Ayyub Ishaq

MrPLC Member
  • Content count

    12
  • Joined

  • Last visited

Community Reputation

0 Neutral

About Ayyub Ishaq

  • Rank
    Sparky

Profile Information

  • Country Saudi Arabia
  1. Dear All! I would like to know that what is the maximum no of PID(close loop controller) a Quantum PLC with CPU434 can support using unity pro. Your response will be highly appreciated.
  2. DEAR FRIENDS I AM HAVING A PROJECT BASED ON FIPIO. I HAVE ONE MASTER PLC WITH BUILTIN FIPIO PORT AND ANOTHER PLC WORKING AS AN AGENT PLC WHICH CONSISTS OF A PCMCIA FPP10 CARD. IF ANY BODY HAVE ANY EXPERIENCE OF THIS COMMUNICATION THEN PLZ LET ME KNOW SO THAT I WILL FURTHER CONTINUE MY DISCUSSION ON THIS TOPIC
  3. DEAR FRIENDS I HAVE TWO SCY11601 MODBUS SERIAL MODULES ON SAME SINGAL RACK WITH PROCESSOR P57104M. THE FIRST SCY11601 IS INSTALLED ON MODULE 3 WHILE SECOND SCY11601 IS INSTALLED ON 4TH MODULE. I AM CONTROLLING 11 TESYS-Us THROUGH MODULE NO 3 SCY11601 AND CONTROLLING 6 ALTISTART THROUGH MODULE 4. I AM ABLE TO CONTROL ONE SCY11601 MODULE AT A TIME MEANS I AM UNABLE TO CONTROL 11 TESYS-Us AND 6 ALTISTART AT THE SAME TIME. ANY GUIDENCE PLEASE.
  4. Dear i have a premium tsxp57104 plc and unity pro v4. I am connected to the plc. the plc has already a program stored. But the upload program is disabled. please guide me in this regard i want that application but how to make upload
  5. i have a premium plc set as Manager PLC and two premium PLCs working as Agent PLC. i am using fipway. The configuration in master or manager plc is the following: Bus no: 2 Agant PLC1=connection point 2 agent PLC2=connection point 4 i want to know that if suppose the agent plc AC or DC power went off which makes this agent plc1 to of condition but how the Manager PLC knows that the Agent PLC1 is disconnected.Is there any special bit to read from agent plc1 or any syntax for reading plz guide me in this regard.
  6. can you give we an example. look if i want to read the inputs from a plc whose input starts from %i0.3.0 and ends with %i0.3.63(64 channels input module), then how can i do this.
  7. Dear friends i have premium plc and im using unity pro.I have connected STB island with plc .So in stb the digital input address is 45392. Inorder to read this address in plc we write 45392-40001=5391, so we write in "REad Slave Index" column 5391.This is ok with me. But how to read the digital inputs from another premium plc for example %i0.3.0 to %i0.3.9
  8. DEAR FRIENDS I HAVE A MAGELIS HMI XBTG2110 AND A TWIDO PLC TWDLMA20DRT.I HAVE FOLLOWING DETAILS: HARWARE SETTINGS::: 1-I AM USING TWIDOSUIT FOR PLC AND VIJEO DESIGNER FOR HMI. 2-I AM USING DOWNLOADING CABLE FOR HMI "XBTZG935" (PC)USB<------------------>USB(HMI) 3-THE CABLE B/W PLC AND HMI IS "XBTZ9780" (PLC)MINI DIN<----------->RJ45(HMI) SOFTWARE SETTINGS::: PLC: 1-OPENED TWIDOSUIT AND IN WORKSPACE OF DESCRIPTION I DRAGED AND DROPPED TWIDO PLC 20DRT AND CLICKED ON TWIDO PLC AND SETTED THE TYPE MODBUS AND ADDRESS AS MASTER. 2-SIMILARLY I DRAGED AND DROPPED MAGELIS HMI AND MADE ITS SETTINGS AS MODBUS AND ADDRESS 1 3- I JOINED THE MIN DIN CONNECTOR OF PLC WITH THE HMI,SO ON WORKSPACE IT SHOWED ME"MY NETWORK 1 ,19200" ,PARITY=EVEN,STOP=1,DATA BITS=8 4-IN PROGRAMMING OF PLC I DIRECTLY ENERGIZED %M0 --------------------------------(%M0) 5- I DOWNLOADED THIS PROGRAM ON PLC. HMI:: 1-OPEN VIJEO DESIGNER CREATED A PROJECT WITH NETWORK AS MODBUS RTU AND SLAVE EQUIPMENT "1" AS HMI ADDRESS IN ABOVE PLC SETTINGS IS MADE ONE(CHECK STEP 2),XBTG MODEL=XBTG2110, 2-SETTINGS ARE ALSO LIKE THEIR IN PLC BAUD RATE 19200,PARITY=EVEN,STOP=1,DATA BITS=8,COM PORT=COM2 3-CREATED A VARIABLE WITH TYPE=DISCREAT, DEVICE ADDRESS %M0,SOURCE=EXTERNAL 4-I M JUST CREATED A CIRCLE AND IN ITS VISIBLE TAB I CHECK BLINKING ANIMATION AND AND SELECTED THE VARIBALE %M0 WHICH I CREATED ABOVE CONCLUSION: I HAVE DIRECTLY ENERGIZED %M0 FROM PLC AND ALSO CREATED A VARIABLE %M0 IN HMI AND TAGGED WITH THE BLINKING CIRCLE AND SELECT COM 2 IN HMI.BECAUSE COM2 IN HMI IS CONNECTING HMI ITSELF AND PLC THROUGH CABLE XBTZ9780 AS I DESCRIBED IN HARWARE SECTION.NOW WHEN I DOWNLOAD THE PROGRAM IN HMI,THERE IS A CIRCLE BUT ITS NOT BLINKING,AND AFTER SOME SECONDS IT SHOWS TIME OUT NO RESPONSE FROM PLC. NOW BROTHERS HELP ME OUT WHY THIS IS SO.WHY %M0 IS NOT LINKED
  9. thanks a lot man you proved for me very helpful.i will check these settings then i will inform you about the result.well thanks again
  10. HI FRIENDS! I HAVE XBTG2110 HMI AND I WANT THE VIJEO DEISGNER 4.5 OR LATER.UNFORTUNATELY THIS SOFTWARE IS NOT AVAILABLE AT SCHNEIDER ELECTRIC'S SITE.SO IF YOU BROTHERS HAVE ANY DOWNLOAD LINK FOR THIS SOFTWARE I SHALL BE THANKFUL TO THEM
  11. SIEMENS LOGO PLC MASTER PASSWORD

    I HAVE A LOGO PLC WHICH I PASSWORD PROTECTED I WANT TO GET THE LADDER PROGRAM FROM ITS MEMORY.BECAUSE OF THIS I CANNOT TRANSER THE LADDER PROGRAM TO MY PC.SO WHAT TO DO NOW .
  12. HI FRIENDS! I AM NEW IN THIS FORUM AND THIS IS MY FIRST POST I HOPE RESPONSE WILL BE VERY HELP FUL.ACTUALLY I GOT A TWIDO PLC TWDMA 20DRT, AN EXTENSION MODULE WITH IT TWDNOZ485T AND A VFD ALTIVAR 71.I WANT TO COMMUNICATE THIS VFD WITH TWIDO THROUGH MODBUS.IN TWDNOZ485T THERE ARE THREE SCREW TERMINALS WRITTEN AS (A+ B- SG).I AM CONNECTING THREE WIRES FROM THESE TERMINALS AND CONNECTING TO ALTIVAR 71 THROUGH RJ45 WITH ALTIVAR PINS 4(A+),5(B-) AND 8(OV). HOPE IM DOING CORRECT HARDWARE SETTINGS. NOW ON THE SOFTWARE SIDE I AM USING TWIDO SOFT AND DOING THE FOLLOWING SETTINGS: 1-OPENED TWIDOSOFT 2-CLICKED ON NEW FILE AND FUNCTIONAL LEVEL MANAGEMENT AUTOMATIC AND HIGHEST POSSIBLE THEN CLICKED OK 3-CHANGED THE BASE CONTROLLER FROM TWDLMDA40DTK TO TWDLMDA20DRT 4-RIGHT CLICKED ON HARDWARE---->ADD OPTION------->TWDNOZ485T 5- NOW I HAVE TWO HARDWARE PORTS: PORT1=REMOTE LINK,,,,AND PORT2=MODBUS ADDRESS 1 6-NOW IM GOING TO CLICK MACROS---->RIGHT CLICK COMM---->EDIT---->CHECK CONFIGURE--->INSTANCE=0--->NETWORK=MODBUS PORT2,ADDRESS=2(I HAVE CONFIGURED MY ALTIVAR TO ADDRESS 2)------>CLICK FUNCTIONS AND ASSIGNED ADDRESSES. 7-WRITTEN A SIMPLE PROGRAM TO WRITE A SINGAL REGISTER 8502(FREQ SETPOINT=50HZ) THIS IS ALL ABOUT TWIDOSOFT IN ALTIVAR 71 IM CONFIGURED COMMAND REFERENCE AS CH1 REF MODBUS NETWORK AND IN ALTIVAR COMMUNICATIONS I HAVE CONFIGURED ADDRESS=2(ALSO DICUSSED ABOVE).ONE THING I AM NOT SURE THAT IN COMMAND WINDOW OF GRPAHIC TERMINAL WHEN I CHOOSE MODBUS THEN THERE ARE TWO OPTIONS.ONE IS I/O PROFILE,SEPARATE AND NOT SEPARATE.THIS THING I COULDN'T UNDERSTAND MAY BE THERE IS A LOGIC BEHIND THIS.