Search the Community
Showing results for tags 'change speed control during operation'.
Found 148 results
-
Hi everyone, I have a question for you all, Is possible to configure CJ2M-CPU11 with tags trough network configurator to connect Control Logix PLC using EthernetIP? I did a configuration with CJ2M-CPU31 and Control Logix PLC with no problem, but now I need to communicate CJ2M-CPU11 with Control Logix PLC using EthernetIP. Some of you did this configuration between this two PLC before? Regards!
-
Training Recommendations for Control Panel Building
LuisGonzalez posted a topic in Control Panel Building
Hello everyone, I'm seeking recommendations for training programs or resources focused on building control panels. I have a basic understanding but want to enhance my skills in design, wiring, components, safety, and troubleshooting. If you have attended any reputable hands-on training programs or know of online courses, I would greatly appreciate your suggestions. Any personal experiences or tips are also welcome. Thank you for your assistance! Best regards, -
508A panel needs to switch a 120v hot from outside the cabinet
abrahamsolar posted a topic in Control Panel Building
Hi from Colorado, Panel Builders @ MRPLC~ I bought a custom 508A assembly from a UL shop (277/480v 3 phase). The prototype didn't work out very well so I'm revising the design for next time. Before I present my "red line" revisions to the fabricator, could someone advise if I'm OK to simplify part of the work in a particular way? I just need to make sure my simplification doesn't run afoul of the 508A standard. My clients requested that a ten watt 120vAC amber LED (distant from the 508A cabinet) should light up whenever the 3 phase bus is energized. The panel fabricator provided an SSR solid state relay to close whenever 277v shows up across the "input" terminals & they fused the 277v hot for the input so that's all good. The "output" terminal is "single pole normally open", rated for 10 amps. The power that I'm sending in from outside the cabinet is from a small UPS system where the inverter is rated for 250VA's--so it can't deliver more than two amps @ 120vAC. It seems to me that I don't need the series fuse that the shop provided to protect the 10 amp rating on the SSR--since my input power is already current limited. It also seems that I don't need to bring the associated single phase neutral wire into the 508A cabinet at all--since the neutral is never switched & it's doing nothing inside the 3 ph. assembly. If I revise the drawings along these lines, I'll eliminate two terminal blocks, a cc fuse/fuse holder & some wire...and this part of the assembly will be simpler & more intuitive. Basically, I want to treat the SSR like a switch leg for the light, running only a 120v hot wire to & from the SSR output terminals. I don't want to revise the drawings, however, unless I'm sure the fabricator won't have to change them back to comply with UL 508A. I don't own the UL "standard" document & I don't know the peculiarities...but I'm sure some of the forum members do. Should I add signage to explain that the 120v hot must be current limited or OCPD protected before it enters the 3 phase cabinet? Thanks in advance for any coaching or suggestions. -
Hi all, Hope everyone is doing well. I'm currently in the process of starting a home based control panel shop. I have about 8 years of control panel building experience and about 2-3 years of being shop team lead/design engineering. I have been planning this for years and now I have my shop full of necessary tools and material to build small/medium sized panels. I have gone through all the training and examination(which was not easy) to be able to produce UL508A approved panels. My goal is to produce a steady work load with great quality. Now I just need an opportunity with customers which I find to be the hard part. I have been contacting local industries but haven't had any luck. If anyone out there is seeking control panels built at a good competitive rate please advice.
-
We are seeking a Control Panel builder in the SE Michigan area. We can supply the drawings, components, enclosure, etc. Typical panels include PLC, HMI, VFDs, and standard components. Please contact us if interested. We can send more details as needed. We typically need 20-30 panels in a year.
-
Problem: I am getting a control sync fault on 2 recently installed kinetix 5500 but only when my programing PC is connected to the machine network. Install and setup all went great over a 5 day period. Then all of a sudden I started to get this fault. Sometimes 100 times in an hour. As soon as I go offline, and unplug my PC the problem goes away. I have also tried another PC connected to the Machine network and still get the same result. Sometimes machine can run for hours with my PC connected with no problem. I do not have to be online with controller for fault to occur. Setup: I have the 2 K5500's ethernet ports daisy chained together, and then connected via shielded CAT 6 cable directly to port 2 of the Compact Logix Controller Coarse Update is set to 3.5ms and utilization's are at 33% and below.(I have tried the default 2ms with same results) Ethernet modules are configured with FW rev 7.013. Machine network is isolated.(not connected to plant network or internet) Equipment: Compact logix L33ERM Running version 30.01. There are a total of four servos in this system all running over ethernet. 2 Kinetix 350's(not affected), and 2 kinetix 5500's. I have tried: separate ethernet cables for each drive ran through a switch different ethernet cables resetting coarse update speed connecting a different PC for programming I am just not sure where else to go with this. Thanks in advance for any help.
- 1 reply
-
- control sync fault
- kinetix
-
(and 3 more)
Tagged with:
-
Hi All, I'm new to using PLC, and my background is majorly programming. I am learning how to control a PLC over the internet using HTTP or TCP/IP. I have a Mitsubishi PLC Melsec FX-5U 32MR and my requirement is, I want to send create a setup where the PLC works more like a Client on the network and reads values from the server (which is a computer). The outputs on the PLC are controlled by the values on the database in server. So, lets assume I have a value like this on the server "1,0,0,1,0,1", it should translate like below: Y0 = 1 Y1 = 0 Y2 = 0 Y3 = 1 Y4 = 0 Y5 = 1 Is there any guidance where I can read through and learn how to do this. I would prefer doing it by ST programming and not Ladder.
-
Logic issue, or problem with Control Expert 14.1? Pop-up box, followed by Control Expert crash. PLC seems to be running fine. "Control Expert Fatal Error" "The thread tried to divide an integer value by an integer divisor of zero" Anybody seen this before? Corrupt file? Reboot? Uninstall/reinstall?
-
EcoStuxure Operator Terminal Expert
jie en posted a topic in Modicon / Telemecanique / Schneider Electric
Hi, I would like to know how can I change screen using PLC program for the HMIST6400. -
Hi Everyone. I have been tasked with changing out an older Flex Drive servo drive to a more modern Micro Flex drive in a machine that has an Omron CQM1H-CPU51 PLC. I'm having a few issues but hope that i can gain some clarity around at least one of the hurdles Im facing from here. Biggest issue for me at this moment is My work hasn't yet purchased a programming lead for this PLC (or even the bits required to make one myself) but i have a feeling the control for the Servo is done via motion control in the PLC. Question here is, if changing from one servo drive to another type, will the motion control code need to be updated to work with the new servo drive? I have very limited experience with motion control itself at this stage so I'm a bit lost when it comes to these sort of details. Regards Kiwi_man82
- 3 replies
-
- motion control
- servo drive
-
(and 2 more)
Tagged with:
-
Hi guys. I found error on PLC and from PLC diagnostic I found this Operation Error 4100 as per attach picture. FYI, there is no SD card mount onto this PLC. I wonder what is ATA card. This error wont affect the operation. Any advise on what to check? This ladder is pop up when I clicked, error jump. Thanks.
-
Can someone please suggest a Control Panel Builder that is located in Germany? I work for a company in Australia and due to Covid 19, we are struggling to meet an onsite date for a project in Germany. This project uses Siemens PLC gear, Danfoss drives, and mostly Schneider electrical gear. The enclosures are custom and stainless steal. I have electrical schematics and enclosure drawings for quoting.
- 1 reply
-
- gernany
- control panel
-
(and 2 more)
Tagged with:
-
PWTech is a rapidly growing company specializing in wastewater treatment equipment. We are currently hiring for a Controls Engineer. This is a full time position with some travel required. Requirements: 3-5 years experience Proficient with Allen Bradley MicroLogix, CompactLogix PLCs, PanelView HMIs Proficient with ladder logic programming Proficient with basic electrical theory, control systems and electronics Familiarity with NEC, with special focus and understanding of articles 409, 430 A high level of proficiency in written/spoken English Familiarity with Unitronics PLC/HMI is desired but not required Duties will include: Producing control panel submittal and as-built layout drawings, components lists, and line diagrams Selection and integration of sensors, motors, control systems and other mechanical and electrical equipment. Coordination with internal and external project engineers to resolve electrical and control questions and issues Programming, modifying and troubleshooting Allen Bradley and Unitronics PLCs and HMIs Providing assistance and remote support to field personnel Maintaining inventory of long lead items for warranty and project purposes. Location: Rosedale, MD (outside Baltimore) Technologies: 50% Allen Bradley 50% Unitronics. Salary: 95k-105 depending on experience. Higher if you have >10 yrs experience. Contact: Kreal@pwtech.us
-
- allen bradley
- unitronics
-
(and 3 more)
Tagged with:
-
Hi guys I have an control logix plc im looking for a module which is the same as 1769-ascii module. I know that module is for compact logix. Unfortunately i didnt find a good one for that purpose. Anybody can help with that ? Thanks ahead.
-
Hey all. Wondering if anyone has an example program they'd be willing to share? Specifically I'm using the 1734-VHSC5/C with a 1769-L18ER-BB1B PLC. All of Rockwell's wonderful information only refers to SLC-500 platform. I'm not trying to do anything terribly fancy, just have a quadrature encoder attached to Channels A & B, then using an output to turn on a valve at 8.0" and turn off at 10.0" Any help would be appreciated.
-
Hi guys! I need some help with a powerflex 525 multi speed configuring. I know I have to set the P046 parameter for 2 “DigIn TrmBlk” (source) and P047 parameter for 7 which means present frequency. This is the speed reference. I need 3 speed, so I will use Terminal 5 and Terminal 6. When both terminal is zero then 10 Hz, when terminal 5 is 1 but terminal 6 is 0 then 20 Hz and lastly if both terminal is 1 then it will be 30 Hz. I will adjust the speed with the parameters: A410, A411 and A412. Terminal 2 would be the forward and terminal 3 would be the reverse direction. I think these two can be two PLC digital output trough one-one relay. It will be counted the distance by an encoder. When it reach the target the run command will be released and the motor will be stopped with the decel time1. Also I will connect the S1 and S2 for safety. My question is do I have to connect other wires ? Also do I have to remove the jumper between terminal 11 and 1 ? Am I forget something ? Any comment would be highly appreciated. Thanks ahead.
-
Powerflex 400 25HP wird amp behavior
Demetrio Urrea posted a topic in Allen Bradley / Rockwell Automation
ello I have a powerflex 400 of 25HP for a 60amp 25HP motor, the motor have a belt that move the clarifier of milk. It is a process that requires strength to move.So I try with the motor without the clarifier the vdf works well with a constant amp of 12 to the max of 50hz that is set up with a ramp of 600 sec.Then I try with the belt that move the clarifier... The vdf start the ramp with a wird amp behavior like 10 sec 100 amp and then 13 amp for 10 sec.When it gets to 50hz (the max) it starts the same behavior 13 amp when it reach the max RPM and when it decrease a little bit it gets 100 amp to get to the max RPM again.In this vdf powerflex 400 I didn't see the % of torque options that the last one Fuji had.Someone told me that powerflex 400 is not for power processed, they are focus in pumps and blowers more alike, and that I need a vdf vectorial like a powerflex 725.What do you think...PD: as the 100 amp is like 10 sec the protections dont show up. PD: I made a try with water and hot water, in that point with the max hz (and 6800rpm) when the hot water start to flow the amp gets constant in 75 amp, but the motor dosnt get to the 6800 rpm again it just keep trying in 6700rpm and it mantains the 75amp triggering the motor protection for overload. -
How long could be INT array. For example can I build INT[365] or DINT[365]? When I use more than [32] my controller fails. Thanks.
-
hi all, i am tring to program my fx1n on to a bag machine where there is a sensor which checks if the bag length is correct by stopping at the appropriate print also we have given a +5 or -5 to check if the print has moved and if moved to cut the bag from where the signal comes. when the colour sensor is off the plc moves the servo motor the the measure we have given and cuts no problem there but as soon as i give it to check the signal from the colour sensor the plc shows different length when i monitor and also it moves past the print and only stops. it seems its not stopping at the interuption. the colour eye is working we checked. if someone can help it would be greatly appreciated. if you can give a small ladder program which works would be even better :)
-
I am trying to online edit a program in a MELSEC QCPU, using GX Works2, but I keep getting this error "A file which does not exist in the PLC was specified" <ES:010a4022> Few weeks ago I had just online edited the same program in the same PLC with the same steps with no problem. There had been no changes to the PLC after that. Just all a sudden when I try to edit yesterday I get this error. Not an expert in Mitsubishi, just started learning the basics. Connection to PLC is by USB cable. Steps I followed to connect to PLC: -Online > Read from PLC -Select PLC Series: QCPU (Q mode) -Select PLC side I/F Serial Setting: Serial USB -Select all target program to Read, then Execute I am editing the file that I had just read from PLC Steps I followed to online edit: -Online > Monitor > Monitor (Write mode) -Execute the function below when mode is changed: Checked all -Edit the program (basically just deleted one -||- contact and drew back the line) -Compile > Online Program Change Then Bam! error get! "A file which does not exist in the PLC was specified" <ES:010a4022> I had tried Verify with PLC, but all results match. Is there something I am missing? Help much appreciated!
-
- mitsubishi
- plc
- (and 6 more)
-
Hi, I have found this forum extremely helpful in the past. I greatly appreciate in advance any help/direction. I am having trouble simply placing/invoking a PRV instruction in CX-Programmer. The program seems to not recognize really any of the High Speed Counter instructions. (working with a CT021. I/O table correct, CJ2H CPU67 PLC rack powered on with all green lights.) Please see attached screenshots for what I mean... the PRV, PRV2, CTBL, SPED, etc instructions just show up red (like they are not understood/recognized PLC instructions/functions) when I try to place in the ladder. There must be something simple that I am not considering. Thanks again for any help. Michael
-
NX1P2 Motion Control change output device with code
BrunoRamos posted a topic in NJ Series / Sysmac Studio
Hi everyone, To explain the problem a little bit: I have 2 systems that are equal, they have 1 PLC, 1 Inverter and 1 Servo Axis (Image01). The devices are connected via EtherCat. The thing here is tht in these systems the PLC and Servo Axis is the same but the inverter is different. My goal is to have the same project on both systems and depending on the inverter detected use the correct program. What worked: If I add the 2 Inverters and 2 Servo Axis on the project on different nodes (Image02), I can detect which is present using the variable _EC_EntrySlavTb[n]. My issue is that if I want to make more replicas of the systems using different inverters I will eventually hit the Axis Number limit for the PLC while in reality I am only using on Servo Axis at a time. What I wanted: I would like to be able to control 1 Servo Axis with 2 different inverters (only one active per PLC) (Image03). What I tried: The axis parameters can be set using a variable of the type _sAXIS_PARAM, however it seems that the option to change the axis basic settings is not available (Manual: NJ/NX-series Motion Control Instructions Reference Manual (W508) page 5-58) (Image04). The axis basic settings is where the definition of the output device plus control words are set (Image05). Is there a work around to solve this issue? I would really like to avoid having to manually change the output device for the Servo Axis every time I make an update on all the systems. Best Regards, BR -
Good afternoon, I have a problem in an application for a rotary knife, I'm using a MR-JE-B servo to make this movement, while my material is powered by an inverter connected to a modbus rs485 network, with a 5v encoder connected directly in motion. I'm having some problems and I think it's my cam curve. I have a very high refeneration, and the system doesn't obey the size of the length I want the cut. It always cuts the same size, regardless of the configuration I use, it always cuts to 245mm. Put some photos, how are my settings. Grateful in advance, if anyone can help me. Dover_roll_1-Motion-configuração_jog_manual.gx3
-
- simple motion cam curve mitsubishi
- motion
-
(and 3 more)
Tagged with:
-
hi, I have a question regarding DH+ network for those who has really experience. 1. I has on plant 5 plc's connected in seral by DH+ network to GW PLC. I would like to de install the last one in chain . question is: while the DH+ disconnection dose all network line will be shut downed? in case of yes how do I minimize the shutdown time? 2. in other case there is HD Remote panel connected in the middle of line . how I can to DE install it with minimum time of shut down for the RIO's tht installed after him in topology. thanks.
-
Good morning guys, in your experience what is the best way to syncrhonize a motor controlled in speed with an inverter and a motor controlled in position with a servo drive? Let me explaine better what is my situation: I have a belt running normally at a certain constant speed. in some moments, I would like to syncrhonize the speed according to an axis controlled from a servo. the command of a servo specific position target and of course speed and acceleration e deceleration rate. I would like to adjust the belt speed in way to follow as accurately as possible the servo movement. Thanks a lot Andrea