Search the Community

Showing results for tags ' redundant profinet'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 28 results

  1. ProfiNet questions

    Hello, What PLC, except Siemens, has Profinet included in its bus communication protocol? What Profinet to Profinet coupler do you know except those from Siemens, Anybus and Helmholz?
  2. ProfiNet questions

    Hello, What PLC, except Siemens, has Profinet included in its bus communication protocol? What Profinet to Profinet coupler do you know except those from Siemens, Anybus and Helmholz?
  3. Hello    I have a question regarding a network infrastructure I hope someone has experience with this My self has very litte knowledge about Profinet.   So there is this site that are running a huge Profinet network and we wonder if it possible to connect two new plc on the profinet network and communicate EthernetIP between the two new NX102 cpus ?   Regarding profinet documention I havent found any limitation to do this, Profinet can coexist with all other ethernet based protocol ? /Best Regards 
  4. Dear Experts I have Compact Logix L33ER processor for Hot Backup Redundancy Purpose in WTP application. Iam using Flexlogix 1794-OB16 DO outputs. Flex adapter for IO communication. Iam trying for Soft Redundancy from main processor to peer and peer to main processor . During Switchover from Main to Peer and Peer to main Processor, the DOs are cut off. While in the middle of the process if the Switchover of PLC happens due to failure of Main or Peer PLC, if the DOs are cut off, Should i Start the process sequence logic from beginning? I tried configuring the DO properties of  Communication Fail Behavior in output modules properties as "Hold Last Output but still the DOS are cut off during switchover. Then also Iam facing the problem of DO cutoff whle switchover. Iam having same program and IO configuration in main and peer plc generated through HotBackup tool. Please let me know if there is any way to Prevent DO cutoff while switchover . Also in Panelview HMI iam using 2 screens for Main and Peer PLC. While switchover the screens in HMI are showing in boxes. Please advise. Regards Krithik.K
  5. Hi Guys I have some issues with profinet configuration Siemens step 7 v5.5 Fanuc robot profinet card cp1616 I have 8 byte safety 16 byte DI16 byte DOI setup DI and DO. No error.But I have  safety comm error 1.1 I put Cp1616 at slot 0safety at slot 1DI at slot 2 DO at slot 3So far slot 2, 3 are ok, (no mismatch ) But safety are no ok, F number is matching between robot and plc side Is there’s anyone can help me on this, I don’t know what I miss. It’s the first time I am configure profisafe for robot Thanks  
  6. ProfiSafe Using TwinSAFE

    Has anyone implemented ProfiSafe over TwinSAFE? Would you recommend it? What obstacles or quirks did you need to resolve? Would you do it again?
  7. Hi,  We have 2 x 1756-L71 Processors joined together with a pair of 1756-RM2/A redundancy modules. The rack also has 1756-EN2T and 1756-CN2R modules.    I was called to the site after a power outage and found that the link between the 2 CPUs had failed with one displaying no program and the link modules with error lights. The ControlNet cards also had red lights on both channels and all of the FlexIO devices were red Xed in RSLinx. I went down the path of trying to get the CPUs up, and running but this was a red herring as I was informed that if the CPU's get out of Sync and have any faults on the cards the secondary one will lose its project. The ControlNet cards were giving a no Active Keeper fault? So we went down the path of the ControlNet cards, I initially thought that it was that the cards had lost their configuration files but we isolated the coax network to just the 2 cards, and the CP's and ControlNet cards came back up online. We joined the network back onto the ControlNet cards and found a faulty 1794-ACNR15/CFlexIO module. Once we replaced this the other devices (48 devices on the network) were not being discovered on the network. We went around and power cycled the IO units and then they started to Auto discover and the site came back up - Note CPUs were in Program mode at the time and I flicked them to Run and the site came back online. Does anyone have any information on why they needed to be power cycled and is there likely to be an underlying issue other than the single failed module pulling the network down?
  8. I am building a redundant system using S7-1515R-2 CPU with TIA V16 version. Creating the hardware, there is not possible to insert any other card to the rack. Even power modules (PM) can not be inserted to the rack. How should I make the power feeding to the CPU. Should I use two power modules/devices or only one. How can I insert IO-cards to the system, is the only possibility to use Profinet IM-cards. In this system I am connecting the bus to the ring and using S2.  
  9. Hello, does anyone know the best connection method between an S71500R/H profinet MRP ring (2 x S7 1500R controllers in redundant profinet ring) and an S7400 DP Master ?
  10. I have a Siemens HMI 6AV2 124-0MC01-0AX0 in my machine. I want to clone the display on the HMI to PC/Laptop. My question is: 1. What software that I need for this task? 2. What kind of interface that I need between the HMI and PC/Laptop (for example ethernet cable, etc)? 3. Do I need to communicate with PLC connected with HMI or can I just connect with the HMI? Thanks in advance for the answer.
  11. Omron CJ1M CPU11 - ProfiNet - Siemens

    Hello guys, newbie here. Wait, where are you all going...? Don't go! I've got *some* experience. And a job on my hands. I've got an Omron CJ1M with a CPU11. Attached, is a PNT21 Profinet IOController. At the other end, it is going to be a Siemens SIMATIC ET 200AL, PROFINET interface module IM 157-1 PN with a couple of digital input and output modules attached. The hardware isn't here yet, otherwise I'd just jump straight into trouble. Probably. I've got it mostly setup in ConfiguratorFDT with the GSD files from Siemens. The question: How do I map the Symbols to the digital IO at the other end of the profinet? Can I just set the symbol address to the IO areas that ConfiguratorFDT show me, ie, 3300 for the inputs, etc? Thanks!
  12. Diagnostic of profinet communication

    Dear Experts, I want a sample block to find out the status of my Profinet cable w.r.t Hardware configuration. whether the cable is connected or disconnected from the node. Either my nodes may be VFD, HMI, SCALANCE, etc...  please share the sample blocks... S/W ===== >Tia portal v14 sp1 update 6  H/W ===== >CPU 1214C DC/DC/RLY hanks in advance
  13. Diagnostic of profinet communication

    Dear Experts, I want a sample block to find out the status of my Profinet cable w.r.t Hardware configuration. whether the cable is connected or disconnected from the node. Either my nodes may be VFD, HMI, SCALANCE, etc...  please share the sample blocks... S/W ===== >Tia portal v14 sp1 update 6  H/W ===== >CPU 1214C DC/DC/RLY hanks in advance
  14. GX Configurator 2.01B

    Hello all,  I'm have an issue with GX configurator, I have a project which includes devices connected to plc (R08) and when I add them manually in GX Configurator and then load to PLC I'm getting connection. But when I want to run diagnostic or detect devices through network detection I'm always getting timeout error: status 33. Anyone got the same problem or know how to solve it? 
  15. Hi, to start, I'm very new to Siemens PLCs, but quite experienced on others (mainly ABB). I'm looking to set up a profinet network between an ABB AC500 PLC and an S7-1200. The goal is to transfer variables from an existing S7-1200 (owned by the customer) to my new AC500. It is required that I do this without having to stop the S7-1200. I can set up the AC500 as a profinet device, and have the S7-1200 remain as the controller, but this requires a config change on the S7-1200, which means I'd have to stop the PLC. I tried setting up the ABB as a profinet controller, but I'm having trouble finding a GSDML for the S7-1200 to allow me to do this.  Can anyone advise me on the best route to take to solve this problem? Thanks in advance.
  16. I'm trying to setup some interlock signals between a CompactLogix L33ERMS and an optical gauge.  The gauge only offers PROFINET as the fieldbus for interlock signals (hard-wiring is not an option).  The PROFINET connection for interlocks in the gauge is supplied via a Beckhoff EL6631-0010 PROFINET RT device terminal (connected to a Beckhoff CX8010 bus coupler, but I assume that is not relevant). The PROFINET connection on the CompactLogix side is supplied via ProSoft PLX31-EIP-PND "EtherNet/IP™ to PROFINET® IO Device Gateway". My PROFINET experience is zero, and the ProSoft gateway was selected before my involvement in the project.  It seems to me that one of the PROFINET devices needs to be a controller or "master" on the network.  Right now, both the ProSoft and Beckhoff devices appear to be devices or "slaves", but the terminology is fuzzy to me (PROFINET IO vs PROFINET RT, etc.). Should I be able to make the connection using current ProSoft Device gateway, or do I need to upgrade to a PLX82-EIP-PNC "EtherNet/IP™ to PROFINET Controller Gateway" or equivalent?  Does at least one of the devices on the network need to be controller-level? Any direction would be greatly appreciated.
  17. I am needing some guidance on an application I'm working on. I'm trying to obtain data from a profinet slave device to an Allen Bradley compactlogix PLC. I am using a Prosoft PLX82-EIP-PNC profinet-/ethernet-ip gateway as a median to allow me to access the profinet data. In RSlogix5000, I have created an EIP Class 1 connection for the profinet controller and AB PLC (248 words of input data, 248 words of output data). The same structure is created in the profinet controller (248 words of input data, 248 words of output data). The profinet gateway and PLC are communicating properly. From my profinet slave device, I have a specification that the data is structured within a 23 byte format. Connecting to my profinet gateway, I can see this data. I have attached an image that shows the specification of the profinet data and the data values displayed inside the profinet controller. From the PLC side, I'm needing to be able to see this data and put it in meaningful values. I am using the profinet slave device's internal temperature as an example to work towards. I'm not sure the best way to be able to handle this data and structure it to a meaningful value inside the PLC. (I am using the device's internal temperature as an example to try and get into the PLC).   Thanks,
  18. I am needing some guidance on an application I'm working on. I'm trying to obtain data from a profinet slave device to an Allen Bradley compactlogix PLC. I am using a Prosoft PLX82-EIP-PNC profinet-/ethernet-ip gateway as a median to allow me to access the profinet data. In RSlogix5000, I have created an EIP Class 1 connection for the profinet controller and AB PLC (248 words of input data, 248 words of output data). The same structure is created in the profinet controller (248 words of input data, 248 words of output data). The profinet gateway and PLC are communicating properly. From my profinet slave device, I have a specification that the data is structured within a 23 byte format. Connecting to my profinet gateway, I can see this data. I have attached an image that shows the specification of the profinet data and the data values displayed inside the profinet controller. From the PLC side, I'm needing to be able to see this data and put it in meaningful values. I am using the profinet slave device's internal temperature as an example to work towards. I'm not sure the best way to be able to handle this data and structure it to a meaningful value inside the PLC. (I am using the device's internal temperature as an example to try and get into the PLC).   Thanks,
  19. All, I am using Keyence CV-X422A vision controller for my application. It is interfaced with Siemens S7-1500 PLC on PROFINET. I am able to communicate with Vision controller through PLC logic command and status IOs. There is some communication issue in updating the o/p values from Camera Controller. I have tried with & w/o Handshake Mode with these settings. The camera display shows the reject but camera never turns ON the NG Status o/p. I tried different things told by Keyence Tech support but none of them worked.  He told me to have you enable the “Result ACK Flag” in the bit allocation area and send  a signal to it. Then trigger it again with a no good part and see if that fixes the issue. I tried setting the “Result ACK Flag” to 1 after I get the “Command Complete Flag” for the trigger signal that I sent. Sometimes this works but still it is not reliable. Do I need to send only a pulse to “Result ACK Flag”? Anyone here has ever faced similar issue?  Thanks for your help. AP
  20. The OPC Server for Siemens Controllers

    Good day to all forum members. I think many engineers are faced with the need to connect Siemens controllers to various SCADA systems. In most cases, the OPC technology is used to make such a connection. We want to offer participants to try our product, the OPC server for the Profinet protocol applied in Siemens controllers. Our OPC server supports the following standards: OPC DA 2.05, OPC HDA 1.2 and OPC UA (transfer of archives is supported too). Controllers of the following series are supported: S7-200, S7-300, S7-400, S7-1200 and S7-1500. The OPC server provides the interactive import of tags from the Tia Portal environment, and this simplifies configuring the server. The OPC server contains the built-in client for monitoring values, and this simplifies communication debug. There are the following modifications of the OPC server: - Demo version (full-featured, 1 hour continuous operation in the runtime mode) - Free version (32 tags at the most) You can download the trial version here: http://opc-server.com/catalog/mullti-protocol/profinet/ In addition to the OPC server for the Profinet protocol, we also support such protocols as Modbus, Omron FINS, Bacnet, IEC 60870-5-104, IEC61850 and SNMP.   We would love to hear feedback and feature requests to our products.
  21. Grupa ProfAs Sp. z o. o. jest firmą doradczą, świadczącą usługi w szeroko rozumianej dziedzinie Human Resources. Specjalizujemy się w rekrutacjach na stanowiska specjalistyczne, średniego i wyższego szczebla. Wierzymy, że nasz Zespół złożony z profesjonalistów jest w stanie zapewnić perspektywiczne spojrzenie i najwyższą jakość wykonywanych usług. Aktualnie dla naszego Klienta - firmy z branży automatyki przemysłowej - poszukujemy osoby na stanowisko: Programista sterowników PLC Kraków / Piła / Poznań ZAKRES OBOWIĄZKÓW: Programowanie sterowników PLC Siemens Wykonywanie aplikacji dla systemów SCADA i HMI Dobór konfiguracji sprzętowych PLC Testowanie i uruchamianie maszyn u Klientów końcowych (delegacje krajowe i zagraniczne) Wykonywanie programistycznych prac serwisowych u obecnych Klientów Sporządzanie instrukcji obsługi maszyn   WYMAGANIA: Bardzo dobra znajomość sterowników PLC Siemens Umiejętność parametryzacji serwonapędów, falowników, etc. Znajomość paneli HMI oraz systemów SCADA Znajomość sprzętowa oraz programowa komunikacyjnych sieci przemysłowych ProfiBus, Profinet, Ethernet, DeviceNet, Modbus, etc. Znajomość zagadnień i komponentów automatyki (przetwornice, serwonapędy, obwody bezpieczeństwa, aparatura modułowa, itp) Mile widziana znajomość programowania innych sterowników: Allen-Bradley, Omron Prawo jazdy kat. B Komunikatywna znajomość języka angielskiego lub niemieckiego OFERUJEMY: Współpracę w oparciu o umowę o pracę Udział w profesjonalnych szkoleniach Korzystne warunki wynagrodzenia Rozwój w firmie z doświadczeniem na rynku międzynarodowym nr w rejestrze 14990 Osoby zainteresowane prosimy o przesyłanie CV na adres k.dominik@profas.com.pl lub kontakt telefoniczny pod nr tel. 881 700 778.
  22. Hi all, I will be starting on my MSc in automation in a couple of days so for that reason i have obtained a S7-1200 series 1211AC/DC/RLY PLC. This is a new area for me as i have been working in offshore since i graduated from my BSc a couple of years ago. I watched some Youtube tutorials on how the programming is done and i am ready to try it out for myself, but i have encountered a little problem.   Problem: I am using the X1 P1 PROFINET (LAN) port as a connection to my PC, this turns the Green Link light on and the Rx/Tx lights blinks orange. Now to the problem, i cannot connect to the PLC through the TIA portal, no matter what settings and connection types i use in the PG/PC interface box. I have had no luck finding leturature adressing how to configure the PC/software and get a connection to the PLC. Do any of you have a PDF or link which can help me through this problem?  Hardware: S7-1200 series 1211AC/DC/RLY 6ES7 211-BE40-0XB0 S C-J5PN 1614 2017 FS:05 Software: TIA Portal Version 13 STEP 7 Professional V13 WinCC Basic V13   Thanks   Best regards   Dennis    
  23. S7-1500 FW v 2 / Profinet issues non-Siemens devices

    Hello: Has any body encountered Profinet IO cyclic communication establishment problems between the latest S7-1500 PLC with firmware 2.0 or later and non-Siemens Profinet devices which had previously passed conformance testing campaigns? Thanks for your comments.    
  24. S7-400H Redundant Confogration

    Dear Expert Is necessary to have both CPU (Master & Slave) same program blocks or only master PLC should have S7-program with blocks  Best Regards Ali