banker

MrPLC Member
  • Content count

    142
  • Joined

  • Last visited

Everything posted by banker

  1. CJ2M 33 Ethernet/IP problem

    Hi I have a problem. I have a PLC CJ2M with Ethernet/IP comms to some Danfoss drives FC280. I can start and stop the drives, control speed ect. BUT when/if my PLC goes into stop the drives continues. The drives have at controlword with a bit 10 Data valid bit ( most be On otherwise controlword will be ignordet ) When the PLC goes into Stop the Ethernet/IP continues to comm. so if i use DM memory for the comms it will not change. If i use CIO memory i all go 0 and the drive ignor the controlword. What to do. ??? Banker  
  2. You can use a browser or there is a software soMove, but for this you will need a special cable. Banker
  3. OneShot CX-programmer

    Hi Programming a CJ2M in ST is there a oneshot instruction and how to use a timer ?  PS I now how to program a oneshot. Banker 
  4. CPU load memory

    Use the cross ref. in CX-programmer Banker
  5. CXSupervisor, CJ2M performance issues.

    Ethernet has most better performance 
  6. Using a AD041 and DA041

    Hi  You need to start the card 2020.0 , 1, 2, 3 one bit pr channel. Sorry my mistake you have already started the card, but the address for writing is 2021 unit no.2 ch.1 Banker   
  7. CJ1W_AD081_V1 Fault after power reboot

    Hi  Use the Cross-ref ( ALT -X ) and you can see that the program use D20XXX in the section Bally_Flow_AVG You have a functionblock AVG300 with AT_D20000     Banker
  8. CX-Supervisor runtime startup question

    The PLC is in run mode. 
  9. 2 CPU CJ2M on one PSU

    HI Is it possible to have 2 CPU on the same PSU ? Banker PS. only using remote I/O
  10. Yes you can install cxs on the same PC as cxone. 
  11. Hi  I got a beta ver 341(3) and I also have isue printing. Banker  
  12. CX-Supervisor 3.4.1

    Problem solved By Omron Denmark: Mark all point and press <Enter> Then Press <OK> 
  13. CX-Supervisor 3.4.1

    Hi After updating CXS to ver. 3.4.1 I can't see point address I can see them when I editing but in the list form only the array len. is shown. When I enter a new point I can see the address. Anybody now hove to solve that ? Banker
  14. By default the address is 192.168.250.1  Banker 
  15. CJ2M 33 Ethernet/IP problem

    Thanks for the suggestion, but I want to avoid a solution with an extra relay. I had this setup with Omron PLC but on profibus, no problem because the comms. stop when the PLC goes into stop. Banker
  16. MAD 42

    Try i out in the simulater and if not make a convert from 16 binary to INT or use ther >S  ¨Banker  
  17. Cx-programmer -Flowmeter

    Hi Kenra What do not match ? the program is a totalizer I7.13 input oneshot. D3174+D3175 is the totalized value.  Banker
  18. Remote NX IO via NXEIP202 card

    Hi In france but maybe it can help. https://www.youtube.com/watch?v=oP5RQ7BHx5M
  19. Remote NX IO via NXEIP202 card

    Hi I think you need Netconfigurator in CXOne  
  20. How to connect Cx designer to PC

    Hi  In you can run your cxdesigner project in test mode on you PC at connect the project to a PLC. Banker  
  21. Analog Input to CP1E from MX2 Drive

    BobB it a function blok
  22. CJ2M-CPU33 bus unit

    You have already ethernet/IP in this CPU.
  23. First program reading analog input

    Look in the download section there is a function block for scaling Banker
  24. CX-Server Detected A Problem

    Hi Have tryed the same, solved by creating a new point and then run the project again. Banker