ErikSN
MrPLC Member-
Content count
4 -
Joined
-
Last visited
Posts posted by ErikSN
-
-
Joe E.
Thanks! Those seem like good options to confirm that comm between PLC and SCADA are up. Will look into it.
-
Hi,
I was wondering if it's possible to detect a changed/updated value in a data block even if the value remains the same as before.
The reason I ask is because we have a SCADA system providing a setpoint for a temperature every x minutes. The value of the setpoint can remain unchanged for hours even days.
However we still want the PLC to be able to detect wheather it's setpoint is updated every x minutes or not.
Any good solutions?
Thanks!
-
Hi,
I was wondering if anyone have experience with Tia Portal Step7 v.14 and Step7 Classic v.5.5 located on a remote server?
We have several persons working on our PLC's. As it is they all have their own PC with Step7 + licenses.
We were thinking about moving the software environment onto a server to reduce license and maintenance costs.
Does anyone else have this setup? If yes do you have any tips or comments? Pros/cons?
I already know now that you cannot autodetect/configure new devices from a remote server as the Step7 detection protocol doesn't work through a router. We can live with that.
We need both TIA Portal and the Step7 Classic on the same server.
Thanks
Limiting on-line connections to a S7-1500 PLC
in Siemens
Posted · Edited by ErikSN
Hi,
I was wondering if there is a way to limit the number of allowed on-line connections at a time to a PLC?
Like can you somehow set in the PLC parameters that only 1 'connection' can be on-line in the device at a time?
Thanks
Edit: I'm referring to connections from the TIA portal - not HMI / ethernet connections and so forth