ex_ilustre

MrPLC Member
  • Content count

    21
  • Joined

  • Last visited

Community Reputation

0 Neutral

About ex_ilustre

  • Rank
    Sparky

Profile Information

  • Country Philippines
  1. Wireless Devicenet - just asking

    I've figured it out. These are my settings: CJ1W-DRM21: Unit #: 00 Node Add: 00 WD30-ME01: NNODE:01 WNODE:02 WCH:03 WD30-SE01: NNODE:02 WNODE:02 WCH:03 Thank you PMCR and TK_STUART for the tip that I should start with the slave side..and follow section 2-4. It worked even without purchasing the connector...just belden wires with small ferrules that fits through the pins. Thank you guys. More power!!!
  2. Wireless Devicenet - just asking

    I followed the steps in section 2-4(Devicenet Slave Entry)..but in the last step..when I set the Mode Select Switch to "RUN".,the NS did not lit Green as expected. MS is Red and flashing and the Error Code is F3. What does this means? What the manual says about error code F3 is "check the switch setting and reset correctly" . Which Switch? What do I do?
  3. Wireless Devicenet - just asking

    Hello, I have a devicenet master and a wireless devicenet master(WD30-ME01). I have a slight prob...unfortunately the CONNECTOR for connecting wireless devicenet master to the devicenet master(connected to the PLC) is not included in the box upon purchasing. Is there an alternative way to replace the connector..or does it have a wiring configuration? Thank you.
  4. Is this possible?

    hello, thank you so much for your help. I figured it out. Actually, what I wanted was to used any status of module LED..ie..SF, BATF, STOP, RUN..BUSF..etc. I already configured BATF. I used OB81, Move SSL ID(W#16#22) to MW, compare as an integer and turned ON an output address. Whenever I remove the Battery of S7-300, OB81 is called and turned ON an indicator lamp. It's enough for my project that I've used one status of module LED. I also tried to use the other Module LED's like the BUSF of profibus expansion(Im using CPU 315-2DP), but have no luck of triggering any OB's yet. Is it possible to use another OB to trigger for Bus fault(BUSF)? How do we deal with the reading of this fault?
  5. Is this possible?

    oh..thank you so much for that information. Is it possible to use the status of the Stop LED, even if the PLC is in the Stop mode? Because I want to turn ON a Lamp or an indicator like LED outside a panel. The PLC is inside the panel..so when the PLC turns to Stop mode due to some errors, we don't have to open the Panel to see the STOP indicator of the PLC is lit. thank you.
  6. Is this possible?

    Hey there, Is it possible to turn on an indicator(LED) in siemens S7-300 using the SF error? I mean, when the SF error indicator lit(RED), this signal may also be used to turn on an indicator outside the panel that and error occurs in the PLC inside the panel. Of course, we will also consider that when SF error is lit, the CPU is in the STOP mode. This means that we cannot use the I/O's of the PLC. If this is possible, give me example program please.
  7. SFC51 - HOW?

    The link you gave me sends me to a Product list and Order Number of Siemens product. I get the idea that in OB81, the status information is held in the TEMP area...but don't know how to read it. likewise in RET_VAL of SFC51...don't know how to read the data for usage. That's my problem. Can you please just send me an example program (or picture of the program) using OB81 or SFC51 to detect Battery Fault(BATF). thank you.
  8. SFC51 - HOW?

    hello, I don't have problem with manuals. I just don't know how to use the RET_VAL of the SFC. About using OB81, how do I use the OB81_FLT_ID? Can you send me a program or bitmap using OB81 to detect batf? Thank you.
  9. SFC51 - HOW?

    hellow, Thank you for the quick reply jylilaht and GixRamones. Yes, I do have SFC51 on my S7 manager and I've already tried F1 help but can't really understand it all. I'ts supposed to be 19 and not 119..sori about that. I want to use the status of Module LED's. Its 19 I guess. I'm using CPU 315-2DP(6ES7 315-2AF02-0AB0). I want to use the Status of Module LED's specifically the BAF(Batt fault) thats why my index is W#16#0008.... but I dont know how to used the RET_VAL to turn a Memory address(M79) or an alarm. I also don't know what to put in BUSY, SZL_HEADER and DR. Does the SZL_ID different for every CPU type? I think I will need your example..because I will also use profibus..ET200M. Your reply is really helpful. Problem Summary: I want to use BATF,Profibus error..and all other possible basic hardware error.. using SFC51 to trigger an alarm. Example: 1.)When the battery is shorted or removed, BATF will cause an alarm to signify Batt error is occurring. 2.)When the profibus cable is accidentally cut or removed,.an alarm sound signifying there is error due to profibus cable. How do we deal with this.?
  10. SFC51 - HOW?

    hello, Can somebody helo me with SFC51? I need to know what parameters are needed at the RET_VAL, BUSY, SZL_HEADER and DR(see attached file). I've seen the simatic help but can't understand,havent used to SFC's yet. What I want is to use the BATF of S7-300 to trigger a Memory address(M79) when there is a battery failure. You may send me bitmap/pic of the program similar to the attached file if you can. Thank you so much for your time. I_dont_know_this.bmp
  11. A1SCPU Manual

    I am using GX developer.
  12. A1SCPU Manual

    Hello, Thank you so much for your help. But I am looking for the Programming manual. Can you please send me a link on the programming manual of A1SCPU..
  13. A1SCPU Manual

    hello, There is no manual of A1SCPU in the download section of this site, right? What I find was A1N manual and not A1S. I tried to find in the mitsubishi site here in our country, but can't find one. I need your help. Please send me a link for Mitsubishi A1SCPU PROGRAMMING manual... Ty
  14. Good day! I want to convert 4 special addresses of A1SCPU of Mitsubishi to siemens Step7 program. These addresses are M9000(fuse blown), M9005(AC down detection), M9006(battery low) and M9008(self diagnosis error). I just don't know what OB's to use. Should I use OB81 and OB82? How do I configure these OB's? Need help... Any help you'll give will be appreciated. Thnx.
  15. Good day, Please help me on how to convert special addresses M9000,M9005,M9006 and M9008 of Mitsubishi A1SCPU to siemens step7 program. I dont know what OB's I need to use and I don't know how to use yet. Any information you can give would be appreciated. Thank you guys.