Search the Community

Showing results for tags 'communication cimplicity with control logix ab'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 261 results

  1. Error Indicator on FX3U-ENET-ADP

    Hi all, I have finished installing ethernet adapter module FX3U-ENET-ADP on the FX3U-48M PLC. From the ethernet module, i connected it to a wireless router and then i am planning of connecting to the ethernet module using GXWorks 2 on my laptop through wireless router. On the ethernet module, the error indicator LED is on (red). From the FX3U-ENET-ADP, it means that there might be setting or hardware errors.  I am asking if i have missed some steps on the installation process and if any of you have experience with similar problems. Thanks in advance for the answers.
  2. Hi all,  I want to ask some questions regarding Ethernet Communication with FX3U PLC series. I have 2 PLCs of FX3U series (FX3U-48M and FX3U-64M) and I want to monitor its data (input and output) using ethernet communication in real time. My questions are: 1. Does FX3U PLC have ethernet port so I can connect it directly to my Laptop/PC? 2. If no, do I need to use FX3U-ENET-ADP and can it be used for 2 PLC or only 1? 3. What software do I need to use to configure the communication between PLC and FX3U-ENET-ADP? 4. Does this configuration change the existing PLC program? 5. Can i transmit the data wireless-ly using some kind of ethernet to wifi adapter and what additional hardware do i need for that?  
  3. I am now part of a startup company based on energy optimisation of HVAC in buildings. I am assigned to have research on which SCADA system to select for HVAC energy optimisation. The model is in such a way that, we need to create a SCADA / HMI for the client's building on top of existing Building Management System (BMS) to achieve energy saving.  I am still an intern and I am requested to research on various SCADA options available in the market. I have few doubts regarding: 1. How can I select one SCADA / HMI over the other?  2.GE Cimplicity and Niagara 4 are two option which I am interested in. What is the major difference between both? (Price and functionality) 3. Is Tridium Niagara 4 a SCADA software? ( I read about it but I didn't understand as I am new to this field). Is it same like tia portal which is a software that is used to program plc and create user interface??
  4. Create TCP/UDP Socket

    I'm trying to send an int over TCP using a MSG Socket,  Compactlogix ==> Arduino Ethernet Shield I have set up TCP communication between two Arduino Uno's using Ethernet shield. I've set up the one as a server, the other as a client. server IP: 192.168.1.21 port 23. If the client is connected it reads incoming data as a byte or an array of bytes. The data between the two has been verified to work. I'm now trying to transition the communications between a compact logix-L32E. I'm looking to send a byte (or int being as there's no byte data type) from the Compactlogix to the Arduino using TCP. To my understanding I need to use a socket create, open, read/write, close. The manual to do this is vague as a step by step procedure. Does anyone have an example code for socket programming? I can open rs500, rs5000, and studio 5000 programs. If I can open a file to use as a reference I can translate it on my own. Any help/advice would be greatly appreciated. 
  5. Check serial connection to Omron PLC

    Hello, I am building an application in CitectSCADA and I want to communicate with an Omron Sysmac CS1G. The connection between the plc and the Citect computer is through an ethernet to serial adapter (the computer doesn't have com ports on board). I'm having some difficulty establishing the communication and I want to make sure that I can actually reach the plc. Is there a way to check that the computer can reach the plc over the serial connection without using CX programmer? Maybe using Hyper Terminal, Putty or something similar. Thank you, Liron
  6. I'm having trouble with some Powerflex 525 drives. Right now what I need to do is run them manually from the keypad to test conveyor belts.  Is there a way to do this and if so how?   Thanks in advance.
  7. I have a purchased Machine that came with a Siemens LOGO 8.FSR PLC (Smart Relay). Generally we use Allen Bradley or Mitsubishi. Anyway, we need to communicate data between the LOGO and an Allen Bradley Compact Logix.  I do not desire to add an additional network to the AB but as best i can tell the LOGO is exclusively Modbus TCP/IP. Has anyone come across a similar situation?  I look online and did find an  Anybus module that claims to be able to link them together.  Looking for anyone who has faced this challenge and succeeded, or failed.   Thanks
  8. Hello Everyone. We have Schneider TM241 PLC Along with Citect SCADA System at 100MWp Solar Power Plant to monitor and control various equipments like Inverters, Switch-Yard, MFMs, Weather Monitoring Systems etc... Government Authority here asked every solar plant to control the generation as per the instructions by Load Dispatch Center, for that we need to implement logic to control Generation as per requirement. For that we are controlling generation from inverters by giving them generation setpoints calculated by PLC using PID function.   But we are facing one problem while using PID. (FB_PID of Toolbox Library)   Suppose we need to generate only 60MW out of 100MW. So we set PID setpoint to 60MW and according to that we get PID output and according to that PID output value we provide generation setpoint to every inverters.   This system works very fine until the clouds comes into the picture.   Now suppose Setpoint of PID is 60MW and PV is also near about 60MW, and suddenly large cloud comes over plant and block solar radiation.   In this case generation comes down to 10MWp(or any value below 60MW), So output of PID will Increase and keep increasing and settle at the Maximum value. but without solar radiation generation value stays very down then Setpoint.   Now suddenly Cloud moves and again solar radiation increase, but the PID output is maximum at that time so, Suddenly Generation goes from 10MW to near about maximum capacity (100MW) instead of 60MW, and then it will slowly comes down to 60MW.   We need to rectify this generation shoot up when cloud moves. Anyone have idea how can we solve this problem or anyone have programmed PID in this kind of situation.   Is there any function block available to do this correctly like function block of PID with two Reference or something like that...   We are using TM241 which is CoDeSys based PLC.
  9. Hello everyone, I have a Kinetix 6000 CIP drive (unwind) and I need to control its speed by a PID controller. I have everything working except the MCD instruction doesn't pick up on the PID output value change. It changes the JOG speed, which I use to control the unwind, if I set the speed manually, which is slow. The PID changes the speed almost continuously. Any suggestions are welcome. This is how I'm attempting to control the speed: A1_r_JogSpeed = PID output value   Thank you    
  10. InTouch Comms

    Hi Everyone, I've just installed InTouch V10 and am trying to develop communication with Emulate5000, for educational purposes. I looked over the internet and found some videos on how to develop communications by setting up the topic name and node name in DA Server manager, but the issue I'm facing is that my SMC only shows logViewer and nothing else (snapshot attached). Am I missing some vital component or dirver? Or is there some problem with my installation? Help would be much appreciated.   P.S: Window Maker and Viewer are working fine. Thanks, Sabih
  11. hello expert i want ask some help So i tried to communicate my Omron PLC (cj2m cpu31) with SCADA from Schneider (power logic) on my omron side the comunnication on PLC already take to communication to NB so i add communication module CJ1W-SCU41-v1 I want asking how to open the communication if i want the scada become a master and my plc become slave i got this from omron website is that program compete for my case? i need configuration for scu41 module also to communicate or if you have suggestion i really open i just need to open port RS232c from scu41 so scada can read the data from my plc  tahnkyou for your help MRTU_CPU_Slave.zip
  12. Siprotec Relay 7sj62

    I have 24 Siemens Siprotec relay(7sj62) which i want to communicate with Scadapack 330E (Schneider) on 103 Protocol. but every time I try to communicate it shows Slave device is failed to communicate. trying to communicating via serial (RS-485). What should i do..?? or do i need to communicate it with Siemens PLC..?? If so which PLC should use..??
  13. PC to PLC Kommunikation

    Hello, i want to connect my PC to the PLC(RSLogix5561)  over TCP/IP. In rslinx the Ethernet driver are configured. My PLC IP Adresse is 192.168.1.100 and my PC Adresse is 192.168.1.105. From my PC i can successfully ping the PLC IP Adresse, but from the PLC i can't see my PC. And it does'nt schow in RSlinx. Is there anything i am missing?
  14. Hello there, I am new to OMRON so need some help to communicate two PLC over FINS.   Here are the description of the system... (IO Table image is attached)   PLC1-  CJ2M-CPU33 IP- 10.113.218.34 SUBNET-255.254.0.0 UNIT NO - 00 (set the dial available on the CPU in HEX) NODE - 22 (set the 2 dials available on the CPU in HEX) PLC2-  CJ2M-CPU33 IP- 10.113.218.35 SUBNET-255.254.0.0 UNIT NO - 01 (set the dial available on the CPU in HEX) NODE - 23 (set the 2 dials available on the CPU in HEX)     Now, what i have to do is to transfer the D100 to D110 from PLC1 to PLC2's D200 to D210 and Transfer the D100 to D110 from PLC2 to PLC1's D200 to 210.   I have tried RECV and ECHRD blocks but didn't succeed yet.   Two CPU are connected over ethernet via a industrial switch.   Can you help me to achieve data transmission please...
  15. HMI and PLC Communication problem

    hi there. .. i am new to plc programming.. Right now i am having problem related to communication between hmi and plc.. i have HMI WEintek 6070ip and plc mitsubishi FX2n.. i have written a program in gx developer . and communicate it with EASY Builder for HMI. so for now plc is communicating with my program written for hmi on pc. but when i downlaod to hmi and connect plc cable to hmi then hmi shows no plc communication. i am having a problem for communication between hmi and plc. any help will be a life saver. thanks in advance
  16. Hi everyone! I got this machine with a CP1H PLC and NS8-TV00B-V2 as PT. I was told that they were working fine, but suddenly, It appeared a communication issue: black screen and "connecting..." at right bottom. I dont know if It is a configuration problem or some hardware damage.  These are the configuration in the PT and the PLC. The communication is through RS232 Serial.  I tried to communicate another PT screen with the same communication settings and IT WORKED!. ' I've been thinking that, perhaps, the serial port A is damaged, I have tried to set port b, but I havent could. How can I configurate PORT B??   THANKS...  
  17. Hey all - I am working on a car wash system design that will utilize the Nayax payment system. Has anyone utilized them? How do I incorporate the device with PLC to automate the system. After payment is approved how can I send out that signal from them, all via ethernet on a managed switch w/ wifi for exterior comms for the Nayax.
  18. Constant Web Tension Control

    So I'm having trouble writing a FBD within my current program for a slitting line. I need to keep a constant tension on my web as it is being recoiled onto our recoiler. I wrote a simple program using a sensor to read the growing rate of the coil to get a radius and I have feedback on my torque on the recoiler motor. The simplest math for this application without getting into anything too fancy should be Tension(lbs)= Torque(ftlbs)/coil radius. only problem is when its less than a foot then my calculation is thrown off and it actually shows tension goes up until it reaches the one foot mark then it seems to scale correctly. Do I need to scale something else? Any help on this would be appreciated.
  19. Hi All, Hope you all doing well in this pandemic life.  I would need your expertise with an issue I have been struggling with for past few days and thought to reach out here. I am working on a migration project with GE PLC and Citect SCADA 7.10. The GE PLC is migrated to ControlLogix L74 Rev24.10 while Citect SCADA is retained. For testing I only have L71 and L82 and could not managed to organise L74. When the code the loaded in L71 and connected to Citect, I cannot see tags in Graphic page but I see the subscription.txt in Debug folder shows all tags good . The same code when loaded in L82, the Citect works instantly.  Does anyone know this behaviour of PLC and SCADA? Regards, DeeEngr    
  20. Axis Attribute Error

    Hello All, First time working with PLC. Get the hang of it from stuff I researched. Having an issue with an axis setup for a servo motor.  When I try to do an auto tune it gives me an error that axis is not configured.  Source: Config Fault    Condition: MotorDeviceCode- INvalid attribute      ACtion: Immediate Stop Fault Entry: Type 8, code 9 subcode: 1314 stopaction: 4 Statechange: 3   I was wondering what am I doing wrong? Any leads or source information I can use to solve this. 
  21. Hello Dear Colegues. I am using historian 7.0SP6 (enterprise license). I have installed OPCAE collector to collect alarm and events data from a project in cimplicity in order to have an historical data of it. Also I have checked the Historian OPCAE interface box in the cimplicity project´s properties. The problem is that when I try to see the tags from OPCAE collector on historian administrator I have the following error "No Tags Matched The Criteria You Have Entered. Please Try again or Cancel your Search". Also, I am not able to see the "last 10 alarms in the collector´s configuration tab. What could causing this problem?
  22. Signal Tower Error Code(s)

    Hi, got a mental block lol.  Got a machine we are modifying, currently got most of the code in place. Working on a fault routine now. This machine doesn't have an HMI or wide array of PL. Nothing major just a simple vision system check. Currently have 6 faults that will stop the cycle running. I'm wanting to have the beacon light (Red light) blink for the cause of the fault. For example: Scenario 1- Fault stop for bottle check NG:  (two) .5 sec blinks -  2 sec red light off -  (two) .5 sec blinks ..... repeat  Scenario 2- Fault stop for bottle check NG and reject sensor blocked:  (two) .5 sec blinks -2 sec red light off - (three) .5 sec blinks - 2 sec red light off....... repeat I have the code a few different ways but it looks "dirty". Any suggestions? Thanks in advance  
  23. Can someone please suggest a Control Panel Builder that is located in Germany?   I work for a company in Australia and due to Covid 19, we are struggling to meet an onsite date for a project in Germany.   This project uses Siemens PLC gear, Danfoss drives, and mostly Schneider electrical gear. The enclosures are custom and stainless steal.    I have electrical schematics and enclosure drawings for quoting.
  24. Mitsubishi FX5-4LC

    Hello Guys,                      can anyone help me programming of FX5-4LC temperature control module with FX-5U80MT PLC. I want to Read present temperature value of each channel and want to set Temperature Set value from PLC.
  25. Fatek PLC Communication Problem

    hy all. i am having an error while communicating with fatek plc. when i communicate it gives an error. " Com port open fail, plz check if this port is used by other programme when we online the PLC (Fatek/ WinProLadder). kindly Guide me   as it looks like port is already used by another program . and i dont know how to kill that program ..