Search the Community

Showing results for tags 'control logix compact logix'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 147 results

  1. Hello everyone,   I'm seeking recommendations for training programs or resources focused on building control panels. I have a basic understanding but want to enhance my skills in design, wiring, components, safety, and troubleshooting.   If you have attended any reputable hands-on training programs or know of online courses, I would greatly appreciate your suggestions. Any personal experiences or tips are also welcome.   Thank you for your assistance!   Best regards,
  2. Hi from Colorado, Panel Builders @ MRPLC~ I bought a custom 508A assembly from a UL shop (277/480v 3 phase). The prototype didn't work out very well so I'm revising the design for next time. Before I present my "red line" revisions to the fabricator, could someone advise if I'm OK to simplify part of the work in a particular way? I just need to make sure my simplification doesn't run afoul of the 508A standard. My clients requested that a ten watt 120vAC amber LED (distant from the 508A cabinet) should light up whenever the 3 phase bus is energized. The panel fabricator provided an SSR solid state relay to close whenever 277v shows up across the "input" terminals & they fused the 277v hot for the input so that's all good. The "output" terminal is "single pole normally open", rated for 10 amps. The power that I'm sending in from outside the cabinet is from a small UPS system where the inverter is rated for 250VA's--so it can't deliver more than two amps @ 120vAC.  It seems to me that I don't need the series fuse that the shop provided to protect the 10 amp rating on the SSR--since my input power is already current limited. It also seems that I don't need to bring the associated single phase neutral wire into the 508A cabinet at all--since the neutral is never switched & it's doing nothing inside the 3 ph. assembly. If I revise the drawings along these lines, I'll eliminate two terminal blocks, a cc fuse/fuse holder & some wire...and this part of the assembly will be simpler & more intuitive.  Basically, I want to treat the SSR like a switch leg for the light, running only a 120v hot wire to & from the SSR output terminals. I don't want to revise the drawings, however, unless I'm sure the fabricator won't have to change them back to comply with UL 508A. I don't own the UL "standard" document & I don't know the peculiarities...but I'm sure some of the forum members do.  Should I add signage to explain that the 120v hot must be current limited or OCPD protected before it enters the 3 phase cabinet? Thanks in advance for any coaching or suggestions.      
  3. control panel for sale

    Hi all, Hope everyone is doing well. I'm currently in the process of starting a home based control panel shop. I have about 8 years of control panel building experience and about 2-3 years of being shop team lead/design engineering. I have been planning this for years and now I have my shop full of necessary tools and material to build small/medium sized panels. I have gone through all the training and examination(which was not easy) to be able to produce UL508A approved panels. My goal is to produce a steady work load with great quality. Now I just need an opportunity with customers which I find to be the hard part. I have been contacting local industries but haven't had any luck. If anyone out there is seeking control panels built at a good competitive rate please advice.
  4. We are seeking a Control Panel builder in the SE Michigan area. We can supply the drawings, components, enclosure, etc. Typical panels include PLC, HMI, VFDs, and standard components. Please contact us if interested. We can send more details as needed. We typically need 20-30 panels in a year.
  5. Problem: I am getting a control sync fault on 2 recently installed kinetix 5500 but only when my programing PC is connected to the machine network.  Install and setup all went great over a 5 day period.  Then all of a sudden I started to get this fault. Sometimes 100 times in an hour.  As soon as I go offline, and unplug my PC the problem goes away.  I have also tried another PC connected to the Machine network and still get the same result.  Sometimes machine can run for hours with my PC connected with no problem.  I do not have to be online with controller for fault to occur. Setup: I have the 2 K5500's ethernet ports daisy chained together, and then connected via shielded CAT 6 cable directly to port 2 of the Compact Logix Controller Coarse Update is set to 3.5ms and utilization's are at 33% and below.(I have tried the default 2ms with same results) Ethernet modules are configured with FW rev 7.013. Machine network is isolated.(not connected to plant network or internet) Equipment: Compact logix L33ERM Running version 30.01. There are a total of four servos in this system all running over ethernet.  2 Kinetix 350's(not affected), and 2 kinetix 5500's. I have tried: separate ethernet cables for each drive ran through a switch different ethernet cables resetting coarse update speed connecting a different PC for programming   I am just not sure where else to go with this.  Thanks in advance for any help.  
  6. Hi All, I'm new to using PLC, and my background is majorly programming. I am learning how to control a PLC over the internet using HTTP or TCP/IP. I have a Mitsubishi PLC Melsec FX-5U 32MR and my requirement is, I want to send create a setup where the PLC works more like a Client on the network and reads values from the server (which is a computer). The outputs on the PLC are controlled by the values on the database in server.  So, lets assume I have a value like this on the server "1,0,0,1,0,1", it should translate like below: Y0 = 1 Y1 = 0 Y2 = 0 Y3 = 1 Y4 = 0 Y5 = 1 Is there any guidance where I can read through and learn how to do this. I would prefer doing it by ST programming and not Ladder.
  7. Logic issue, or problem with Control Expert 14.1?   Pop-up box, followed by Control Expert crash.  PLC seems to be running fine. "Control Expert Fatal Error" "The thread tried to divide an integer value by an integer divisor of zero" Anybody seen this before?  Corrupt file?  Reboot?  Uninstall/reinstall?
  8.  I've been debating whether to stay at my current employer who uses Emerson PAC software, vs going back to a similar company that uses Rockwell (compact/control logix) mainly because A-B is used by most companies around here. I work as a technical temp, usually 12 month contract jobs. Learning the Emerson PAC (aka Prophecy) seems to be a waste of time, since I am not aware of any companies that use it, other than my current employer. My placement company is pushing back, but I know I am correct. I do not have hard numbers, but I've been around the industry for 20+ yers, and have only seen 1 company use Emerson.   Does any one agree or disagree, or have some circumstantial evidence of the actual market share of A-B vs Emerson. I am mainly working in the Auto industry, in Michigan. Just looking at this site, there are 3200 postings for GE and Emerson combined, vs 58,000 postings for A-B. 
  9. Been seeing a high failure rate on these PLC's on 2 of our processes. The control power is feed through a APC UPS to a 24VDC power supply to power the unit. Getting a hard fault where the OK LED comes on red and stays red. It never sequences through all the LED on power up. Tried the hard boot by holding in the reset button and applying power. Has anyone on else seen a high failure rate on this model PLC? TIA..
  10. Morning all, first off, when it comes to controls I’m pretty green so please bear with me.  I have a bunch of old Modicon TSX Compact plc controllers. Some of them have randomly stopped controlling the outputs, I replaced the output card (module? I don’t know what to call it), but no change. I don’t know if the program is messed up, or the main board or something else. I want to read the plc but don’t have and can’t find the software to do so. Any suggestions is greatly appreciated. 
  11. Motion Control

    Hi Everyone.   I have been tasked with changing out an older Flex Drive servo drive to a more modern Micro Flex drive in a machine that has an Omron CQM1H-CPU51 PLC.  I'm having a few issues but hope that i can gain some clarity around at least one of the hurdles Im facing from here. Biggest issue for me at this moment is My work hasn't yet purchased a programming lead for this PLC (or even the bits required to make one myself) but i have a feeling the control for the Servo is done via motion control in the PLC.  Question here is, if changing from one servo drive to another type, will the motion control code need to be updated to work with the new servo drive?  I have very limited experience with motion control itself at this stage so I'm a bit lost when it comes to these sort of details. Regards Kiwi_man82
  12. Can someone please suggest a Control Panel Builder that is located in Germany?   I work for a company in Australia and due to Covid 19, we are struggling to meet an onsite date for a project in Germany.   This project uses Siemens PLC gear, Danfoss drives, and mostly Schneider electrical gear. The enclosures are custom and stainless steal.    I have electrical schematics and enclosure drawings for quoting.
  13. Hi, I need help finding the length of a string.  I am using an In-sight 9000 series camera with a compact logix 5380 and communicating over ethernet. Unfortunately, the string length is not provided in the AOP, and the barcode length will constantly change. I told to use the FSC instruction, but I cannot get it to work. Thanks 
  14. I have a old  PannelView 550 that have lost the screen so i would like to hear if there is any possibilety to get it  working using a PannelView 800 7" and logix 5555. I only have serial rs 232 in the plc.   Thank you in advance. Peter Jensen
  15. PV 550_TO_800

    Version 1.0.0

    0 downloads

    86_upload_11_1_22.PVA S86_0645_90_000.ACD
  16. PV 550_TO_800 View File 86_upload_11_1_22.PVA S86_0645_90_000.ACD Submitter Peter Jensen Submitted 02/21/22 Category PLC Sample Code
  17. PWTech is a rapidly growing company specializing in wastewater treatment equipment. We are currently hiring for a Controls Engineer. This is a full time position with some travel required. Requirements: 3-5 years experience Proficient with Allen Bradley MicroLogix, CompactLogix PLCs, PanelView HMIs Proficient with ladder logic programming Proficient with basic electrical theory, control systems and electronics Familiarity with NEC, with special focus and understanding of articles 409, 430 A high level of proficiency in written/spoken English Familiarity with Unitronics PLC/HMI is desired but not required Duties will include: Producing control panel submittal and as-built layout drawings, components lists, and line diagrams Selection and integration of sensors, motors, control systems and other mechanical and electrical equipment. Coordination with internal and external project engineers to resolve electrical and control questions and issues Programming, modifying and troubleshooting Allen Bradley and Unitronics PLCs and HMIs Providing assistance and remote support to field personnel Maintaining inventory of long lead items for warranty and project purposes. Location: Rosedale, MD (outside Baltimore) Technologies: 50% Allen Bradley 50% Unitronics. Salary: 95k-105 depending on experience. Higher if you have >10 yrs experience. Contact: Kreal@pwtech.us
  18. Hi guys I have an control logix plc im looking for a module which is the same as 1769-ascii module. I know that module is for compact logix. Unfortunately i didnt find a good one for that purpose.  Anybody can help with that ? Thanks ahead.         
  19. VHSC5/C

    Hey all. Wondering if anyone has an example program they'd be willing to share? Specifically I'm using the 1734-VHSC5/C with a 1769-L18ER-BB1B PLC. All of Rockwell's wonderful information only refers to SLC-500 platform. I'm not trying to do anything terribly fancy, just have a quadrature encoder attached to Channels A & B, then using an output to turn on a valve at 8.0" and turn off at 10.0" Any help would be appreciated.
  20. ello I have a powerflex 400 of 25HP for a 60amp 25HP motor, the motor have a belt that move the clarifier of milk. It is a process that requires strength to move.So I try with the motor without the clarifier the vdf works well with a constant amp of 12 to the max of 50hz that is set up with a ramp of 600 sec.Then I try with the belt that move the clarifier... The vdf start the ramp with a wird amp behavior like 10 sec 100 amp and then 13 amp for 10 sec.When it gets to 50hz (the max) it starts the same behavior 13 amp when it reach the max RPM and when it decrease a little bit it gets 100 amp to get to the max RPM again.In this vdf powerflex 400 I didn't see the % of torque options that the last one Fuji had.Someone told me that powerflex 400 is not for power processed, they are focus in pumps and blowers more alike, and that I need a vdf vectorial like a powerflex 725.What do you think...PD: as the 100 amp is like 10 sec the protections dont show up. PD: I made a try with water and hot water, in that point with the max hz  (and 6800rpm) when the hot water start to flow the amp gets constant in 75 amp, but the motor dosnt get to the 6800 rpm again it just keep trying in 6700rpm and it mantains the 75amp triggering the motor protection for overload.
  21. How long  could be INT array. For example can I build INT[365] or DINT[365]? When I use more than [32] my controller fails. Thanks. 
  22. Dear Experts In our plant, we have only one Allen Bradley PLC (Compact Logix L24ER) in one of our testing machines. We need to check online reason for error :LH Motor Negative overtravel Please let us know if it is possible to get communicating software RS Logix 5000 for trial Regards  
  23. Hi everyone, To explain the problem a little bit: I have 2 systems that are equal, they have 1 PLC, 1 Inverter and 1 Servo Axis (Image01). The devices are connected via EtherCat. The thing here is tht in these systems the PLC and Servo Axis is the same but the inverter is different. My goal is to have the same project on both systems and depending on the inverter detected use the correct program. What worked: If I add the 2 Inverters and 2 Servo Axis on the project on different nodes (Image02), I can detect which is present using the variable _EC_EntrySlavTb[n]. My issue is that if I want to make more replicas of the systems using different inverters I will eventually hit the Axis Number limit for the PLC while in reality I am only using on Servo Axis at a time. What I wanted: I would like to be able to control 1 Servo Axis with 2 different inverters (only one active per PLC) (Image03). What I tried: The axis parameters can be set using a variable of the type _sAXIS_PARAM, however it seems that the option to change the axis basic settings is not available (Manual: NJ/NX-series Motion Control Instructions Reference Manual (W508) page 5-58) (Image04). The axis basic settings is where the definition of the output device plus control words are set (Image05). Is there a work around to solve this issue? I would really like to avoid having to manually change the output device for the Servo Axis every time I make an update on all the systems.   Best Regards, BR  
  24. FX3U to FX3U via wifi

    Good day fellow PLC ninjas! I have a question/ concern which I would love your opinions on. We have 3 FX3U PLC’s+ENET cards. Two of the 3 PLC’s move around in an EMS trolley. The other is a ‘base station’ with a GOT2000 connected via Ethernet. Base PLC IP = 192.168.1.11 HMI IP = 192.168.1.31 Carrier 1 IP = 192.168.1.61 Carrier 2 IP = 192.168.1.62 I have programmed the base PLC to use Active communication; we are using fixed buffer communication to send and receive data to/ from the Carriers. The carriers are set up as Fullpassive ‘slaves’. This part works well and the update time changes (using a counter in the base station) from 1s to 100ms (because it enters a different work station).  My issue is the following: using a network sniffer (WireShark), I pick up plenty of re-transmits and sequence number errors coming from the base PLC’s ENET card. This is troublesome and causes delays when the update time is required to be fast (100ms). I am sending and receiving 10 words of data. The wifi seems stable, and there is minimal noise in the area. The power has been turned down and the antennas used are suited well for the application. The antennas are at a similar height to minimize possible loss of signal. I have LOS (line-of-sight) to the carriers at all times; to at least one of the antennas (I am using 802.11n). Has anyone picked up issues or found settings which can be used for comms over wifi? I can easily do this using a S7-1200 Siemens PLC and have done so using 12x S7-1200 clients and 2 AP’s with 1 base PLC. I have also successfully done this using 8xFX3U client with a System Q base PLC. My suspicion is that the delay in reading and writing to/ from the BFM in the ENET card is causing this. I am not sure that if I change to a FX5U will help. The communication cards on the Mitsubishi PLC’s seem very limited. Does anyone have any technical details on the access times between the CPU and communications cards’ BFM? Help is as always, appreciated.
  25. simple motion cam curve

    Good afternoon, I have a problem in an application for a rotary knife, I'm using a MR-JE-B servo to make this movement, while my material is powered by an inverter connected to a modbus rs485 network, with a 5v encoder connected directly in motion. I'm having some problems and I think it's my cam curve. I have a very high refeneration, and the system doesn't obey the size of the length I want the cut. It always cuts the same size, regardless of the configuration I use, it always cuts to 245mm. Put some photos, how are my settings. Grateful in advance, if anyone can help me. Dover_roll_1-Motion-configuração_jog_manual.gx3