Search the Community

Showing results for tags 'Relay Output'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 56 results

  1. My Powerflex 525 VFD “Output Frequency” starts to drop out (20, 19, 18, 17, 16, 15, 14, 14, 0, 13, 0, 12, 11, 10, 0, 9, etc.) when the Command Frequency approaches and falls below approx. 14HZ. The “Command Frequency” however does hold steady and does not drop out (20, 19, 18, 17, 16, 15 14, 13, 12, 11, 10, 9, etc.). The Pulse In Scale is set to 64. I'm using the Pulse Train Input, and as a test started the frequency of the Pulse Train Input at a frequency such that the Command Frequency started at 20HZ, and then slowly adjusted the frequency of the Pulse Train Input down such that the Command Frequency decreased down towards 0Hz. I did notice that this apparent drop out point is exactly one tenth of the Max Hz value. So for example, with Max Hz set to 140, the dropout starts to occur at approx. 14 (140 x 0.1 = 14). This apparent one tenth drop out point held true for other Max Hz values we tried, including: Max Hz set at 60 started dropping out at 6 Max Hz set at 100 started dropping out at 10 Max Hz set at 140 started dropping out at 14 Max Hz set at 180 started dropping out at 18 Max Hz set at 190 started dropping out at 19 Max Hz set at 200 started dropping out at 20 Max Hz set at 250 started dropping out at 25 Max Hz set at 400 started dropping out at 40
  2. Hi, New to the forum and pretty new to PLC programming. I took the 3-day Sysmac training a couple months ago, but just recently set up one of the NX1P2 units that we'll eventually use for a robotics application. Right now I've got it set up just to experiment with, so I have 3 physical switches (1 momentary, the other 2 toggle) and 4 indicator lights hooked up. Ladder program is set up to light up different LED's when the momentary contact switch  I_SW1  is pressed, based on the position of the other 2 switches. Here's the issue:  When both of the toggle switches are ON (see lines 4 thru 8), all of the LED's light up as expected as soon as the momentary switch I_SW1 is pressed. However, if either or both of the toggle switches are OFF (see lines 0 thru 3), even though it seems like the logic is correct, nothing happens on the output. Lines 0&1 were modified as shown to see if using the variable O_Light1 instead of going directly to O_L1 output would work, but it didn't make any difference.   See attached images for example of working and not working ladder sections as the momentary switch is pressed. In the "working" image, both the toggle switches are on. In the "not working" image, both toggle switches are off. PLC's input & output indicator lights match what Sysmac is showing in the monitor screen, so I'm pretty sure it's in the ladder logic and not the physical wiring.   Thanks for any advice.
  3. Origin search - different position

    Hi I have servo motor controlled by smartstep 2 and controlled by PLC with pulse output. Origin search I have set as below Sometimes I have problem with correct home position. Normally when original Input signals become ON drive slows and after 1 cm I have home position due to slowning ramp, but somtimes drive stops immediately on the edge of original input sensor. I have no idea why it is like that. Maybe you can advise sth or get some clue thanks in advance for any help
  4. FR-A740

    Hi One of my friend want use more analog output on his vfd. Its a Mitsubishi FR-A740 type. Currently the AM signal is for current, but he needs the speed and frequency too.  As we saw its only one analog output is avaiable, but you guys might know better. Can someone confims our theory.   Thank you.
  5. Hello, I am trying to flash an indicator light (Banner  K70LBGYRPQ ) every .5 seconds.  The PLC manual says 2.5A per channel.  The light uses roughly 113mA max current @ 24vdc.  I am using output 0 to do this (O:0/0).  I think I may have ruined the output by flashing the indicator light.  Has anyone ever experienced this before?  Is there a minimum pulse time for this PLC?  What do people normally do when wanting to flash an indicator light such as this?  This is not the first time I have seen this happen.   Thanks in advance!
  6. Hi,I want to read transducer signal on PLC.I am using 7kg60008ab/nn transducer and it's analog (4-20mA) output is connected with analog meter.Can I connect the transducer current output (4-20mA) signal to PLC analog input in series with analog meter display???So that I can read the value on PLC simultaneously with analog meter?
  7. Hello,  I am using Omron’s safety G7SA to relay 24 volt line. But the strange thing happening is that, one relay’s output is only 5 voltage, even the relay is on. I exchanged relays, it remains the same. Maybe the base socket is problematic?  Or is this just G7SA failure? 5v (exactly 4.96v) is strange. Please give me some advice.   Many thanks in advance.   Ting    
  8. Output polarity selection

    Hello to everyone. Nice to meet you all. How are you? I hope you are doing well. I’m developing a program with the purpose of make something similar to a pulse train in the output. However, sometimes I need the output to be a “positive” pulse and sometimes a “negative” one. By positive and negative I mean the polarity in relation to the pulse train source. I’m trying to use a pair of bits in order to switch between the two choices of polarities. I attach a simplified version of the ladder diagram I’ve made. When I thought about the logic, it seemed logical to me, however, it isn’t working as supposed. SM0.4 is a pulse train source. According to the software manual, it is a pulse train with 50% duty cycle and a cycle time of 2 s. That it to say it says at TRUE for one second and return to FALSE for another second. I assign the value of that variable bit to the M0.0 memory bit. I get the negative version of the pulse train logically negating it in the Network #2.                 I assign the value of two inputs, I0.0 and I0.1, to other two memory bits, M0.1 and M0.2. ·         When both inputs are in a FALSE state, the output stays FALSE, disregarding the state of SM0.4. (Case #1) ·         When I0.0 is TRUE, M0.1 is TRUE. However, Q0.0 stays at FALSE no matter SM0.4 is TRUE or FALSE. I attach a pair of pictures. (Case #2) ·         On the other side, when I0.1 is TRUE, M0.2 is TRUE. In this case, the output shows the correct behavior. It is the negated version of the pulse train source. (Case #3)                 Has any of you experienced something similar? Is there a better way to execute my purpose?                 I’m not executing the program, just simulating it with KincoBuilder from Kinco. However, it has always worked fine for me. Thanks for you attention. I look forward for your responses. Kind regards!
  9. I have a question regarding hazardous zone design. My control cabinet will be in safe area but I need to have e-stop and safety limit switch located in hazardous area, Div 1 Zone 1. I am assuming that I can use zener barriers or isolators between the field devices and safety relay. I just wonder if the safety relay will function properly with barriers in between? Also do I have to use 24VDC safety relay for this application? I don't know what voltage/current is present on the terminals connecting to safety devices.
  10. Hello guys, how many (maximum) analog inputs/outputs can CPU 1215C can reach without any issue?   I try to search in google but can't find convincing answer.  Thanks for your help.
  11. Hi everyone, To explain the problem a little bit: I have 2 systems that are equal, they have 1 PLC, 1 Inverter and 1 Servo Axis (Image01). The devices are connected via EtherCat. The thing here is tht in these systems the PLC and Servo Axis is the same but the inverter is different. My goal is to have the same project on both systems and depending on the inverter detected use the correct program. What worked: If I add the 2 Inverters and 2 Servo Axis on the project on different nodes (Image02), I can detect which is present using the variable _EC_EntrySlavTb[n]. My issue is that if I want to make more replicas of the systems using different inverters I will eventually hit the Axis Number limit for the PLC while in reality I am only using on Servo Axis at a time. What I wanted: I would like to be able to control 1 Servo Axis with 2 different inverters (only one active per PLC) (Image03). What I tried: The axis parameters can be set using a variable of the type _sAXIS_PARAM, however it seems that the option to change the axis basic settings is not available (Manual: NJ/NX-series Motion Control Instructions Reference Manual (W508) page 5-58) (Image04). The axis basic settings is where the definition of the output device plus control words are set (Image05). Is there a work around to solve this issue? I would really like to avoid having to manually change the output device for the Servo Axis every time I make an update on all the systems.   Best Regards, BR  
  12. I have an analog output card 1734-OE2V. As a default, there is selected fault mode as 'Go to Low Clamp'. I am using output range -10V to 10V. What is the value for Low Clamp. Is it 0V or -10V? If I want it to be 0, do I need to select 'use fault value' and set the fault value to '0'.
  13. FX3U Output

    Hi,   we have  a FX3U 128 PLC. I connect 24V to COM and all the output in the partition Y0, Y1,.. have 24V even if some output are ON and some are OFF. Why?
  14. I need to use digital outputs of PF527 drive. Controlling the outputs, it does not do anything. Relay outputs are working fine, but opto outputs do not work. For the outputs, there are relays connected, using pin 6,7 and 17.
  15. Evening, I struggle with simple task... I need to activate PLC Output at the specific time of a day. I`m using GSV to obtain PLC time, data is being moved to DIN[7] registers. Then I have three EQU (Hour / Minute / Second) and at the end of rung there is OTL for output. Rung below I have two EQU (Hour / Minute) to disable output at different time - OTU. However every time OTL is energised , OTU on rung below is fired too. What am I doing wrong here ?
  16. Hello, I need to control a stepper motor(have stepper driver) using NX-PG0232-5 with NJ301 PLC. The function is simple, i need to run the stepper motor continuously at a specified velocity. So, in NX-PG module I've made the settings (Ch1 output mode as "Velocity continuous pulse output") and given the tags to IO (as shown below, sorry i'm not able to attach image). I've also added the initialization program to switch on the vfd. Now to move continuously i should should just give speed in pps in "PG_Ch1_Command_Velocity" right?      Ch1 Controlword    Control word 1    W    WORD                 Ch1 Switch On    Switch ON for pulse output 1    W    BOOL    PG_Ch1_SwitchOn        Global Variables     Ch1 Enable Voltage    Start turning on the power for pulse output 1.    W    BOOL    PG_Ch1_Enable_Voltage        Global Variables     Ch1 Quick Stop    Immediate stop for pulse output 1    W    BOOL    PG_Ch1_QuickStop        Global Variables     Ch1 Enable Operation    Start operation for pulse output 1    W    BOOL    PG_Ch1_EnableOperation        Global Variables     Ch1 Fault Reset    Reset errors for pulse output 1    W    BOOL                 Ch1 External Output    Aggregated data of external outputs for pulse output 1    W    BYTE                 Ch1 Command Position    Command position of pulse output 1    W    DINT    PG_Ch1_Command_Position        Global Variables     Ch1 Command Velocity    Command velocity of pulse output 1    W    DINT    PG_Ch1_Command_Velocity        Global Variables  
  17. I have a Base tag of BOOL logic that will not activate the MOV output.  The Base tag is paralleled with an Alias tag for a NO pushbutton.  When the pushbutton is actuated it produces the desired output.  Has anyone encountered this issue from a togglebit base tag before?  Why would a base tag produce a different outcome from that of an alias tag that function properly?
  18. Siemens IEC 60870-5-103

    Hello!, im having some troubles communicating Siemens Relay 7SJ622, with the IEC 60870-5-103 protocol, with some SEL controller, i don't have any signal of the slave relay 
  19. Siprotec Relay 7sj62

    I have 24 Siemens Siprotec relay(7sj62) which i want to communicate with Scadapack 330E (Schneider) on 103 Protocol. but every time I try to communicate it shows Slave device is failed to communicate. trying to communicating via serial (RS-485). What should i do..?? or do i need to communicate it with Siemens PLC..?? If so which PLC should use..??
  20. rc01cpu and r60da4 help needed

    Hi every body, could you please help me; i have a mitsubishi plc serie iq-rwith the followings modules:powersupply r61p, r01cpu , rx40c7 inputs , ry10r2 outputs , r60adv8 analoginputs and r60da4 analog outputs. i am newbe with mitsubishi plc ;i would like to learn using the analog output of the R60DA4.for exemple i would send a digital value to the ch1 and convert it a voltage that i can mesure on the output of channel1.i have tried but i didn't succeed.i am using gxwork3.i have configured channel1 as +10v -10v output, normal mode , normal output;then i made a simple program in sfc to try this conversion but i get nothing in the output of channel1. i found that the digital value should be sent to the adress D11 wich is the adress of channel1.here you will find the file i made with gxworks3.could you please help me. ANALOGOUTPUTSCF.gx3
  21. Good Afternoon  im a complete newbie when it comes to PLCs but have done plenty of PIC programming in the past. I've been gifted a couple of FX0s 20mr units to try to repair something I made with PICs years ago. It got damaged during a move and I can’t see well enough now to make PCBs anymore so thought that this might be a solution. The basic operation is  1. switched on 2. motor A moves till hits limit switch (X000) 3. Wait 2 seconds 4. motor reverses till hits second limit switch (X001) then once this has been completed then the following  5. Motor B turns clockwise for 30 seconds then stops  And while Motor B is turning I need Motor C to turn until hitting limit switch (X002) I then need to get it to repeat on the press of a button but I need to reverse operation of Motors B and C I am using double position relays to drive the motors so motor A is on Y000 and Y001 if I power either relay the the motor turns in that direction. Same with Motor B and C Y002 to Y005 is this something that’s possible with one of these controllers or am i going to be programming a PIC to control the PLC ?   All the various COM and powers are connected up, I can individually make every motor do what I want, but the program doesn't flow from one item to the next. but this is probably just me      
  22. Hi all,  I am in the process of doing a project for some school work and need to do a SWOT analysis of the latest modular PLCs from Mitsubishi (R series), Siemens (S7-1500) and Allen Bradley (ControlLogix).  So I thought what better way than to ask the people on what they think are the pros and cons of each! Thanks for your responses in advance!
  23. Is there any reason not to have input and output modules on the same rack as the processor and Ethernet cards? We have RIO’s and sometimes have networking outages, I want to move critical IO to Rack0 the same rack as the processor, is this bad practice?  I've seen architecture for BMS that only have Ethernet cards and processors in Rack 0... 
  24. Control Panel

    Is it possible to view the values / states of all inputs, outputs and workbits (e.g. 64.00 through 64.15 on Omron CQM1 PLC) on a single screen or control panel within CX-Programmer software?  I'm trying to troubleshoot some ladder logic that I wrote and need to know the values of 5 or 6 inputs/outputs/workbits simultaneously.  Having to scroll up and down through my ladder logic repeatedly does not work well with code that changes state every 5-10 seconds or so. Any help is welcome.
  25. Using a AD041 and DA041

    Hi, I'm using a CJ2M CPU 33, and also a CJ1m Ad-041-V1 Analog Input and DA-041 Analog Output card.  I am using the Analog input to measure my current in my one heating application and  Ihave that reading and scaled correctly, but now  I want to use my Analog output to replace the Rheostat  we have in the system. I'm having some issues setting the range and getting voltage to vary. I also am a little new to Analog Outputs and don't know what I'm doing wrong. I have attached my program here. Any help would be greatly appreciated. Analog Heat.cxp