Search the Community

Showing results for tags 'compactlogix encoder'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 94 results

  1. I have a machine with NJ501-1400 controller. I have some NX-ECS212 SSI encoder input cards. I use Encoder axis with that SSI encoders. I need to change the encoder axis value with the real value of the machine. I tried to use "MC_HomeWithParameter" instruction but I cannot do it because must'nt be used with encoder axis. If I put it at a virtual encoder axis I cannot change actual axis position. I tried to use "MC_SetPosition" instruction but it isnt retentive area and when I lost power I lost reference value too. How can I do it? Thanks! Josep Torres.
  2. CompactLogix to 1769 I/O Cable?

    Looking for some help that i cant seem to find online - I have a  CompactLogix 5370 L1 Controller part number 1769-L16ER-BB1B and would like to connect a 1769-IF4 and a 1769-OF2 Analog expansion modules. Rockwell sales tell me they are compatible The Compactlogix looks to be a "slide in" and the expansion modules are Plug Type. Is there a cable or base rack I can use? Thanks in advance.
  3. Create TCP/UDP Socket

    I'm trying to send an int over TCP using a MSG Socket,  Compactlogix ==> Arduino Ethernet Shield I have set up TCP communication between two Arduino Uno's using Ethernet shield. I've set up the one as a server, the other as a client. server IP: 192.168.1.21 port 23. If the client is connected it reads incoming data as a byte or an array of bytes. The data between the two has been verified to work. I'm now trying to transition the communications between a compact logix-L32E. I'm looking to send a byte (or int being as there's no byte data type) from the Compactlogix to the Arduino using TCP. To my understanding I need to use a socket create, open, read/write, close. The manual to do this is vague as a step by step procedure. Does anyone have an example code for socket programming? I can open rs500, rs5000, and studio 5000 programs. If I can open a file to use as a reference I can translate it on my own. Any help/advice would be greatly appreciated. 
  4. How to connect + Program wire encoder

    Hi all, I am not a PLC expert but can find my way within the program and would like to develop much more. For work (We sell industrial bandsaws) we have purchased a Posital Fraba wire encoder, and we would like to hook it up to our Mitsubishi FX3G PLCs to measure at what height the saw bow of the bandsaw is at that moment. Unfortunately I have little experience with connecting these things, as other encoders used in our machines are pre-installed by our factory. Below is described what functions the wires have. What I thought was the following: Pin 1 goes to an input of the PLC Pin 2 goes to + (or 24V) Pin 3 doesn't go to "Ground" as they describe, but instead to - (or 0V), which is technically ground Pin 4 and 5 we don't use, correct me if I am wrong. The saw bow goes up and down only, and I thought we don't need to use these wires.   I connected it like this, connected wire 1 to X0 on PLC and just to test I made the program read:   M8000 ------------------------------ C235 k99999   But the value stays 0, whether I pull the wire or not. So something is wrong, but what, I really can't figure out. Hope someone can help!  
  5. How do you test PLC logic?

    We have been working with PLCs for long time. We used to develop PLC logic, partly test it on an emulator and test the rest on the partly energised equipment. From time to time working with computer software development (C# and JavaScript) I was always looking for something similar to unit testing in the PLC world. As I couldn't find anything at that time I've started developing own automated testing tool. Now we use this tool, which basically simulates PLC inputs in defined actions and checks expected behaviour of internal tags or/and PLC outputs. If it behaved the way we expected, it's PASS, otherwise it's FAIL. We break complex logic into small parts and create unit tests for it. By creating more of these unit tests we can test PLC logic of any complexity. The software called PLC Logic Prover and it's free at https://www.controlx.io Recently, I've been told that there is no point to develop anything new if there are already great tools on the market. Honestly, I didn't do proper research earlier, so I'm here asking the experts. What do you use to test PLC logic? What automated testing tools do you use? Is it using IO simulation or it can test logic by other means? Your replies are appreciated. Thanks, Alex
  6. Hello Everyone, I am struggling with interfacing Incremental encoder with FX5U PLC, Does anyone have parameter setting and sample program for same. i am unable to fetch counts...   Encoder: 500ppr, 24V line drive, A-B phase,  PFA datasheet
  7. Hi:         I am planning to use NX with Encoder Card  couple with Omron Rotary Encoder for measuring product length. ( GX-EC0211 /EC0241) or may be (NX-EC0112, I read there is proble with this card , here https://forums.mrplc.com/index.php?/topic/34896-problem-pulse-reading-with-fast-counter-card-in-nx2/ ), but whatever it is I need to know is there any specific Instruction in Sysmac Studio that is tailored for Fast Counter or Encoder (something Like PRV in CX Programmer or special function in CJ-CT021 where start/stop counter and changeable preset counter are available).  The Length measurement is straight forward and is only a small part of the overall program.  Basically is Start ---> measure to length----> Cut --->Repeat again.  I read through the Instruction Reference Manual and I am unable to find one.   Anyone have any idea or any sample program (Sysmac Studio only ) that I can refer to ?    Thanks     
  8. Signal Tower Error Code(s)

    Hi, got a mental block lol.  Got a machine we are modifying, currently got most of the code in place. Working on a fault routine now. This machine doesn't have an HMI or wide array of PL. Nothing major just a simple vision system check. Currently have 6 faults that will stop the cycle running. I'm wanting to have the beacon light (Red light) blink for the cause of the fault. For example: Scenario 1- Fault stop for bottle check NG:  (two) .5 sec blinks -  2 sec red light off -  (two) .5 sec blinks ..... repeat  Scenario 2- Fault stop for bottle check NG and reject sensor blocked:  (two) .5 sec blinks -2 sec red light off - (three) .5 sec blinks - 2 sec red light off....... repeat I have the code a few different ways but it looks "dirty". Any suggestions? Thanks in advance  
  9. Is there a way to monitor the Temperature of a Servo Motor on Allen Bradley Servo motors... MPL? PLC: CompactLogix 1769-L30ERM Drive: Kinetix 6500   Motors: MPL-B310P-MJ72AA, and  MPL-B560F-MJ72AA I would like to be able to monitor the temperature, and flash a warning screen on the HMI if the Motor gets too hot, or perhaps shut down the operation before the Motor overload trips. The drive and PLC are connected through Ethernet IP What I don’t know is if that Motor heatsink temperature information is available to the PLC.
  10. ACD file to PDF

    Hello, I have an .ACD file but do not have any software to read the controller tags. Can anyone please help me convert the file into a pdf? I can see from Notepad that is was made using RSLogix 5000 V21.   Thanks! G Pump_17_11_09.ACD
  11. This is a bizarre one... CompactLogix, 1769-IF8 with 1492-AIFM8-F-5 wiring system. My client has reported several instances where one of his flow rate displays is frozen at its maximum value.  Each time, I have gone to the site, found that the value in the analog input tag is at full scale, and measured more than 20mA at the input - as much as 28mA!  I measure it using a clamp-on meter and I measure it at the input module (1769-IF8) and the external, pre-wired terminal block (1492-AIFM8-F-5).  I cycle power to the PLC.  No change.  I cycle power on the transmitting device.  No change.  I disconnect and reconnect the input (signal wire at the module or the terminal block) and everything goes back to normal.  This has happened on multiple channels on multiple input modules and with two different types of transmitters. I didn't install this system, but it seems to have been done properly and it had been running fine for many years.  These problems just started happening out of the blue. Has anyone out there had any similar experience?  This is a new one for me after more than 25 years in the business.
  12. converting rs232 data

    Hello, I am trying to receive data from a scale via rs232. my setup; compact logix l18er with a 1734-rs232ascii point IO module to receive the data. I am receiving data from the scale, but I have very little understanding of ascii, so I do not know how to convert the data I am receiving to something use-able. any help on how to convert the data to something I can use or where to even start would be much appreciated. using a scientech ZSA 210 scale https://scientech-inc.com/media/downloadable/files/links/1/2/12222-d_rev-f_instruction_manual.pdf
  13. Hello guys, I am running an application for packaging measurement using a sick DFS60B incremental encoder (programmable from 1 to 10000 PPR). In more detail, it passes packaging on a conveyor belt and we have created an inspection station and an expulsion station (defective packaging), so we use the encoder to check at specific points of the packaging for defects (we use special sensors to check defects). ) (there are four in total). However, the problem we are having is the following: When reading the encoder in the PLC, the same means that performs "jumps" and does not enter the windows (GRT and LES) created on the ladder, ie, as if it were not continuous. . I understand that because the VHSC24 card works at 1 MHz in counter mode, this type of problem should not occur according to our application is not even 100 KHz. For example, our case: Using 1000 PPR and the motor speed (coupling output) is 3600 RPM (in practice it is around 1750 RPM) the frequency is calculated as follows: F = (PPR X RPM) / 60. : F = (1000x3600) / 60 = 60 KHz, ie 60 KHz is much less than 1 MHz, I think this kind of problem does not occur. Application Info: . Studio 5000 V31 . PLC Model: Rockwell 1769 - L19ER-BB1B CompactLogix 5370 . Encoder Card: 1734-VHSC24 / C . Incremental Encoder: Sick, DFS60 up to 10,000 PPR and HTL Electrical Interface. Using a 200 mm circumference / perimeter wheel. . Motor Nameplate Data: 1670 RPM, 0.37 kW / 0.5 HP, 60 Hz . Inverter: Weg CFW500, Output Frequency 62 Hz. Card Settings we use RPI: 2 ms Type: Counter, but we already use it as Encoder X1 Store Count Mode: Disabled Filter: No Filter, but we use 50 KHz and 5 Khz filters in our tests. Counter Attenuator: 1 Wiring Diagram VHSC24 We turn on encoder A at input 0 and encoder Aret at input 1 In logic (Structured Text) Using the PMUL instruction to convert encoder (Pulse) data to mm scale. (Ladder) The window comparisons part (GRT and Les) and other part of the process. We emphasize that we performed the tests also only with the reading and comparison part of the data, excluding the other parts, precisely to verify the issue of Scan, but the problem persisted. If anyone here in the forum has some information that can help us, I would appreciate it.
  14. hi, We want to integrate Allen Bradley L16-ER with Zebra Printer GT800 and Zebra Scanner Li4278 with RS232 extension Card. We have hardware : 1.ABPLC L16-ER 2.1734-232ASC 3.Zebra Printer GT800 4.Zebra Scanner Li4278 5.Communication Cables  We are not able to receive and transmit data from and to Printer and Scanner
  15. Trying connect baumer EAL 580... Ethhercat absolute encoder with Beckhoff C6015. Ethercat connection is From PLC to EL6695 module(This module is connected to KUKA robot for mater to master communication) and from Out port of EL6695 to In port of Baumer Encoder. It is not getting scanned nor manually appended. But when i connect it directly to PLC it works fine(gets scanned). Any solution?
  16. Hi all, I am taking a Kubler draw wire encoder back to a 1734-VHSC24 and having a little bit of an issue with the rollover.  With the draw wire untouched the output value seems to be fluctuating over time and appears to be drifting backwards to the rollover value making our distance measurements completely useless.  Does anyone have any insight as to why that might be?
  17. This may be more of a Zebra question than a PLC question but I will post it here. I am using Zebra's Network Connect to enable communication between a CompactLogix L13ER and a ZT410. My issue is that the QR Code omits the 5 elements of the array in Field 1 of the CompactLogix. I expect the first two elements in the array to be ignored per the manual but the first 5 has me puzzled. All the characters in the text shows up fine. I have attached what I am seeing. If you have a QR Code reader, you can scan the QR Code.
  18. Remote Access to CompactLogix PLC

    Can the PlC be accessed remotely. If I hook the CompactLogix L32E up to the internet WAN, would it be possible for an engineer to access and make changes to the program remotely?? Or does it have to be done onsite through the LAN.
  19. Hi, I can’t find an answer to the following and I was advised to ask it here.I’m programming an Omron CJ2M with an MD212 high speed I/O card. I usually do all my programming in Structured text, simply because I like it a lot over ladder or sft.Now, if I want to read the hight speed counter (incremental encoder), I have to make a ladder section and use the PRV instruction to store the present value in a chosen location.The manual says the current PV is stored in A271, but I can’t get a readout there. Apparently the only way to read it is through this instruction.Does anyone know if there is an equivalent to the PRV instruction for Structured text? or another way perhaps? Again, when I check the actual memory adress, there’s no value there withouth the use of the PRV instr.
  20. s7 214

    Dear All ,  I need to connect two encoder to S7 214 PLC  any one have information about 1-If it applicable to connect encoder  2-How adjust it on S/W and H/W to work good  thanks in advance
  21. Autotuning Kinetix 350

    Hell PLC World! I have been trying for several weeks in my spare time at work to tune an Allen Bradley Servo Motor.  Below is the list of hardware I am currently using: - CompactLogix Motion Controller (1780-L33ERM) - Kinetix 350 Driver (2097-V34PR5-LM) - MPL Series Rotary Servo Motor (MPL-B310P-MJ74AA) I have been using RSLogix5000 for testing and I plan to use it to develop a simple conveyor type program later.  I have tried a list of things which will be below, but to no avail, I cannot simply jog the motor for any period of time without triggering a position, velocity or bus voltage error.  I have tried changing the motor, driver and feedback cable to no avail.  Here is the process I have used: 1) Add the hardware to RSLogix5000 (PLC, Driver and Motor) 2) Configure the motor 3) Run the hookup test.  This works flawlessly.  The motor will slowly turn independently on the feedback test for as many revolutions as I input.  This is what makes me think I am doing something wrong in the tuning process. 4) Run autotune process with the velocity, acceleration and jerk set well below the limits of the hardware.   5) Attempt manually control motion 6) Recieve error I have tried changing the input from trapezoidal to S-Curve, changed velocity and position limits, manually tuned velocity gains in a myriad of configurations.  I have swapped legs on the 3 phase input (which made matters worse). I suppose it is possible that multiple pieces of hardware are faulty because this equipment was previously used, but I still cannot wrap my head around why the hookup test would work so flawlessly, yet I cannot just get the servo to rotate at an equivalently low speed. If anyone recognizes my mistake, I would be eternally grateful.  I am an intern studying control systems in graduate school and as popular as AB is, I would sure like to get some experience with it.  Thanks in advance!  
  22. CompactLogix E/IP to Kuka KRC 4

    Hello everyone,   I need to communicate a CompactLogix to a Kuka KRC 4 by Ethernet/IP but I do not know to generate the EDS file..... any clue please ?
  23. Cp1h-y - encoder issues.

    My issue and goal. - Trying to get an encoder (Automation Direct TRD-N30-RZVWD) connected to a cp1h-y to read wheel position(coupling) and have a pulse trigger at certain positions is this possible? I currently have the encoder wired up to highspeed counter 1 and am using PRV(881) port #0010 control data #0 with an P_On always on flag.  wanting to see  values change but nothing is being changed in the watch window. I'm reading the programming in section  3-20-2 HIGH-SPEED COUNTER PV READ: PRV(881), but I'm struggling.  any help is much appreciated.    
  24. M7 486 SIEMENS cpu

    Dear all ,  I have PLC M7 486 and connected encoder on EXM card 478 on the same rack  I need to know encoder address on PLC  programmer was written in C language  
  25. Hi guys. I have a new SRM50-HAV0-K01 sick encoder for my ELAU servo motor (model: ELAU sm 070-60-010-P0-45-M1-B0), and need to program it according to an old one (which seemingly is broken) via hiperface. device: PGT-11-S LAN software: SOPAS 2018.3 build 4.1.1.324 (Vm version 1.8.0_73) I tried to find any certain way for programming of sick encoders on the net using the mentioned device and software, but cant. all is only about datasheet or how to use teh software without an specific instruction. I am not even sure of that the old one is broken, except that in the analysis mode of the SOPAS (entering via hiperface) I can see the the  sin-cosin graph out of its limitation line. The thing is I have bought a special tool which has not any specific instruction and SICK group does not reply any exact instruction for my issue. Here is my questions:   How can I program the new encoder just according the old one?   And how can I assure that the new one programmed just as the old one?    and what is the definite sign of a broken encoder?   anyone experienced?