Mark-
MrPLC Member-
Content count
301 -
Joined
-
Last visited
Posts posted by Mark-
-
-
Do you have a communication protocol specification for the device?
-
From: FX3U-ENET-ADP User's Manual
- Up to 4 connections can be established and used at the same time in the Ethernet adapter.
-
1 hour ago, Goran Vuckovic said:As I stated before, I never had experience with FFP...
Right, I thought you might have created some since your post. Check you PM, I sent a small program.
-
On 11/21/2022 at 4:09 PM, Goran Vuckovic said:Just by looking at it, it seams to that simple bit(s) shifting...
Interesting. What about the byte order?
The next day. Years ago I wrote some routines to covert to/from FFP - 754. I went and looked at the code and while it has some bit shifting it is not only shifting. For example the exponent is biased differently. If you have some working code that converts both directions, is only shifting and maybe an and/or or two, I would really like to see and test the code.
-
2 hours ago, Goran Vuckovic said:...but I really do believe that there ways to copy this registers in memory and convert them bit by bit.
IIRC, the PLC provides routines to convert from/to SAIA native Motorola FFP and IEEE 754.
-
Hello,
Or perhaps you could use a program, like PeakHMI, that can access the SAIA PLC using native SAIA protocol.
FYI, SAIA uses the "Motorola Fast Floating Point", FFP for floats.
-
Very good.
I suspect the port number was OK, you can test it. Setting up the send and receive fixed buffer.
-
Using PeakHMI or your code?
-
-
Zip up the GXWorks project and post it here or PM me
-
Hello,
There is configuration that is required.
See my first response in this thread: https://forums.mrplc.com/index.php?/topic/41731-fx3ge-communication-with-kepserverex-via-udp-protocol/#comment-190141 It might help.
-
On 12/9/2020 at 5:56 AM, Mark Short said:FWIW my experience with the Large Forward Open service and Allen Bradley devices is that the Logix range will only support a connection size of about 4000 bytes...
I had the same results, 4003 bytes.
-
2 hours ago, pturmel said:What software produced that log? The expected boundaries for EtherNet/IP are not obvious. Please use wireshark instead. It will decode much of this for you.
His original post had MODBUS and the point about using Wireshark is 100% spot on.
-
Hi,
PeakHMI could work for you.
-
1 hour ago, tingxing said:I read in a manual (W227E12_FINS_Commands_Reference_Manual.pdf) that there seems to be a command capable of doing such task.
I read the manual portion (MULTIPLE MEMORY AREA READ) and yes that does what you want if your PLC supports "C" series commands. Nice find.
-
You could convert to string and process each character to a number.
Or you could divide by 10, multiple the remainder by 10.
Then subtract the remainder from the divide result and repeat the above line until a single digit remains.
1 person likes this -
33 minutes ago, NotaMaster said:ooh i see, but what do you mean with "finger pointing"?
In this instance, "Finger pointing" is when X points at Y and says it is not our problem it is Y's problem and Y points at X and says it is X's problem and you are in the middle, possibly with no assistance from either.
Finger-pointing: a situation in which someone is blamed for something that goes wrong
-
3 hours ago, vikrantragit05 said:Thanks for the support. The verification was successful with the tool [PeakHMI] mentioned above.
Still I am unable to connect KEPServer to PLC with same config. If there's anything you have tried, please so share.
Of course I would say "Switch to PeakHMI", it has OPC DA server included. As to Kepware, I have only looked at the trail versions and each time it worked as expected. I have not trialed Kepware with FX3.
-
You can download the trial version of PeakHMI and try the FX3 UDP port for verification.
I do recall configuring the controller for UDP was interesting.
Something like this:
-
3 hours ago, Tirello said:Hi friend! Please,
I can't read your message.
You can write in English?
Thanks!
Using online translation he wrote:
are you having problems with the extended module of PLC fx3u 32 MR-ES.?
Specifically, what. X0-X7 sequence. X10-X17. The X20-X27, Y0-Y27 is right?
Me:
Is your 485 terminated properly? I ask because you have not provided much information on the problem.
Error codes?
How is it wired?
Tried another expansion module?
Does the 485 bus work with any device?
etc.
-
And if English is not a language for you, you can use a free online translator. Create the message in Portuguese, use a translator, and paste the result here. I used Bing's translator for this message.
E se o inglês não é um idioma para você, você pode usar um tradutor online gratuito. Crie a mensagem em português, use um tradutor e cole o resultado aqui. Usei o tradutor do Bing para esta mensagem.
1 person likes this -
Hello,
1 hour ago, franckcl said:Who could help me ? What is wrong ?
Download the trial/demo version of PeakHMI and use it for generating request to the PLC.
Use WireShark to capture and analyze the request/response packets.
-
Did you enable the "Show Plus Sign" checkbox/property?
-
17 hours ago, GreenMan said:Hi
That is correct.
Thanks
Melservo J5 by HMI control without PLC
in Mitsubishi
Posted
I do not know. But, if you find one or more send it to me and I will read it.