Search the Community

Showing results for tags 'Control VFD from S7 1500'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 122 results

  1. Beckhoff Control panel testing?

    I am a technician at a large repair facility and we often have Beckhoff control panel displays come in for repair. I'm having trouble using Twincat to set up the buttons on a CPxx to test the buttons and assignable leds. We have a PC running windows XP with the twincat software, a CP9035 pci card to connect the CP to the pc, i can see the PC's display on the CP and also recognize the CP in twincat, just unsure how to map testable functions to the keys on the CP. Hope this all makes sense. Hopefully there is a Twincat guru out there that knows how to do this. Thank you!!
  2. Ground Loop

    Hello everyone, I have a quick question regarding Din rails, chassis ground and ground loops. Here is where I am getting confused. I connect my back panel to earth ground which, connects my control panel chassis to earth ground. I screw din rails on my back panel. Question #1: logically, my din rails are now connected to earth ground through the screws connecting to din rails to the back panel. Am I wrong here? As I have seen in many control panels, I connect a ground terminal block to my din rail and connect it to earth ground (the terminal block couples with the din rail through metal clamps). I now use that ground terminal block as a single point source to ground all my other components in the control panel (I connect my ground terminal block to earth ground using a wire).. *** the ten thousand dollar question is Didnt I just create a ground loop between my ground terminal block mounted on the din rail and my back panel chassis ground. For one reason or another the two different location might be at slightly different potentials causing current to flow. Where is my logic off here???? Thank you
  3. Hi, I was wondering if there is a way to limit the number of allowed on-line connections at a time to a PLC? Like can you somehow set in the PLC parameters that only 1 'connection' can be on-line in the device at a time? Thanks Edit: I'm referring to connections from the TIA portal - not HMI / ethernet connections and so forth
  4. hI.. I've asked for this in the past and, so far, haven't been very lucky.  Most of the projects I run into have 4 or 5 axis, lots of analog and sensor input.. or don't have the HMI part of the "Machine" I have a nice NJ 101-1000 with the NA 7 inch HMI.. along with a R88BD-KNA5L-ECT servo and a 50W  G5 motor.. type  R88M-K05030H-S2.  All On a nice rack with power supplies and some EtherCAT I/O  (It all functions .. even "MC Test Run" gets the motor to jog ..    But.. no way to "home" it.... The motor is in "rotary mode"   but... it's NOT got an Absolute encoder.. it's a incremental... sniff!     I just want it to stop on zero ..Or anywhere, and call it zero ... and make moves plus an' minus in degrees, that's all....  I assume I have to send it some signal (push button) while it's spinning that tells it it's in "Proximity" to home and it then it does something which makes it end up on zero.    I've homed a lot of linear motors (LinMot) an' they are very easy to work with.    But, Omron has 10 different homing modes .. and they aren't very well explained.  Well, they aren't explained at all in that 502 page user manual... you have to already know how to do it, in order to understand the explanation... Example:  Take the "Home Proximity Input Signal"  .. I can imagine what it might do, to help control a move to home.  I can even imagine what's making the signal .. and that somewhere there is a place where the homing parameters are set... like the "axis setting table"  .. but, it's not a Global Variable, or a Data Type .. I could imagine it gets into the system from the CN1 I/O connector? or some I/O somewhere? But.. I grow weary of imagining how this system actually works..  Building a simple working project, from a tutorial, or even downloading a simple working project (.smc2 file) and making the minor adjustments to fit my equipment ... would make all the difference in the world.   I've searched Omron's Libraries of .smc2 files.  Haven't found any yet that aren't on the level of "Top Gun" (a seriously complicated project for a 1-week training class) ... Oh there are several.. related to IAG object files .. but those Library files are not "working projects" intended to serve as a Tutorial.. they are limited projects, ready to be configured with IAG Object files, and "your" programming ... So that you can write the programs you need "faster"... which is nice... but, no help here. Somewhere out there.. is a nice simple .smc2 project file where you get to control a simple motor from the HMI  ..Preferably using an NJ CPU and a NA HMI .. home the motor.. jog the motor and input a few "go-to" positions... sigh!..   Like you would do in a One or Two Day class...   This kind of thing should be already be available in the Sysmac Library ... Thanks much for listening..  sorry about the rant.  
  5. schneider somachine

    hello everyone,  Im new with schneider electic , ı m planing to work with Altivar 630 variable speed drivers and i want to control it with M241 plc in somachine . but when i want to configure in somachine i could not add the driver to my hardware. is there any document about it ? or does anybody control it like this ? 
  6. Hello all I want to know if is possible implement the standard IEC 61499, for distributed control, in a PLC Micrologix 1500, this standard proposes use function blocks, but this blocks are different to the blocks proposes for the IEC 61499
  7. Temperature controling with module

    Hello to everybody! This time I need to make a program to control temperature ... Some help? I don't know how to use an analog module, I'm just starting to working with them. The PLC I have a FX3u-32MR/ES (Mitsubishi), and I have the modules; FX3u-4AD-ADP and FX3u-4AD-PT-ADP for temperature measurement. PLEASE HELP? Have a good day!
  8. i need a example code for position control of MR-J3-20A with QD75D4 as intelligence module. and i want to see the parameter if possible  
  9. EMS provides low cost analog sensors useful for PLC analog inputs. For example the $25 temperature sensor (+/- 2%) is a useful and inexpensive way to monitor for an over temperature condition in a panel cabinet. emssensors.com AC voltage and current transmitters can be a useful way to monitor motor performance. Even the sound level sensor can be a good way to generate an alarm condition for a bearing failure.
  10. We are replacing the Old hardware from PLC to new Control logix hardware. wondering Application of IEC-61508 and IEC-61511 compliance in this brown field project. Any Thoughts ??
  11. We have a Panelview Plus 600. One of our panels is labeled "Motor Control," in charge of turning on/off different pumps. The problem is while the system is running, clicking the on/off button will not turn any pump off. When the system is shut down, the pumps can be turned on and off but not when the system is running. I'm trying to shut off one pump without shutting the whole line down. Any help is appreciated. Thanks.
  12. We have a Panelview Plus 600. One of our panels is labeled "Motor Control," in charge of turning on/off different pumps. The problem is while the system is running, clicking the on/off button will not turn any pump off. When the system is shut down, the pumps can be turned on and off but not when the system is running. I'm trying to shut off one pump without shutting the whole line down. Any help is appreciated. Thanks.
  13. Elecrical Control Panel

    Which type of electrical panel is most reliable, give some idea about that ..?
  14. PCS7 with S7-410 for Dummies

    I just need to understand a little bit more about the PCS7 architecture, if someone could point me to a document or a video or something, or just give me a few sentences to break it down it would be greatly appreciated. The reason being, we have a quote that we are working on for a customer over seas and are being told to quote our equipment with an S7-410 PLC.  I am very unfamiliar with Siemens in general, but completely unfamiliar with the PCS7. Our equipment is typically if not almost always stand alone equipment that communicates discretely to the rest of the facility.  Our equipment is not part of a process line, but rather feeds the process line equipment what it needs to perform its operation. I have been led to believe that the S7-410 PLC must be part of a DCS, so it does not seem like the correct fit for our equipment.  I just want to confirm this and learn a little bit more so I can explain to our sales folks and ultimately the end user why it is the wrong option for us and our type of equipment.   Thank you!!! Heather  
  15. Hi Everyone, I have a PowerFlex 525, in Velocity Mode with a Encoder Card "25-ENC-1". We are controlling this drive via TCP/IP with a 1769-L32. Through the PLC if I try to toggle the Bit for "Pos Redefine" in A560 [Enh Control Word] it instantly turns back to 0. But through the Parameter List Editor I am able to toggle A560. For My function I need to have the drive in Velocity Mode, If I change the drive to Position Mode I am able to toggle "Pos Redefine"   Any Thoughts would be great      
  16. Hi guys, been using this site for a long time, it has come in handy alot. However I have recently taken on my first servo project, heres an overview of the project We have a filling machine that has a separate dosing system to the filler head. It used to keep the dosing in time by adjusting a 0-10v signal to an inverter to make sure that a flag makes a sensor in a set window. I have installed an encoder on the filling head and an mpl servo to the dosing. I have then used an MAPC instruction to follow the encoder, the cam is 0-360 and it follows a straight linear line. I have installed of this as a temporary set up on one of the filling machines (we have 2) and it is working perfectly. I have now installed this on the second machine as a permanent set up with a panelview plus 7, L71 cpu. However it is giving a very strange problem on first power up, the encoder is giving the exact same position as before it was powered down. however as soon as the MAPC executes the servo axis  faults, giving an overspeed fault. the servo doesnt even look like its attempting to move (however it is through a 10-1 gearbox). if i then home the encoder it then runs absolutely perfectly until it is powered down again. I am beginning to think it may be to do with the master lock and cam lock position, as the cycle stop position of the two machines are different. however I just cant seem to get my head around i the difference between them.   Hopefully that makes sense any help would be greatly appreciated Thanks Rhys   c1_dosing.ACD
  17. Hi, Is there any setup to manage alarms in one PLC from multiple CX-Supervisor runtimes running on different computers? If I get an alarm, it shows up on both runtimes. If I acknowledge from one runtime, I also want it to be gone from the list in the other runtimes.
  18. Hi All. i got a problem when accessing local reporting service website using microsoft web browser control at HMI. it showing only half of page. when i open the website from internet explorer at same server where i develope HMI, i got no issue. please your advice. thank you.
  19. FC1 Two hand anti tie down

    Version 1.0.0

    130 downloads

    Logic takes two inputs (I0.0, I0.1), debounces each (T0, T1), looks for actuation during a timed period (T2), and provides validation (M20.0). This logic is not designed, nor intended, to replace the use of any OSHA required two-hand safety control relay. It is provided for the sole purpose of it's educational value.
  20. FC1 Two hand anti tie down View File Logic takes two inputs (I0.0, I0.1), debounces each (T0, T1), looks for actuation during a timed period (T2), and provides validation (M20.0). This logic is not designed, nor intended, to replace the use of any OSHA required two-hand safety control relay. It is provided for the sole purpose of it's educational value. Submitter pop29684 Submitted 03/22/16 Category PLC Sample Code
  21. I need to learn about position control for 2 axis with a QD75MH2 module. I know how the basics about programming with the Q Series PLC but I've never done any positioning control. I'm having a really hard time understanding the program I have to modify and I don't know where to start. Is there any course you might recommend? Even if I have to pay for it. Thanks.
  22. S7-1500 HW Interrupt

    Hi Guys, I'm still here asking your help because i need to reproduce a previous work that i did on omron series. Now i'm using a Siemens 1510SP-1PN CPU, with a DI 24VDC module assigned in the first slot. I would like to know how to call an interrupt task every time that a rising edge on E0.0 and E0.1 occurs. I  have configured the I/O settings of the module, to call the OB40 hardware interrupt block, but unfortunately i don't know how to assign the addresses to a specified OB, otherwise i noticed that if this option is enabled, instead of the default settings, the CPU can't see the input addresses rise up or turn on; If i configure back the default settings i can see again in a variable table the address E0.0 turn on, why this happens? Is this meaning that i can't use this address for other tasks or other functions? Can i call a hardware interrupt or something like that with an internal variable like a merker? What instructions i must use to enable and activate the OB40? Thank you! Best Regards.
  23. PAROCK1 for HMI/SCADA View File Now a software solution is available for your Modbus (MB) needs in Rockwell/Allen-Bradley Control Logix or Compact Logix (Clgx) family processors, instead of a traditional 3rd party hardware like Prosoft MVI-56, Molex SST-SR4-CLX-RLL etc.  It is an Add-on instruction (AOI) for PLC/PAC firmware v16 or later, (other solutions are available for pre v16 systems).  For hardware interface, use PLC’s channel 0 (serial) or TCP/IP Interface module(s) to have as many MB TCP/IP devices or serial devices.  (Some limits apply based on system configurations, Comm. settings depending on HW used.) Connect any MB Client/Master or Server/Slave device(s) to your CLgx PLC, including flow computers, analyzers, VFDs, Power Monitors, Level gauges, Smart I/O, etc.  All the MB public/native function codes are supported.  32-Bit integers/floats as single entity are supported with byte and word level swapping. A separate utility automates the data mapping to your PLC logic.  Features -Serial Master (BASIC required Option); TCP; Slave; Redundancy; More than 5000 accumulative registers; MB CFC (Custom/Private Function Code) Support; Data mapping too – Between PAROCK1 & your PLC logic; Packaged with Rockwell; TCP/IP Interface Module; Volume Discounts; Annual Support Requirements -Rockwell/AB-CLgx processor with v16 or later.  Contact PCI for earlier versions. -If using CPU’s Chan0, you cannot use Chan0 for any other user mode activity. You can use it for non-user mode activities -TCP/IP Interface Modules from Rockwell/AB supported, are: -1756-EN2xx ControlLogix® Ethernet/IP communication modules, firmware revision 5.007 or later -1756-EWEB ControlLogix Ethernet/IP web server module, firmware revision 4.006 or later -1768-EWEB CompactLogix Ethernet/IP web server module, firmware revision 1.002 or later -1769-L30ER, 1769-L30ERM, 1769-L30ER-NSE, 1769-L33ER, 1769-L33ERM, and 1769-L36ERM CompactLogix controllers, firmware revision 20.011 or later -1769-L24ER-QB1B, 1769-L24ER-QBFC1B, 1769-L27ERM-QBFC1B CompactLogix controllers, firmware revision 20.011 or later -1769-L16ER, 1769-L18ER, 1769-L18ERM CompactLogix controllers, firmware revision 20.011 or later Other Related Services/Items -Custom PLC Add-on instructions building -PLC upgrades, troubleshooting, applications -PC Windows, iOS5, Linux, Mobile devices Comm. Drivers -Custom development, Technology Transfer Services  -Other Non-AB communication drivers for serial or TCP  -Full control system integration, training, architecture design This driver can be conviniently used with Visual Studio in development of complete large scale complex HMI/SCADA Systems. It can be used to perform advanced reporting MES, analytics, IoT, Big data type apps. One example is available to download here For More Info Overview of Parijat Drivers: Click here  Additional supporting Info about Parijat Drivers:Click here Complete Related Driver options: Click here     Submitter Scadadoctor Submitted 03/10/16 Category Other PLC Demo Software
  24. C200HW-MC402.pdf View File C200HW-MC402-E Motion Control Unit Operation Manual Produced June 2001 Submitter IO_Rack Submitted 03/09/16 Category Manuals