIn the PATH tab, i then put the following in: Path: LocalENB, 2, [iP ADDRESS OF SOURCE MACHINE]When I test the edits, I then get the ERR bit activate with error 16#0004 when the message rung runs. Anyone got any ideas where Im going wrong? I've practically copied another MSG instruction from further up the ladder but it doesn't seem to work
  25. Hello guys, i would like to know if is possible keep always active the run command in a vf drive and for stopping the motor only send 0 reference. It´s possible??? because I want to program a ramp function in my plc for start and stop one motor. could someone tell me how to do this type of control please?.