Search the Community

Showing results for tags 'INCOM IMPACC Modbus network'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 292 results

  1. Has anyone successfully used a 1783-NATR for Modbus TCP communication between a ProSoft MNET card (in the ControlLogix rack) and a Modicon Quantum? ProSoft MNET:  10.x.y.z Modicon Quantum:  192.168.1.x There is one (1) ProSoft MNET and four (4) Modicon Quantum's. NOTE:  I know there are other devices that support this behavior...the NATR is the suggested standard hardware.  We are getting various responses from distribution and support.  ...I was hoping someone in the community could confirm.   Thanks for your time!  
  2. Hi I'm trying to set up Modbus RTU communication between FX3U PLC and a weigh module. I would use the ADPRW command using 0X03 to read the 16 bit Holding Register but in the weigh module the Data Address/Holding Register of the value I want to get is 400047 - 400048. How to translate the value in 16 bit?   Thanks, Fabio
  3. Hi,   we have a Mitsubishi PLC Fx3U-128MT and a A&D weighing module AD 4212L. The weighing module supports MODBUS RTU communication via RS-485. We are looking for the most affordable and simpler way to establish communication between PLC and weighing module. At pag 20 of the manual " MODBUS Serial Communication Edition " https://dl.mitsubishielectric.com/dl/fa/document/manual/plc_fx/jy997d26201/jy997d26201g.pdf there are three options of communication equipment. According to your experience, what specific interfaces do you suggest us to invest in? Thanks    
  4. Hello,   Any one  have idea how to read and write variable for Schneider tm221 plc with Modbus function codes 3,6,16. I attached file for power supply communicator with registers, I need to adjust power supply from 25% up to 100. Please need help. Best regards,   Chyngyz   Modbus OPERATING INSTRUCTIONS.pdf
  5. Hi all, I'm having an issue with EcoStructure Control Expert where when using DTM browser I try to connect but I get a message "No Ethernet/IP device at specified address...." My issue is that I had a device communicating using modbus but it has stopped and I cannot diagnosis the issue. I can ping the address and run a modbus poll from a PC on the network and everything performs correctly. Any help would be greatly appreciated. 
  6. Need help in table scrolling

    Hi all, We have a DOP 107CV HMI we interface this HMI with microcontroller through RS485 Modbus protocol. I'm new to HMI and PLC's although we are successful in interfacing HMI with Controller(Communication Established successfully) We made a table in HMI and allotted some registers to Modbus address and data is transferred from controller to HMI up to this we are good in communicating Since the table created is static and we cannot scroll down from that table so, to overcome this problem we found History buffer and made PLC trigger and allotted address. In that History Buffer we created 7 rows and the data is sample whenever we triggered the PLC in that case scrolling is working fine, but the problem we are facing is whenever we update 3 rows out of 7 and triggered the PLC only 3 samples are updated in first column and in the next step we updated the other 4 rows and triggered the PLC the data is sampled on next column but we required it to be sample on first column instead of second.  
  7. Delta plc Communication Issue

    Dear allI have DVP14SS211R series Delta PLC Which is having 24V DC supply voltage. I am using PLC as master and My end device as slave. My slave device set device_iD=1I am using Modbus RTU protocol for Function code1baud rate =9600parity =noneStop bit=1data length=8I would like to know how to send request with Function code 1(Read coil Register). i have attached code reference. Communication block it wont give error it shows 0 .means No error
  8. modbus rs232 communication error

    hi I am traying to connect 10 plc's FX3U to a scada system, on the plc's there are a rs232db and FX3U-232ADP-MB cards. i have devices transmit the rs232 by lan or any thing I need (rut955) my problem is when i download the program on plc same times the communication go right , but if i powering pls off then on the communication fail down. I initialized the plc  like photo https://drive.google.com/file/d/1Tr367wfVCRG6vvKcsOFyTKG_FExAsnVy/view can any one help me? sorry for my English
  9. Hi experts :D Can anyone help/try to help  with the following conundrums: a) when changing the Ethernet Operation settings from Binary code to ASCII code, the setting are 'saved' in PLC settings, meaning that ASCII code is read as selected after a restart, but the PLC accepts commands and responds in Binary code. b) when adding a new TCP port, the new port is 'saved' in PLC settings, meaning that read as selected after a restart, but the PLC refuses commands on that port (the "Open" LED on the Q71E71-100 card turns on for the duration of the transmission but no reply is received from the PLC) notes: setting software: GX Works 2 target test software: Custom made Driver for MC protocol. (tested and working with FX and Q series  and with ASCII and Binary code) PLC model Q02 (reset performed by removing the battery for more that 2 hours) ports used for test are: 5500 and 4999 (decimal) found 5002 port opened by default (no open setting required) PLC network module Q71E71-100 (new)   I would upload screenshots of the settings but I get this error: "There was a problem processing the uploaded file. Please contact us for assistance."
  10. CJ1M+ETN21 Modbus TCP

    Hello. I'm trying to use Omron ETN21 as master for ModbusTCP protocol. I can communicate with 1 SLAVE UNIT (standard modbusTCP slave) using FB MTCP_ETN_Client.zip  from https://www.myomron.com/index.php?action=kb&article=1245. It works perfectly. But I have three SLAVE UNITS to communicate to. I'm trying to do this using [524]Modbus_TCP_FB.zip sample. I have copied SECTION1 to SECTION2 and changed IP number and SOCKET number. But this doesn't work. I would realy appriciate a working sample where OMRON PLC is MASTER for THREE (or more) SLAVES. I'm attaching code file... Thanks. Best regards, Andrej. Modbus_TCP_FB.cxp Modbus_TCP_FB.opt
  11. Hello out there   I've searched for quite some time but unable to find any information helping me through this. I got a Omron PLC NX1P2 where im supposed to setup modbus communication over TCP/IP but so far i've only been able to find information regarding RTU setup. But seen forums mention its possible to setup via TCP/IP Anybody who can help. A program sample would be helpfull aswell. Im a trainee as automationengineer and this is my first encounter with Omron PLC and Modbus so quite new to the field.   kind regards Ivan T.
  12. Hello, I'm trying to connect a CJ1M-ETN21 as slave Modbus TCP with a Modbus/Dali Gateway. I download from Omron website some FB with ones should be possible.   https://www.myomron.com/index.php?action=kb&article=1245 The FB only can be used with the direction unit 0, but we can change some directions inside the FB and can be adjusted to other units. In the download I found this FB: MTCP_ETN_Connect, MTCP_ETN_Fn01, MTCP_ETN_Fn02, MTCP_ETN_Fn03 .... Supposed with connect we can establish the connection with the master, but the FB never make nothing. Should I make some special configurations to use this FB? I appreciate any help. Thanks
  13. Indusoft Web Studio

    i am using indusoft web studio for the modbus logging. program runs successfully but after a half day or a day it shows error " error initializing the driver modbu 10.10: invalid serial port "any suggestion will be appreciated.RegardsZubair Ahmed
  14. Modbus with CJ1W SCU31-V1

    Hi every one, I want communication Inverter mitsubishi D700 with module CJ1W SCU31-V1,  any one give me a correct solution and send any sample program. Thanks
  15. I'm trying to communicate with INVT PLC and DGM8002(grain moisture analyzer) via mobus RTU.   Can anyone explain about these Modbus address ? Please kindly see in picture . example working mode address K0 (0-stop ,1-manual,  2-Auto) Actual Moisture Address K6 What is meaning of K0,K1,K3,K6.  https://drive.google.com/file/d/1-mGzpEvw4UlewWhR9k3wOd1mO-uhsklL/view?usp=drivesdk Is that K0= 0000 K2 = 2000. K3=3000 ? Any suggestion please. I'm really appreciated your comments.❤️  
  16. - i'm from VietNam, Who can help me?? - I cannot communicate the RFID card reader with the FX3U PLC using the FX3U-485ADP-MB module; - register error D8438 = 3821; D8423 = 1025; D8422 = 212. - Here is the connection picture and my PLC code thanks !!!!
  17. Q03UDVCPU Modbus Setup

    Hi Guys, I need help to set up modbus tcp/ip parameter for Q03UDVCPU, i want to use the predifined protocol and built in ethernet port. do you guys have some usefull references how to setup modbus tcp/ip, or is there any example program from mitsubishi? Thanks
  18. Dear Engineerds,   My Master (non siemens) doesn't see the Holding Registers of the Slave (S7-1200) plc. However the Q coils are fine and all Diagnostics don't show errors. The Hardware: S7-1200 – CPU 1215C CM PtP – CB1241 RS485 (6ES7 241-1CH30-1XB0) - Half Duplex RS584   Firmware: Modbus_Comm_Load (V3.1) Modbus_Slave (V4.0)   I've tried with various DB, UDTs and manipulating HR_Start_offset parameter with no success. Could you advise what am I possibly missing? Modbus_Comm_Load_DB_Snapshot.xlsx Modbus_Slave_DB_Snapshot.xlsx
  19. CJ1W-EIP21 To CJ2M-CPU33 Setup

    Hi All,     I am working on a system that uses multiple Ethernet IP devices to control Pneumatic valves and D I/O. We have integrated several (smaller systems) with success. However, these systems are using a large amount of network words. One system uses 210 Byte Produce and 210 Bytes Consume. My Current count of these systems on one machine is Six masters. I need a total of 2,520 Bytes plus some for other devices in my network configurator.  My controls vendor told me I could expand the network by adding a CJ1W-EIP21 Card to help run these masters. After about 24 Hours of reading the Manual w465 I still dont quite understand how I am supposed to run these valves with this card or with Tag Data Links. Currently I have a network config. with all my masters networked to a CJ1w-EIP21 Card and TagData Links that were setup through the Tag Data Link Wizard via Network Config. I need help setting up variables in the CJ2M_CPU33 using tag link data that will allow me to output data to these masters. All assistance and Information is much appreciated.    Nate
  20. I have a purchased Machine that came with a Siemens LOGO 8.FSR PLC (Smart Relay). Generally we use Allen Bradley or Mitsubishi. Anyway, we need to communicate data between the LOGO and an Allen Bradley Compact Logix.  I do not desire to add an additional network to the AB but as best i can tell the LOGO is exclusively Modbus TCP/IP. Has anyone come across a similar situation?  I look online and did find an  Anybus module that claims to be able to link them together.  Looking for anyone who has faced this challenge and succeeded, or failed.   Thanks
  21. From DM:   Hi; my name is Metin , I live in turkey. unfortunately I have a problem that I could not reach a conclusion here. I hope you can help. I need to communicate with CJ1W-ETN21 with a device via modbus tcp and read information. I downloaded ready-made protocols on omron site, connection is established but I cannot read. I tried the attached protocols. the device I am trying to communicate with :  https://www.gmweighing.com/products/weighing-indicator-m02  I will get the weight information from the weighing device. Thank you in advance for your help. MTCP_ETN_Client.zip
  22. Hi there, Im having issues controlling ATV 320 VSDs over Modbus RTU with a M221 plc, does anyone have any pointers for me to look at? I believe I Have set everything up correctly but when I run the program on the plc the atv's just stay in 'NST' state I have included screenshots if they are any use   My speed reference in this example is taken from the memory word %MW0 which I am inputting via a HMI   I have addressed all my ATVs accordingly in there setting with the correct Modbus parameters and selected Modbus under the FR1 configuration, am I missing anything?? Any help is appreciated as I am really struggling   Tom
  23. Hi everyone I'm new bie, I try to control VDF-M via fx1n-485-db. please help!! Thanks.
  24. Hi everyone I'm new bie, I try to control VDF-M via fx1n-485-db. please help!! Thanks.
  25. hello expert i want ask some help So i tried to communicate my Omron PLC (cj2m cpu31) with SCADA from Schneider (power logic) on my omron side the comunnication on PLC already take to communication to NB so i add communication module CJ1W-SCU41-v1 I want asking how to open the communication if i want the scada become a master and my plc become slave i got this from omron website is that program compete for my case? i need configuration for scu41 module also to communicate or if you have suggestion i really open i just need to open port RS232c from scu41 so scada can read the data from my plc  tahnkyou for your help MRTU_CPU_Slave.zip