Search the Community
Showing results for tags '1769-of4ci - output always @12ma'.
Found 59 results
-
Hi, New to the forum and pretty new to PLC programming. I took the 3-day Sysmac training a couple months ago, but just recently set up one of the NX1P2 units that we'll eventually use for a robotics application. Right now I've got it set up just to experiment with, so I have 3 physical switches (1 momentary, the other 2 toggle) and 4 indicator lights hooked up. Ladder program is set up to light up different LED's when the momentary contact switch I_SW1 is pressed, based on the position of the other 2 switches. Here's the issue: When both of the toggle switches are ON (see lines 4 thru 8), all of the LED's light up as expected as soon as the momentary switch I_SW1 is pressed. However, if either or both of the toggle switches are OFF (see lines 0 thru 3), even though it seems like the logic is correct, nothing happens on the output. Lines 0&1 were modified as shown to see if using the variable O_Light1 instead of going directly to O_L1 output would work, but it didn't make any difference. See attached images for example of working and not working ladder sections as the momentary switch is pressed. In the "working" image, both the toggle switches are on. In the "not working" image, both toggle switches are off. PLC's input & output indicator lights match what Sysmac is showing in the monitor screen, so I'm pretty sure it's in the ladder logic and not the physical wiring. Thanks for any advice.
-
Hi I have servo motor controlled by smartstep 2 and controlled by PLC with pulse output. Origin search I have set as below Sometimes I have problem with correct home position. Normally when original Input signals become ON drive slows and after 1 cm I have home position due to slowning ramp, but somtimes drive stops immediately on the edge of original input sensor. I have no idea why it is like that. Maybe you can advise sth or get some clue thanks in advance for any help
-
Hi all. I have a 1769-IT6 thermocouple/mv input module. It is connected to a micrologix 1500 unit. The green okay light illuminates on power up, but after you download the program and put it in run mode the processor faults. Terminal block with the cjc's are on the unit. The error message just says the I/O module has encountered an error. The hex code under status bit 6 is 179h. This error code is not in the manual. Has anyone else encountered this? Oh and I only have channel 0 enabled for type k thermocouple. Has anyone else had this issue, or know if it is a configuration issue. Any help would be appreciated. Thank you.
-
How to connect to a PLC from Studio 5000 on a VMware
NewEric posted a topic in Allen Bradley / Rockwell Automation
Hi and thanks for youre time I am a newbie trying to connect to a 1769-L30ERMS using an Ethernet cable. I am using Studio 5000 and RSLinx Classic lite for programming and communication. However Studio 5000 and RSLinx Classic lite are installed on av virtual machine using VMware. So my problem is two fold. Connect the VM so that it reads from the real computers ethernet port Find and communicate with the PLC from the VM There are guides on how these problems are addressed seperatly. For example https://www.youtube.com/watch?v=JdArYVceO1I and https://www.youtube.com/watch?v=ERLTvcBBK_w however I have not been able to get them to work together. So I was wondering if you, the sages of PLC programming might have some tips or trix that I could test or perhaps even a guide for how to do? Mvh Eric- 3 replies
-
- studio 5000
- vmware
-
(and 2 more)
Tagged with:
-
Hi One of my friend want use more analog output on his vfd. Its a Mitsubishi FR-A740 type. Currently the AM signal is for current, but he needs the speed and frequency too. As we saw its only one analog output is avaiable, but you guys might know better. Can someone confims our theory. Thank you.
-
Micrologix 1400 1766-L32BWA-"Burnt" Output
robmx57 posted a topic in Allen Bradley / Rockwell Automation
Hello, I am trying to flash an indicator light (Banner K70LBGYRPQ ) every .5 seconds. The PLC manual says 2.5A per channel. The light uses roughly 113mA max current @ 24vdc. I am using output 0 to do this (O:0/0). I think I may have ruined the output by flashing the indicator light. Has anyone ever experienced this before? Is there a minimum pulse time for this PLC? What do people normally do when wanting to flash an indicator light such as this? This is not the first time I have seen this happen. Thanks in advance!- 7 replies
-
- relay output
- welded
-
(and 3 more)
Tagged with:
-
Hi,I want to read transducer signal on PLC.I am using 7kg60008ab/nn transducer and it's analog (4-20mA) output is connected with analog meter.Can I connect the transducer current output (4-20mA) signal to PLC analog input in series with analog meter display???So that I can read the value on PLC simultaneously with analog meter?
- 3 replies
-
- analog input
- analog output
-
(and 3 more)
Tagged with:
-
Hello to everyone. Nice to meet you all. How are you? I hope you are doing well. I’m developing a program with the purpose of make something similar to a pulse train in the output. However, sometimes I need the output to be a “positive” pulse and sometimes a “negative” one. By positive and negative I mean the polarity in relation to the pulse train source. I’m trying to use a pair of bits in order to switch between the two choices of polarities. I attach a simplified version of the ladder diagram I’ve made. When I thought about the logic, it seemed logical to me, however, it isn’t working as supposed. SM0.4 is a pulse train source. According to the software manual, it is a pulse train with 50% duty cycle and a cycle time of 2 s. That it to say it says at TRUE for one second and return to FALSE for another second. I assign the value of that variable bit to the M0.0 memory bit. I get the negative version of the pulse train logically negating it in the Network #2. I assign the value of two inputs, I0.0 and I0.1, to other two memory bits, M0.1 and M0.2. · When both inputs are in a FALSE state, the output stays FALSE, disregarding the state of SM0.4. (Case #1) · When I0.0 is TRUE, M0.1 is TRUE. However, Q0.0 stays at FALSE no matter SM0.4 is TRUE or FALSE. I attach a pair of pictures. (Case #2) · On the other side, when I0.1 is TRUE, M0.2 is TRUE. In this case, the output shows the correct behavior. It is the negated version of the pulse train source. (Case #3) Has any of you experienced something similar? Is there a better way to execute my purpose? I’m not executing the program, just simulating it with KincoBuilder from Kinco. However, it has always worked fine for me. Thanks for you attention. I look forward for your responses. Kind regards!
-
how many (maximum) analog inputs/outputs can CPU 1215C can reach without any issue?
Jairus posted a topic in Siemens
Hello guys, how many (maximum) analog inputs/outputs can CPU 1215C can reach without any issue? I try to search in google but can't find convincing answer. Thanks for your help. -
NX1P2 Motion Control change output device with code
BrunoRamos posted a topic in NJ Series / Sysmac Studio
Hi everyone, To explain the problem a little bit: I have 2 systems that are equal, they have 1 PLC, 1 Inverter and 1 Servo Axis (Image01). The devices are connected via EtherCat. The thing here is tht in these systems the PLC and Servo Axis is the same but the inverter is different. My goal is to have the same project on both systems and depending on the inverter detected use the correct program. What worked: If I add the 2 Inverters and 2 Servo Axis on the project on different nodes (Image02), I can detect which is present using the variable _EC_EntrySlavTb[n]. My issue is that if I want to make more replicas of the systems using different inverters I will eventually hit the Axis Number limit for the PLC while in reality I am only using on Servo Axis at a time. What I wanted: I would like to be able to control 1 Servo Axis with 2 different inverters (only one active per PLC) (Image03). What I tried: The axis parameters can be set using a variable of the type _sAXIS_PARAM, however it seems that the option to change the axis basic settings is not available (Manual: NJ/NX-series Motion Control Instructions Reference Manual (W508) page 5-58) (Image04). The axis basic settings is where the definition of the output device plus control words are set (Image05). Is there a work around to solve this issue? I would really like to avoid having to manually change the output device for the Servo Axis every time I make an update on all the systems. Best Regards, BR -
I am looking help with an issue I have trying to connect to a 5370 Controller 1769-L33ER. The controller firmware is 20.014 and my studio does not have 20.014 firmware. I have downloaded the firmware and do not know how to get it extracted to my PC. Any help with this will be grateful. Regards
-
tldr: How can I release/close CIP connections to a 1769-L35E CompactLogix (rev. 17.12)? Starting having communications issues with the controller out of nowhere - no recent changes, been running for years, etc. Tag update rates on the Wonderware InTouch sessions are really slow and could not get online with the controller until the Wonderware DAS was disabled, thereby freeing up a connection. Max number of allowed CIP connections is 32, but, per Task Monitor, there are 35 active connections. How can I drop all CIP connections so that only the valid ones come back? Anyway to do it without cycling power or going from run->prog->run? There are a number of cached message blocks, a 1794-AENT FlexIO Adapter, 10 other generic ethernet devices, and the connection to the WW DAS. Thank you for your help.
-
I have an analog output card 1734-OE2V. As a default, there is selected fault mode as 'Go to Low Clamp'. I am using output range -10V to 10V. What is the value for Low Clamp. Is it 0V or -10V? If I want it to be 0, do I need to select 'use fault value' and set the fault value to '0'.
-
Hi, we have a FX3U 128 PLC. I connect 24V to COM and all the output in the partition Y0, Y1,.. have 24V even if some output are ON and some are OFF. Why?
- 3 replies
-
- mitsubishi
- fx3u
-
(and 1 more)
Tagged with:
-
I need to use digital outputs of PF527 drive. Controlling the outputs, it does not do anything. Relay outputs are working fine, but opto outputs do not work. For the outputs, there are relays connected, using pin 6,7 and 17.
- 3 replies
-
- pf527
- opto output
-
(and 1 more)
Tagged with:
-
Hello Im using a 1769 HSC card with a L35E and trying to get the RPM. Ive been reading through forums for a couple days trying all the ideas from people who have had similar issues but I still cant get the current.rate(x) working. Im using a single channel encoder at 60ppr. I believe the card is set up right and the channel is enabled. The counter seems to work fine but the rate stays 0 when im spinning the encoder slow but will jump to 100 or 200 if I spin it fast. Any help would be appreciated. Thanks
-
Looking for some help that i cant seem to find online - I have a CompactLogix 5370 L1 Controller part number 1769-L16ER-BB1B and would like to connect a 1769-IF4 and a 1769-OF2 Analog expansion modules. Rockwell sales tell me they are compatible The Compactlogix looks to be a "slide in" and the expansion modules are Plug Type. Is there a cable or base rack I can use? Thanks in advance.
-
Activating PLC Output at the specific time - please help
MRPLC82 posted a topic in Allen Bradley / Rockwell Automation
Evening, I struggle with simple task... I need to activate PLC Output at the specific time of a day. I`m using GSV to obtain PLC time, data is being moved to DIN[7] registers. Then I have three EQU (Hour / Minute / Second) and at the end of rung there is OTL for output. Rung below I have two EQU (Hour / Minute) to disable output at different time - OTU. However every time OTL is energised , OTU on rung below is fired too. What am I doing wrong here ? -
Using NX-PG0232-5 to control Stepper Motor (NJ PLC)
ragzz1995 posted a topic in NJ Series / Sysmac Studio
Hello, I need to control a stepper motor(have stepper driver) using NX-PG0232-5 with NJ301 PLC. The function is simple, i need to run the stepper motor continuously at a specified velocity. So, in NX-PG module I've made the settings (Ch1 output mode as "Velocity continuous pulse output") and given the tags to IO (as shown below, sorry i'm not able to attach image). I've also added the initialization program to switch on the vfd. Now to move continuously i should should just give speed in pps in "PG_Ch1_Command_Velocity" right? Ch1 Controlword Control word 1 W WORD Ch1 Switch On Switch ON for pulse output 1 W BOOL PG_Ch1_SwitchOn Global Variables Ch1 Enable Voltage Start turning on the power for pulse output 1. W BOOL PG_Ch1_Enable_Voltage Global Variables Ch1 Quick Stop Immediate stop for pulse output 1 W BOOL PG_Ch1_QuickStop Global Variables Ch1 Enable Operation Start operation for pulse output 1 W BOOL PG_Ch1_EnableOperation Global Variables Ch1 Fault Reset Reset errors for pulse output 1 W BOOL Ch1 External Output Aggregated data of external outputs for pulse output 1 W BYTE Ch1 Command Position Command position of pulse output 1 W DINT PG_Ch1_Command_Position Global Variables Ch1 Command Velocity Command velocity of pulse output 1 W DINT PG_Ch1_Command_Velocity Global Variables- 6 replies
-
- nx-pg0232-5
- nj
-
(and 1 more)
Tagged with:
-
RSLogix 5000 BOOL Base tag not activating output
Kris Salmons posted a topic in Allen Bradley / Rockwell Automation
I have a Base tag of BOOL logic that will not activate the MOV output. The Base tag is paralleled with an Alias tag for a NO pushbutton. When the pushbutton is actuated it produces the desired output. Has anyone encountered this issue from a togglebit base tag before? Why would a base tag produce a different outcome from that of an alias tag that function properly? -
Hi every body, could you please help me; i have a mitsubishi plc serie iq-rwith the followings modules:powersupply r61p, r01cpu , rx40c7 inputs , ry10r2 outputs , r60adv8 analoginputs and r60da4 analog outputs. i am newbe with mitsubishi plc ;i would like to learn using the analog output of the R60DA4.for exemple i would send a digital value to the ch1 and convert it a voltage that i can mesure on the output of channel1.i have tried but i didn't succeed.i am using gxwork3.i have configured channel1 as +10v -10v output, normal mode , normal output;then i made a simple program in sfc to try this conversion but i get nothing in the output of channel1. i found that the digital value should be sent to the adress D11 wich is the adress of channel1.here you will find the file i made with gxworks3.could you please help me. ANALOGOUTPUTSCF.gx3
-
Comparison of Mitsubishi, Allen Bradley & Siemens
Gibblet posted a topic in General Topics - The Lounge
Hi all, I am in the process of doing a project for some school work and need to do a SWOT analysis of the latest modular PLCs from Mitsubishi (R series), Siemens (S7-1500) and Allen Bradley (ControlLogix). So I thought what better way than to ask the people on what they think are the pros and cons of each! Thanks for your responses in advance!- 10 replies
-
- swot
- comparison
-
(and 9 more)
Tagged with:
-
Is there any reason not to have input and output modules on the same rack as the processor and Ethernet cards? We have RIO’s and sometimes have networking outages, I want to move critical IO to Rack0 the same rack as the processor, is this bad practice? I've seen architecture for BMS that only have Ethernet cards and processors in Rack 0...
- 9 replies
-
- controllogix
- rio
-
(and 2 more)
Tagged with:
-
Is it possible to view the values / states of all inputs, outputs and workbits (e.g. 64.00 through 64.15 on Omron CQM1 PLC) on a single screen or control panel within CX-Programmer software? I'm trying to troubleshoot some ladder logic that I wrote and need to know the values of 5 or 6 inputs/outputs/workbits simultaneously. Having to scroll up and down through my ladder logic repeatedly does not work well with code that changes state every 5-10 seconds or so. Any help is welcome.
- 7 replies
-
- cx-programmer
- control
- (and 12 more)
-
Hi, I'm using a CJ2M CPU 33, and also a CJ1m Ad-041-V1 Analog Input and DA-041 Analog Output card. I am using the Analog input to measure my current in my one heating application and Ihave that reading and scaled correctly, but now I want to use my Analog output to replace the Rheostat we have in the system. I'm having some issues setting the range and getting voltage to vary. I also am a little new to Analog Outputs and don't know what I'm doing wrong. I have attached my program here. Any help would be greatly appreciated. Analog Heat.cxp