Search the Community

Showing results for tags ' use plc’s channel 0 (serial) or tcp/ip interface module(s) to have as many mb tcp/ip devices or serial devices. (some limits apply based on system configurations'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 142 results

  1. HI All,  I have an issue with my SCU32 communication.  Back ground Two SCU32s  (top and bottom side) connected via a 1100M datacable  using port1 ( 9600bps,  8-2-E, start code FF, end code FE, Tx save to d1000-d1200 , Rx save to d2000-d2200). PORT2 of bottom SCU32 is connected to a compass( 2 wire, 8-1-N, 19200 bps, serial gateway MODBUS ). Refer to photo Issue  Without compass, the receiving data at top is very stable and is didn't see any fluctuation. But if is compass is connected at bottom side port2, there is a fluctuation at the top side RX data(specifically d2000-d2005 ) .  I checked the data a bottom side TX (d1000-d1200) and it is stable. Only after sending the data and Receiving at Top side, then only the starting words fluctuate. I am not sure sure what is wrong, I am using logical ports for the DTXDU/DRXDU and compass.   Appreciate all your feedback and suggestions.  
  2. Hello all, I am working on a project where I am communicating with a Mensor CPT6100 pressure transducer using a Micro-850 PLC. For this, I have used an AWA instruction to write some ASCII characters to the sensor. The sensor then responds to the write instruction by sending ASCII characters to the RX buffer and I used ACB and ARD instructions to read the ASCII characters. Now, I have set the ACB trigger type to 0 (msg triggered only once) and it successfully reads from the sensor. However, when I set the ACB trigger type to 1 (msg triggered multiple times), I do not get any reading in the ARD block. As a matter of fact, the ACB Q bit switches off every time the program is executed when the trigger type is set to 1. I am trying to get continuous readings from the sensor, but when the trigger type is set to 0, the program latches on to the first and only reading and it won't change. My question is, how can I change my program so that it can continuously and autonomously read from the sensor without me having to manually trigger the AWA and ACB instructions every time. I am attaching the program to this thread for your reference.  ASCII_Test_Copy.ccwarc
  3. Sorry for my bad english speaking. I want to change the baud rate to 19200,38400,.... for send it via Programmer-Serial-Port. The software GX-Developer can do it!.  
  4. Hello Sirs! I have a problem with PF527. I get alarms 'control sync alarm' and 'module sync alarm' occasionally. I suppose this meaning that PLC is missing some data from the PF527 device. How to confirm this or what should I do with the problem? Any ideas? Motion group update period is 8ms. Also this device is the last device in the ethernet line. I am thinking to pull the cable directly to the switch near PLC. I am not sure does it help?  
  5. Hey Everyone,   My company decided to purchase a piece of equipment from China, and I have the pleasure of updating its terrible existing controls. We were given the PLC program by the manufacturer, so I was able to make my changes pretty easily - or at least that would be the case if I could actually connect to the dang thing. The source program is indeed openable and editable via GX developer (the original configuration shows it as an FX3). I figured connecting should be straightforward, but I was wrong.    I initially used a serial/usb converter that I've used on some older Allen Bradley equipment (which worked fine for that). However, after no luck using it on the "Mitsubishi", I purchased a different cable that I found recommended on this forum (Tripp Lite USA-19HS - https://www.alliedelec.com/product/tripp-lite/usa-19hs/70101537/?gclid=Cj0KCQiAj9iBBhCJARIsAE9qRtB_n8TVAnJdFyYokoEu42W6H6LaT4kVsgJQI1qvPUsUF3rFviKpbt0aApLHEALw_wcB&gclsrc=aw.ds). Still, no luck. I've tried 7E1 and every baud rate possible, as well as some other bit/parity configurations (and yes, I've verified that I'm using the right com port, as well as tried moving the converter to different ports and trying those). Nothing seems to go through.  I have almost no experience with Mitsubishi beyond a couple of FX5s (which have worked fine, but I connect to those via ethernet). Any help would be greatly appreciated; if I can't make these changes, I'm going to end up rebuilding the whole cabinet with a PLC I can rely on.   Thanks in advance.
  6. Hi, I have an Omron NSJ5-SQ00B-M3D Programmable Terminal (HMI) that I am trying to get to communicate with an Omron CJ2H PLC through a DeviceNet module (DRM21) in the main PLC rack.  I don't see how to configure CX-Designer to communicate via DeviceNet.  How is this done?  Many thanks for any help.
  7. Hello, We have a FX3G connected to a FX3U-ENET-ADP inside a main cabinet. We are then using that master PLC to collect data from 2 other fx3g plcs in a node:node serial network. I was assigned a small project of pricing out some wireless adapters so we can upload/download to the two slave plcs. My question is, is it possible to upload/download programs to/from the slave plcs through the ENET adapter and serial network in the main plc? It would save us some money if possible. thanks.
  8. Proface with Serial Printer

    Dear Sir, Good day. I facing difficulty on using proface to print out the data using serial printer. I did follow all the instruction on proface reference manual but still fail to print out anything. Anyone here having experience on this issue? Thanks. 
  9. I have a Siemens HMI 6AV2 124-0MC01-0AX0 in my machine. I want to clone the display on the HMI to PC/Laptop. My question is: 1. What software that I need for this task? 2. What kind of interface that I need between the HMI and PC/Laptop (for example ethernet cable, etc)? 3. Do I need to communicate with PLC connected with HMI or can I just connect with the HMI? Thanks in advance for the answer.
  10. Hi Everyone,   I have  NT31C-ST142-V2 and it has a prompt of "System Program not exist or incorrect." I am trying to transfer via NT Series System Installer but I am getting a time-out error. I have Xm2S-09 serial cable with ATEN serial-to-USB cable.I know it is not broken since I can still Upload/download on a CJ2 PLC. I just want to know what other things I can do upload a systemprogram. I have seen a comment on this site that he remove the battery then tried to upload again.   NT is almost 15 years old. I have a back-up program.   I can't seem to upload by this time for pictures of theH MI and the screenshots of software .
  11. connection to omron CJ1M PLC

    I have an omron PLC (CJ1M type) at home which I would like to connect to, however, lately, I can't anymore.  I'm trying on two different PC's a newer and an older one, both running on windows 10. 1 is just mentioning a DLL error and I can't even start cx-programmer, the other one seems to work, however, when I try to go online it always fails I'm using a usb to serial device and after some searching on the net, I thought the issue was with the prolific driver.  I tried all kind of fixes, but nothing seemed to work.  I have now purchased another device, the XS8801 from usconverters and installed the latest driver.  I have checked if cx programmer is set to work with the correct port and this is the case. My knowledge is very limited but I would really want to connect to that PLC again, so hoping someone out here is able to help me. Thanks a lot    
  12. FBs-CBE distortion

    Hi every one After sending some command to plc using fatek FBs CBE module , router internet connection goes off and internet LED turn red. i mean it works fine for a minute.. then internet connection of router will be off...  why this happens?
  13. Hi All! Can anyone help me regarding the following logic: 1. I have four Silos and one filling station. 2. The filling of silos starts on the bases of silo demad (i.e demand is a digital signal that comes when silo is empty) 3. I have to fill all silos according to their demand 4. Whose demand is first that is filled first 5. for e.g if all four silos are empty they all generate a demand signal. 6. If Filling of silo 1 is done and filling is in progress at silo 2 after that filling will start  in silo 3 then silo 4 as they are empty 7. In the mean time  if silo 1 empy again and filling is in progress at silo 2. The system must fill silo 3 and 4 first then go to silo 1  8. It means which demands first that is filled first (first come first serve)   
  14. Check serial connection to Omron PLC

    Hello, I am building an application in CitectSCADA and I want to communicate with an Omron Sysmac CS1G. The connection between the plc and the Citect computer is through an ethernet to serial adapter (the computer doesn't have com ports on board). I'm having some difficulty establishing the communication and I want to make sure that I can actually reach the plc. Is there a way to check that the computer can reach the plc over the serial connection without using CX programmer? Maybe using Hyper Terminal, Putty or something similar. Thank you, Liron
  15. QD75M4 AND MR-J2S-40B

    Hello i have problem about connection between QD75M4 AND MR-J2S-40B  now MR-j2S is display "Ab" every time i can't solve this problem 
  16. I need a Red Lion HMI to communicate with an IO module (8) IO's ... I don't really need a PLC.  Because the control of a certain LinMot drive for a linear motor can be activated by IO's.  This LinMot drive can store up to 100 curves... which can simply be called into operation by a single binary number between 0 & 255,  defined by eight IO's ..  you input the number on the HMI, the HMI converts to binary and set the (8) IO's in the module which sends the binary number to the LinMot drive..   Yes, there are some other IO's for starting and stopping ... and it may be unrealistic for me to not use a PLC.   I'm trying to get the cost way down...    If a "stand-alone" IO module does not exist... then is there a simple, low budget PLC out there, with 8 or 16 IO's available..?    Thanks much, Michael
  17. IC200ALG264 Analog Input module

    Hello all, Thanks for the forum which has provided me with a lot of help overtime. I'm posting my first thread since I can't seem to find an answer to my issue. I'll quickly explain the situation: I'll be installing a RTD sensor to a GE Fanuc IC200ALG264 analog input module using a 4-20mA converter. Everything is fine except I can't seem to understand the polarities of the Fanuc inputs. I'll explain better: the module has an IC200CHS022 for the terminals, 15 terminals total, and the manual is reporting a "number" and a "connection" for each terminal. Now, the "number" seems to correspond to the visible pin of the terminal. But the positive and negative symbols are represented on the "connection", which I can't seem to wrap my head around what it means. Attached are abstracts from the manual and a photo of the terminals. Please tell me where to connect positive and negative outputs of the 4-20mA converter. Thank you. Terminals Table Terminals drawing Terminals photo (front)
  18. Hi! I would like to ask how could I send data from PC to CJ1M PLC, by SCU-41 module and RS232 cable, in order to activate an actuator (LED)? In my environment, I have a sensor that sends data from PLC to PC (I'm checking data, "HelloWrld" with Putty), with this configuration: And I have another section where I want to read the data from the PC in ordr to activate a LED I would like when I send for example a letter 'a' trough Putty, the LED activates. How could I do that? Thank you very much!
  19. Hi All need to convert a Decimal Value into Ascii code to send out on serial 485. eg. Weight comes in as Int 12345 i need to send it out in Ascii as 23 32 20 31 32 33 34 35. I have created an array 0 of 8 (Word) DB. Is there an easy way split the int into Digits convet in into HEX and slot the value into the various array positions? Array 0 of 8 = 23 means # Array 1 of 8 = 32 means 2 (Station ID) Array 2 of 8 = 20 means Space Array 3 of 8 = 31 means 1 Array 4 of 8  = 32 means 2 Array 5 of 8 = 33 means 3 Array 6 of 8 = 34 means 4 Array 7 of 8 = 35 means 5 Array 8 of 8 = D means CR    this sends the value of 12345 to Display ID 2 . need help to convert the decimal number in ascii. the decimal number will be max of 5 digits and less than 32000   any help will be greatly appreciated.
  20. friends, forgive me for my english.  I have a problem.  omron nt620c panel cannot access the system menu.  I reinstalled the system program through NT-SYSTEM INSTALLER.  after which I get the message: no direct information is set !!!  please use the support tool to set the pt control area and the pt notify area.  go to the system menu does not work.  I swing the corners of the screen as described in the manual.  from a video from YouTube I realized that there should be a message connecting to host
  21. Hey everyone, I have a CJ1M PLC with a CJ1W-SCU21-V1 serial card. It is unit 6 and I am using port 1. I have bit 1659.06 ((1500 + 25 * Unit #) +9, bit 6) as "characters in buffer" but it never comes on (data is being received through the port successfully). It is on No-Protocol mode. Does anyone have any ideas as to how I can detect data in the buffer?
  22. Serial comm with FX1N PLC

    I need to communicate with a Mitsubishi PLC using Matlab. To do that, I open a serial communication with the appropiate parameters (7,e,1,9600), and write an ASCII message based on the manual I have (attached). I have tried examples as the one in the attached image. The response starts with a 6, that is, the ASCII number for ACK, so something must be working. But the rest of the response is junk (149, 149, 149...), although its length depends on the input length (if I add terminator, the response is longer, and so on). I am completely stuck. Some information that might be helpful: I am using a Serial to USB converter that I have used successfully with other PLC (which used Modbus, so everything was easier) There's a VB application (of which I don't have the code) that is able to connect to the PLC (I need to connect directly without using this intermediate app). I have decompiled it trying to get some info, but was just able to confirm the 7,e,1,9600 parameters, since the rest of the code is too mangled to analyze The attached manual was sent to me by the guy who designed the PLC and its ladder code, so I guess it is the correct one I have tried the echo mode (TT) to no avail, response is always the same I have some doubts regarding the reading of a value (see attached image). Why is there a second message from the PC? Shouldn't I just need to read the response? GX Developer tells me that the address D8120 (which is supposed to define the comm format and protocol) contains a 0, which seems weird. Any help or hint would be greatly appreciated. Thanks jy992d69901e.pdf
  23. Hi all! We have a problem with a Mitsubishi system. After switch off the machine in home position and back on, it resets the servo encoder value to 0.  I checked the servo parameters, and the Absolute encoder is enabled, the ext. battery is ok and no zero reseting in the program ( I think...). Is there a parameter I should check or some setting in the intelligent module? The system consists Q01CPU, QD77MS2 im., J4 200B amp with 6v battery, and HG-SR152 motor.
  24. PID Loop Review

    Hi all, I am trying to set up a PID loop for a project I'm working on, and I was hoping someone could take a look at it for me. Most of what is written comes from the Q, L programming manual, but I've changed a few things so that the program can write changes to the SV as needed. The processor is a Q03UDE and the Analog Module is a Q64AD2DA, using only channels 1 and 5. Thanks for looking! PID Project.gxw
  25. Connection cable for Sinumerik810

    Hi, I am trying to connect my M2 pg with a Sunumerik 810 cnc.    does anyone have the part number or pin out of the 25 pin-25pin tty cable that’s needed for this.    thanks