Search the Community

Showing results for tags 'Micro800 series'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 106 results

  1. Hi everyone,  I am trying to use Kepware to communicate with my PLC setup which is the iQ-R Series R08PCPU.  I read the documentation which is available at https://www.kepware.com/getattachment/3daf1ac3-5c76-49ce-bbfe-f0fb1015f6cc/mitsubishi-ethernet-manual.pdf I read through the setup for Kepware and the setup procedure for iQ-R series but it still didn't work.  From the documentation, it said something about "using special ladder logic to enable ethernet communications is required.", I couldn't find anything about this online.  Here what I did in addition to the documentation: - Enabled IP Packet Transfer - Ping the PLC's IP Address which was successful Does anyone have any idea what I didn't do to establish that communication between Kepware and R08PCPU?  Thank you in advance. 
  2. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.
  3. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.
  4. Fuji Wsz plc

    Please send Fuji Wsz plc software download link  
  5. Cable pin configuration required.

    Required cable PIN configuration for Nexgen 1000 series PLC, MS-40M-E, NT11-SF121B-EV1 , GT1020-LBD.  
  6. GX Works2 Q Series TCP issues

    Hey guys, been looking around for a solution and I was brought here.  I'm a programmer at a place that just put in a bunch of these Mitsubishi Q series QJ71e71-100 ethernet controllers.  I wrote a TCP server in Java to try and talk to them.  I'm trying to get data sent over from a little GOT1000 test terminal.  The zp.open command is working fine and i'm seeing a good syn-ack handshake, and if i push some text to the plc from the program I get a response (even if it is always the same nonsense).  but when i try to use the zp.send it fails, I get error C1A6 on the ladder program and the q series lights up the comm error light.  I know I'm being super vague here, I was just hoping to gain some insight.  I don't much know what to expect from this forum if you guys are active or if my question even has an answer but i've been banging my head against the wall for days now.  I'm just using a tutorial program from the q series manual and a super basic tcp handler in java.  If there's any other information I can provide let me know.
  7. I'm having trouble in finding a complete manual instruction and set-up on setting up a communication on a Q-series PLC to a inverter a700/a800 via RS-485. I have a manual for fx series, are the parameters the same as the fx series? how about the program, like  starting or stopping the motor? Are they same or not? In the Q-series, do i leave switch-5 "station no. setting" blank? i just started this so i hope that i can make this work after new year. This is the manual for the fx-series plc====> http://www.automationsystemsandcontrols.net.au/PDF%27s%20Mitsubishi/Manuals/FPLC/FX%20SERIES%20USER%27S%20MANUAL%20-%20Data%20Communication%20Edition.pdf   PS: I'm mostly self study because i don't have proper training yet and my school sucks.
  8. edit comment directly from got

    hello everyone using gt designer 3, got 2000 series and IQ-R series want confirm something. it`s possible to edit comment group (that use for history, fault,etc)  directly on GOT using GOT tool or object or script? for script, searching on gs, gd list but find nothing. where the comment group is saved? thank you  
  9. Version 1.4.0

    37 downloads

    This is a custom template created for nb7w tw01b HMI. hope someone finds it useful. If you want to create custom templates for NB series hmi feel free to ask me. Cheers.
  10. View File Template for NB series hmi NB7W_TW01B This is a custom template created for nb7w tw01b HMI. hope someone finds it useful. If you want to create custom templates for NB series hmi feel free to ask me. Cheers. Submitter Aneesh Submitted 10/27/17 Category Other Omron Products
  11. Hello, Everyone . Do anyone has experience in FX1N-232-BD connect to GT11 (or other model) from Panasonic ? I try to connect them via RS232 port and I setup parameter following HMI manual but It doesn't work at all only RX led on 232-BD blinking Any suggestion ?    Matcha IMG_39346964.MOV
  12. View File GE SRTP Ethernet Driver for .NET .NET Component for use in Visual Studio.NET to create HMI/SCADA apps that communicate with GE SRTP devices via Ethernet. Supports PACSystems, Series 90, and VersaMax.   Supports PACSystems symbolic variables and CPU rack + slot specification. Does not require 3rd party drivers Does not require OPC x86, x64, and Any CPU compatible Visual Studio.NET 2005, 2008, 2010, 2012, and 2013 Compatible Most .NET targets are supported, including Web, Win Forms, WPF, console, and service apps. Build Windows Forms, console, and ASP.NET applications that run on Linux with Mono framework. Extremely high performance - 5~10 mSec typical transaction time Optimizes multiple register configurations into minimal transactions Tag database can be configured via code or visual designer Abstract base classes allow you to write generic code that works with all drivers Synchronous and asynchronous read/write methods Data change notifications Provides common user interface across all driver classes No limit on number of devices or data points Multi-threaded for high data throughput Includes extensive help system Windows, Console, and Web Example applications with VB and C# source code included. Easily connect office systems to factory floor. Free 30 day fully functioning trial version available for download Runtime-free for qualified applications   Submitter Automated Solutions Submitted 05/09/09 Category Demo Software
  13. HMI not recognized via PC

    I am trying to connect HMI( GS Series) to Laptop but every time it says " Device not recognized ".  Tried changing the port, Laptop, whole HMI.  It was working for 2-3 times after installation of new software( both Windows and GX Designer). Tries uninstalling and installing GX designer. Pls help.
  14. Hi Everyone! I try to read Analog Data in PLC Master through Salve Module (ECT-21) but i dont see any data, with an Digital Module i can read and write, but with analogic module i can't do anything. The analog module works perfect, i have 4-20ma Simulator and work fine. Modules: PLC: NJ501-1300 Slave: ECT-21 Analog: ADO81-V1 Can u help me? Regads..
  15. hello, i'm using Micro830 to receive serial data from matlab and hyperterminal. i followed article 448488 - how to read ASCII in Micro800 controller. However, ACB can receive data but ARD can not.   Then i added a contact before ARD. Once i check and recheck it, then ARD can receive data and ACB value will be cleaned. the 55 showed on the ARD is the value from previous buffer  
  16. Hi, I have a question about error clear on Mitsubishi Q Series (Q03UDE). Is there a way to clear 4100 error without power cycle CPU??? I've cleared the cause of the problem and I've tried to clear CPU error using SM50. I've put code 4100 into SD50 and then turned SM50 off and then on again, but CPU is still in ERROR state and I cannot switch it back on into RUN mode. I have to turn the power off then on again and that is solving the problem. The problem is that sometimes it is very hard to get to control cabinet to power cycle CPU. I would like to clear this error remotely if possible. Any ideas???
  17. Hi all. My experience is using Studio5000 / RSLogix5000 to program CompactLogix PLC's. I need to use a basic (cheap) PLC to get data from a Control Techniques Drive (about 9 DINT's for Speed, Torque, etc) and then display on a PanelView Plus 600. Its a bit extravagant to use even a basic CompactLogix for this, so I believe the most basic AB solution I can go for is the Micro820.In Studio5000, to add in CT Drive comms, I simply just add a Generic Ethernet Module and setup the IP address of the CT Drive and the Connection Parameters and that is pretty much it. I look in the Controller Tags and there is my DINT array that I can interrogate for the information. Very simple.Anybody any clue how to replicate this in Connected Components Workbench for the Micro820? I cant seem to fathom it out at all?Just to clarify, I am not doing any control of the Drive from the HMI or Micro820, merely displaying on the HMI parameters like speed, Torque, etc.Thanks.
  18. Help with CC - Link IE Field

    Hi Im working with an iQ-R CPU wich controls 6 conveyors with a CC-Link IE Field Network, the CC-Link module is a RJ71EN71. Each conveyor has a remote I/O (NZ2GF2B1-16TE Digital outputs main module with a NZ2EX2B1-16D extension for Digital Inputs). The communication in the CC - Link IE Field diagnostic appears to be OK, but I can´t send or receive IO signals from the Batch Monitor of Gx Works 3. Thanks for your attention!
  19. Hello all, I have 7 Q series PLCs on a Melsec net/h network, Ladder Programming none of that fancy smancy ST stuff LOL. Were running the QJ71LP21-25. Now to keep it short I have used all most all my devices in my Network Range Assignment. I can not set up low speed range as I do not have enough Link relays and registers at all stations. No memory for more devices just trust that I can not do it... However I have an abundance of File Registers ( no I cant buy B or W in the PLC File params, well I can but it wont help because only one CPU is UDE the rest are H.) I have a project in which I must see about 50 words for each Station at every Station. I figured while I am setting up a Transient Transfer I will make a bunch of extra room for future updates and junk. My answer good or bad, is to set up some Send/Recv commands and do some Transient Transfer. I think I have it just about all figured out just a few questions. I have two manuals I have been getting my info from Q MELSECNET/H Network System Reference Manual ( I think SHNA080049)  and the Melsecnet/h training manual.  1.Any one have any better manuals that better cover transient transfer? Or that are new enough to mention GX Works2 instead of Developer? 2. Is there a max device for each send/recv? (I keep thinking it is 980 per station but no idea where I got this number)( I will increase the max # of transients in the supplementary settings under network range...) 3. Any precautions or advice like, Hey don't do this, I did this once and.... 4. It looks like as long as I use different logical channels for each station I should be able to send and receive multiple "messages" at once with no error?? (I will test this and look for the "no room in receive buffer area f222 error)  5. Will this slow down the Cyclic transfers (I will be watching the SW006D and so on to make sure it does not slow my regular transmission down.) 6. I will be using several special relays and registers in the program of course. Any I should use that are not obvious?  
  20. We have L61's and L63's and are looking at upgrading them to the L7 equivalent. Has anyone had any experience of this and any pitfalls to avoid? Tech support have said that there might be issues with the comms cards resolved by updating their firmware. Is the upgrade that simple? We currently use Logix5000 at version 20.01 but are preparing to go to Studio5000 as part of the upgrade.
  21. Mitsubishi equipment

    Not sure how many people are reading the "For sale" section in this forum, so I'm linking my recent post here. I hope it's OK for the moderators (and others). http://forums.mrplc.com/index.php?/topic/32746-mitsubishi-equipment-for-sale-q-and-fx-series/
  22. Hi all. I have some equipment not in use anymore. I'm able to send anywhere in the world for pre-paid items. PM me for prices/questions. Remember to be specific about which item(s) you are interested in as some of the equipment has been used and some are barely used.   1: Brand new (purchased about 1 year ago - never used): 1x 8slot backplane 1x Q03UDE CPU 1x QX80 input card 2x QY80 output cards 2x Q68TD-G-H01 temp input cards 2: Used for LAB about 2 years: 1x 8slot backplane 1x Q61P Power supply 1x Q03UDE CPU 3: Used for LAB: 1x Q33B 3-slot backplane (used about 6 years) 1x Q61P Power supply (used about 6 years) 1x Q03UDE CPU (used about 3 years) 1x Q03UDV CPU (used about 1 year) 1x QJ71MT91 ModbusTCP card (used about 3 years) 1x QJ71E71-100 Ethernet card (used about 3 years) 4: Used for production about 7 years: 1x 8slot backplane 1x Q61P Power supply 1x Q04UDEH CPU (used about 4 years) 2x QJ71E71-100 Ethernet card 1x QJ71MT91 ModbusTCP card 1x QJ71C24N-R4 serial card 1x QJ71MES96 Simple MES card 5: Brand new (purchased about 6 months ago, used for two days in LAB) 1x FX3U-16MR-ES  
  23. Good morning,   I want to connect my Micro820 to a load cell, read its value and then send it to a printer so I can have a generate a label with the product's weight.   I'm open about the printer model but I really don't know where to start and couldn't find any good articles about  it. Does anybody know where I could find some more information about the subject or even program examples? Thank you  
  24. Has anyone discovered a laptop that will connect to all mitsi PLC types (and Melfa Robots) via MELSOFT TCP connection. My Dell 5510 seems to have the most random dislike for this kit. at the moment it is happy to link to Q series but wont touch FX at the moment (this has not always been the case). I have checked all basics I know; 1. Pinging 2. Port setting to Melsoft 3.  Direct connection to FX3U-ENET avoiding the unmanaged switch (altering settings to suit). 4. Using FX Configurator to try and diagnose,checking the module settings in the project. 5. Disabling laptop wifi connections 6. Disabling firewall and AV. 7. Trying to setup a UDP connection (this seemed to work on Q series) Pffff..... Any thoughts?....I am obliged to use a site networked laptop so there maybe IT issues....however due to my ongoing frustration I will order a laptop and use offline like a wild man
  25. Hi! Here I am again but this time with Micro800 "issue". I use the Micro820 2080-LC20-20QWB (relay output) with a Beijer HMI panel. I notice that the Micro820 internal RTC is not so accurate (as datasheet said). So I decide to sync it every hour with the Beijer one with the RTC_SET instruction block. All works but if the sync come concurrently with an exited output the output relè seems to vibrate (anyway the related led stay on!). So i thinked that the problem is the Beijer sync method and I try to compile the simpliest program to test the issue. I attached it to this post. Inside "Prog1" program I put the "Out_Act" to activate the output 00 and inside the "Date_Hour" I put the RTC_SET instruction. Try to set the bit "Out_Act" and after that put some date setting on  try to set the "RTC_Enable_Set" bit. What happens to you? Somebody that can test if the issue appear? My Micro820's firmware is already upgraded to 10 as also the CCW is 10.001   Do you think that is a firmware bug?...   Thank you! Test_RTC.ccwarc