Search the Community

Showing results for tags 'FX3U as Modbus slave'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 318 results

  1. Hi I'm trying to set up Modbus RTU communication between FX3U PLC and a weigh module. I would use the ADPRW command using 0X03 to read the 16 bit Holding Register but in the weigh module the Data Address/Holding Register of the value I want to get is 400047 - 400048. How to translate the value in 16 bit?   Thanks, Fabio
  2. Hi,   we have a Mitsubishi PLC Fx3U-128MT and a A&D weighing module AD 4212L. The weighing module supports MODBUS RTU communication via RS-485. We are looking for the most affordable and simpler way to establish communication between PLC and weighing module. At pag 20 of the manual " MODBUS Serial Communication Edition " https://dl.mitsubishielectric.com/dl/fa/document/manual/plc_fx/jy997d26201/jy997d26201g.pdf there are three options of communication equipment. According to your experience, what specific interfaces do you suggest us to invest in? Thanks    
  3. Hi , we have Fx3U-128MT and a Hybrid Stepping Motor 2 Phase (17HS4401).   Do we need to install  FX3U-2HSY-ADP to control the stepping motor or we can program it no problem using  PLC User's Manual - Positioning Control Edition? Do we need  a Driver?
  4. FX3U Output

    Hi,   we have  a FX3U 128 PLC. I connect 24V to COM and all the output in the partition Y0, Y1,.. have 24V even if some output are ON and some are OFF. Why?
  5. Hello,   Any one  have idea how to read and write variable for Schneider tm221 plc with Modbus function codes 3,6,16. I attached file for power supply communicator with registers, I need to adjust power supply from 25% up to 100. Please need help. Best regards,   Chyngyz   Modbus OPERATING INSTRUCTIONS.pdf
  6. Hi all, I'm having an issue with EcoStructure Control Expert where when using DTM browser I try to connect but I get a message "No Ethernet/IP device at specified address...." My issue is that I had a device communicating using modbus but it has stopped and I cannot diagnosis the issue. I can ping the address and run a modbus poll from a PC on the network and everything performs correctly. Any help would be greatly appreciated. 
  7. GXWorks2 - FX3U Special Module

    Hi guys. So I try to read FX3U PLC using GXWorks2. There are 2 unit of Analog Input module installed but I cannot read the module from GXWorks2. I am trying to find input mode setting in the program to define the AI range but cannot find any. D2002 is the AI channel. I back-traced from GOT address. Any advise? Thanks!      
  8. Need help in table scrolling

    Hi all, We have a DOP 107CV HMI we interface this HMI with microcontroller through RS485 Modbus protocol. I'm new to HMI and PLC's although we are successful in interfacing HMI with Controller(Communication Established successfully) We made a table in HMI and allotted some registers to Modbus address and data is transferred from controller to HMI up to this we are good in communicating Since the table created is static and we cannot scroll down from that table so, to overcome this problem we found History buffer and made PLC trigger and allotted address. In that History Buffer we created 7 rows and the data is sample whenever we triggered the PLC in that case scrolling is working fine, but the problem we are facing is whenever we update 3 rows out of 7 and triggered the PLC only 3 samples are updated in first column and in the next step we updated the other 4 rows and triggered the PLC the data is sampled on next column but we required it to be sample on first column instead of second.  
  9. Delta plc Communication Issue

    Dear allI have DVP14SS211R series Delta PLC Which is having 24V DC supply voltage. I am using PLC as master and My end device as slave. My slave device set device_iD=1I am using Modbus RTU protocol for Function code1baud rate =9600parity =noneStop bit=1data length=8I would like to know how to send request with Function code 1(Read coil Register). i have attached code reference. Communication block it wont give error it shows 0 .means No error
  10. modbus rs232 communication error

    hi I am traying to connect 10 plc's FX3U to a scada system, on the plc's there are a rs232db and FX3U-232ADP-MB cards. i have devices transmit the rs232 by lan or any thing I need (rut955) my problem is when i download the program on plc same times the communication go right , but if i powering pls off then on the communication fail down. I initialized the plc  like photo https://drive.google.com/file/d/1Tr367wfVCRG6vvKcsOFyTKG_FExAsnVy/view can any one help me? sorry for my English
  11. CJ1M+ETN21 Modbus TCP

    Hello. I'm trying to use Omron ETN21 as master for ModbusTCP protocol. I can communicate with 1 SLAVE UNIT (standard modbusTCP slave) using FB MTCP_ETN_Client.zip  from https://www.myomron.com/index.php?action=kb&article=1245. It works perfectly. But I have three SLAVE UNITS to communicate to. I'm trying to do this using [524]Modbus_TCP_FB.zip sample. I have copied SECTION1 to SECTION2 and changed IP number and SOCKET number. But this doesn't work. I would realy appriciate a working sample where OMRON PLC is MASTER for THREE (or more) SLAVES. I'm attaching code file... Thanks. Best regards, Andrej. Modbus_TCP_FB.cxp Modbus_TCP_FB.opt
  12. Hello out there   I've searched for quite some time but unable to find any information helping me through this. I got a Omron PLC NX1P2 where im supposed to setup modbus communication over TCP/IP but so far i've only been able to find information regarding RTU setup. But seen forums mention its possible to setup via TCP/IP Anybody who can help. A program sample would be helpfull aswell. Im a trainee as automationengineer and this is my first encounter with Omron PLC and Modbus so quite new to the field.   kind regards Ivan T.
  13. Hello, We have a FX3G connected to a FX3U-ENET-ADP inside a main cabinet. We are then using that master PLC to collect data from 2 other fx3g plcs in a node:node serial network. I was assigned a small project of pricing out some wireless adapters so we can upload/download to the two slave plcs. My question is, is it possible to upload/download programs to/from the slave plcs through the ENET adapter and serial network in the main plc? It would save us some money if possible. thanks.
  14. Hello!  I was trying to set an value on "d" register to use him like a parameter. We are talking of connections of m0 on the next image:   the system works as follows: when pressing a button (M0), it moves the variables typed in the HMI (D14 and D16) to D10 and D12, at the same time that it takes these values and generates the parameter of minimum (D8) and maximum (D60). And its works perfectly, at least while on. When the clp is turned off and on, the variables are reset to zero, even if the only way to change the values is to press the set button again. What can I do to make it keep the information that has been moved?
  15. Mitsubishi PLC with Fernhill SCADA

    Hi, Has anyone here has experience of using Fernhill SCADA with Mitsubishi PLC FX3U Series? I want to monitor PLC's data in real time through FX3U-ENET-ADP ethernet adapter using Fernhill SCADA software. Thanks in advance for the answer.
  16. Hello, I'm trying to connect a CJ1M-ETN21 as slave Modbus TCP with a Modbus/Dali Gateway. I download from Omron website some FB with ones should be possible.   https://www.myomron.com/index.php?action=kb&article=1245 The FB only can be used with the direction unit 0, but we can change some directions inside the FB and can be adjusted to other units. In the download I found this FB: MTCP_ETN_Connect, MTCP_ETN_Fn01, MTCP_ETN_Fn02, MTCP_ETN_Fn03 .... Supposed with connect we can establish the connection with the master, but the FB never make nothing. Should I make some special configurations to use this FB? I appreciate any help. Thanks
  17. Indusoft Web Studio

    i am using indusoft web studio for the modbus logging. program runs successfully but after a half day or a day it shows error " error initializing the driver modbu 10.10: invalid serial port "any suggestion will be appreciated.RegardsZubair Ahmed
  18. Modbus with CJ1W SCU31-V1

    Hi every one, I want communication Inverter mitsubishi D700 with module CJ1W SCU31-V1,  any one give me a correct solution and send any sample program. Thanks
  19. I'm trying to communicate with INVT PLC and DGM8002(grain moisture analyzer) via mobus RTU.   Can anyone explain about these Modbus address ? Please kindly see in picture . example working mode address K0 (0-stop ,1-manual,  2-Auto) Actual Moisture Address K6 What is meaning of K0,K1,K3,K6.  https://drive.google.com/file/d/1-mGzpEvw4UlewWhR9k3wOd1mO-uhsklL/view?usp=drivesdk Is that K0= 0000 K2 = 2000. K3=3000 ? Any suggestion please. I'm really appreciated your comments.❤️  
  20. Error Indicator on FX3U-ENET-ADP

    Hi all, I have finished installing ethernet adapter module FX3U-ENET-ADP on the FX3U-48M PLC. From the ethernet module, i connected it to a wireless router and then i am planning of connecting to the ethernet module using GXWorks 2 on my laptop through wireless router. On the ethernet module, the error indicator LED is on (red). From the FX3U-ENET-ADP, it means that there might be setting or hardware errors.  I am asking if i have missed some steps on the installation process and if any of you have experience with similar problems. Thanks in advance for the answers.
  21. - i'm from VietNam, Who can help me?? - I cannot communicate the RFID card reader with the FX3U PLC using the FX3U-485ADP-MB module; - register error D8438 = 3821; D8423 = 1025; D8422 = 212. - Here is the connection picture and my PLC code thanks !!!!
  22. Hi all,  I want to ask some questions regarding Ethernet Communication with FX3U PLC series. I have 2 PLCs of FX3U series (FX3U-48M and FX3U-64M) and I want to monitor its data (input and output) using ethernet communication in real time. My questions are: 1. Does FX3U PLC have ethernet port so I can connect it directly to my Laptop/PC? 2. If no, do I need to use FX3U-ENET-ADP and can it be used for 2 PLC or only 1? 3. What software do I need to use to configure the communication between PLC and FX3U-ENET-ADP? 4. Does this configuration change the existing PLC program? 5. Can i transmit the data wireless-ly using some kind of ethernet to wifi adapter and what additional hardware do i need for that?  
  23. Q03UDVCPU Modbus Setup

    Hi Guys, I need help to set up modbus tcp/ip parameter for Q03UDVCPU, i want to use the predifined protocol and built in ethernet port. do you guys have some usefull references how to setup modbus tcp/ip, or is there any example program from mitsubishi? Thanks
  24. Dear Engineerds,   My Master (non siemens) doesn't see the Holding Registers of the Slave (S7-1200) plc. However the Q coils are fine and all Diagnostics don't show errors. The Hardware: S7-1200 – CPU 1215C CM PtP – CB1241 RS485 (6ES7 241-1CH30-1XB0) - Half Duplex RS584   Firmware: Modbus_Comm_Load (V3.1) Modbus_Slave (V4.0)   I've tried with various DB, UDTs and manipulating HR_Start_offset parameter with no success. Could you advise what am I possibly missing? Modbus_Comm_Load_DB_Snapshot.xlsx Modbus_Slave_DB_Snapshot.xlsx
  25. Designed a SCADA System using VB.NET. Everything working fine but coming to performance getting 2 to 3 seconds delay. Using FX3U32m Plc with ENET Module for Data reading and writing. I am having 200 addresses to read. Using MX Component as communication interface between PLC and SCADA. Is there any alternative or solution for this problem. Using one timer to read all data and update properties based on received data.    Thank you..