Search the Community

Showing results for tags 'allan bradley panelview'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 280 results

  1. Hello,  I have two pressure transmitters connected to a tank. One at the top and one at the bottom. How can I calculate the level of the tank ? I know the height and Specific gravity of the materials.    Thank You  Pratik Jain
  2. Hi there! I've been looking for some fault codes table for the 1734-AENTR adapters, since I'd like to show a message in HMI with some information when there is a faulty adapter, but I haven't found anything on the internet. So my question is, is there any type of table like this for these adapters? Right now I have a PLC with some AENTR adapters in the program for testing, and since there is actually no adapter connected to it, I can see a 16#2024 error in the module properties, but can't seem to find that info in the module variables.   Do you guys have any clue on how to find this information in order to show it?   Thanks in advance!
  3. I need to Migrate 10 micro logics 1100/1400s. They are all in the same room but in different cabinets. Changing any wiring would be expensive and not an option. They all have small projects and have between 0 and 30 I/O each. The processes are critical and can not shut down or be unreliable in any way. Option one: Micro 800s and CCW.   I realize this is the straight forward answer but my customer hates CCW and may refuse this. Option two: Install one nice modern controller to replace all of them and use remote I/O. This is my first instinct but I am worried about these critical processes now depending on Ethernet networking to function, I doubt the customer wants to pay for network upgrades. Option three: Multiple compact logics i.e. L306s To me this is nice, but overkill and expensive.   Any better option?   Open to opinions     
  4. Hey everyone, I'm new to programming PLCs and I've run into a problem. I have a Micrologix 1400 Series B PLC, and for the past month, I've been using a free trial of RSLogix 500 Starter. But now, the trial ran out, and so I bought a license for "RSLogix Micro Starter". The problem is that when I downloaded my updated file to the PLC for the first time with micro starter, the PLC's outputs don't work anymore. I checked the PLC screen and the inputs from the HMI screen are getting recognized, but the inputs from the physical sensors are not. Also, none of the outputs are being activated on the PLC at all, which I can tell by looking at the I/O status on the PLC screen itself. I then uploaded a new test program, where you press a button and a light turns on, but that doesn't work either. I haven't changed any of the physical wiring, only thing I've changed is that I'm using RSLogix Micro Starter as opposed to RSLogix 500 Starter. I spoke to a Rockwell technician about this and he said that there shouldn't be any problem, as I haven't done anything wrong. So I now ask everyone on this forum if they could help me out a bit.
  5. I have an Allen Bradley 5069-L306ER CompactLogix 5380 Controller that I cannot connect to. I tried pinging the controller and I did not get a single reply. I went on RSLinx Classic and I can find it there. My coworks have no issues connecting to it. They use the same cables and adapters that I use.  What am I doing wrong. I can go to different PLCs in our plants and I have no issues connecting to them.
  6. Hello! First time poster!I am trying to access a PDF file on the removeable SD on the back of the panelview (Storage Card2) and get an error using ActiveX Controls;"There was an error opening this document. Sharing Violation!"The HMI is a  2711P-RDT15C I have called Rockwell support, as well as used various articles from the RA DB and still nothing. Things I have tried: - Reading from various storage cards and USB devices - Reading from my documents - Various syntaxes:       "\Storage Card2\M1.pdf"       "Storage Card2\M1.pdf"       "Storage Card2/M1.pdf"       Many others as well w changes in slashes, spaces, etc - Power cycling between failed reads FoxItReader CAN open. The file CAN also be selected and opened by browsing the OS on the PV - both on the storage card and when moved into my documents. The current parameters for the ActiveX program launcher are: Program location: "foxitreader.exe" Program Parameters: "Storage Card2\M1.pdf" If anybody has any insight into this issue it would be greatly appreciated.
  7. Hi everyone! I am attempting to read EIP tags from an Allen-Bradley ControlLogix from an Omron NX1P2 using the Sysmac Studio function block "CIPUCMMRead." I have been successful in reading arrays and single variables no problem. However, when I want to read arrays from a structure in the Allen-Bradley PLC, I always get an error code in the CIPUCMMRead ErrorID of either 0400 or 1C00 for ErrorID and ErrorIDEx is FF00 2105 depending on what I enter in for Size on the function block (attaching screenshots with both error codes).   The errors show on multiple "read" function blocks at once but it only affects data coming out of the function block where I try to read in a BOOL array from a structure in the ControlLogix PLC. If I enter a UINT#1 for the Size, I get ErrorID 0400. If I enter UINT#2, 3, or 4, I get ErrorID 1C00 with ErrorIDEx being FF00 2105. I've been digging for a while and can't find that specific combo of codes, but it looks like it's a size issue. From what I can tell, the Size is in Bytes. So if I have 32 Bools it should be a Size of UINT#4 max, right? Any help would be greatly appreciated! The function block having issues is setup the exact same as the other two that read from the same structure; I even copied and pasted them from each other and just changed the FB name and the postfix in the SrcDat string (from MyBools to MyDints/MyReals). Here are the screenshot: 1. Allen-Bradley Structure 2. CIPUCMMRead Function Block with size 4 3. CIPUCMMRead Function Block with size 1
  8.  Hey guys, I'm on site with some old AB hardware. I have a DH+ loop with several panelviews 300's, 1000's. Customer wants me to modify one of the PV 1000 HMI's and I cannot open the panel that the screen sits in. It's an explosion proof room, and the system will shut down if I depressurize the enclosure. I do have a saved copy of the PV program to work on off-line.   I do have access to the other PV's and the main PLC, a 5/03 with DH+. There are no AIC modules in the loop. I have the proper serial and round port A-B cables. Can I upload/download to one of the PV's through the SLC processor? I see there are some pass through instruction dealing with serial connection between the PLC and the Panelview. But this is using DH+ between the PLC and Panelview, so the instructions don't work as written.  Rockwell document 2711-um014-en-p.pdf, page 202 has some pass through instructions.   
  9. Hi there! I have an Allen-Bradley SCL05/04 PLC. It has an RS-232 port, a 3 DH+ connector and a circular port with programming pins. An NB-Omron HMI is connected to the RS-232 port. And of course I can only have the screen connected. Is there any possibility to connect through the PLC programming port to be able to follow the program online?   Here is atached photos of the PLC: https://imgur.com/a/PEPI4Wl      
  10.   Replacing dead powerflex 700 with 753 talking via ethernet. Any good instructions on how to update the file from 700 to 753 on rslogix 5000?                                    
  11. Hi, Does anybody know if its possible to access the "Inhibit Module" tick box within the Hardware Device Connection tab from the PLC code? I'm hoping to turn this on / off depending on whether certain modules of machine are physically installed.  e.g. A Kinetix Drive / Point IO etc. Thanks
  12. I'm trying to exchange some data between two controllers. I've used a manual which describes Tag Datalink communication. Everything works fine on the Bradley side, which means I can read values from Omron without problems. However, on the CJ it isn't working. In the Network Configurator I get error every 10 sec (Tag data ling error, code 03D5) and cannot read any data from AB. When I open Connection Structure Tree I see that the input tagset from AB has 'Broken path (0000000000000)' and Unknown Device right next to IP address. I've tried using EDS from the Rockwell as well as uploading it from AB PLC directly - I don't know if it might be EDS issue. The only thing I noticed that inside CJ2M-EIP21 EDS it says that Ethernet/IP is Class 1 connection, however in the 1769-L35E EDS Ethernet/IP is Class 2 connection. Have anyone ever had such a problem?
  13. Been seeing a high failure rate on these PLC's on 2 of our processes. The control power is feed through a APC UPS to a 24VDC power supply to power the unit. Getting a hard fault where the OK LED comes on red and stays red. It never sequences through all the LED on power up. Tried the hard boot by holding in the reset button and applying power. Has anyone on else seen a high failure rate on this model PLC? TIA..
  14. Hi! I hope you could help me with the problem I've been having with this HMI. Usually I use the Instruction-based alarms (ALMD) in the program of my PLC Controller (ControlLogix 5580) to be able to send Alarm Messages to my View Designer Panel View. However, on this new HMI I'm getting the alarm trigger on the Panelview (I get the prompt on the Alarm Summary, and get the Alarm TAG of the ALMD Instruction associated with the alarm), but for some reason the Alarm Message is on blank. It´s the same for all the alarms on the controller. I checked again and the "Message" parameter of the ALMD is configurated, and even test just typing "a" as an Alarm Message to see if it was that the string was too long, but even with that the message didn't show up. Can you help me understand what I'm doing wrong?
  15. Hello, I am experiance a problem with a consumer tag staying stuck on. Producer and Consumer PLC are turned on. Information is getting transfered like it should. The Producer PLC gets powered off and the tag that is getting transfered over is ON before it gets powered down. When I check the tag in the Consumer PLC the consumer tag is still ON. Shouldnt the consumer tag go to the OFF state once the commincation has been lost?
  16. Greetings!I am using a PvP 7 4" screen which is sized at 480X272 pixels. The numeric keypad (and especially the alphanumeric keypad) are pretty small in trying to press the buttons for values.Does anyone know of a way to scale these keypads to a more user-friendly (larger) size?
  17. Hi Everyone, I have a small project where I need to detect temperature and smoke using Allen Bradley Micro820 PLC and send email when the temp is above or below a set limit. And since I'm new to PLC world I'm not quite sure which sensors would work with my plc model. It would be really helpful if anyone could guide me through and suggest any sensors appropriate for temperature (surrounding temp not liquid temp) and smoke. 
  18. Hello guys! I'm interesting about rfid communication. I currently using control logix and compact logix plcs, and rslogix 5000 software. I'm wondering if someone can help me with a sample project, or any documentation. Its also can be wonderful if someone can share a project with panelview if its possible. I wanna know about reading and also writing. What type of device do you guys using ? I would like to make a simple program what is contain reading and writing. Thank you ahead any help of yours.     
  19. Please let us know if anyone needs any of their Allen Bradley plc equipment repaired. We do component level repairs to restore your defective units back to full functionality. You can reach us at CustomerService@OttoAutomation.com or visit us at www.OttoAutomation.com to get a free quote. If you have a part you need repaired that you can not find, please contact us.  All repairs come with a full 1-Year warranty and also include a complete refurbishment and testing to extend your units life cycle. Any member of this site will also get a twenty percent discount.  Thank you, Otto Automation
  20. Hello, I'm new to setting up my controllers and communication between devices.  We wanted to see if using Modbus TCP/IP to communicate to a load bank was the right path for us.  I was able to configure my Micrologix 1400 controller Channel 1 for Modbus and set the data files.  I set up a read holding register 03 message, two write single register 06 messages and one write multiple registers 16.  I was able to read the data from the load bank, but I was unable to send any write commands.  I didn't get any errors in the messages.  I was able to send write commands through my pc to the load bank and it responded properly.  So I was thinking I must of missed something in my set up in the PLC. I'm attaching the PLC Program and the command set from the manufacturer.  Any help would be greatly appreciated. BENCH_TEST.RSS ALx Series Input Command.pdf ALx Series PWR Command Page.pdf ALx Series Setpoint Command.pdf
  21. Hi, So I have a problem, that BootP DHCP server doesn't find my 1734 AENTR series B and so I can't assign IP address to it. Been trying many things. Any advice? I'm new to AB and I guess it may be a really easy thing but so far I didn't find a solution. 
  22. Hi All, Has anyone had the experience of connecting two Fernhill Scada units using an OPC UA?  I am intending to use Fernhill Scada on my Master PLC to read tags from my Slave PLC's Fernhill Scada. Then, displaying local tags (Master PLC, "Fernhill SCADA Unit 1") and read/scanned tags from the Slave PLC, "Fernhill SCADA Unit 2". In the meantime, I am trying to use both of my Fernhill SCADA units interact with each other (one unit to read tags from the other unit) by using Internal Digital Tag on the Fernhill SCADAs.  Any help would be appreciated.
  23. Hello all,    I have 3 kinetix 5500 drives connected in series but some how the 3rd drive lost power. all the fuses in the cabinet look good. nothing else is tripped either.    any advice is appreciated.  thank you   
  24. Can anyone tell me an easy way to extract or view the configuration of a PanelView Plus 700. Do I need to purchase FactoryTalk or some other software or is there a configuration viewer on the PanelView? I am trying to duplicate the information on this local PanelView panel onto our site HMI system (Citect) and am hoping to do this by installing a DigiOne IAP in between the MicroLogix 1500 and the PanelView. This is a on old third-party installed system an no-one on site seems to have the tag addressing information,
  25. Hey guys,   I am looking to query a database through FactoryTalk SE.  I will be scanning packages, and using that bar code to find a lane assignment from the database.     My question has to do with where the VB script will reside in the FactoryTalke SE program.  I want this script to run at all times.  I see that each screen has a "VBA Code" but I am assuming that these will only run when the screen is visible.   Where does this have to be stored in order to run all the time?   Thanks In Advance!