Jdeloz828

MrPLC Member
  • Content count

    2
  • Joined

  • Last visited

Posts posted by Jdeloz828


  1. Hello,

    -I'm considering using an AB 1734-IB8 to count input pulses from a Micro Motion flow meter transmitter and, since I'm very new to this stuff, would like a little guidance as to how/if this can be done.

          My first concern is the wiring. The manual for the transmitter shows this wiring diagram for the specific model I'm using.

          flowmeterwiring.PNG.39094ce4aaef789ed665

    Here, B would represent the 1734-IB8 module. I'm not going to be using the analog loop. In addition to this wiring, terminals 9 & 10 on the transmitter will be wired to the same 24V and Common as my PLC modules. 

          The 1734-IB8 manual shows this diagram for wiring.

          1734IB8wiring.PNG.493b9a251a3a4a9f20721b

    Should I consider the pulse output of the transmitter as a 3-wire device, connect terminal 3 of the transmitter to my 1734-IB8 input terminal and disregard the connection from terminal 4 of the transmitter, or should I just tie terminal 4 to my common?

    Or, Should I consider my pulse output as a 2-wire device, tie terminal 3 of the transmitter to my 24V and terminal 4 to my input module?

    My guess is the pulse output should be considered a 3-wire device with terminal 4 of the transmitter tied to my common, but I'd like a little bit of explanation with this.

    -My second main concern has to do with the capability of the 1734-IB8 module to read pulses. More specifically, I would like to know what parameters of the module I need to research to see if it will be possible to read the pulses from my transmitter in the application I'm considering. If the 1734-IB8 can't be used, I would end up going to a high-speed counter card.

     

    Thanks