Search the Community

Showing results for tags 'clk21 controller link'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 93 results

  1. Hello. What is the best option using TCP/UDP communication to use CP1L-EM40 as SLAVE / IO Expansion? For MASTER I’m using CJ2M-CPU31. Since now I’ve used FINS _CPU010_SendData and _CPU011_ReceiveData function blocks. The problem is, that I’m communicating with 6 slave IO units and to read/write all 6 units it takes up to 1 – 2 seconds. I’ve tried Ethernet/IP protocol but CP1L units doesn’t support this protocol. Is there some kind of different TCP/UDP protocol which is faster than FINS?  In older days you could use PC Link but this protocol is for RS232 / RS485 comm. I know I could use CP1W-EIP61 but I don't have this adapter and I can't afford to buy one Thanks. 
  2. I am trying to create an Alarm handler for an NA5 HMI that can tell the end-user the 1SAN Drive AL Status code and an Annunciation according to the manual: I621. I already am using a similar method to use MFaultLvl.Codes in a Case statement that creates a message found in motion controller manuals. Ie. 16#6449: Fault_Axis0 := '1S Axis Immediate Stop Input'; I want to use the AL Status to create messages based on the Hex Code generated by the Alarm ie 16#20: DriveAlarm_Axis1 := '1S Overload Error'; 20hex being the AL Status from the Drive. However I  cannot find how to access AL Status from the Troubleshooter.   Thanks
  3. Hi everyone, I have a question for you all, Is possible to configure CJ2M-CPU11 with tags trough network configurator to connect Control Logix PLC using EthernetIP? I did a configuration with CJ2M-CPU31 and Control Logix PLC with no problem, but now I need to communicate CJ2M-CPU11 with Control Logix PLC using EthernetIP. Some of you did this configuration between this two PLC before? Regards!
  4. I am trying to setup a CC Link between two machines. I have done this before without issue, but for some reason this is not going well.. I added a second CC link card to CPU2 and set it as ST 24 for the CPU1 network.  CPU 1 : Master.   cc0.jpg.   The original machine was setup using TO/From for each station, so i couldn't add this new link through the GUI.  CPU 2: Local cc1.jpg  When i try to use the GUI to setup this side the buffer stops working. but if i activate any TO/From instruction here i get a system fault with a 2110 SP. Unit Error CPU2 buffer cc2.jpg. But when i block the TO/From you can see the buffer is working at that exact same location specified.    2110 error says I am addressing the wrong card but the buffer proves that I am not. 
  5. Hey guys,  I'm trying to build a therapy tank for burn victims that requires a few automated processes of which I need help! Essentially this device will function a lot like a temperature controlled "hottub" with an circulation pump but on a much smaller scale (like 10 gallons). I would also like to be able to observe and control the device remotely outside of the users direct control for programming therapy temperatures. The goal with most patients is to start them at a temperature just under body temp (around 94) degrees and the get them down to treatments in mid 60's over time. The machine will used a liquefied burn gel that has a consistency like thin vegetable oil.  Here's what I need in a controller: ON_OFF functionality for a liquid chiller.  Contact relay for reed switch to disconnect power to device when lid is open. (this is a safety feature - when the treatment tank lid is opened I would like for a relay to disconnect the chiller's power through LV to ensure there is no chance of electrical shock.  "Delay On" relay (The chiller is and on_off refrigerant based device that will require a "delay on" relay to allow head pressure to dissipate before restarting) (See below) ON_OFF relay with programmable timer functionality for a liquid circulation pump. (to be set at intervals throughout the day) Temperature controller for K-type thermocouple - this will be used to monitor, maintain, and cool liquid. PID or Arduino? (Will need the ability to establish limits on backend) The ability to display temperature in either F or C Functionality: Ideally each unit would have a controller similar to an on_off temp controller or PID so that the home user could manipulate controls within a limit on the device locally. The device would then automatically maintain temperature based on set point and would have timed on_off sequences throughout the day for the liquid pump which were programmed into the device logic. This functionality in addition to the safety cut off features for use are all I need this device to do. Safety feature - being that this device could be in the middle of a chilling cycle when a patient would want to use it, I would like for the device to have the ability to instantaneously cut power to the HV 110V 16A Pump and Chiller without damaging those devices upon restarting... For instance if someone were to open the lid to feel the water and close the lid again quickly, the on_delay timer set to around 5min would prevent the compressor from restarting until the 5 minutes passed, thus keeping the short cycling from damaging the refrigerant system.   Remote monitoring and commands I would like to have the ability to push settings to these devices all across the city/state in peoples homes. The controller would need the ability to connect to wifi and transmit information as well as receive commands. This feature would be for those who would be put on a therapy program where we would control and push temp settings to their device remotely. Mobiel User Interface The BIG goal would be to tie all of this together and be able to control a device via iPhone or android. User downloads the app - The app has the ability to: turn on off off the device  adjust temperature (again within limits) turn on a timer 15 minute filter cycle with the press of a button Select/program a filter schedule with up to 8 time slots Circulation filter replacement reminders (messaging function) Therapy reminder.  Opt in for therapy pre programming pushes - me pushing temp settings to their device. Thats the novel for now!! Looking for someone interested in building this, or anyone willing to guide me through the process. This is just an idea and my 9-5 is a physical therapist, but I would love to bring this vision to life!   Sorry if this is fragmented or ignorant, but I just need help getting started or pointed in the right direction! 
  6. CC-Link IE Protocols

    Hello, There seem to be a lot of different CC-Link IE protocols: CC-Link IE Field Basic CC-Link IE Field CC-Link IE Field Motion CC-Link IE Field Safety CC-Link IE Control CC-Link IE TSN This causes me some confusion. Are there as many variations of Ethernet/IP and PROFINET? Can you point me to a good comparison of the different CC-Link IE protocols? My understanding is that: CC-Link IE Field Basic: 100 Mb/s Non-deterministic? Good for non-time-critical communications (e.g., setting a drive speed) Implemented in software Traffic can co-exist with other TCP/IP traffic Max 64 stations Addressed by IP address Star topology I believe the other protocols are all 1 Gb/s, are deterministic, are addressed by station number, are implemented in hardware and each needs its own isolated network. CC-Link IE Control is used for communications between PLCs and robots. CC-Link IE Field is used for remote I/O and CC-Link IE TSN is used for even faster remote I/O communications. Please let me know if any of this is inaccurate. Thanks,
  7. Siemens Moore Mycro 352

    Hi, I was wondering if anyone knows where I can get the configuration software or the manual for Siemens Moore 352 and 353 digital loop controllers? I would be willing to purchase the software if anyone has a copy. Thank you. 
  8. Hello, I currently have a PLC in a machine that is a CP1H. A newly developed machine uses a CP2E PLC. The newly developed machine is supposed to communicate with the CP1H where the CP2E is a slave. I am not able to find much documentation on this specific set-up. I was wondering how to set this up. As the shared words of each PLC are on different adresses. I can't really find any documentation or any examples on how to do this. Can somebody help me with where to start with this?   kind regards, Ralf
  9. controller is not coming online with rslogix 5000, but i can ping the ip from the pc. getting the error message says "controller failed to come online - error 701-8004250B" appreciate ur help.
  10. Hello friends I have worked with other series of omron plc but this is the first time I am working with cqm1h cpu51 series. In a factory, 4 of these PLCs exchange data with each other with a clk21 card. After a problem with one of the CPUs and replacement, I was never able to download the datalink settings. I did all the steps in the manuals step by step but I did not succeed. In cx-net software, after selecting online, I selected the data link menu, but as you can see in the attached image, the setup button is never activated. Thanks for guiding me
  11. NE1A-SCUP02-EIP

    Does anyone have experience with the NE1A-SCUP02-EIP safety PLC? We had a machine shutdown yesterday with a L9n4 error on the NE1A unit. The manual says this is a tag data link error. Does this cause the safety PLC itself to shutdown? I always thought the EIP portion of the safety PLC was only used for status reporting to the PLC. The safety portion is strictly on DeviceNet and is independent of the EIP network.  The CJ2 PLC's error log tells me it had problems communicating with the safety PLC, the VFD, and NX I/O's which were all in the same panel going through an Ethernet switch. 
  12. Hi All, I am a new user to this Forum and definitely a newbie PLC user, so I'm not sure if this is a simple mistake. I am currently trying to correct the logic (of a sensor) on a PLC program to get a manufacturing machine back up and running. This is an issue that I have fixed via PLC several times previously, but for some reason I am having issues fixing it this time. The issue that I am having is that when I try to dig into the Logic of the PLC program (Programming > POUs > Programs > Logic > ...), nothing shows up where there is typically a PLC command ladder. I get the error "No instruction in rung" next to all of the PLC program modules. I am connecting to a Omron NX1P2 CPU via laptop & Ethernet cord. To give you background on my troubleshooting process, I have verified that the I am connected to the PLC controller, by using the Windows Run program to ping the IP address of the controller. After verifying connection, I attempted to connect to the controller using SYSMAC studio. At this step, a troubleshooting window appeared with the issue "Minor fault" "Tag Data Link Connection Timeout". When I look at the Controller Status at the bottom right corner of SYSMAC, it says that I am online and connected to the correct IP address (green circle). Under that, ERR/ALM has a red circle next to RUN Mode. Ignoring the troubleshooting window, I can click Synchronization and "Transfer from Controller". A dialog box pops up and reads "...Controller does not have the POU program source...". Pressing yes to ignore this, the transfer completes. This is where I encounter the issue of having nothing show up within the path of Programming > POUs > Programs > Logic > ... . I have a feeling that this is a connectivity or settings issue, but I am not sure. I have checked my ethernet splitter (D-Link DES-105) and everything seems to be connected and working. If anyone has some insight into this issue I would greatly appreciate any help. Thank you in advance! Best cszikszai    
  13. can i cc link  Fx3U-64CCL  with FX2-32CCL without any problem
  14. Remote Omron and Yaskawa control

    Information : On the websites - https://abrysshost.web.app (and https://abrysshost .firebaseapp.com ) detailed information about the construction of remote diagnostics and control (Iot) systems for control systems of objects based on OMRON and Yaskawa controllers. The information is presented in Russian and English.
  15. Hey Guys,  So i am working with Omron software to integrate it with the HMI screen.  Whenever I receive a user alarm, I have an acknowledge button on the screen, but when I click on it,  the alarm does not go away from the screen,  it is acknowledged though.    Can anyone please guide me to what changes I have to make in the system to make the alarm notification go away, or is this any sort of a bug in the Omron software ??   Please help guys !!!
  16. Input cards, DI8x24VDC BA, 6ES7 131-6BF01-0AA0, NEW in box ,quantity 10 IO-Link CD-Master 4SI SIRIUS, 3RK1 005-0LB00-0AA0, NEW in box, quantity 4 IO-Link Master 4SI IO-Link, 6ES7 138-4GA50-0AB0, NEW in box, quantity 3 IO-Link Communication Module, CM 4xIO-Link, 6ES7 137-6BD00-0AB0, NEW in box, quantity 1 CM AS-Master ST, 3RK7 137-6SA00-0BC1, New in box, quantity 1   Located in USA.  Make offer, shipping included.   Pictures available on request, send email address in a PM.
  17. I am new to PLC programing, I want to connect FX5U and MR-JE-_C via CC-link. When I connect FX5U and MR-JE-_C directly everything works, but when I connect them in HUB (I need to use HUB because later I want to connect GOT2000) I am getting error 86.1(network communication error) on amplifier. Previously I set up IPs shown on pictures below, now sometimes works, sometime doesn't work and sometimes works for 30 seconds and I get same error. Did I miss something? I don't know what to try else.  
  18. Omron NJ501 - IFM IO-Link - Wenglor U1KT001

    Hi, I am looking at reading an ultrasonic sensor value through IO-Link, using a Omron NJ501-1320 PLC connected through EtherCat to a IFM AL1332 master with a Wenglor U1KT001 Ultrasonic sensor. I have managed to read the 2 outputs of the sensor using this: Output_1 := TestABit(USINT_TO_BYTE(TxPDO_input_byte_1_6000_02),USINT#0); Output_2 := TestABit(USINT_TO_BYTE(TxPDO_input_byte_1_6000_02),USINT#1); But cannot read the ultrasonic sensor distance value, this is what page 2 in the manual says: Measured Value in 1/10 mm 2…15 14 Bit 300…4500 Octet 1 Subindex 3 (LSB) 2 1 Bit Offset 7 6 5 4 3 2 1 0 I tried a couple of conversions but couldn`t get the distance reading. Any ideas? Help appreciated.
  19. Hello,  Sorry I'm newbie with omron plc programming. I'm wondering how can i simulate plc program on sysmac studio with Hmi on Nb designer without hardware. because I want testing my program and my plc and hmi connection before buying hardware. Thanks in advance !
  20. Hello everyone! I've installed GX works 3 according to the instructions in "https://plc4me.com/gx-works3-v1-308q-mitsubishi-full-real-100/". I don't get any errors, I can run the PLC and simulate completely OK. In the communication test, when the configuration is missing some components in the module list: Input, output, I / O module,... (https://ibb.co/ZVMcmQn) I hope you can answer for me?
  21. Hello everyone, As the title suggests I am trying to display on a GOT1000 the real time frequency that the inverter is running at. I have attached my CC-Link settings and the associated programming as well. I tried using the example program from Mitsubishi but I got lost. From my understanding I should be seeing the output frequency in W3C4 however, I am not receiving any data. Any help would be appreciated. 
  22. HMI on CC LINK IE FIELD

    Hello all, kinda lazy question, but I'll rather ask, before I'll went to deep into HMI scripting. Because of a design of CC link, there are RWr and RWw Is there any simpler solution for displaying value stored in PLC, while also letting HMI operator change the value and save it to PLC, than scriting in HMI? hope it makes sense to you thank you in advance
  23. The CC-Link system on a machine has been intermittently dropping out.  Normally the Link Scan Time runs at a solid 87ms.  When the system "drops out", the link scan time will increase.  Sometimes double, triple, or go up 10x. It happens when the machine is running or when it sits idle. There are 33 stations on the network.  The same stations do not always fault but sometimes all of the stations will fault at once (as seen in the attachment pictures.) We have changed the main QJ61BT11N, the processor, the Q62N power supply, the main backplane (base unit), all cards on the main backplane.  Is it possible for one station or one of the cables to create a network wide problem?  Any ideas thrown at us would be appreciated. 
  24. CC-Link Protocol with a CJ2

    I have an IAI servo that was sent to us with CC-link protocol. I have never in my life used cc-link and can find very little on the topic on integrating with an Omron CJ CPU. I am curious as to whether this has been done, or is even possible given the protocols Omron works with. And if so, what did you have to do to get the PLC to communicate via CC-link. Thanks in advance for the responses!
  25. Hello Engineers, I  am Will from Levetop semiconductor. Our main product is LCD/TFT graphic controller. Support 8/16-bits MCU parallel interfaces, and SPI, I2C serial interfaces Built-in Ggeometric Drawing Engine: provide Point Drawing, Line Drawing, Curve Drawing, Ellipse, Triangle, Rectangle, Rounded Rectangle Drawing Built-in 2D Graphics Processing Unit: provide Magic Rotation, Reflect, PIP (Picture in Picture), Hybrid Graphics and Transparent Display Built-in 128Mbit Display Memory Support 16/18bits RGB type TFT Panel from 320*240  QVGA to 1280*1024 SXGA Built-in Standard ISO/IEC 8859 Fonts Built-in Two 16-bits PWM Timer Support SPI and I2C Master Interface Three Power Saving Modes: Standby,Suspend and Sleep mode Package: 128pin LQFP We have STM32/ST51C demo code open for developers, function libarary and Arduino Library available, too. Our product P/N as follow: LT7681   640*480   8/16bits/SPI/I2C LT7683+  1024*600    8/16bits/SPI/I2C LT7686   1280*1024  8/16bits/SPI/I2C LT7680A  640*480   SPI/I2C LT7680B  800*600   SPI/I2C LT7680+  1280*1024  SPI/I2C any questions, feel free to contact us   www.levetop.tw/en