Search the Community

Showing results for tags 'Control Logix 5000'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 220 results

  1. Hi! A have a question about how can I send the current User data from the Panelview (HMI) to the PLC. Its an allen bradley PLC 1756 L71. In the Factory Talk view I tried to make a register and to move in it the current user, but unfortunatelly its not working. Is anybody here who can help me with this ? Thanks ahead. Br.
  2. Dear Team,   We are looking for a suggestion to drive a motor which is away about 2100 Meter from its starter. The Pump is located in a pond in the forest which is 2000 Meters away from the nearest building. The pump capacity is 55kW and we are considering 55kW HD VFD as a starter. As we see the distance is much higher we are looking for you valuable suggestion about how this thing is gonna work without any abnormalities.
  3. I have just started my youtube channel The Control Philosopher wherein I will regularly post topics of interest to people in this Automation community. So far, I have posted just 4 Videos  1. Connecting PLCs to MCCs  How to safely interface PLC IOs to Motor control Centres 2. Understanding the Basics of VFDs Part-1. The Very basics 3. Understanding VFDs Part-2 Covers Load Types, Energy saving principles 4. Understanding VFDs Part-3 Covers Selection, Configuration and Harmonics
  4. I want  increase the length of string from 82 to 150. By default it comes 82 is it possible to do so in Studio 5000
  5. Problem: I am getting a control sync fault on 2 recently installed kinetix 5500 but only when my programing PC is connected to the machine network.  Install and setup all went great over a 5 day period.  Then all of a sudden I started to get this fault. Sometimes 100 times in an hour.  As soon as I go offline, and unplug my PC the problem goes away.  I have also tried another PC connected to the Machine network and still get the same result.  Sometimes machine can run for hours with my PC connected with no problem.  I do not have to be online with controller for fault to occur. Setup: I have the 2 K5500's ethernet ports daisy chained together, and then connected via shielded CAT 6 cable directly to port 2 of the Compact Logix Controller Coarse Update is set to 3.5ms and utilization's are at 33% and below.(I have tried the default 2ms with same results) Ethernet modules are configured with FW rev 7.013. Machine network is isolated.(not connected to plant network or internet) Equipment: Compact logix L33ERM Running version 30.01. There are a total of four servos in this system all running over ethernet.  2 Kinetix 350's(not affected), and 2 kinetix 5500's. I have tried: separate ethernet cables for each drive ran through a switch different ethernet cables resetting coarse update speed connecting a different PC for programming   I am just not sure where else to go with this.  Thanks in advance for any help.  
  6. I have some older RSLogix 5000 software I would like to run on a newer Dell 64bit laptop. It's RSLogix 5000 V13.03.00. I can buy a full Windows license for an older Windows OS and not connect to the internet. What OS was my RSLogix 5000 software originally designed for? Was V13 a 32bit software?
  7. Hello everyone, I'm facing an issue while trying to go online with a PLC. The firmware revision of the controller is 34.011, but the offline project I have is showing a firmware revision of 33.xx. Due to this mismatch, I'm unable to establish a connection. I'm relatively new to this company and recently learned that the program on my computer may have been modified by a contractor company, which might explain the version difference. I suspect they may have used a higher version of RsLogix when making the changes. I'm looking for guidance on how to proceed in this situation. Is there a way to update the offline project's firmware revision to match the controller's firmware revision? Or is there another solution to resolve this compatibility issue? Any help or insights would be greatly appreciated. Thank you!
  8. Hello everyone, I'm trying to import the I/O module configuration file (extension XHW), but this option is blocked in Control Expert. I'm trying to import an existing configuration file so that I don't have to reconfigure the I/O boards manually. Does anyone know how to enable these import and export options or is there another method to import the file? Thanks 
  9. I have this hardware configuration of an extension rack for a M580 PLC projet using EcoStruxure Control Expert I export the.XHW file by following the procedure below: https://www.se.com/uk/en/faqs/FAQ000256454/ And I am trying to rename the DD1602 card using the file, however, when I rename the card as a show in the next image (selected in green), and re-change the file to the .XHW extension, when I re-import it into Control Expert, I get an error saying: unknown fatal exception, even though the only change I've made is to the name of the card. I know I can rename IODDTs instances manually in Control Expert, but in fact I'm trying to automate the process of renaming IODDTs because I have a lot of IODDTs to rename, which is why I thought of using the XHW file. Does anyone have an idea of what I could do? Thanks in advance
  10. I recently had surgery on my arm. I'm in a cast from finger tips to shoulder.  I have a major Logix 5000 program to write. Has anyone used Win10 Speech Recognition to operate Studio 5000? I tried today and it didn't work out well! Any suggestions?
  11. Hi everyone, I have a question for you all, Is possible to configure CJ2M-CPU11 with tags trough network configurator to connect Control Logix PLC using EthernetIP? I did a configuration with CJ2M-CPU31 and Control Logix PLC with no problem, but now I need to communicate CJ2M-CPU11 with Control Logix PLC using EthernetIP. Some of you did this configuration between this two PLC before? Regards!
  12. Hello everyone,   I'm seeking recommendations for training programs or resources focused on building control panels. I have a basic understanding but want to enhance my skills in design, wiring, components, safety, and troubleshooting.   If you have attended any reputable hands-on training programs or know of online courses, I would greatly appreciate your suggestions. Any personal experiences or tips are also welcome.   Thank you for your assistance!   Best regards,
  13. Hello,   I'm seeking some guidance and assistance regarding an issue I've encountered while configuring a Proline Promag W 400 flow meter module in Logix Designer. I'm experiencing the following error:   Error Code: 16#0009 Fault Additional Code: 16#0000 Fault Description: Module Configuration Rejected: Parameter Error   I've carefully reviewed the module documentation, verified the wiring connections, and ensured compatibility between the flow meter module (Serial Number: T711F49000) and Studio 5000 Logix Designer (Version 33.00.00 Full Edition). However, I'm still facing this parameter error during the configuration process.   I've also attempted to access the web service provided by the flow meter module to view its configuration and parameter settings, but I haven't been able to identify the specific cause of the error.   I would greatly appreciate any insights or suggestions from the forum members who might have encountered a similar issue or have expertise with the Proline Promag W 400 flow meter module and Logix Designer. Specifically, I'm interested in any troubleshooting steps or guidance that could help resolve the parameter error and successfully configure the module.   https://files.fm/u/brm2ebkry
  14. I have 2 vm’s, 1 with FactoryTalk and 1 with Studio 5000 and Studio 5000 emulate and I need the Factorytalk to communicate with the emulated plc on another vm and wondered if this is possible.
  15. Hi from Colorado, Panel Builders @ MRPLC~ I bought a custom 508A assembly from a UL shop (277/480v 3 phase). The prototype didn't work out very well so I'm revising the design for next time. Before I present my "red line" revisions to the fabricator, could someone advise if I'm OK to simplify part of the work in a particular way? I just need to make sure my simplification doesn't run afoul of the 508A standard. My clients requested that a ten watt 120vAC amber LED (distant from the 508A cabinet) should light up whenever the 3 phase bus is energized. The panel fabricator provided an SSR solid state relay to close whenever 277v shows up across the "input" terminals & they fused the 277v hot for the input so that's all good. The "output" terminal is "single pole normally open", rated for 10 amps. The power that I'm sending in from outside the cabinet is from a small UPS system where the inverter is rated for 250VA's--so it can't deliver more than two amps @ 120vAC.  It seems to me that I don't need the series fuse that the shop provided to protect the 10 amp rating on the SSR--since my input power is already current limited. It also seems that I don't need to bring the associated single phase neutral wire into the 508A cabinet at all--since the neutral is never switched & it's doing nothing inside the 3 ph. assembly. If I revise the drawings along these lines, I'll eliminate two terminal blocks, a cc fuse/fuse holder & some wire...and this part of the assembly will be simpler & more intuitive.  Basically, I want to treat the SSR like a switch leg for the light, running only a 120v hot wire to & from the SSR output terminals. I don't want to revise the drawings, however, unless I'm sure the fabricator won't have to change them back to comply with UL 508A. I don't own the UL "standard" document & I don't know the peculiarities...but I'm sure some of the forum members do.  Should I add signage to explain that the 120v hot must be current limited or OCPD protected before it enters the 3 phase cabinet? Thanks in advance for any coaching or suggestions.      
  16.   Replacing dead powerflex 700 with 753 talking via ethernet. Any good instructions on how to update the file from 700 to 753 on rslogix 5000?                                    
  17. I have a new PC that is running Windows 10, I have RSLogix 500 loaded and working no problem, along with RSLinx, Factory Talk Activation... etc. I also loaded the Studio 5000 package and it loaded without a problem however will not run. It starts and allows you to pick a project to work on, then will display the Logix 5000 splash window for a second, then just close. No error message, crash or idea of what it is doing, just closes. So far no help from AB, perhaps someone here is running this on Windows 10 or has an idea how to figure out why it is closing. Thanks
  18. control panel for sale

    Hi all, Hope everyone is doing well. I'm currently in the process of starting a home based control panel shop. I have about 8 years of control panel building experience and about 2-3 years of being shop team lead/design engineering. I have been planning this for years and now I have my shop full of necessary tools and material to build small/medium sized panels. I have gone through all the training and examination(which was not easy) to be able to produce UL508A approved panels. My goal is to produce a steady work load with great quality. Now I just need an opportunity with customers which I find to be the hard part. I have been contacting local industries but haven't had any luck. If anyone out there is seeking control panels built at a good competitive rate please advice.
  19. We are seeking a Control Panel builder in the SE Michigan area. We can supply the drawings, components, enclosure, etc. Typical panels include PLC, HMI, VFDs, and standard components. Please contact us if interested. We can send more details as needed. We typically need 20-30 panels in a year.
  20. Hi, Does anybody know if its possible to access the "Inhibit Module" tick box within the Hardware Device Connection tab from the PLC code? I'm hoping to turn this on / off depending on whether certain modules of machine are physically installed.  e.g. A Kinetix Drive / Point IO etc. Thanks
  21. Hi All, I'm new to using PLC, and my background is majorly programming. I am learning how to control a PLC over the internet using HTTP or TCP/IP. I have a Mitsubishi PLC Melsec FX-5U 32MR and my requirement is, I want to send create a setup where the PLC works more like a Client on the network and reads values from the server (which is a computer). The outputs on the PLC are controlled by the values on the database in server.  So, lets assume I have a value like this on the server "1,0,0,1,0,1", it should translate like below: Y0 = 1 Y1 = 0 Y2 = 0 Y3 = 1 Y4 = 0 Y5 = 1 Is there any guidance where I can read through and learn how to do this. I would prefer doing it by ST programming and not Ladder.
  22. Hi  I am working on a project in Studio 5000 with 5069-L310ERS2 controller.  How can i simulate the program with RSLogix Emulate 5000?  and When i try to add a new module in RSLogix Emulate 5000 it is only possible to choose version 20. When working in Studio 5000 v32 should I not be able to choose version 32?  Thanks  
  23. Logic issue, or problem with Control Expert 14.1?   Pop-up box, followed by Control Expert crash.  PLC seems to be running fine. "Control Expert Fatal Error" "The thread tried to divide an integer value by an integer divisor of zero" Anybody seen this before?  Corrupt file?  Reboot?  Uninstall/reinstall?
  24.  I've been debating whether to stay at my current employer who uses Emerson PAC software, vs going back to a similar company that uses Rockwell (compact/control logix) mainly because A-B is used by most companies around here. I work as a technical temp, usually 12 month contract jobs. Learning the Emerson PAC (aka Prophecy) seems to be a waste of time, since I am not aware of any companies that use it, other than my current employer. My placement company is pushing back, but I know I am correct. I do not have hard numbers, but I've been around the industry for 20+ yers, and have only seen 1 company use Emerson.   Does any one agree or disagree, or have some circumstantial evidence of the actual market share of A-B vs Emerson. I am mainly working in the Auto industry, in Michigan. Just looking at this site, there are 3200 postings for GE and Emerson combined, vs 58,000 postings for A-B. 
  25. Hi guys!  I have several questions connected to kinetix 6000 servo amplifiers. I have a system with AB plc and AB kinetix servo drive. The communication is sercos. Earlier I was worked drives with ethernet communication. I think its better, I could monitor the parmeters durnig as its works. But with the sercos communication I am no longer to be able to do it. One of my question is that like it is possible to check the parameters somehow. I have some problem myabe with the overcurrent recently. But for now I even cant see what is the limit. Is it possible to find it somewhere ?   Also when Im watching the parameters in the RSlogix 5000 which is belongs to the servo drive. I can see a row like (servoname)axis fault code and (servoname) axis code. Is there any table where I can see which number belongs to which fault or status?  If anyone can help me I just appreciate ahead. Thanks Guys.