Rishikesh
MrPLC Member-
Content count
14 -
Joined
-
Last visited
Posts posted by Rishikesh
-
-
-
Is CP1H with Ethernet option board (CP1W-CIF41) is capable to communicate More than one client? If yes what settings I need to be Done?
-
If I Connect SCADA only then it works fine. SCADA is read only,HMI is read/Write in my case.
Is CP1H with Ethernet option board (CP1W-CIF41) is capable of More than one client?If yes what settings I need to be Done.
-
-
Your Laptop IP address should be in same series of PLC to open in Web browser.
ex-192.168.250.120 (In ur case).
-
yes..All Devices Have Unique IP Address.
On local network HMI connected to PLC through Kepware OPC and SCADA PC used as read only SCADA.
Whenever I connect only HMI it works fine as soon as i connect to SCADA and HMI both it starts swapping values in parameter(PLC Data Register).
-
-
On 08/05/2017 at 7:54 PM, Michael Walsh said:What is your subnet mask? If it is 255.255.255.0 and that managed switch is not a router as Crossbow has suggested, then this will not work.
255.255.255.0 is subnet mask.
-
17 hours ago, Crossbow said:Is that managed switch a router? If not, they are 2 separate networks. A managed switch is not typically a router.
yes its right, Managed Switch is not router it is in VLAN. But on SCADA PC i can go online to PLC through CX Programmer(It means it is in Network), but can not connect to PLC through kepware OPC.
-
Thanks For Ur Reply Mr.Pfort,
I have configured device as CJ1 in kepware.
Actually i am able to Connect to kepware on local network(i.e. 10.11.87.xx) but not able to connect on different network (i.e. 10.11.90.xx) .
-
Delta PLC Analog Noise Reduction
in Other PLCs
Posted
Hello All,
I am Using Delta SE Series PLC and 06AD Module for Pressure Transmitter.
But Analog input get fluctuate continuously.
Is anybody have program for analog scaling.