lostcontrol
MrPLC Member-
Content count
521 -
Joined
-
Last visited
Content Type
Profiles
Forums
Downloads
Calendar
Everything posted by lostcontrol
-
Hi I am testing the NB as a modbus master with mixed results. It seems I am able to write to the salve device, but not read correctly. I switched to just using multiway, & all appears correct when monitoring the send/recv strings, but the value on the NB does not update & a comm error is displayed. I am pretty sure I have the wiring correct, using 485 from pins 6&8 through a 485/232 converter to multiway. Any suggestions on where I might be going wrong?
-
Are all the FB's always enabled? Do they have any other conditions pertaining to the reset? Assuming they all in a cyclic task?
-
Have you checked what the peripheral servicing is set to? This could be having an affect, but 3sec seems way too slow. How are you monitoring? I normally always setup a register that monitors the PLC Clock second, this should always be updating 1 increment at a time, if not then there is problems. Have you tried testing with a smaller tag count?
-
Without the FB?
-
CJ2M connected by ethernet to Yaskawa A1000 Inverters
lostcontrol replied to Yurigas75's topic in Omron
The manual is always a good place to start. Most VSD's I hav used on E/IP have an area where parameters are exchanged with the master. This area had In/Out setup that you can plug the parameters that you want to exchange with the master. Does the yaskawa have this? Do you have a link to the manual? -
Does the NJ also do structures? And, do we assume that it automatically assigns the tags/structure to memory like Rockwell does?
-
Not quite, the output side of the rung is still processed. I think this is a common mis-understanding of using the Always Off contact. Yes, the scanning of the inputs after the always off are no longer scanned, but the output side must be. How else does a standard output coil switch off?
-
You will most likely need a routing table in the PLC as well
-
Use a loop to advance through each index?
-
You should be able to make the control word dynamic I would do a loop, & write the carriage return after x writes.
-
Magelis Download over VPN
lostcontrol replied to lostcontrol's topic in Modicon / Telemecanique / Schneider Electric
Maybe ignore this, it came up quite easy in the end. I will check with IT to see if this port is open. http://www.global-download.schneider-electric.com/85257563005C5B79/all/706555C0D7F4E969C12579040029FAA5?OpenDocument&L=EN&p=1054&idxUrl=mainRepository\index.nsf&XID=&XHOST=http://logi5.xiti.com/&HOSTIP=http://www.global-download.schneider-electric.com/&OTrSer=http://www.download.schneider-electric.com/& -
Magelis Download over VPN
lostcontrol posted a topic in Modicon / Telemecanique / Schneider Electric
Hi, I am connected to a remote site over VPN. I can ping all of the Magelis terminals on site, so they have the correct gateway/mask etc. But, when I try to download target, it cannot be reached. I have no idea why, so am speculating. Could it be the port that Vijeo Designer uses? Does anyone know what that is? Or, is there a download utility that will allow me to download locally? I have a terminal on site that I can do this with the Rockwell ME transfer utility. On that note, I have been able to download to the PV+'s on site before, but started doing it locally once we got a terminal there, as over the VPN it took too long. -
Using ModbusRTU Easy Master Function to control Inverter 3G3JX?
lostcontrol replied to Linhvct's topic in Omron
Is your PLC Ethernet then? -
Using ModbusRTU Easy Master Function to control Inverter 3G3JX?
lostcontrol replied to Linhvct's topic in Omron
How is your NS connected to the PLC? I doubt you can simulate the CX if it is serial -
Editing function blocks in Logix5000
lostcontrol replied to Automation Spec's topic in Allen Bradley / Rockwell Automation
Try the BOR -
This is unfortunate, but you only have yourself to blame.
-
You could probably even use the in-built PLC-PLC links, think that will work between 2x PLC serial ports...
-
What Interrupt interval were you hoping to achieve? Looking at your .cxp files, you have 10mS as your setup, with a value of 500 in your MSKS instruction. This will result in a interrupt of 5sec, does this need to be interrupt driven? Also, there looks like a lot of code in the Int 02 task, too much IMO. Can you not move some of it to be cyclic? Are you trying this on actual hardware? In projects I have recently done with a CJ2, I have MSKS 14 &10 with a 1ms Interrupt Interval set, which = 10mS. MSKS 14 = Reset/Start, but looks like it is only valid for CJ CPU's, I am trying to find the reference for the CS... Apart from all that, providing you have transferred the Code & settings, then cycled power to the CPU, this should work. If not, I would be starting with a blank program with just the MSKS & Int 02 tasks. For testing, I often put a un-conditional ++ instruction in the Int 02 task so that I can see the value incrementing at the required interval.
-
Please attached the files using the Forum functions, I cannot read what the links were to that site, nor fancy downloading from something like that sorry
-
Scheduled interrupts are a hardware feature. I very much doubt they work in Simulation mode, you need an actual PLC. If you are using an actual PLC, then post your .cxp file.
-
Multiple Omron PLC's - need to change TCP port
lostcontrol replied to Marcusk's topic in CX-Programmer
Sorry for the delay, but attached is 2x Pic's of the Ethernet config that we used. You can see in ETN 1.PNG that FINS/UDP was 9601, this was used for the SCADA ETN 2.PNG shows the FINS/TCP connection table, from memory this was done as some of the other PLC's were on different subnets. The standard FINS/TCP port of 9600 was still used though. Hope this helps -
Multiple Omron PLC's - need to change TCP port
lostcontrol replied to Marcusk's topic in CX-Programmer
Does TopServer use UDP or TCP? If it is anything like Kepware, I think it uses UDP IIRC, I will need to check tho. You only need to change either the UDP or TCP to make this work. We have had the same issue with a site that had Kepware on multiple ports & PLC communicating. I am not in office so cannot check, but will in next day or 2. -
Not that I know of, the only way that the NS can be restarted is via the Reset button on the back, or by cycling the power. I don't even think accessing the system menu & returning again classifies as a restart... 2 Questions: 1. Why do you want to do a restart..? 2. If you have to do a restart, why?
-
Still does not explain why it did not work on your desk CPU... This would be a valuable answer to find.
-
You must have an I/O server licence? InTouch has DASOMFINSEnet, this will communicate with your CJ2 very easily.